Adding Second 50AMP Power Inlet

I have a 2016 25FB with dual 15k BTU A/C's and 50AMP service. The 50 AMP power Inlet is to the rear of the trailer. I would like to add an additional power Inlet to the front of the trailer so it's more convenient when operating off of the generator. Is this possible?
Dannyfishes is offline   Reply With Quote
Old 05-13-2017, 08:11 AM   #2
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
Yes it can be done but you will want an isolation switch to select which umbilical cord you are using. This is to insure no voltage at the end of the unused cord. The switch for 50amps will not be cheap.

it would be a lot easier to just use an extension cord added to the umbilical to reach the front. I often have to use an extension to reach shore power.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 05-13-2017, 08:34 AM   #3
Rivet Master
 
AnnArborBob's Avatar
 
2014 27' FB Eddie Bauer
Chelsea , Michigan
Join Date: May 2010
Posts: 1,792
Images: 12
Done properly, I would guess that this would cost between one and two thousand dollars (including professional labor.) Your current 50 amp cord is probably plenty long to reach from the front of the trailer where you want to place your generator to the existing inlet, so what's the problem you are trying to solve?
__________________
Bob Martel
WBCCI# 5766
AnnArborBob is offline   Reply With Quote
Old 05-13-2017, 09:25 AM   #4
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by Dannyfishes View Post
I have a 2016 25FB with dual 15k BTU A/C's and 50AMP service. The 50 AMP power Inlet is to the rear of the trailer. I would like to add an additional power Inlet to the front of the trailer so it's more convenient when operating off of the generator. Is this possible?
If you would be happy without an automatic switch and you are a DIY person with basic electric wiring skills and tools, adding a power inlet can be done economically. You would need a manual throw switch, wiring, and a power inlet. Both power cords would feed the switch. The switch would feed the existing distribution center. The hardest part is finding a suitable location for the switch box and running the wires where they would be hidden.
Those switches can be fairly large and not pretty to look at. I think it would cost less than $500 in materials.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 05-13-2017, 09:46 AM   #5
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,653
Blog Entries: 1
That's why the extra 30 amp outlet on the new one AC Airstreams is genius.
If you just want to avoid dragging out the 50 amp power cord, I bought one if these. It's a 25' cord with a 50amp female and a 30 amp male, just to reach the truck bed.
Quote:
Voltec Industries 16-00588 30-Ampere to 50-Ampere RV Locking 10/3 STW Cord, 25-Feet
If you want to use the generator while driving, then you need the switch. I suspect AS doesn't offer that as a feature on the 50 amp service because the extra hardware for two 50 amp circuits is not profitable.
Mollysdad is offline   Reply With Quote
Old 05-13-2017, 01:44 PM   #6
Antiquepedaler
 
Antique Pedaler's Avatar
 
2010 25' FB Flying Cloud
Currently Looking...
Laramie , Wyoming
Join Date: Sep 2002
Posts: 831
Images: 11
Blog Entries: 1
Hmmm. My 2010 25 FB with 30 amp service came with power inlets both fore and aft.
__________________
Antique Pedaler
2021 Caravel 20 FB
Antique Pedaler is offline   Reply With Quote
Old 05-13-2017, 02:24 PM   #7
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,653
Blog Entries: 1
Quote:
Originally Posted by Antique Pedaler View Post
Hmmm. My 2010 25 FB with 30 amp service came with power inlets both fore and aft.
Yes, and one A/C unit.
Mollysdad is offline   Reply With Quote
Old 05-13-2017, 03:02 PM   #8
2 Rivet Member
 
1978 31' Sovereign
2016 25' International
Bryan , Texas
Join Date: Feb 2013
Posts: 20
I could add just a 30AMP if that would be easier. I'll just be using it to plug in the generator.
Dannyfishes is offline   Reply With Quote
Old 05-13-2017, 03:38 PM   #9
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,455
Images: 7
You will have to install a manual "Break Before Make" 50 amp rotary switch "or" a 50 amp automatic transfer switch plus wiring from the switch to each inlet.

To just run wire straight from one inlet to another is dangerous since once connected to power both inlets would be hot all the time. The above switches isolate the inlets so only one inlet can be hot at any one time.
__________________
Garry
garry is offline   Reply With Quote
Old 05-13-2017, 08:39 PM   #10
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by Dannyfishes View Post
I could add just a 30AMP if that would be easier. I'll just be using it to plug in the generator.
Having 30 amp in the front and 50 amp in the rear would be more difficult to do correctly, since the 50 amp is 240v and the 30 amp is 120v. You would have to add a switch of some sort and modify the distribution panel wiring. I think you would have to add a secondary distribution panel to do it correctly. (more new things to locate in your small space)

In your trailer's present configuration, one air conditioner is on each of the two 120v legs of the 240v circuit. With a 30 amp only you would not be able to run both AC's. If you re-arranged the circuits to put both AC units on the same 120v leg you would loose the ability to charge the battery and run the fridge on 120v. The use of these 4 items only would exceed the 30 amp capacity.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 05-13-2017, 09:22 PM   #11
2 Rivet Member
 
1990 25' Excella
St Lawrence , Pennsylvania
Join Date: Aug 2010
Posts: 38
Why could you not just buy a 50 amp receptacle that is not wired to anything.

The 50 amp cord is always plugged into this in the storage compartment.

When the 30 amp cord is plugged into the generator, the 50 amp cord will be energized but no harm since in plugged into the "dead" receptacle.
rjmaype is offline   Reply With Quote
Old 05-14-2017, 08:59 PM   #12
4 Rivet Member
 
2015 28' Flying Cloud
Newtown , Pennsylvania
Join Date: Jan 2015
Posts: 315
wow!!!
__________________
50 amp, Awning package
2015 Ram 2500 6.7 TD, Blue Ox 1000 lb.
400ah LiFePo4, 800 watts solar, 2x eu2000i Propane
PD9160 converter, Prosine 1800 inverter
2x Victron 100/30 Smart Solar, Victron Smart Shunt
AstroBruce is offline   Reply With Quote
Old 05-14-2017, 09:45 PM   #13
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,653
Blog Entries: 1
Quote:
Originally Posted by A W Warn View Post
Having 30 amp in the front and 50 amp in the rear would be more difficult to do correctly, since the 50 amp is 240v and the 30 amp is 120v.
Not really. In the RV a 50 amp inlet is two 50 amp 125v. lines. 30 amp is one 30 amp 125 v. line.
The problem is you need the 50 amp inlet to be available for shore power or generator power, so you can't just combine the two legs like in a 30-50 dogbone.
The danger of paralleling the two inlets is that if you're plugged into the rear one, the male terminals of the front one are hot! That's why you need a transfer switch.
Either/Or. If it was easy, AS would do it.
Mollysdad is offline   Reply With Quote
Old 05-14-2017, 09:50 PM   #14
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,653
Blog Entries: 1
Quote:
Originally Posted by rjmaype View Post
Why could you not just buy a 50 amp receptacle that is not wired to anything.

The 50 amp cord is always plugged into this in the storage compartment.

When the 30 amp cord is plugged into the generator, the 50 amp cord will be energized but no harm since in plugged into the "dead" receptacle.
Did I ever tell you about my idea for using the generator in the event of a power failure at home? Make a AC cord with a male plug on both ends. Plug one into the generator and the other into a wall outlet. Then any outlet on that buss is energized.
"Here hold my beer, watch this!"
Mollysdad is offline   Reply With Quote
Old 05-15-2017, 02:16 AM   #15
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
Too many people do this every year. Some of them forget to disconnect from utility service , putting line workers at risk. It will work and it is reasonable safe as long as you isolate the energized circuit and preferably open your main breakers.

Larry
lsbrodsky is offline   Reply With Quote
Old 05-15-2017, 10:52 PM   #16
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by Mollysdad View Post
Not really. In the RV a 50 amp inlet is two 50 amp 125v. lines. 30 amp is one 30 amp 125 v. line.
The problem is you need the 50 amp inlet to be available for shore power or generator power, so you can't just combine the two legs like in a 30-50 dogbone.
The danger of paralleling the two inlets is that if you're plugged into the rear one, the male terminals of the front one are hot! That's why you need a transfer switch.
Either/Or. If it was easy, AS would do it.
You must have missed the part in my post where I said "correctly", and described that. The concept is simple basic electrical stuff. The equipment is readily available off the shelf. Finding a place for the new extra equipment inside a trailer makes it more challenging.

Feeding from two different power sources is done safely every day. It requires a new secondary/auxiliary panel and a transfer switch. It is done exactly the same way on a trailer as it would be when using a 120v generator to power some 120v circuits in a house, where the primary power source is 240v.

ps:
I notice you said 125v and I said 120v. I've heard some people say 110v and others say 115v. Generally the utilities proved a range of power that varies depending on where one is and the utilities equipment. I think the allowable range is ~110 to ~125v AC. Where I live it is pretty steady around 120v.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 05-25-2017, 08:01 PM   #17
Rivet Master
 
gklott's Avatar
 
2004 30' Classic
Johnson City , Texas
Join Date: Jun 2003
Posts: 591
Images: 86
When upgrading our trailer from 120 VAC 30 amp to 240/120 VAC 50 amp, we installed an Eaton 14-space 240/120 VAC loadcenter, CH14B100BP.

For the switch from shore to generator, we use the manual Eaton CH8BFM loadcenter mechanical interlock cover. It's fully UL listed for switching between sources. Make sure that you use only a ETL, UL, CSA, or similarly "listed" device specific for this purpose.

There's a 50A, 2-pole OCPD (circuit breaker) when on shore, and there's a 30A, 2-pole OCPD when attached to our Honda EU6500 generator. Using either, we connect 240 VAC into the trailer.

Our shore-power 4-wire SmartPlug is street-side just forward of the front wheel, and the generator-power 4-wire SmartPlug is on the front, street side of center. Agree that most times, we could reach the side-mounted SmartPlug from the generator in the truck bed. I had the space to add the second plug up front, and so I did.

73/gus
__________________
Gus - KR4K : Mary - K5MCL
2004 30ft. Classic
2017 Infiniti QX80 Limited
ProPride 3P/Prodigy P3
gklott is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Converting 50amp power source to 30 amp trailer danandmimi On The Road... 19 09-29-2016 10:30 PM
What power supply to replace with on 50amp 2016 classic Clozzzer Electrical - Systems, Generators, Batteries & Solar 45 08-29-2016 11:56 PM
Furrion Stainless Steel 30A inlet and TV inlet Gsmblue Electrical - Systems, Generators, Batteries & Solar 4 07-27-2015 06:58 PM
Power Inlet 50amp markdoane Electrical - Systems, Generators, Batteries & Solar 4 10-14-2005 08:25 PM
Adding a second battery... drboyd Electrical - Systems, Generators, Batteries & Solar 3 07-28-2003 12:45 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 05:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.