Can Generators Run Both AC's While Boondocking?
Hello members
Just traded in my 2015 FC 25 twin for 2017 FC 28 with 2 ac. Quick
question, does anybody run both ac's at the same time using shore power? Or if boon docking, can you run them with 2 2200 watt generator s?
Thanks
|
|
|
02-05-2017, 07:30 PM
|
#2
|
Rivet Master
Commercial Member
Vintage Kin Owner
Naples
, Florida
Join Date: Dec 2005
Posts: 7,508
|
Quote:
Originally Posted by Flht2k
Hello members
Just traded in my 2015 FC 25 twin for 2017 FC 28 with 2 ac. Quick
question, does anybody run both ac's at the same time using shore power? Or if boon docking, can you run them with 2 2200 watt generator s?
Thanks
|
RV air conditioners typically operate at 14-16 running amps. A pair of Honda 2000s would just be passable for operation of 2 A/Cs, but they will not have the overhead capacity to provide for the 50+ amp transient starting load required by the compressor of each unit.
You would need a pair of 3000s for running 2 roof A/C units, or a robust lithium bank and 3000 watt hybrid inverter with a pair of 2000s. I would think that the 3000s would be significantly less expensive that the lithium system.
And yes, your 50 amp shore connection will enable you to operate both A/Cs at the same time from a proper 50 amp shore connection. You could even run a third if you had one.....just like the large diesel motor homes do every day here in FL
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
|
|
|
02-05-2017, 07:38 PM
|
#3
|
Rivet Master
2019 30' Classic
Canfield
, Ohio
Join Date: Jul 2015
Posts: 2,559
|
Quote:
Originally Posted by lewster
RV air conditioners typically operate at 14-16 running amps. A pair of Honda 2000s would just be passable for operation of 2 A/Cs, but they will not have the overhead capacity to provide for the 50+ amp transient starting load required by the compressor of each unit.
You would need a pair of 3000s for running 2 roof A/C units, or a robust lithium bank and 3000 watt hybrid inverter with a pair of 2000s. I would think that the 3000s would be significantly less expensive that the lithium system.
And yes, your 50 amp shore connection will enable you to operate both A/Cs at the same time from a proper 50 amp shore connection. You could even run a third if you had one.....just like the large diesel motor homes do every day here in FL
|
Check out Micro- air's easy-start. One 2000w gen per AC. Lowers initial demand. Designed originally for the marine industry.
__________________
"At some point, throwing money at the problem *is* the right answer", Uncle Bob
x\x/x\x/x\x/x\x/x\101970\x/x\x/x\x/x\x/x\x/x\/x\x/x\x/x
Tom & Doty
2019 Airstream Classic 30 Twin
|
|
|
02-05-2017, 07:43 PM
|
#4
|
Rivet Master
2019 30' Classic
Canfield
, Ohio
Join Date: Jul 2015
Posts: 2,559
|
Check out the thread " should I keep my 2x Honda generators "
__________________
"At some point, throwing money at the problem *is* the right answer", Uncle Bob
x\x/x\x/x\x/x\x/x\101970\x/x\x/x\x/x\x/x\x/x\/x\x/x\x/x
Tom & Doty
2019 Airstream Classic 30 Twin
|
|
|
02-05-2017, 07:48 PM
|
#5
|
4 Rivet Member
2016 30' International
Florence
, Alabama
Join Date: Oct 2016
Posts: 493
|
Quote:
Originally Posted by Flht2k
Hello members
Just traded in my 2015 FC 25 twin for 2017 FC 28 with 2 ac. Quick
question, does anybody run both ac's at the same time using shore power? Or if boon docking, can you run them with 2 2200 watt generator s?
Thanks
|
Shore power - you'll need a 50a hookup or it's dicey. The manual says no, but it could be done as long as both weren't starting at the same time and other loads were minimal (think fridge and water heater on propane).
If I'm planning a campground stay I look for 50 a hookups because I like it cool.
|
|
|
02-05-2017, 08:04 PM
|
#6
|
3 Rivet Member
2018 33' Classic
Newport
, Pennsylvania
Join Date: Nov 2014
Posts: 239
|
I use a Honda 7000 I generator and run both air conditioner
|
|
|
02-05-2017, 08:28 PM
|
#7
|
Rivet Master
South East
, Michigan
Join Date: Apr 2016
Posts: 552
|
x2 on the Micro-Air Easy Start. One big downside - installing will likely void your AC warranty.
__________________
Al
2017 29' SOB, 2022 Platinum F-150 SCrew, ProPride
|
|
|
02-05-2017, 08:33 PM
|
#8
|
Rivet Master
2019 30' Classic
Canfield
, Ohio
Join Date: Jul 2015
Posts: 2,559
|
Talk with Matteo at micro air. He will go to bat for you with dometic. I believe dometic uses a similar system on a commercial unit they make.
__________________
"At some point, throwing money at the problem *is* the right answer", Uncle Bob
x\x/x\x/x\x/x\x/x\101970\x/x\x/x\x/x\x/x\x/x\/x\x/x\x/x
Tom & Doty
2019 Airstream Classic 30 Twin
|
|
|
02-06-2017, 04:03 AM
|
#9
|
3 Rivet Member
2018 33' Classic
Newport
, Pennsylvania
Join Date: Nov 2014
Posts: 239
|
Here we go again, let's cheat the system micro air instead of a correct sized generator???? "He will go to bat for you " means what after you ac's are damaged possibly your holding the bag. My thought would be to take Lewsters advice and skip trying to beat the system
Earl
|
|
|
02-06-2017, 07:46 AM
|
#10
|
4 Rivet Member
2016 30' International
Florence
, Alabama
Join Date: Oct 2016
Posts: 493
|
Quote:
Originally Posted by EarlM
Here we go again, let's cheat the system micro air instead of a correct sized generator???? "He will go to bat for you " means what after you ac's are damaged possibly your holding the bag. My thought would be to take Lewsters advice and skip trying to beat the system
Earl
|
Actually this is just thinking smarter rather than working harder. It's kind of ridiculous to have to size generators 50% bigger than you need just to handle the transient startup draw that lasts less than 1 sec. Here's a guy who's figured out a safe way (which by the way actually increases component life by easing the startup cycle from such an abrupt, jerky start) to reduce the transient requirements - and he's done such a good job that the manufacturers have taken notice and are even offering his solution as a factory option in some cases.
Having him willing to go to bat - and knowing his relationship with the manufacturers - gives this solution a lot more credibility that most hacks.
|
|
|
02-06-2017, 09:28 AM
|
#11
|
Full time Airstreamer
2014 30' FB FC Bunk
Anywhere
, USA Living.Somewhere.Yonder
Join Date: Jan 2014
Posts: 1,359
|
I'd ask weather your really need to run both air conditioners.
__________________
@living.somewhere.yonder | Instagram
|
|
|
02-06-2017, 11:22 AM
|
#12
|
4 Rivet Member
2017 28' International
Virginia Beach
, Virginia
Join Date: Jul 2016
Posts: 405
|
I have two a/c units on my 2017 28' Serenity and have run both on my Honda 2000s. They were not started together and I had both my refer and hot water on propane. However, once I proved that it could be done, I shut down one. Honestly, I did just fine with running one a/c unit off the generators. It kept my AS cool.
|
|
|
02-06-2017, 11:23 AM
|
#13
|
Rivet Master
2019 30' Classic
Canfield
, Ohio
Join Date: Jul 2015
Posts: 2,559
|
I'll be installing mine (one AC ) and documenting it here somewhere in the forum. Micro air is offering $50 off ($250) through the summer.
Joshjack is right. Dometic already has a startup capacitors in their unit. This is the way most manufacturers handle this issue. Problem is there is still a micro second burst that overpowers the generator causing it to shut down. Its hard on the AC and hard on the generator. If the Easystart eliminates most of the "punch" and slowly engages the generator, it has to be better for all devices concerned. The easystart also has a 6 second delay to allow a 2000i generator to get out of eco mode and get to full speed. Nice touch!
__________________
"At some point, throwing money at the problem *is* the right answer", Uncle Bob
x\x/x\x/x\x/x\x/x\101970\x/x\x/x\x/x\x/x\x/x\/x\x/x\x/x
Tom & Doty
2019 Airstream Classic 30 Twin
|
|
|
02-06-2017, 11:25 AM
|
#14
|
Journeyman
2016 25' International
Amherst
, Massachusetts
Join Date: Apr 2016
Posts: 956
|
Quote:
Originally Posted by joshjack
Actually this is just thinking smarter rather than working harder. It's kind of ridiculous to have to size generators 50% bigger than you need just to handle the transient startup draw that lasts less than 1 sec. Here's a guy who's figured out a safe way (which by the way actually increases component life by easing the startup cycle from such an abrupt, jerky start) to reduce the transient requirements - and he's done such a good job that the manufacturers have taken notice and are even offering his solution as a factory option in some cases.
Having him willing to go to bat - and knowing his relationship with the manufacturers - gives this solution a lot more credibility that most hacks.
|
Agree. Carrying twice the genny is costly and inefficient especially when most of us carry a genny solely for AC.
|
|
|
02-06-2017, 11:25 AM
|
#15
|
Rivet Master
2019 30' Classic
Canfield
, Ohio
Join Date: Jul 2015
Posts: 2,559
|
The Easystart also monitors voltage and will shut down for a 5 minute period if voltage were to drop. The delay also allows for the pressures to equalize before starting the AC again.
__________________
"At some point, throwing money at the problem *is* the right answer", Uncle Bob
x\x/x\x/x\x/x\x/x\101970\x/x\x/x\x/x\x/x\x/x\/x\x/x\x/x
Tom & Doty
2019 Airstream Classic 30 Twin
|
|
|
02-06-2017, 12:06 PM
|
#16
|
2 Rivet Member
2017 27' Flying Cloud
2017 30' Classic
Sulphur
, Oklahoma
Join Date: Sep 2016
Posts: 54
|
Quote:
Originally Posted by Flht2k
Hello members
Just traded in my 2015 FC 25 twin for 2017 FC 28 with 2 ac. Quick
question, does anybody run both ac's at the same time using shore power? Or if boon docking, can you run them with 2 2200 watt generator s?
Thanks
|
You can run two 3,000 watt Honda generators
but you must have a parallel.
Champion also makes a 3,000 watt gen. That are half the price.
Camping world sells them.
|
|
|
02-06-2017, 12:14 PM
|
#17
|
Rivet Master
2015 25' Flying Cloud
2016 30' Flying Cloud
Blenheim Ontario
, Ontario
Join Date: May 2015
Posts: 1,263
|
Quote:
Originally Posted by lewster
RV air conditioners typically operate at 14-16 running amps. A pair of Honda 2000s would just be passable for operation of 2 A/Cs, but they will not have the overhead capacity to provide for the 50+ amp transient starting load required by the compressor of each unit.
You would need a pair of 3000s for running 2 roof A/C units, or a robust lithium bank and 3000 watt hybrid inverter with a pair of 2000s. I would think that the 3000s would be significantly less expensive that the lithium system.
And yes, your 50 amp shore connection will enable you to operate both A/Cs at the same time from a proper 50 amp shore connection. You could even run a third if you had one.....just like the large diesel motor homes do every day here in FL
|
Wouldn't the two gennys have to be paralleled?
|
|
|
02-06-2017, 01:46 PM
|
#18
|
Rivet Master
2017 30' Classic
Anna Maria
, Florida
Join Date: Jul 2013
Posts: 1,645
|
Quote:
Originally Posted by thiel
Agree. Carrying twice the genny is costly and inefficient especially when most of us carry a genny solely for AC.
|
I have a Champion 3100 Watt Inverter generator we use to run the 2 ACs on our 30' International for two years now. I bring the AC units on line one at a time and normally set them at slightly different temperatures.
I have yet to overload the generator even using the microwave and other misc. appliances. The two AC units run just fine at the same time and generator purrs right along.
I consider lifting the 85 lbs unit in an out of the truck part of my work out routine. :-)
|
|
|
02-06-2017, 04:28 PM
|
#19
|
2 Rivet Member
2014 25' Flying Cloud
Mount Dora
, stevenwilliams
Join Date: Sep 2016
Posts: 42
|
We also use the EasyStart from Micro Air to run our A/C with a 2000 watt Yamaha. They should be standard so that everyone can use a lighter, quieter generator.
http://www.microair.net/main/products/product.php?id=20
|
|
|
02-06-2017, 05:18 PM
|
#20
|
Rivet Master
2000 25' Safari
Davidson County
, NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
|
Quote:
Originally Posted by lewster
>> snip>> You would need a pair of 3000s for running 2 roof A/C units << snip<<
|
I'm wondering how to hook up the 50 amp power cord to two Hondas so they would run two AC units. I did not know they could be paired in this manner.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
|
|
|
|
|