Exclamation 2 inverters in 2 mos., both SMOKE!

Hi folks. Looking for ideas on what could be wrong with our inverter setup, or if this is normal behavior?

We have a brand new Victron Multiplus 3000 (120V) hybrid inverter/charger. The cooling fan kicks on after about a minute running the 1500W water kettle or any other appliance in that wattage ballpark, then we see/smell smoke.

The inverter is 3000W, so this load should be no problem. It's installed in a interior storage closet in the bedroom. The closet has a door and is approx. 15L x 15W x 30H in. The inverter is upright and mounted to the back wall with 5 in. or more of space around all surfaces except the back.

After seeing a lot of smoke coming from the closet (on the first day we used it! scary!!), we installed a smoke alarm in the closet. It now goes off every time we run a "heavier" load but there are never any warning lights on the inverter itself (i.e. overload, high temperature, etc.).

The smoke smells the same as the normal electrical smell when the inverter is running, only a lot stronger...no rubber smell. Our previous (also brand new) Victron 3000W inverter did the same thing, so we replaced it with this unit because our installer (an AM Solar certified tech) thought the last one was faulty. It also smoked on Day 1. Our electrical system is 30A btw.

I will say that even while smoking, the inverter seems to be functioning fine. I'd be surprised if smoke is a byproduct of normal operation, but this is our first inverter and first RV, so I can't say for sure. This situation stinks on more than one level...

Thanks for any replies from those more familiar with these issues.
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 09:15 AM   #2
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 6,406
Images: 2
Blog Entries: 2
I would NOT run the converter until the problem is solved. Fire is not your friend... especially in an RV.

Is there a fuse in the converter for the DC output? Do you have batteries?
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 06-25-2017, 09:28 AM   #3
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
It seems highly unlikely that 2 new Victron units are faulty; wiring is more likely. You are pulling more than 100 amps at that load so there should be evidence that something smoked. Get the cover off your I/C and look at the cables and connections. If you had a tech do this and you are not comfortable with the troubleshooting, get him back to fix it.
Larry
lsbrodsky is offline   Reply With Quote
Old 06-25-2017, 09:32 AM   #4
Rivet Master
 
Rich W's Avatar

 
2006 23' Safari SE
I'm In , Kentucky
Join Date: Dec 2012
Posts: 4,251
Images: 5
Have you gone to the manufacturer's web site or called their support line? Provide them with the same information you have given here and see what they say.
__________________
-Rich
Rich & Yvonne
2006 Safari SE -Dora-
2004 4Runner SE 4.7L V8
Rich W is offline   Reply With Quote
Old 06-25-2017, 11:05 AM   #5
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,674
Hi

I'd bet you a warm can of beer that the wires to the inverter are not fat enough or that the connector(s) on the wire are to small / poorly connected.

The inverter is going to try to deliver the required load. Let's say that's 1350 W and the inverter is 100% efficient. It will pull 100A off of a 13.5V fully charged battery to do that with monster large wires. If the wires have 1V of drop, it will try to pull 108A. The drop will be more with the higher current so now you are maybe at 12.0 V and 112A.

If you have the "normal" battery setup, you have about 200AH of battery. (Your custom setup may be very different). Pulling 100A off of a 200AH battery is going to drop the output voltage more than a little, up goes the current some more. It can quickly turn into a death spiral. At some point the inverter will cut out to protect it's self. Depending on the design, that may not be util a pretty low voltage (like 9.5V on your unit).

If you are right at the magic 9.5V point on the inverter, the 1500 W load will pull 173A from the battery. That's at a 90% efficiency on the inverter. That's a lot of current .... 2/0 cable is the smallest you should risk at that point. If you *do* go that small, you will get > 5V of drop in a 20' long cable pair. For a ~1V drop you would need to go to something in the 6/0 to 8/0 range.

None of this gets you to the 3KW rating on the inverter, we're still poking around at 1/2 output ....

Bob
uncle_bob is offline   Reply With Quote
Old 06-25-2017, 11:36 AM   #6
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by cwf View Post
I would NOT run the converter until the problem is solved. Fire is not your friend... especially in an RV.

Is there a fuse in the converter for the DC output? Do you have batteries?
@cwf: Thanks for the reply Channing. I agree wholeheartedly, but we're full-timing, so not much choice if we want to have electricity. We have four 6V sealed AGM batteries rated at 220Ah each. Yes, there's a 400A fuse between the DC output and the inverter.
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 11:44 AM   #7
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by lsbrodsky View Post
It seems highly unlikely that 2 new Victron units are faulty; wiring is more likely. You are pulling more than 100 amps at that load so there should be evidence that something smoked. Get the cover off your I/C and look at the cables and connections. If you had a tech do this and you are not comfortable with the troubleshooting, get him back to fix it.
Larry
@lsbrodsky: Thank you for the reply. I agree, but it's been difficult to find the source of the smoke. When I took off the cover on the first unit, I didn't see any evidence of burning whatsoever. Same with all of the wires. The tech who installed the replacement unit inspected the wiring and couldn't find any fault or evidence of burning, and I haven't seen anything on this one either when removing the face plate.
Attached Thumbnails
Click image for larger version

Name:	FullSizeRender.jpg
Views:	166
Size:	320.8 KB
ID:	288156  
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 11:53 AM   #8
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by richw46 View Post
Have you gone to the manufacturer's web site or called their support line? Provide them with the same information you have given here and see what they say.
@richw46: Thanks for your reply. I called Victron early last week right after we had the new unit installed and it smoked. They were super duper unhelpful. The woman just repeated that they service dealers first, so basically no customer service for owners. ::{

I haven't contacted the dealer yet, because what more more can they do? They were super cool about replacing the first unit under warranty, without any hassle at all. The dealer even worked together a bit with the installer before I bought the final setup to make sure it had all the right components.
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 12:00 PM   #9
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
So if you have the cover off, where is it smoking when you run it?
Larry
lsbrodsky is offline   Reply With Quote
Old 06-25-2017, 12:02 PM   #10
Rivet Master
 
AWCHIEF's Avatar
 
2006 23' Safari SE
Biloxi , Mississippi
Join Date: Nov 2011
Posts: 8,278
Images: 33
Quote:
Originally Posted by GinaParmesan View Post
@cwf: Thanks for the reply Channing. I agree wholeheartedly, but we're full-timing, so not much choice if we want to have electricity. We have four 6V sealed AGM batteries rated at 220Ah each. Yes, there's a 400A fuse between the DC output and the inverter.

You do have a choice if you do not want to burn your trailer to the ground. Stop using the inverter Immediately. Find a professional to look at your system ASAP.
__________________
MICHAEL

Do you know what a learning experience is? A learning experience is one of those things that says "You know that thing that you just did? Don't do that."
AWCHIEF is offline   Reply With Quote
Old 06-25-2017, 12:21 PM   #11
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by lsbrodsky View Post
So if you have the cover off, where is it smoking when you run it?
Larry
@lsbrodsky: It must be coming from somewhere deeper inside the unit. All I see is smoke coming out of the closet into the bedroom. Nothing comes directly out the front of the unit or the wires below or around it, either, even when I looked with a flashlight.

The second tech who installed the replacement unit said a lot of inverters have a coating on the interior coils that burns off with use... most people probably install these in an exterior storage bay and wouldn't notice burn-off... but visible clouds of smoke seem too much to be normal in my mind.
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 12:27 PM   #12
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by AWCHIEF View Post
You do have a choice if you do not want to burn your trailer to the ground. Stop using the inverter Immediately. Find a professional to look at your system ASAP.

@AWChief: Thank you for your concern! The certified tech who looked at my setup last week at an RV repair center had 30+ years of experience and he didn't see anything amiss. I specifically asked him to look for problems and evidence of burning. The dealer is shipping the first unit back to Victron, so maybe they'll be able to tell. Neither unit displays a warning light, even while smoking.
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 12:59 PM   #13
2 Rivet Member
 
1987 29' Airstream 290
Los Angeles , California
Join Date: Dec 2016
Posts: 74
Quote:
Originally Posted by uncle_bob View Post
Hi

I'd bet you a warm can of beer that the wires to the inverter are not fat enough or that the connector(s) on the wire are to small / poorly connected.

The inverter is going to try to deliver the required load. Let's say that's 1350 W and the inverter is 100% efficient. It will pull 100A off of a 13.5V fully charged battery to do that with monster large wires. If the wires have 1V of drop, it will try to pull 108A. The drop will be more with the higher current so now you are maybe at 12.0 V and 112A.

If you have the "normal" battery setup, you have about 200AH of battery. (Your custom setup may be very different). Pulling 100A off of a 200AH battery is going to drop the output voltage more than a little, up goes the current some more. It can quickly turn into a death spiral. At some point the inverter will cut out to protect it's self. Depending on the design, that may not be util a pretty low voltage (like 9.5V on your unit).

If you are right at the magic 9.5V point on the inverter, the 1500 W load will pull 173A from the battery. That's at a 90% efficiency on the inverter. That's a lot of current .... 2/0 cable is the smallest you should risk at that point. If you *do* go that small, you will get > 5V of drop in a 20' long cable pair. For a ~1V drop you would need to go to something in the 6/0 to 8/0 range.

None of this gets you to the 3KW rating on the inverter, we're still poking around at 1/2 output ....

Bob
@uncle_bob: Thank you for your detailed reply, much appreciated. I prefer my beer warm, so I'll take your bet. : I included a pic of the inverter in another reply above, and I'm attaching the diagram of the components here. Looks like #4/0 wire was used for the inverter...was that too small?

Just checking that I get what you're saying... do you mean that when draw is getting closer to the battery-bank's capacity, no matter how charged up they are, the batteries will have trouble delivering the necessary voltage to the inverter? And bigger cable from the batteries to the inverter is the solution?

A few more details: The inverter is almost directly above the battery bank—under 5 ft. of cable between them. Victron claims a max efficiency of 93% for this unit. The batter bank is 220Ah, from four sealed 6V AGMs. The water kettle for example, shows about -145Ah on the BMS...for about 2 min. I now shut off/unplug whatever I can before turning it on, so I'd guess around 6-8Ah of that is the inverter itself, plus solar charger and maybe a couple LED bulbs.
Attached Thumbnails
Click image for larger version

Name:	Screen Shot 2017-06-25 at 2.32.16 PM.png
Views:	172
Size:	334.3 KB
ID:	288159  
GinaParmesan is offline   Reply With Quote
Old 06-25-2017, 01:12 PM   #14
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
4/0 wire is plenty big. But, I just installed one of these in November, inside, under the bed. I got no smoking at startup or now. The biggest load I have put on mine is my microwave.

Larry
lsbrodsky is offline   Reply With Quote
Old 06-25-2017, 01:46 PM   #15
4 Rivet Member
 
fran&frank's Avatar
 
2016 27' Flying Cloud
Hartsburg , Missouri
Join Date: Dec 2015
Posts: 464
I have the same inverter and its never smoked, even when running the air conditioning off my battery. In addition to the face plate you can remove the top plate of the inverter case, perhaps you can get a better view of where the smoke is coming from that way.--Frank
__________________
Frank & Fran
2016 27' FC FB with 600 W solar
2016 Ford F150 EcoBoost
Equalizer Hitch
fran&frank is offline   Reply With Quote
Old 06-25-2017, 02:19 PM   #16
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,674
Hi

At 5' of cable, 4/0 should be ok. it certainly is big enough that it will not smoke running a 1.5KW load. That does not let the cabling off the hook as the source of the smoke, just the wire (the connections are still in the running). The idea that a brand new inverter sends out clouds of smoke is bunk. That goes double for a well known and respected brand. It goes at least double that when run at 1/2 the rated load. So, no this is not some sort of "expected result" running an inverter.

Backing up a bit, 3KW at 90% and 12V gets you to 275A. That's running your batteries at a discharge rate above their amp hour rating. That 200 AH rating is likely at a 10 or 20A rate. At 200A, there rating might be 120AH rather than 200AH. Simply put, your battery bank is a bit small for a 3KW inverter. It *will* drop voltage under load pretty fast. Consider tripping the number of batteries in the bank if you want to get 5 or 6 years use out of them and will be running the full or near full output on a regular basis.

Smoke generally means 451F is being approached. (Yes, it's a Sci Fi reference ... sorry about that). Normal electronics should never get above about 150F. Wire and cable - same thing. You will get steam at 220F, but that's not smoke. If it's getting hot enough to generate smoke, it *will* leave a trace. If that trace is not obvious, an infrared camera or cheap IR thermometer (< $30) will likely spot it for you. If you don't mind getting burned, poking here and there will spot it as well. BE VERY CAREFUL OF 120V LINES if you do the poke method.

My guess is it's not the inverter at all. They generally have high temperature shut down features that kill them when they go hot. I'd bet on a poorly done connection somewhere or a cable that has a deep gouge in it. A really scary thought is that it's not on the 12V side but on the 110 V side of things ... yikes !!!

Bob
uncle_bob is offline   Reply With Quote
Old 06-25-2017, 03:01 PM   #17
4 Rivet Member
 
2004 22' Safari
Albuquerque , New Mexico
Join Date: Apr 2014
Posts: 374
Quote:
Originally Posted by AWCHIEF View Post
You do have a choice if you do not want to burn your trailer to the ground. Stop using the inverter Immediately. Find a professional to look at your system ASAP.
Best advice on the thread.
Silver.Sanctuary is offline   Reply With Quote
Old 06-25-2017, 04:26 PM   #18
Rivet Master
 
Currently Looking...
Mantua , Ohio
Join Date: Jul 2005
Posts: 7,062
Blog Entries: 2
For years we didn't know what an inverter was, I'd stop using it, now.
xrvr is offline   Reply With Quote
Old 06-25-2017, 05:52 PM   #19
3 Rivet Member
 
2002 25' Classic
Kalama , Washington
Join Date: Feb 2003
Posts: 187
Your battery bank (composed of 4 6v @220Ah) will deliver 440Ah wired for 12v, not 880Ah, right? AND, discharging <50% now limits draw to 220Ah. You're asking your bank to do more than it should (which could only be managed by trimming the minutes (seconds?) of use. I wonder if you demonstrated the smoking behavior to your technician that looked it over. There is no safe circumstance where electrically generated smoke (of ANY kind) is acceptable in an RV. Your system is capable of harming you. Be cautious/get help with this.
nwclassic is offline   Reply With Quote
Old 06-25-2017, 06:17 PM   #20
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
Their battery capacity is plenty, something else is wrong here.
Larry
lsbrodsky is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Smoke, Smoke Everywhere ncbambi 2008 Safari SE 14 07-25-2010 06:28 PM
THE ADVENTURE BEGINS - 6 mos Full Time Phantom On The Road... 3 10-17-2008 05:18 PM
Voltage Inverters mcostanzo Electrical - Systems, Generators, Batteries & Solar 12 08-01-2006 10:37 PM
Inverters again ! Tinsel Loaf Electrical - Systems, Generators, Batteries & Solar 8 08-22-2004 07:22 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:22 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.