What gauge wire?

I am at the wiring stage of my redo. Wondering what size wire to use for my coach battery.
The battery was there but wires were all gone.
I've googled this and get a variety of answers.
Thanks!
Dingo Girl is online now   Reply With Quote
Old 12-21-2015, 11:07 AM   #2
Rivet Master
 
1955 22' Safari
Laredo , Texas
Join Date: Nov 2013
Posts: 1,342
I sized mine based on max current output by my converter (45 amps), using the attached chart:
http://assets.bluesea.com/files/reso...on_chartlg.jpg
55AS is offline   Reply With Quote
Old 12-21-2015, 04:46 PM   #3
Rivet Master
 
Dingo Girl's Avatar
 
1967 17' Caravel
Oak Creek , Colorado
Join Date: Jul 2009
Posts: 1,560
Images: 3
Thank you! I have a 45 amp converter as well
Dingo Girl is online now   Reply With Quote
Old 12-21-2015, 05:35 PM   #4
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
What gauge wire?

Be sure that you use the 3% column for voltage drop as the wiring you described definitely is considered 'critical'.

Also, your 45 amp converter should be placed into the 50 amp column, not the 40 amp column.


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-22-2015, 03:51 AM   #5
Rivet Master
 
Dingo Girl's Avatar
 
1967 17' Caravel
Oak Creek , Colorado
Join Date: Jul 2009
Posts: 1,560
Images: 3
Thank you Lewster!
I will be working on it over my short Christmas break.
Dingo Girl is online now   Reply With Quote
Old 12-22-2015, 05:47 AM   #6
Rivet Master
 
1955 22' Safari
Laredo , Texas
Join Date: Nov 2013
Posts: 1,342
So the short answer is Use 6 gauge wire between the converter and battery.
55AS is offline   Reply With Quote
Old 12-22-2015, 06:21 AM   #7
Zil
4 Rivet Member
 
Curtis Wright
Currently Looking...
Eyren Haven , South Jersey
Join Date: Apr 2014
Posts: 326
The short answer is to size the wire to the maximum load you will place on the battery, not the converter.
Zil is offline   Reply With Quote
Old 12-22-2015, 12:29 PM   #8
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
What gauge wire?

I wasn't referring to the battery DC load, but the cable running from the converter to the DC fuse block and corresponding negative cable.

Cable run length, load and bundling should always be considered when planning for a new cable. Also, the chart above is for single conductors. The ampacity changes as cables are run in bundles.


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-22-2015, 03:37 PM   #9
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Quote:
Originally Posted by lewster View Post
I wasn't referring to the battery DC load, but the cable running from the converter to the DC fuse block and corresponding negative cable.

Cable run length, load and bundling should always be considered when planning for a new cable. Also, the chart above is for single conductors. The ampacity changes as cables are run in bundles.


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357

By single run, you mean 1 b+ and 1 b- ? Bundled you mean multiple pos and neg in same proximity in the run?


Sent from my iPad using Airstream Forums
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 12-22-2015, 06:38 PM   #10
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by dznf0g View Post
By single run, you mean 1 b+ and 1 b- ? Bundled you mean multiple pos and neg in same proximity in the run?


Sent from my iPad using Airstream Forums
Since the table referenced ABYC standards, and specifically E-11 (which I am intimately familiar with having just completed my ABYC Master Marine Electrician certification course), the definition of a single conductor is one wire not bundled, sheathed or in conduit.

I just pulled up my E-11 wiring tables and the chart above seems to be a combination of the 2 pictorial (in an easier viewing form) of the E-11 charts for conductor length of a wire run of the 2 types of circuits (critical and non-critical) for the ungrounded (current carrying) conductors. For RV use, I would stick to using the critical designation (3% voltage drop) for all wiring.

NOTE** ABYC CONSIDERS THE LENGTH OF A CONDUCTOR TO BE FROM THE SOURCE OF CURRENT TO THE LOAD DEVICE AND BACK TO THE SOURCE!!

This means that if your converter is 10 feet from your battery, the circuit length is effectively 20 feet. This WILL change wire gauges used in many of the circuits at 3% voltage drop and should be carefully calculated.

The bundling, sheathing or use of conduit will further derate the ampacity of the wire gauges, and specifications for those are contained in different tables. There are 2 tables that apply to DC circuits; one that considers a single conductor that is not bundled, sheathed or in conduit and up to 3 current carrying conductors that ARE either bundled, sheathed or in conduit. ABYC does not consider derating of ampacity over 3 bundled DC conductors, but does have further derating specifications for bundles of AC conductors up to 25 or more bundled current carrying conductors.

I know what the next question is……………What is considered a current carrying conductor? In a DC circuit, BOTH positive AND negative are current carrying. In an AC circuit, only the hot (ungrounded), and neutral (grounding) conductors are considered current carrying. The actual ground conductor (grounded) is NOT considered current carrying, as in a properly wired and normal functioning AC circuit, the ground (grounding) conductor should have no voltage on it. The terminology in parenthesis is from ABYC, as they do not typically use the terms 'hot, neutral and ground' to describe AC circuits.

Now that you are probably totally confused, use the chart above from Blue Sea Systems, but remember to use the TOTAL length of your circuit (from the current source AND BACK) in your calculations. Since most RVs don't bundle their cables (Airstream actually does with the DC wires that come from the fuse block), you really don't have to consider this type of derating of the cable's ampacity.

I have noticed though, that Airstream now fuses 12AWG DC cables from the fuse block at 15 amps, when one would normally fuse them at 20 amps (as they have done in the past). This is a result of derating the ampacity due to bundling and something that I did not mention, the temperature rating of the wire's insulation.

I use 105ºC rated cable, which is standard marine cable. Most RVs use cabling rated at 60ºC, which further derates the ampacity of the cables used.

Sorry to go on for so long, but there is MUCH MORE to figuring a wire's ampacity than just the AWG of the cable.

I'M DONE NOW!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-22-2015, 10:20 PM   #11
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 9,180
Law, you done good! Very clear explanation.


Sent from my pocket Internet using Airstream Forums
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 12-23-2015, 03:40 AM   #12
Rivet Master
 
Dingo Girl's Avatar
 
1967 17' Caravel
Oak Creek , Colorado
Join Date: Jul 2009
Posts: 1,560
Images: 3
Lewster you have made this much less daunting than it was.
Google searches did nothing but confuse and contradict.
I feel much better about my project now.
Happy Holidays to you!
Dingo Girl is online now   Reply With Quote
Old 12-23-2015, 06:13 AM   #13
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Thanks Gang!

Happy Holidays to all!!!!!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-23-2015, 09:36 AM   #14
Zil
4 Rivet Member
 
Curtis Wright
Currently Looking...
Eyren Haven , South Jersey
Join Date: Apr 2014
Posts: 326
"Since the table referenced ABYC standards, and specifically E-11 (which I am intimately familiar with having just completed my ABYC Master Marine Electrician certification course), the definition of a single conductor is one wire not bundled, sheathed or in conduit."
Congratulations, Lewster
Zil is offline   Reply With Quote
Old 12-24-2015, 09:18 AM   #15
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Thanks!


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-29-2015, 04:14 AM   #16
Rivet Master
 
Dingo Girl's Avatar
 
1967 17' Caravel
Oak Creek , Colorado
Join Date: Jul 2009
Posts: 1,560
Images: 3
My plan to do start the wiring at Christmas was postponed due to a storm and power outage.
It did give me the opportunity to draw out all the circuits measure for wire and order most everything I will need.
If it all arrives for the New years break I can get started then.
Thanks again for steering me in the right direction.
Dingo Girl is online now   Reply With Quote
Old 07-25-2016, 10:19 AM   #17
Rivet Master
 
Dingo Girl's Avatar
 
1967 17' Caravel
Oak Creek , Colorado
Join Date: Jul 2009
Posts: 1,560
Images: 3
this is the panel I made for my 12v fuse panel.
It will be mounted to the floor near where the old Univolt was.
My walls are back in new wire in place now to hook it all up.
Attached Thumbnails
Click image for larger version

Name:	1469463496312.jpg
Views:	157
Size:	60.7 KB
ID:	267686  
Dingo Girl is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Best wire connector for 12 gauge stranded wire jcarnevale Lights - Interior & Exterior 6 04-14-2014 08:18 PM
What gauge wire do I need for my converter? 72Blazerod Electrical - Systems, Generators, Batteries & Solar 1 10-20-2006 08:13 PM
Proper gauge of wire? 65 overlander Electrical - Systems, Generators, Batteries & Solar 8 01-22-2006 10:20 PM
What size breaker for 8 gauge wire? guy99 Electrical - Systems, Generators, Batteries & Solar 7 11-20-2005 12:24 PM
Wire ,wire, oh wire can it be ? 69 Silverback Electrical - Systems, Generators, Batteries & Solar 8 05-15-2003 11:09 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:04 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.