Old 07-17-2015, 09:35 PM   #43
3 Rivet Member
 
1978 28' Argosy 28
Austin , Texas
Join Date: Apr 2015
Posts: 207
OK. update. I stopped at home depot on the way home for a $4 breaker. I installed it first because, to be honest, it was the path of least resistance. And.. success. System works great off the genny. I ran the genny and AC for nearly 2 hrs while my wife and I worked inside. The old breaker was toast, although it would manually trip and reset just fine. No signs of damage, just wasn't working. ??????
This is a band-aid for sure. I still have no idea why I have a breaker there (much less a 20amp), or why I have a 50A breaker on the genny... but our family is headed to MN in less than a week and I'm moving on to other projects already. I'll dig into the WHY after our trip. For now, will try not to overload the system while on genny power. SO happy to have house AC while on the road in Texas heat. Going to be 100 next week when we leave.
Big smiles over here that this was a $4 fix. Brad, I broke out the ohm meter but happily put it away unused. There will be an update to this thread later this year. Can't say enough thanks to you all for helping. Would have cost me a fortune at a local shop.

Ben

What a trip...
__________________

__________________
bpg_austin is offline   Reply With Quote
Old 07-18-2015, 06:39 AM   #44
Airstream Driver
 
PeterH-Airstreamer's Avatar

 
1997 30' Excella
1983 31' Airstream310
Austin , Texas
Join Date: Feb 2002
Posts: 3,373
Images: 51
Congrats Ben!! Love those forum members induced success stories
Another $4.- for a 30 amp would ease your mind or if your alternator charging system is wired correctly, unplug the new converter when on the road. Then you only run the fridge and the A/C on the genny power.
__________________

__________________
1990 29' Excella Trailer
1996 Airstream B190
1997 30' Excella Trailer
AIR #13
PeterH-Airstreamer is offline   Reply With Quote
Old 07-18-2015, 06:47 AM   #45
Rivet Master
 
mayco's Avatar

 
1982 31' Airstream 310
champaign , Illinois
Join Date: Jun 2013
Posts: 2,760
Beautiful
__________________
mayco is offline   Reply With Quote
Old 07-18-2015, 07:28 AM   #46
Rivet Master
 
bkahler's Avatar

 
1974 20' Argosy 20
Richmond , Kentucky
Join Date: Jan 2003
Posts: 6,350
Quote:
Originally Posted by bpg_austin View Post
OK. update. I stopped at home depot on the way home for a $4 breaker. I installed it first because, to be honest, it was the path of least resistance. And.. success. System works great off the genny. I ran the genny and AC for nearly 2 hrs while my wife and I worked inside. The old breaker was toast, although it would manually trip and reset just fine. No signs of damage, just wasn't working. ??????
Great!!

My guess is what happened is when you shutdown the genset last time with the AC on high there was a current surge that melted/fried the breaker points. What happens is when you lower the voltage (which happens when the generator is winding down) on something that is running the current requirement goes up. A rough example would be if the AC requires 15 amps when running at 120vac then at 80vac it might require 50 or so amps. That's more than enough to damage the breaker contacts, heck that's more than enough to damage the generator itself. I don't know what the real numbers would be but hopefully you get the idea.

What baffles me a little is why you generator was so hard to start with the breaker in the condition it was. Somehow that breaker had to have shorted to a ground point inside which was effectively shorting out the generator. That's the only thing I can think of that could affect the generator trying to start.

I'm gonna have to think about this one. Maybe you could dismantle the bad breaker and take a picture or two.

Quote:
This is a band-aid for sure. I still have no idea why I have a breaker there (much less a 20amp), or why I have a 50A breaker on the genny... but our family is headed to MN in less than a week and I'm moving on to other projects already. I'll dig into the WHY after our trip. For now, will try not to overload the system while on genny power. SO happy to have house AC while on the road in Texas heat. Going to be 100 next week when we leave.
Big smiles over here that this was a $4 fix. Brad, I broke out the ohm meter but happily put it away unused. There will be an update to this thread later this year. Can't say enough thanks to you all for helping. Would have cost me a fortune at a local shop.

Ben

What a trip...
I wouldn't call it a band aid. That's a text book example of how to troubleshoot a problem. You check the simple things first and then move onto the more difficult/expensive checks.

Look at it this way, if that 20 amp breaker hadn't been in the circuit imagine what would have happened to the generator. Remember the generator has a 50 amp breaker installed right now instead of what we all agree it should be a 20 or 30 amp breaker. Instead of $4 you might be spending $3000 for a new generator

Enjoy your trip...

Brad
__________________
Air forums # 1674
1974 20' Argosy Motor Home
1974 31' Excella trailer (parting out, as of 4/1/2015 I have wheels, brake drums, windows & holding tanks left to sell)
bkahler is offline   Reply With Quote
Old 07-18-2015, 08:22 AM   #47
Rivet Master
 
mayco's Avatar

 
1982 31' Airstream 310
champaign , Illinois
Join Date: Jun 2013
Posts: 2,760
OK. update. I stopped at home depot on the way home for a $4 breaker. I installed it first because, to be honest, it was the path of least resistance. And.. success. System works great off the genny. I ran the genny and AC for nearly 2 hrs while my wife and I worked inside. The old breaker was toast, although it would manually trip and reset just fine. No signs of damage, just wasn't working. ??????
This is a band-aid for sure. I still have no idea why I have a breaker there (much less a 20amp), or why I have a 50A breaker on the genny... but our family is headed to MN in less than a week and I'm moving on to other projects already. I'll dig into the WHY after our trip. For now, will try not to overload the system while on genny power. SO happy to have house AC while on the road in Texas heat. Going to be 100 next week when we leave.


Its a good dea to have that breaker inline from your genny. Those push button breakers on the genny are pretty unreliable is what Ive been told. I think I would look into replacing the 50 with a 30 and replacing the 20 with a 30. The thing Im wondering about is why a PO would have installed those in the first place. Could have been as simple as thats what they had available. Or they may have been having some issues with the genny and that was their solution to make it work..........who knows! But logic would tell you that it doesnt make sense to have it set up thst way. Have a great, trouble free trip.
__________________
mayco is offline   Reply With Quote
Old 07-18-2015, 12:32 PM   #48
Rivet Master
 
bkahler's Avatar

 
1974 20' Argosy 20
Richmond , Kentucky
Join Date: Jan 2003
Posts: 6,350
Quote:
Originally Posted by mayco View Post
Its a good dea to have that breaker inline from your genny. Those push button breakers on the genny are pretty unreliable is what Ive been told. I think I would look into replacing the 50 with a 30 and replacing the 20 with a 30. The thing Im wondering about is why a PO would have installed those in the first place. Could have been as simple as thats what they had available. Or they may have been having some issues with the genny and that was their solution to make it work..........who knows! But logic would tell you that it doesnt make sense to have it set up thst way. Have a great, trouble free trip.
I'm with Mike, replace the 20 amp with a 30 amp and get rid of the 50 in favor of a 30 amp.

With the 20 amp breaker installed you've effectively restricted your coach to about 20 amps max from the generator whereas if you switch to a 30 amp breaker you'll have the full 28-30 amp output of the generator available to use.

Brad
__________________
Air forums # 1674
1974 20' Argosy Motor Home
1974 31' Excella trailer (parting out, as of 4/1/2015 I have wheels, brake drums, windows & holding tanks left to sell)
bkahler is offline   Reply With Quote
Old 07-18-2015, 07:24 PM   #49
3 Rivet Member
 
1978 28' Argosy 28
Austin , Texas
Join Date: Apr 2015
Posts: 207
Brad, I fished the breaker out of the trash and will split it open when I get a chance. You might have to be a bit patient with me. I am interested to see though! lots on my plate at the moment.

I'm in agreement with the thinking of swapping the genny breaker for a 30A and upping the in-line breaker to a 30. Seems redundant though, doesn't it? Could I just bypass the genny breaker completely (hard wire leads together) and replace the inline with a 30? Wouldn't that effectively bring be back to 'stock'? Then I'd have a reliable genny breaker that's not susceptible to vibrations. ? Just relocating the genny breaker really.

BG
__________________
bpg_austin is offline   Reply With Quote
Old 07-19-2015, 06:56 AM   #50
Rivet Master
 
bkahler's Avatar

 
1974 20' Argosy 20
Richmond , Kentucky
Join Date: Jan 2003
Posts: 6,350
Quote:
Originally Posted by bpg_austin View Post
Brad, I fished the breaker out of the trash and will split it open when I get a chance. You might have to be a bit patient with me. I am interested to see though! lots on my plate at the moment.
No hurry on my part, just curiosity

Quote:
I'm in agreement with the thinking of swapping the genny breaker for a 30A and upping the in-line breaker to a 30. Seems redundant though, doesn't it? Could I just bypass the genny breaker completely (hard wire leads together) and replace the inline with a 30? Wouldn't that effectively bring be back to 'stock'? Then I'd have a reliable genny breaker that's not susceptible to vibrations. ? Just relocating the genny breaker really.

BG
Electrically I know of no reason you can't eliminate the 50 amp breaker at the genset. Although per the NEC code book (I'm not sure if the NEC applies to RVs) normally with circuit breakers you put a breaker close to the power source. For example your home entrance breaker panel is situated right where the power lines enter the house.

One thing to consider is insurance coverage. If the 50 amp breaker was eliminated and for some reason while running on generator power your motorhome burned up it's possible the insurance company could see the breaker was eliminated and not want to pay due to an "altered" generator. Just trying to look at the worst case scenario here.

With that being said If it was my generator most likely I would eliminate the 50 amp breaker and just tie the wires together.

Brad
__________________
Air forums # 1674
1974 20' Argosy Motor Home
1974 31' Excella trailer (parting out, as of 4/1/2015 I have wheels, brake drums, windows & holding tanks left to sell)
bkahler is offline   Reply With Quote
Old 07-22-2015, 07:57 AM   #51
3 Rivet Member
 
1978 28' Argosy 28
Austin , Texas
Join Date: Apr 2015
Posts: 207
Here's a shot of the toasted breaker. Click image for larger version

Name:	ImageUploadedByAirstream Forums1437569819.198670.jpg
Views:	41
Size:	61.8 KB
ID:	243617Click image for larger version

Name:	ImageUploadedByAirstream Forums1437569855.248547.jpg
Views:	42
Size:	52.1 KB
ID:	243618
__________________
bpg_austin is offline   Reply With Quote
Old 07-22-2015, 08:30 AM   #52
Rivet Master
 
bkahler's Avatar

 
1974 20' Argosy 20
Richmond , Kentucky
Join Date: Jan 2003
Posts: 6,350
Ben, those breaker points are most definitely fried! They are probably as bad as I have ever seen.

There is only one scenario that we (my electrical engineering co-workers) can come up with that would cause the generator to be sluggish to start when the breaker was on. That scenario is as follows:

Genset plugged into motorhome
Breaker on
Some sort of 120 VAC load within the coach

With the breaker contacts burned as badly as they are with the breaker in the closed position the contacts would actually act like a resistor instead of a short circuit. However for this resistor to have an impact on the generator when starting there had to be some sort of electrical load in the circuit inside the coach.

A load could be as something as simple as a clock, door bell or some other item that draws power from the 120 VAC system. The burned breaker contacts would make this small load seem like a large load to the generator.

Assuming the above is correct what would happen is when you tried to start the generator the small 120 VAC load plus the high resistance through the burned circuit breaker contacts would cause a high load on the generator causing it to be hard to start (i.e. turn over).

Without some sort of load being present we can't think of any scenario that would cause the symptoms you were experiencing.

One way to check for an AC load on the coach side would be to unplug the genset (and shore power) cord and using an ohm meter check for any readings between the hot (black) and neutral (white) wires of the female socket. If there are no loads present you should have no reading, with any sort of load present you will get some sort of resistance reading.

Hope this all makes sense!

Brad
__________________
Air forums # 1674
1974 20' Argosy Motor Home
1974 31' Excella trailer (parting out, as of 4/1/2015 I have wheels, brake drums, windows & holding tanks left to sell)
bkahler is offline   Reply With Quote
Old 07-22-2015, 12:38 PM   #53
3 Rivet Member
 
1978 28' Argosy 28
Austin , Texas
Join Date: Apr 2015
Posts: 207
Yes, I think I get it. Though electricity is basically a foreign language to me.. At any rate, I've got the band-aid installed for the time being and we're headed out in a few hours. I'll dig into my electrical mysteries when I get back. Aside from the random breaker, my remote genny start doesn't work as well as my entire Monitoring system.. For another day.
I'll be posting up on the forum if I'm somehow stranded and need some expert advice. Otherwise, hope to be 'unplugged' for a week!

Best,
Ben
__________________
bpg_austin is offline   Reply With Quote
Old 07-23-2015, 09:15 AM   #54
Rivet Master
 
bkahler's Avatar

 
1974 20' Argosy 20
Richmond , Kentucky
Join Date: Jan 2003
Posts: 6,350
Quote:
Originally Posted by bpg_austin View Post
Aside from the random breaker, my remote genny start doesn't work as well as my entire Monitoring system.. For another day.
When you get spare time describe what's happening (or not happening) with the remote start.

Quote:
I'll be posting up on the forum if I'm somehow stranded and need some expert advice. Otherwise, hope to be 'unplugged' for a week!

Ben
Good deal! Hope you have a great time
__________________

__________________
Air forums # 1674
1974 20' Argosy Motor Home
1974 31' Excella trailer (parting out, as of 4/1/2015 I have wheels, brake drums, windows & holding tanks left to sell)
bkahler is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing Onan for a portable generator Paul Daugherty Airstream Motorhome Forums 7 06-15-2012 09:43 AM
Need help/advice -- Onan generator failed Taxman Generators & Solar Power 1 05-11-2007 10:14 AM
Onan Generator - Help gdeterra Land Yacht/Legacy Motorhomes 1 03-12-2007 06:57 AM
Cheapest New Generator (Onan) ZenRVer General Motorhome Topics 2 08-11-2003 08:37 AM
Generator onan Paul Daugherty Airstream Motorhome Forums 6 11-26-2002 01:51 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.