You will not be able to run the ac with one honda 2000.
__________________

__________________
@living.somewhere.yonder | Instagram
SCOTTinNJ is offline   Reply With Quote
Old 08-25-2015, 11:37 PM   #16
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Generator Sizing?

If you have a 15K BTU roof A/C, you will need a minimum of 3000 watts from your generator to start the compressor. A Honda or Yamaha 2000 will 'operate' the A/C, but will not have the transient reserve power needed for the compressor.

We are installing 3000 watt hybrid inverters with our new 400 amp/hour lithium batteries that will start and run a single roof air using a 2000 watt genny.

The inverter supplies the required transient start up amperage for the compressor and the 2000 watt genny takes over to operate the unit.

Very neat and very seamless!!!


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center
Lifeline Batteries**Magnum Inverters
541-490-6357
__________________

__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 08-26-2015, 12:42 AM   #17
3 Rivet Member
 
Tuco's Avatar
 
1988 32' Excella
Ojai , California
Join Date: Aug 2014
Posts: 189
Images: 1
Quote:
Originally Posted by lewster View Post
If you have a 15K BTU roof A/C, you will need a minimum of 3000 watts from your generator to start the compressor. A Honda or Yamaha 2000 will 'operate' the A/C, but will not have the transient reserve power needed for the compressor.

We are installing 3000 watt hybrid inverters with our new 400 amp/hour lithium batteries that will start and run a single roof air using a 2000 watt genny.

The inverter supplies the required transient start up amperage for the compressor and the 2000 watt genny takes over to operate the unit.

Very neat and very seamless!!!


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center
Lifeline Batteries**Magnum Inverters
541-490-6357
What balances the load between the inverters and the generator? I would assume that you get full generator output and any extra current needed is provided by the inverters, is this correct?
__________________
Dave & MJ
1988 32' Excella 1000 (Beauty)
1999 White Dodge SLT Laramie 3500 Dually, 4x4, 5spd, 5.9 CTD 245k+ (The Beast)
Tuco is offline   Reply With Quote
Old 08-26-2015, 12:48 AM   #18
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 5,139
Images: 2
Blog Entries: 5
Generator Sizing?

Who do you call when the inverter craps out in the middle of the woods? I would think a second 2K watt generator for those rare occasions that one might need A/C in Canada would be a more practical and less expensive approach.
If you camp in the interior of BC or anywhere east of the Canadian Rockies in the summer months A/C would sure be nice.


Sent from my iPod touch using Airstream Forums
__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 08-26-2015, 08:49 AM   #19
Moderator
 
DKB_SATX's Avatar

 
2017 26' Flying Cloud
1976 Argosy 28
Alamo Heights , Texas
Join Date: Aug 2006
Posts: 6,400
Images: 1
Blog Entries: 7
Quote:
Originally Posted by TG Twinkie View Post
Who do you call when the inverter craps out in the middle of the woods? I would think a second 2K watt generator for those rare occasions that one might need A/C in Canada would be a more practical and less expensive approach.
If you camp in the interior of BC or anywhere east of the Canadian Rockies in the summer months A/C would sure be nice.


Sent from my iPod touch using Airstream Forums
I would guess it's the same thing you'd do if your generator craps out in the middle of the woods... decide if it's hot enough that it's time to go home.
__________________
David

Zero Gravitas 2017 Flying Cloud 26U | Il Progetto 1976 Argosy 28 Center Bath | WBCCI# 15566

He has all of the virtues I dislike and none of the vices I admire. Sir Winston Churchill
DKB_SATX is online now   Reply With Quote
Old 08-27-2015, 11:10 AM   #20
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 4,799
Images: 8
To start the 15,000 BTU air conditioner an a 27' Airstream, the starting surge of power will require the power associated with the two Honda (or equivalent) 2,000 watt generators as a paired set so one can use the 30 amp power outlet of the companion model into the trailer. Once the air conditioner is running, then a 2,000 watt generator would carry the load.

We are modifying our 23D with 500 watts of solar panels and a Magnum MSH-3012 inverter/charger that could take power from the 300 amp-hour lithium iron phosphate battery to augment the power from a single 2,000 watt Honda Companion (30 amp outlet) to start the 13,500 BTU air conditioner and then keep it running on the generator alone.

Having crossed the age 70 threshold, I can still lift both of the Honda 2,000 watt units one at a time, but the heavier units are now out of my lifting capacity.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic model 30 twin beds, 50 amp service, 900 watt solar system, Centramatics, Dill TPMS, disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 08-27-2015, 11:38 AM   #21
Rivet Master
 
KJRitchie's Avatar

 
2008 25' Classic
Wichita Falls , Texas
Join Date: Nov 2012
Posts: 4,217
When running two Honda 2000 for AC can you run them on Economy mode and they ramp up for the compressor to start and once the compressor is running they switch down to Economy? This is given there are no other loads on the 120v system

If the two Hondas have to run full bore all the time the AC is running how long would the small fuel tanks last?.

I like the idea of the compactness of the Honda 2000 and if we decide to use AC while dry camping just purchase the companion.

I don't think I would like to haul a 3000 generator on/off the back of my Ram 2500 as the truck sits so much higher than a 1/2. Not sure the wife is able to lift half the weight of a Handi or Champion 3000.

Kelvin
__________________
2008 Classic 25fb "Silver Mistress"
2015 Ram 2500 6.7L Cummins. Crew Cab, 4x4, Silver
KJRitchie is offline   Reply With Quote
Old 08-27-2015, 12:24 PM   #22
Rivet Master
 
mefly2's Avatar
 
2015 25' FB Eddie Bauer
Western , ** Big Sky Country ** Montana
Join Date: Feb 2010
Posts: 2,283
After noting the drop in rpms with paired EU2000 gens (one set to eco and the other in standard mode) when the AC compressor switched on as well as the delay in the companion ramping up, we were concerned about the longevity of the AC compressor... so we upgraded to a 3000iS with electric start. It stays in the back of the truck for the season and only gets moved at the beginning and end of the season. I kept one of the 2000s "just in case" but have not used it in two years - it has a semi permanent place in the garage. I would not switch back to a pair of 2000s - if for no other reason than the lowered sound level of the 3000iS ... not to mention the electric start on cold mornings. The single 3000 appears to be more fuel efficient than were our pair of 2000s.

It appeared to us that a single 2000iS could run the AC after it started, but not have the ability to start the AC on our 25. In eco mode, the delay in ramping up the rpms on the companion gen was a huge concern for us and we usually took both gens out of eco mode for starting the AC. It was OK to go back to eco as long as the AC compressor stayed on; but if the AC began cycling on/off, we would again hear the delay in the gens ramping up to the needed demand level. See Lew's note above about transient reserve power [and potential damage during compressor starts].
__________________
mefly2 is offline   Reply With Quote
Old 08-27-2015, 12:38 PM   #23
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,401
Images: 5
Am I wrong, or does Honda not recommend a paired set be run with one in eco and one not? Thought I read that somewhere.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 08-27-2015, 12:43 PM   #24
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,401
Images: 5
Here it is from the Honda manual:

"AC PARALLEL OPERATION
PARALLEL OPERATION CABLE
(optional equipment, see page 70)
Before connecting an appliance to either generator, make sure that it is
in good working order and that its electrical rating does not exceed
that of the receptacle.
Most motorized appliances require more than their electrical rating for
startup. When an electric motor is started, the overload indicator (red)
may come on. This is normal if the overload indicator (red) goes off
within 4 seconds. If the overload indicator (red) stays on, consult your
generator dealer.
Connect the parallel operation cable between the EU2000i
Companion to either an EU2000i or another EU2000i Companion
generator following the instructions supplied with the cable kit.
During parallel operation, the Eco-Throttle switch should be in the
same position on both generators"



and this:

"Appliances with large start-up power demands may not allow the
engine to reach normal operating rpm when they are connected to the
generator. Turn the Eco-Throttle to the OFF position and connect the
appliance to the generator
. If the engine still will not reach normal
operating speed, check that the appliance does not exceed the rated
load capacity of the generator.
If high electrical loads are connected simultaneously, turn the
Eco-Throttle switch to the OFF position to reduce voltage changes.
The Eco-Throttle system is not effective for use with appliances or
tools that require only momentary power. If the tool or appliance will
be turned ON and OFF quickly, the Eco-Throttle switch should be in the
OFF position."
__________________

__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inverter sizing for factory convection/microwave oven? myoung Electrical - Systems, Generators, Batteries & Solar 11 10-03-2005 08:24 PM
sizing a converter MarkR Electrical - Systems, Generators, Batteries & Solar 10 05-26-2005 01:09 PM
AC Sizing Over59 Furnaces, Heaters, Fireplaces & Air Conditioning 5 04-28-2005 05:41 PM
Furnance sizing Over59 Furnaces, Heaters, Fireplaces & Air Conditioning 1 07-06-2004 01:18 PM
Tire sizing question casarodante Tires 5 07-02-2002 11:19 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:42 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.