Old 09-21-2017, 11:04 PM   #61
1 Rivet Member
 
San Tan Valley , Arizona
Join Date: May 2017
Posts: 7
Blog Entries: 1
Low Pressure External Port does not work with my Champion 3500/3100 Dual Fuel

I see others on this thread have been successful running propane generators using the external low pressure port of their AS. I have a 2017 International Serenity 19ft. I connected my Champion Dual Fuel 3500/3100 watt generator to the outside propane port using the 6 ft propane hose that came with the AS that I added a 3/8 quick connect male fitting to attach to the generator. This hose does not have a regulator and relies on the internal AS regulator. I could not get enough propane pressure necessary to run my generator. I called Airstream Customer Service and they told me the AS internal regulator has pressure of an 11 in column of water (the measurement the regulator gave to AS. The AS Customer Service person said the external propane port is only meant to use with a small propane stove/grill and does not have enough pressure to run a generator. I also tested the generator by removing one of the 30 gal propane tanks from the AS and using the 6 ft hose and regulator that came with the generator. That worked fine. Does anyone know what I can do to get the external propane port to work with my generator?
AZBob1 is offline   Reply With Quote
Old 09-22-2017, 12:55 AM   #62
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
Quote:
Originally Posted by AZBob1 View Post
. . .
. . . Does anyone know what I can do to get the external propane port to work with my generator?
I don't think this is possible IMO. The only way is to do what you did, but you don't have to remove the tank from the trailer. Just get a longer hose for your gen, and use your regulator to attach the hose to one of the tanks.

You gen needs more propane at a higher pressure than the AS's low pressure port can supply. [IMO]

Some folks add an Easy Start device to one of the air conditioners, and use a 2000 watt gen/inverter off the low pressure port. There are tons of threads on this solution.

Good luck,

Peter
OTRA15 is offline   Reply With Quote
Old 09-22-2017, 02:04 PM   #63
Rivet Master
 
CruizinDux's Avatar
 
2014 20' Flying Cloud
Washington , Missouri
Join Date: Mar 2014
Posts: 2,591
Quote:
Originally Posted by OTRA15 View Post
I don't think this is possible IMO. The only way is to do what you did, but you don't have to remove the tank from the trailer. Just get a longer hose for your gen, and use your regulator to attach the hose to one of the tanks.

You gen needs more propane at a higher pressure than the AS's low pressure port can supply. [IMO]

Some folks add an Easy Start device to one of the air conditioners, and use a 2000 watt gen/inverter off the low pressure port. There are tons of threads on this solution.

Good luck,

Peter
Peter so for your setup on your FC20, from the low pressure port, you can run your Honda 1000 (I believe), and most if not all of the appliances (fur, WH, refer, oven/stove). What's your experience if any on what has to be throttled back/turned off while the genset is running?

Bob
CruizinDux is offline   Reply With Quote
Old 09-22-2017, 05:16 PM   #64
2 Rivet Member
 
2017 26' Flying Cloud
2018 27' International
carbondale , Colorado
Join Date: Sep 2017
Posts: 66
Now, I'm confused . Are the AS tanks with the external quick disconnect not capable of running a gen, either the honda 2000 or the yamaha 2400, or any other. Thats what I read from AZ bob report from AS customer service. I have been reading this whole thread believing people have been mostly using the two AS propane tanks. Answers???
capt_ron777 is offline   Reply With Quote
Old 09-22-2017, 05:56 PM   #65
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
Quote:
Originally Posted by capt_ron777 View Post
Now, I'm confused . Are the AS tanks with the external quick disconnect not capable of running a gen, either the honda 2000 or the yamaha 2400, or any other. Thats what I read from AZ bob report from AS customer service. I have been reading this whole thread believing people have been mostly using the two AS propane tanks. Answers???
I have run my EU2000i from the quick disconnect I added to my trailer. It will provide enough propane for the generator at full power but I haven't tried to run anything else at the same time. The regulator is supposed to provide enough propane to maintain the 11" WC spec (about 0.4 psi) with all appliances operating.

The EU2000i is claimed to run 3.4 hours at full load on a gallon of gas. That would be equivalent to 114,000 BTU/3.4h or 33,500 BTU/h. The furnace in my trailer is 35,000 BTU. So I would guess that I could certainly run everything except the furnace while running the 2000i, and might even run the furnace depending on how much flow margin the regulator selected by Airstream has.

Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 09-22-2017, 05:56 PM   #66
3 Rivet Member
 
Dave-n-Janet's Avatar
 
2017 26' Flying Cloud
Moss Point , Mississippi
Join Date: Jun 2017
Posts: 196
There has been a lot of discussion about this on some other threads. Basically the 3500 (or 3400) Champion has 2 regulators. To use the low-pressure disconnect, you have to take the small regulator (high pressure) off the Champion propane hose and get hardware to mate up with the quick disconnect. I have not used on the road yet, as my plan is to just fill the gas tank on the gen since at this point it is just backup. Should I need it and use up the 1.6 gal of gas, then I have propane. Also, living on the gulf coast in hurricane country, the 3500 watt Champion also gives me the options of gas (usually 5-10 gal around for lawn mower), propane (a couple of 20 lb BBQ tanks lying about) or the propane on AS should we ever have extended power outage.

Note - the AS low pressure is only rated for 25,000 BTUs, while the 3500 watt generator could pull more. May be a problem with extended use, I just don't know yet, although I haven't seen any problems reported on forum yet.
Dave-n-Janet is offline   Reply With Quote
Old 09-22-2017, 06:45 PM   #67
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
Quote:
Originally Posted by CruizinDux View Post
Peter so for your setup on your FC20, from the low pressure port, you can run your Honda 1000 (I believe), and most if not all of the appliances (fur, WH, refer, oven/stove). What's your experience if any on what has to be throttled back/turned off while the genset is running?

Bob
I have not really tested other propane-fired uses while the small Yamaha 1k inverter gen is running. I think the water heater may have run at the same time, but probably not the oven, range top burners, or the fridge (on propane), and definitely not the hot air furnace.

My guess would be that the trailer's propane system could handle almost all propane-fired uses at the same time, as the only one pulling off the low-pressure port is the small gen.

Sorry I don't have any usage/capacity stats available, nor the time or expertise to theorize. When the weather gets cold, I may try a full-scale test-run.

Have a good weekend.

Peter
OTRA15 is offline   Reply With Quote
Old 09-22-2017, 10:42 PM   #68
Rivet Master
 
CruizinDux's Avatar
 
2014 20' Flying Cloud
Washington , Missouri
Join Date: Mar 2014
Posts: 2,591
Quote:
Originally Posted by OTRA15 View Post
I have not really tested other propane-fired uses while the small Yamaha 1k inverter gen is running. I think the water heater may have run at the same time, but probably not the oven, range top burners, or the fridge (on propane), and definitely not the hot air furnace.

My guess would be that the trailer's propane system could handle almost all propane-fired uses at the same time, as the only one pulling off the low-pressure port is the small gen.

Sorry I don't have any usage/capacity stats available, nor the time or expertise to theorize. When the weather gets cold, I may try a full-scale test-run.

Have a good weekend.

Peter

Peter thanks. No problem on the experience. I suspect you're correct, but things could easily be scaled back if needed. If you're using the oven the furnace would likely be overkill . And like you said with a longer house and two tanks....

Bob
CruizinDux is offline   Reply With Quote
Old 09-23-2017, 03:52 AM   #69
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
Quote:
Originally Posted by CruizinDux View Post
. . . And like you said with a longer house and two tanks....
Bob
Tanks for the suggestion, and

. . . tanks again!


OTRA15 is offline   Reply With Quote
Old 09-23-2017, 06:03 AM   #70
Rivet Master
 
GammaDog's Avatar
 
2014 25' FB Eddie Bauer
Vero Beach , Florida
Join Date: Sep 2014
Posts: 695
Images: 26
See post,#6 in this thread where Rocinante quoted a number of prior posts including mine. A few thoughts on the recent additions to this thread:

- The low pressure port on our 2014 model trailer is rated for devices of up to 25,000 BTUs. I have not attempted to calculate a BTU rating for generators, but I recall someone on the Forums did and concluded that a single 2000 watt generator would exceed the rating. In other words, Airstream isn't claiming we should be able to meet our trailers' electric needs with the power from that port.

- The factory installed port on our trailer is an MB Sturgis model 250 low pressure propane disconnect (or equivalent... in any event, fittings that comply with that standard seem to be compatible with our trailer). This is a 1/4" series brass fitting. I know that many generators (including my two Honda's with the PropaneCarbs.com conversion kits) use 3/8" rubber tubing. Note that the port itself is a bottleneck in a system plumbed with 3/8" tubing.

- I have run tests with two Honda 2000s running simultaneously at full throttle off the trailer's low pressure port using a 1/4" tee. That's documented in the post Rocinante linked to, I believe. I had every propane source in the trailer running at the same time including the furnace and all three stove burners. The generators still produced 120 volts to the trailer's 120 volt system.

- Propane evaporation is strongly affected by ambient temperature. When I ran my tests, it was a warm day in Florida. Clearly, I was exceeding the design limits of the system as Airstream expressed them. I doubt that test could be repeated with the same results at colder temps. I would not advocate running that much propane load on the system at once, but for my own purposes I wanted to see if the system was capable of it. In practice, I do run both generators simultaneously off the trailer's low pressure port with a tee fitting and 10' Camco extension hose successfully, but I turn off all other propane loads when I do that. Note, I only need that much generator capacity to run my AC, so by definition it is hot when I do that and the heat supports higher levels of propane evaporation from the active 30 pound tank.

- I appreciate that the Forums have become prime advertising space for EasyStart products as the solution to generator capacity issues. Note that the specs on some Dometic Penguin II models indicate that a "2000 watt" generator (the Honda 2000's are actually rated at 1600 watts continuous output) or even 2400 watt models may not maintain full 120 volt output with the AC running and certainly would not if any other load is present... even the trailer's converter. Voltage drop is a sign that the electric load is exceeding the capacity of the source. If I was attempting to cut corners on generator capacity I would make sure I had a surge protector with a low voltage shutoff between the generators and all of the electric/electronic stuff in my trailer. That may just be me.

- Although I have not had an issue with our Airstream, there are many posts in the Forums about primary regulators delivering more or less pressure to the system than the stated "11 inches of water column" that the book says. In my opinion, if tests like people mentioned above did not work, the first thing I would check is whether the trailer's low pressure system was actually at 11 inches. Primary regulators are often adjustable and are certainly replacable. If the pressure wasn't at or very close to 11 inches, I'd get that addressed before drawing any other conclusions.
GammaDog is offline   Reply With Quote
Old 09-23-2017, 07:17 AM   #71
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,223
Images: 9
One needs to remember that the larger generator in post #61 would draw more gas than the 2,000 watt Honda I use with our 2015 23D. Since we have a Magnum hybrid MSH-3012 converter/inverter connected to a 300 amp-hour lithium battery, the additional current to start the air conditioner is provide by the battery. The running current of the 13.5K A/C is less than the maximum continuous power rating of the 2,000 watt Honda and works just fine.

Just like with the typical 30 amp service, one has to choose what appliances are running at the same time. Power management philosophy has to be applied to the propane use when considering to run the Honda generator.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 09-23-2017, 08:31 AM   #72
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,655
Blog Entries: 1
Quote:
Originally Posted by Al and Missy View Post
The EU2000i is claimed to run 3.4 hours at full load on a gallon of gas. That would be equivalent to 114,000 BTU/3.4h or 33,500 BTU/h. The furnace in my trailer is 35,000 BTU. So I would guess that I could certainly run everything except the furnace while running the 2000i,
Okay, now I'm confused on your math. The only power required by the furnace is the 12v. control. The 35,000 BTU is provided by the combustion, not the generator.
Mollysdad is offline   Reply With Quote
Old 09-23-2017, 10:48 AM   #73
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
The furnace's combustion air heats a chamber whose hot air is exhausted by a 12-volt fan which is the main battery drain in cold weather IMO. The newer Alde baseboard system I assume uses a 12-volt circulator pump (or pumps if dual zone), and they would also draw down the batteries.
OTRA15 is offline   Reply With Quote
Old 09-23-2017, 04:21 PM   #74
4 Rivet Member
 
2017 30' Classic
Cave Creek , Arizona
Join Date: Aug 2016
Posts: 282
Blog Entries: 1
I use my Champion 3400 directly off low-pressure port on our Classic. I don't use the regulator that came with the generator in that configuration. I do have to turn the low-pressure port valve to about 3/4 setting - then it works great under any load
__________________
Pete B55
2017 Classic
2017 F-250
Pete B55 is offline   Reply With Quote
Old 09-23-2017, 10:17 PM   #75
Rivet Master
 
2023 23' International
Macon , Georgia
Join Date: Dec 2007
Posts: 705
Images: 1
Quote:
Originally Posted by Pete B55 View Post
I use my Champion 3400 directly off low-pressure port on our Classic. I don't use the regulator that came with the generator in that configuration. I do have to turn the low-pressure port valve to about 3/4 setting - then it works great under any load
I do the same, works great.
Roadtech is offline   Reply With Quote
Old 09-23-2017, 10:41 PM   #76
1 Rivet Member
 
San Tan Valley , Arizona
Join Date: May 2017
Posts: 7
Blog Entries: 1
Quote:
Originally Posted by Pete B55 View Post
I use my Champion 3400 directly off low-pressure port on our Classic. I don't use the regulator that came with the generator in that configuration. I do have to turn the low-pressure port valve to about 3/4 setting - then it works great under any load
I have the Champion 3500 but am not able to get it to run off the my AS's low-pressure port. I do not use the regulator hose that came with my generator. Instead am using the unregulated hose that came with my AS. Not sure what you mean when you say to adjust port value to 3/4 setting. Wouldn't that close off some of the propane flow? I am not getting enough even with the value wide open. Could you please let me know what I am doing wrong??
AZBob1 is offline   Reply With Quote
Old 09-24-2017, 05:27 AM   #77
4 Rivet Member
 
mojoe7009's Avatar
 
Currently Looking...
Green Cove Springs , Florida
Join Date: Oct 2016
Posts: 479
Quote:
Originally Posted by Roadtech View Post
I do the same, works great.


Ditto
__________________
Breathe In, Breathe Out, Move On
mojoe7009 is offline   Reply With Quote
Old 09-24-2017, 08:52 AM   #78
4 Rivet Member
 
dasams's Avatar
 
Palm Desert , California
Join Date: Jul 2016
Posts: 301
Quote:
Originally Posted by AZBob1 View Post
I have the Champion 3500 but am not able to get it to run off the my AS's low-pressure port. I do not use the regulator hose that came with my generator. Instead am using the unregulated hose that came with my AS.
Is the ID of the AS hose large enough? I use the 1/4" GenConnex hose and it works great. Just need to fully prime the carburetor to purge out the air and then it'll fire right up. BTW mine's a Honda.
__________________
2006 Cayenne S with V8, air suspension, factory tow
2018 FC 27 FB
2017 FC 25 RB Gone
dasams is offline   Reply With Quote
Old 09-24-2017, 09:23 AM   #79
Rivet Master
 
FCStreamer's Avatar
 
2014 30' Flying Cloud
Tampa , Florida
Join Date: May 2016
Posts: 1,364
Blog Entries: 1
Quote:
Originally Posted by dasams View Post
Is the ID of the AS hose large enough? I use the 1/4" GenConnex hose and it works great. Just need to fully prime the carburetor to purge out the air and then it'll fire right up. BTW mine's a Honda.
I think the question is whether the larger generators can run as they presumably use more fuel. I’ve read some folks running 3500 watt generators, some can’t. It may have to do with the thickness of the line.

For those who successfully ran a 3500 or higher generator on the AS port, what hose did you use? And did you use the regulator that came with your generator?
__________________
2014 Airstream Flying Cloud 30 Recliner - WBCCI #4850 - AIR #110821
2018 Nissan Armada SL Tow Vehicle, Equal-i-zer Hitch
Visit Our Flying Cloud blog for my latest adventure!
FCStreamer is offline   Reply With Quote
Old 09-24-2017, 09:42 AM   #80
2 Rivet Member
 
Dave18134's Avatar
 
2017 27' Flying Cloud
Beavercreek , Oregon
Join Date: Apr 2017
Posts: 60
It works on my 2017 FC

I use the Champion 3400/3100 dual fuel and it runs off my front accessory quick connect just fine--no fiddling with the valve. I followed the same procedure as posted by @Airmiles (http://www.airforums.com/forums/f42/...ml#post1996143).

In a nutshell: 1) remove the 2" diameter high pressure regulator on the hose supplied by Champion. (This is attached to the 5" diameter disk that acts as a safety valve--leave that on the original hose), 2) attach a female quick connect (QC) in it's place of the 2" regulator, 3) Get a 10-12ft hose made up with male QC's on both ends and connect one end to the accessory port on the AS, 4) connect the other end to your female QC on the hose/valve assembly.

@Airmiles posted a picture that is worth all these words. It works.
Dave18134 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Pressure: Shore pressure high, All pressure in trailer low.... bhooves Sinks, Showers & Toilets 9 10-16-2016 03:22 PM
any residents of Sequim ,Port Townsend or Port Angeles kingfisher24 On The Road... 6 10-15-2013 08:57 AM
Champion 73531i Generator Experiences Anyone? eberrobw Generators & Solar Power 12 07-16-2011 10:05 AM
High Pressure vs. Low pressure Appliances emenriquez General Appliance Topics 2 06-15-2009 01:04 AM
Low pressure / High pressure appliances Rick LP Gas, Piping, Tanks & Regulators 1 06-15-2002 06:29 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:15 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.