Honda 2000s Running the A/C

When running my A/C with my two Honda 2000s, should I use the ECO setting or not?

Brian
__________________
SuEllyn & Brian McCabe
WBCCI #3628 -- AIR #14872 -- TAC #FL-7
2015 FC 25' FB (Lucy) with ProPride
2020 Silverado 2500 (Vivian)
2023 Rivian R1T (Opal)
moosetags is offline   Reply With Quote
Old 05-23-2008, 09:02 PM   #2
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Quote:
Originally Posted by moosetags
When running my A/C with my two Honda 2000s, should I use the ECO setting or not?

Brian
If the a/c will start with them in eco setting, then yes. If you are planning on the a/c running for a long time before the compressor shuts off, then yes.
If the compressor struggles to start, or the generators won't load on eco throttle, then no.
I have a single 2000 that will (barely) start the a/c on our trailer when not on eco throttle. Once it starts, I switch the generator to eco throttle. The generator then throttles down a bit.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 05-24-2008, 06:09 AM   #3
Rivet Master
 
vajeep's Avatar
 
1976 27' Overlander
Richmond , Virginia
Join Date: Jul 2003
Posts: 755
Images: 49
Blog Entries: 2
Brian,
We leave our 2 Hondas in eco mode with no problem when we are running our a/c.
__________________
"Abe" & Melissa Lincoln
1976 Overlander "Spirit"
2020 GMC Denali Duramax
Hensley Hitch
vajeep is offline   Reply With Quote
Old 05-24-2008, 06:23 AM   #4
3 Rivet Member
 
1973 25' Tradewind
Romulus , New York
Join Date: Feb 2008
Posts: 139
You use what you need, trial and error. If any struggling is going on--turn off eco--on both units.
jayray5 is offline   Reply With Quote
Old 05-24-2008, 07:25 AM   #5
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,477
What Terry said pretty much sums it up!
Silvertwinkie is offline   Reply With Quote
Old 05-24-2008, 08:49 AM   #6
3 Rivet Member
 
Raptorrider2001's Avatar
 
Richardson , Texas
Join Date: Aug 2002
Posts: 126
Images: 14
I installed a "Hard Start Kit" on my 11k btu. Made a big difference when using just one gen. Cost around $50 and is an easy install.
__________________
'99 25' Safari
2 Honda 2000i generators
'08 Chevy Duramax
'01 Yamaha Raptor ATV
'07 Yamaha Rhino ATV
2 burgler alarms: Rotweiller and Shepherd
"If you step down to get in, you have to step up to get out"
Raptorrider2001 is offline   Reply With Quote
Old 05-24-2008, 10:43 AM   #7
Rivet Master
 
davidz71's Avatar
 
1986 25' Sovereign
Southern Middle , Tennessee
Join Date: Mar 2002
Posts: 3,319
Images: 23
Quote:
Originally Posted by Raptorrider2001
I installed a "Hard Start Kit" on my 11k btu. Made a big difference when using just one gen. Cost around $50 and is an easy install.
Does Dometic sell the components for the Hard Start Kit or did you pick them up at the local hardware store? I've read about installing a delay for the compressor in one of my RV books but I was just wondering.
__________________
Craig

AIR #0078
'01 2500hd ext. cab, 8.1 litre gas, 5 sp. Allison auto
3.73 rear end
Mag-Hytec rear diff cover
Amsoil Dual by-pass oil filtration system
Amsoil synthetics all around
265 watt AM Solar, Inc. system
davidz71 is offline   Reply With Quote
Old 05-24-2008, 11:22 AM   #8
3 Rivet Member
 
Raptorrider2001's Avatar
 
Richardson , Texas
Join Date: Aug 2002
Posts: 126
Images: 14
Yes, it was from Dometic. The place I store mine also has a repair shop and they ordered it for me. I guess they got it from a supplyier because they received in in a couple of days. They talked like it is pretty common to install them so I would be any rv place would be able to get one. The hardest part was getting on top of the trailer to take the cover off. Easy to do yourself. Undo a couple of screws and wires and replace the old with the new. I was glad I didn't pay the shop the $95 flat rate they wanted to install. Basically all it is is a new capacitor. Give it a try, it is not hard.
__________________
'99 25' Safari
2 Honda 2000i generators
'08 Chevy Duramax
'01 Yamaha Raptor ATV
'07 Yamaha Rhino ATV
2 burgler alarms: Rotweiller and Shepherd
"If you step down to get in, you have to step up to get out"
Raptorrider2001 is offline   Reply With Quote
Old 05-25-2008, 05:34 AM   #9
2 Rivet Member
 
iHayley's Avatar
 
2007 19' Bambi
Portland , Maine
Join Date: Apr 2008
Posts: 73
Images: 5
Quote:
Originally Posted by Raptorrider2001
I installed a "Hard Start Kit" on my 11k btu. Made a big difference when using just one gen. Cost around $50 and is an easy install.
Oooo... tell me more about this "Hard Start Kit"?? I'm looking at buying two of those Honda 2000 generators, but they're quite pricey. I was going to start with just one and see how I did, and then go back for the second later. My big question was if only one was going to be enough to start up the AC.

Hayley
iHayley is offline   Reply With Quote
Old 05-25-2008, 05:56 AM   #10
Moderator
 
moosetags's Avatar

 
2015 25' FB Flying Cloud
2012 23' FB Flying Cloud
2005 25' Safari
Santa Rosa Beach , Florida
Join Date: Jul 2006
Posts: 13,159
Images: 5
Thanx for all the input. I'm going to look at the hard start capacitor also.

Brian
__________________
SuEllyn & Brian McCabe
WBCCI #3628 -- AIR #14872 -- TAC #FL-7
2015 FC 25' FB (Lucy) with ProPride
2020 Silverado 2500 (Vivian)
2023 Rivian R1T (Opal)
moosetags is offline   Reply With Quote
Old 05-25-2008, 09:05 AM   #11
3 Rivet Member
 
Raptorrider2001's Avatar
 
Richardson , Texas
Join Date: Aug 2002
Posts: 126
Images: 14
ihayley- I started out with one also. Worked pretty well after the hard start kit. Once I had the a/c going, I would try to leave the thermostat setting on high to keep if from cycling on and off which sometimes in reat hot weather, would kick the gen. into overload. Sometimes on really hot days, I would run the refrig on gas to keep from drqwing current. I would unplug the refrig on the back side and it would then switch to gas. (I think). But you will have good luck with one if your a/c unit is the 11k. The only reason I bought a second one was a friend upgraded from the 2000 to the 3000 on his mini-motorhome and he made me a deal I couldn't pass up. On days I don't run the a/c, I just run one to keep the battery charged and run the tv and microwave. If you do a search, you can find some pics. I posted of how I hook up a 5 gallon fuel can to run one or both of the gens. That gives you more fuel than you will use in a day pulling both gens. I would give you a link but it has been so long since I was on here I don't remember where they are located. OOps, found the link:
http://www.airforums.com/photos/brow...500&userid=646
__________________
'99 25' Safari
2 Honda 2000i generators
'08 Chevy Duramax
'01 Yamaha Raptor ATV
'07 Yamaha Rhino ATV
2 burgler alarms: Rotweiller and Shepherd
"If you step down to get in, you have to step up to get out"
Raptorrider2001 is offline   Reply With Quote
Old 05-30-2008, 09:45 AM   #12
3 Rivet Member
 
2006 23' Safari SE
Brea , California
Join Date: Aug 2007
Posts: 139
I have 2- 2000's and the AC runs great but I haven't tried to use them in eco mode. I have a problem going from the AC in high mode down to med. It faults out the gens. They work fine while plugged in, it only occurs with the gens. If someone has a thought on this I'd appreciate any suggestions.
Glenn G is offline   Reply With Quote
Old 06-25-2008, 11:23 PM   #13
New Member
 
1987 34' Excella
newark , Delaware
Join Date: Jun 2008
Posts: 4
our air conditioner runs well (the fan) but it does not cool the interior. we were told it is a closed system so it cannot be repaired. replacing is not in the budget. any suggestions?
rcmom6 is offline   Reply With Quote
Old 06-26-2008, 12:48 AM   #14
_
 
. , .
Join Date: Dec 2004
Posts: 8,812
Quote:
Originally Posted by moosetags View Post
When running my A/C with my two Honda 2000s, should I use the ECO setting or not?...
clearly there is some variation based on WHICH ac (size/btu) and WHAT ELSE is drawing electric.

dometic advises 3500 w gensets for the 13.5 and 15,000 btu a/c units.

the local honda sales/service shop advises AGAINST using eco mode with the parallel kit.

i LIKE to run the fridge on electric and other gadgets at the same time the a/c is in use...

and with sudden demand needs (like the a/c) voltage DROPS initially if running in eco mode, according to honda.

so 2 easy checks are...

1. does the 'overload light' on the gensets come ON when the a/c kicks in...
2. does a voltage meter show any drop in voltage and for how long?

i've checked the continuous display voltage meter in my unit and voltage does drop to the 103-105 range briefly is using eco mode.

this drop does NOT happen when eco mode is OFF.

so it may be penny wise, pound foolish to use eco during a/c usage or while in parallel operation with large demand gadgets...

it's not clear how much gas is 'saved' in eco mode/parallel when the a/c is on either, but...

these voltage drops aren't good for the a/c and 'overload' isn't good for the gensets...

if not checking voltage drops and overload alerts, the observation that it 'seems to run ok' may be misleading.

with a smaller a/c this may not be an issue, but checking voltage and overload alerts is still prudent.

cheers
2air'
__________________
all of the true things that i am about to tell you are shameless lies. l.b.j.

we are here on earth to fart around. don't let anybody tell you any different. k.v.
2airishuman is offline   Reply With Quote
Old 06-26-2008, 02:27 AM   #15
Rivet Master
 
TBRich's Avatar

 
2006 19' Safari SE
Tucson , Arizona
Join Date: Jun 2007
Posts: 4,627
Images: 64
Quote:
Originally Posted by iHayley View Post
Oooo... tell me more about this "Hard Start Kit"?? I'm looking at buying two of those Honda 2000 generators, but they're quite pricey. I was going to start with just one and see how I did, and then go back for the second later. My big question was if only one was going to be enough to start up the AC.

Hayley
Halyley...Check what size AC you have 11,000 btu or 13,500 btu...I believe 11,000 is Safari standard and 13,500 is the Safari SE standard size...but check to make sure...should be in your owners manual/materials... Of course, the higher the btu rating the more oomph you need...
__________________
TB & Greg and Abbey Schnauzer
AirForums #21900
PastPrez, 4CU/WBCCI
TBRich is offline   Reply With Quote
Old 06-26-2008, 08:07 AM   #16
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
Quote:
Originally Posted by 2airishuman View Post
clearly there is some variation based on WHICH ac (size/btu) and WHAT ELSE is drawing electric.

dometic advises 3500 w gensets for the 13.5 and 15,000 btu a/c units.

the local honda sales/service shop advises AGAINST using eco mode with the parallel kit.

i LIKE to run the fridge on electric and other gadgets at the same time the a/c is in use...

and with sudden demand needs (like the a/c) voltage DROPS initially if running in eco mode, according to honda.

so 2 easy checks are...

1. does the 'overload light' on the gensets come ON when the a/c kicks in...
2. does a voltage meter show any drop in voltage and for how long?

i've checked the continuous display voltage meter in my unit and voltage does drop to the 103-105 range briefly is using eco mode.

this drop does NOT happen when eco mode is OFF.

so it may be penny wise, pound foolish to use eco during a/c usage or while in parallel operation with large demand gadgets...

it's not clear how much gas is 'saved' in eco mode/parallel when the a/c is on either, but...

these voltage drops aren't good for the a/c and 'overload' isn't good for the gensets...

if not checking voltage drops and overload alerts, the observation that it 'seems to run ok' may be misleading.

with a smaller a/c this may not be an issue, but checking voltage and overload alerts is still prudent.

cheers
2air'
so now my thoughts are wandering ..........

could you use a smaller generator or eco mode IF you had a system with AVR (auto voltage regulation?) to maintain the voltage? yes, a little knowledge IS dangerous.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Honda EU2000i dmac Generators & Solar Power 35 06-01-2010 11:09 AM
Honda EU2000 x 2 vs Honda EU3000 and Yamaha 3000 IntegrityAir Generators & Solar Power 43 07-01-2009 11:19 AM
Honda EU 3000 vs 2x Honda EU 2000 vajeep Generators & Solar Power 93 07-23-2008 11:02 AM
honda gen. ? ticki2 Generators & Solar Power 0 09-15-2006 07:30 PM
Running Honda Generators in Parallel Cracker Generators & Solar Power 16 05-16-2004 06:49 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:34 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.