Low Voltage Disconnect - Parallel Honda Generator One out of Fuel

Anyone use a low voltage disconnect device when running Two Honda eu2000i in parallel to prevent low voltage when one generator runs out of gas and the Air conditioner kicks in?
While there are a huge number of threads on airforum about how people have run the 13,5000 Air Conditioner on a single eu200i, For the purpose of this thread, Assume that there is another device running such as might be the refrigerator/converter as an example. So the single eu2000i is remaining, and the load is above rated 2000 max /1600 steady state:
Does anyone use a low voltage disconnect to protect the motor of the Air Conditioner?
GeeSag is offline   Reply With Quote
Old 07-14-2016, 09:03 AM   #2
2 Rivet Member
 
J2Becker's Avatar
 
2015 27' Flying Cloud
Santa Fe , New Mexico
Join Date: May 2011
Posts: 40
You might need a low voltage disconnect that does NOT disconnect if it detects a floating ground. Mine does so I don't use it withe the generator.


"It's supposed to be a challenge, that's why they call it a shortcut. If it was easy it would just be 'the way'." ~ Rubin, "Road Trip"
__________________
__________________________________________________ ___________________________________________
"The most savage controversies are those about matters as to which there is no good evidence either way." Bertrand Russell
J2Becker is offline   Reply With Quote
Old 07-14-2016, 09:33 AM   #3
3 Rivet Member
 
2015 25' FB Flying Cloud
Sandy , Utah
Join Date: May 2015
Posts: 229
Quote:
Originally Posted by GeeSag View Post
Anyone use a low voltage disconnect device when running Two Honda eu2000i in parallel to prevent low voltage when one generator runs out of gas and the Air conditioner kicks in?
While there are a huge number of threads on airforum about how people have run the 13,5000 Air Conditioner on a single eu200i, For the purpose of this thread, Assume that there is another device running such as might be the refrigerator/converter as an example. So the single eu2000i is remaining, and the load is above rated 2000 max /1600 steady state:
Does anyone use a low voltage disconnect to protect the motor of the Air Conditioner?
This happened to me a couple of weeks ago. The Honda that was still running detected the overload and tripped it's own internal disconnect. The AC unit shut itself down as well. I refueled both of them and they reset automatically.
rocco52 is offline   Reply With Quote
Old 07-14-2016, 09:54 AM   #4
3 Rivet Member
 
2015 25' FB Flying Cloud
Sandy , Utah
Join Date: May 2015
Posts: 229
One thing I need to add. When I start them both I let them run a bit to warm up and then check the indicator lights on the front to make sure they are producing AC. Then I go in the trailer and start the AC. On the flip side, I turn off the AC before shutting down the Honda's. I also run them in Ecco mode. They idle until the AC compressor startup demand is received and you can hear them ramp up to handle it. Running the AC and the Converter in 90 degree weather they both use about one tank/1 gallon every 5 hours.
rocco52 is offline   Reply With Quote
Old 07-14-2016, 12:28 PM   #5
4 Rivet Member
 
2000 30' Excella
Toledo , Ohio
Join Date: Feb 2011
Posts: 493
Add a 6 gallon gas tank to them and they will run for a long time mine ran 12 hrs. and used 3 gallons of gas with the AC running .
woodfox45 is offline   Reply With Quote
Old 07-14-2016, 12:56 PM   #6
Rivet Master
 
GammaDog's Avatar
 
2014 25' FB Eddie Bauer
Vero Beach , Florida
Join Date: Sep 2014
Posts: 695
Images: 26
I use the CAMCO defender and I'm happy with it. It does not disconnect power for certain conditions (e.g.: open neutral) but it does alert to them. It does disconnect for low or high voltage.

Here's an issue to consider. This CAMCO will attempt to reconnect power once voltage is returned to normal. So, if one Honda dies and the voltage drops it will disconect. Once the AC load has been removed, the Honda will restore normal voltage as viewed by the surge protector. It will reconnect power, the AC will attempt to start and the whole process will start over with a low voltage trip.

Maybe someone makes a surge protector with low voltage shutoff that trips itself and does not attempt and automatic reset. I think that's what you'll need.

I run both of my Honda's of a single propane source. If one dies, they both die. That's another solution.
GammaDog is offline   Reply With Quote
Old 07-14-2016, 03:32 PM   #7
4 Rivet Member
 
B00merang's Avatar
 
2010 20' Flying Cloud
Hailey , Idaho
Join Date: Nov 2014
Posts: 414
on a tangent...foolishly let my Honda companion unit run out of gas. Tried for an hour to get it started again after fillup...nothing. Turned out the spark plug had some carbon in the gap (after only two seasons) and the plug was fouled. Just a heads-up in case that happens to you....its a simple thing to check and fix in the field. jon
B00merang is offline   Reply With Quote
Old 07-14-2016, 07:01 PM   #8
2 Rivet Member
 
1970 25' Tradewind
anderson , South carolina
Join Date: Dec 2015
Posts: 37
Honda 2000's

I use two honda 2000s and run the 13,500 ac (old model) and high start up amps. Run one on energy saving mode and one not. One units does fine with refrig. On electric and converter charging the 2000
On economic only kicks in on ac start up. Both Hondas are fed fuel from a 6 gal fuel tank with with y section in fuel line. All works great. Good set up. Toaster
Bob Cooke is offline   Reply With Quote
Old 07-14-2016, 07:06 PM   #9
2 Rivet Member
 
1970 25' Tradewind
anderson , South carolina
Join Date: Dec 2015
Posts: 37
Honda 2000's in parallel

I use two honda 2000s and run the 13,500 ac (old model) and high start up amps. Run one on energy saving mode and one not. One units does fine with refrig. On electric and converter charging the 2000
On economic only kicks in on ac start up. Both Hondas are fed fuel from a 6 gal fuel tank with with y section in fuel line. All works great. Goog set up. Toaster
Bob Cooke is offline   Reply With Quote
Old 07-15-2016, 06:09 AM   #10
Rivet Master
 
2015 30' International
FREDERICK , Maryland
Join Date: Jan 2014
Posts: 539
Quote:
Originally Posted by woodfox45 View Post
Add a 6 gallon gas tank to them and they will run for a long time mine ran 12 hrs. and used 3 gallons of gas with the AC running .
This is what I use as well , I can get 12+ hours even in 100+ degree weather.
http://www.ipiindustries.com/service...ded-run-tank-1
Doc Foster is offline   Reply With Quote
Old 07-15-2016, 08:03 AM   #11
Rivet Master
 
GammaDog's Avatar
 
2014 25' FB Eddie Bauer
Vero Beach , Florida
Join Date: Sep 2014
Posts: 695
Images: 26
Switch to LP

Quote:
Originally Posted by B00merang View Post
on a tangent...foolishly let my Honda companion unit run out of gas. Tried for an hour to get it started again after fillup...nothing. Turned out the spark plug had some carbon in the gap (after only two seasons) and the plug was fouled. Just a heads-up in case that happens to you....its a simple thing to check and fix in the field. jon
For what it's worth... If you google something like "Honda generator won't start" and start reading random forum posts from around the web you'll see that 90%+ of the issues are related to gasoline... especially ethanol spiked gas. There are several pluses to converting to LP. One of the three big reasons is reliability. My generators sometimes sit for months in a hot Florida garage. I don't prep them in any way for storage. They have never failed to start. Since the kits I used are trifuel, I can always use gas if that's all I've got and if I don't mind the reliability hit... or the smelly fuel... or the risk of spill and explosion under my tonneau.

And to the OPs topic, most of us carry plenty of propane.
GammaDog is offline   Reply With Quote
Old 07-15-2016, 09:34 AM   #12
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Quote:
Originally Posted by woodfox45 View Post
Add a 6 gallon gas tank to them and they will run for a long time mine ran 12 hrs. and used 3 gallons of gas with the AC running .
Ditto:

Click image for larger version

Name:	6 gal tank.jpg
Views:	159
Size:	198.1 KB
ID:	266828
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
how low is too low AC voltage? WineStream Electrical - Systems, Generators, Batteries & Solar 64 07-16-2018 08:57 PM
Portable Generator Sound Levels: One Honda EU2000i vs. Two Paralleled Honda EU2000i AndyPenny Generators & Solar Power 19 06-05-2017 03:04 PM
Low Voltage Disconnect - Where to integrate? trekerboy Batteries, Univolts, Converters & Inverters 14 04-21-2016 07:28 AM
Parallel non inverter generator with inverter generator? mtbguy Generators & Solar Power 3 07-15-2015 01:48 PM
Parallel Honda 2000 Generator Question Sky King 1970 -1973 Ambassador 3 09-06-2014 08:35 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.