Generator Questions from a Rookie

Hi Everyone.
First let me say how helpful so many of you have been. I am new to all of this, but I am learning, thanks to many of you.

Ok...
I have purchased a Honda EU2oooi generator and the companion EU2000i.
I have them connected with parallel cables and everything works fine.

Supposedly, I am able to run just about anything in my 28' Safari with this set up. Here is my current dilemma. When I am hooked up to shore power everything works...microwave, Air Conditioning, Fridge, convenience outlets etc. However, when I disconnect from shore power and hook up to the generators I am not getting power to the microwave, Air Conditioning, and convenience outlets etc. I have the proper adapter to plug into the 30 amp twist lock receptacle. So as far as I know I have things hooked up properly but I still do not get any power into the Stream. The microwave does not work and the fridge will not work on the AC setting.

What am I doing wrong? Thanks in advance.

Bert
bertheep is offline   Reply With Quote
Old 10-09-2010, 07:18 AM   #2
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
I would suspect the adapter of being bad. I would check the output of the generators with a meter, and if the output is good, I'd change the adapter.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 10-09-2010, 07:29 AM   #3
3 Rivet Member
 
dick&claire's Avatar
 
2011 30' Flying Cloud
North Falmouth , Massachusetts
Join Date: Jan 2008
Posts: 144
The problem sounds like it is in the generators. Start by taking a multimeter and see if you are getting 120-130 volts at three places: the generator outlet itself, the outboard side of the adapter that plugs into the generator, and at the end of the 30 amp cord where it enters the trailer.

I don't know the innards of Airstreams electrical system but use one of those plug in monitors to make sure your polarity and ground are OK.
__________________
Dick and Claire Wiklund
North Falmouth, Massachusetts
"Judgement is based on experience and experience is based on poor judgement"
dick&claire is offline   Reply With Quote
Old 10-09-2010, 07:37 AM   #4
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
One more thing, but may be too obvious...make sure any circuit breakers on the generators are not tripped.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 10-09-2010, 09:34 AM   #5
Moderator
 
moosetags's Avatar

 
2015 25' FB Flying Cloud
2012 23' FB Flying Cloud
2005 25' Safari
Santa Rosa Beach , Florida
Join Date: Jul 2006
Posts: 13,159
Images: 5
Greetings from the Florida Panhandle

I also have 2 of t Honda 2000's, and I had a similar problem a couple of years ago. Mine had the very same symptoms, but they had worked previously. I have the external (add on) parallel unit. The 30 amp breaker in this unit had gone bad. In the new companion generator, there is probably a built-in 30 amp breaker that may be tripped or is not functioning at all like mine was.

As previously posted your RV plug adapter could be bad.

Check the generator out. Using a 30 to 20 amp adapter, plug your Airstream into one of the 20 amp outlets on one of the generators. Test your 110 outlets, your television, refrigerator, etc. Test each of these outlet successively. If these all work properly, it is one of the two problems outlined above.

Let us know what happens.

Brian
__________________
SuEllyn & Brian McCabe
WBCCI #3628 -- AIR #14872 -- TAC #FL-7
2015 FC 25' FB (Lucy) with ProPride
2020 Silverado 2500 (Vivian)
2023 Rivian R1T (Opal)
moosetags is offline   Reply With Quote
Old 10-09-2010, 01:00 PM   #6
2 Rivet Member
 
Ely , Minnesota
Join Date: Jul 2010
Posts: 59
Thanks Folks...
I have a feeling it is either the locking adaptor or the 30 amp receptacle on the generator that is bad.

I will try the 30 to 20 amp adaptor in one of the 20 amp outlets. Good advice.
bertheep is offline   Reply With Quote
Old 03-15-2011, 02:15 PM   #7
4 Rivet Member
 
Zigidachs's Avatar
 
2017 23' International
Ridgefield , Washington
Join Date: Oct 2010
Posts: 306
Images: 1
Reverse polarity?

We dry camped for the first time in our new AS with the Honda combo 2K units (wired correctly in parallel) and found that when plugged into the front access electrical port that the current input monitor inside the AS alarmed. The alarm indicated a possible polarity problem?!

All the appliances worked fine including the microwave and coffee pot while connected to the generators.

When in a camp ground I connected the shore power to the front of the AS and there was no indication of a problem, so that would rule out the AS port as ? defective.

The catch on this dilemma is that I ran the current from the twin Hondas through a Surge Guard as I always do......! Any ideas on what to do next?

I am of course concerned about the "polarity" warning when connected to the generators, but if there had indeed been a problem the Surge Guard should have detected it and cancelled transmission into the AS. no?
Zigidachs is offline   Reply With Quote
Old 03-15-2011, 02:21 PM   #8
4 Rivet Member
 
Zigidachs's Avatar
 
2017 23' International
Ridgefield , Washington
Join Date: Oct 2010
Posts: 306
Images: 1
ps

As an aside, we installed a 145 Watt solar panel. We have 2 "27" AGM batteries which carry up to 14.4 V. Running the furnace overnight ( cold this time of year in Yosemite) drained the batteries to 1/2, and during the day the panel restored the battery to 3/4 of full charge. Seems like an adequate recharge. Running the Honda's for an hour seemed to bring the batteries up to enough charge to run the furnace the next night.

Zigi
Zigidachs is offline   Reply With Quote
Old 03-15-2011, 03:39 PM   #9
2 Rivet Member
 
2011 27' FB Classic
Masontown , West Virginia
Join Date: Oct 2010
Posts: 77
Don't Panic

Zigi--I can't do justice in a response due to my lack of technical smarts, but the short of it is that I suspect your warning is caused by your system's not detecting a proper ground from your Honda's.

Had the problem and ignored it, but finally fixed it by creating a "shunt" that had the appearance of creating a ground - methink this is done by running the ground and neutral (white) together by one of several means. Your generators do not create a ground to earth as your monitoring system expects to "see". This is normal and short of creating an earth ground (not practical or recommended), you'll have to do a work around.

Do a Google search for "Honda generator grounds" and you'll find several sources for a fix - -I know there is one on the Woodall discussion site and I also think you'll find one on the Honda discussion group on Yahoo.

Check the several sources and/or others smarter than I who will chime in here.

Good luck, Bill
__________________
Bill & Dorothy Reeves
2011 27FB
2016 F250 6.2L
TAC # WV-2
MountaineerStreamer is offline   Reply With Quote
Old 03-15-2011, 06:45 PM   #10
Rivet Master
 
Mexray's Avatar
 
1978 28' Ambassador
Morada , California
Join Date: Jan 2006
Posts: 1,584
Having only one 2K Honda, we use it to recharge our batteries (using the AS shore power 30 amp connection) all the time - it works great for this purpose, and a 2nd Honda would ONLY be needed to run the AC unit...

We also fire up the Honda to use the microwave - works great...

Those of you with 'paired' Honda's - do you run them both all the time? If so, why? It would seem to me running both for anything but powering the AC, is a waste of fuel and extra wear and tear on the 2nd unit...

Our old AS isn't equipped with the 'generator option' I've seen on new AS's - As I understand it, the 2nd (generator) receptacle is used for the generator 'input' to the AS - as such, is there a 'control' switch or relay that connects the 2nd receptacle to the AS's AC circuits? Or are both AC 30 amp input receptacles merely wired in parallel? If there's a 'control' device involved, I look here for AC input problems, as well...
__________________
Ray & Pat; Morada, CA
Mexray is offline   Reply With Quote
Old 03-16-2011, 06:48 AM   #11
2 Rivet Member
 
2008 19' International CCD
Spring , Texas
Join Date: Sep 2009
Posts: 60
We had a problem with one our two Hondas right after purchase; no power. Took it back to the dealer for warranty repair; loose wire.

Also; check the RV adapter plug and the receptacle.

Ed
eleighj is offline   Reply With Quote
Old 03-16-2011, 10:50 AM   #12
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
As Bill points out correctly upthread the alarm is due to the floating ground because of the absence of bonding between ground and neutral.

With shore power the ground and neutral are connected together (bonded) somewhere in the campground's wiring. There can still be a small to moderate voltage between the neutral and ground because of the voltage drop between the bonding point and the shore power receptacle.

With a generator the ground is isolated and not connected to neutral anywhere. In theory, if you have a transfer switch, the transfer switch is supposed to bond neutral to ground when the generator is supplying power. Not all of them do.

Some older generators bond the neutral.

RVers blame all kinds of failures on bonding problems though IMO there's rarely any relationship (Just as the guy who sells you an air conditioner likes to blame failures on low voltage, the guy who sells you a generator likes to blame failures on grounding problems. In both cases they find it inconvenient to blame a shoddy product). The lack of bonding can potentially create a safety problem, as can the lack of a true ground. The extent to which this is a practical problem in the real world of RVing is disputed.

To do it by the book in the U.S. you're supposed to drive a ground rod 6' deep and connect a ground wire from that to the generator, and then bond the ground and neutral at either the transfer switch or breaker panel. But, you can't bond at the breaker panel when you plug into shore power.

I don't think I've ever seen that done. I don't do it.

And I don't believe that bonding in an RV being powered occasionally by a generator, with modern wiring and GFCIs, provides a safety benefit, in the absence of a ground rod. In fact it may worsen the risk of shock.

The situation is different in a campground because the ground connection is shared and proper bonding prevents bad stuff from happening due to a combination of wiring faults in two or more trailers.

By international standards the way grounding is handled in the U.S. is kooky even in houses and commercial buildings. The RV, campground, and generator portions of the NEC being unruly stepchildren of the more widely applied portions of the code means that these regulations are even worse.
Jammer is offline   Reply With Quote
Old 03-16-2011, 11:36 AM   #13
3 Rivet Member
 
Currently Looking...
Austin , Texas
Join Date: Mar 2008
Posts: 213
Jammer,

I believe the Honda and Yamaha inverter generators have bonded neutrals. The generator in question is a Honda 2000 being run in parallel mode.

When for example a Yamaha ef6300isde is used as a backup home generator, Gen Tran requires a Switched Neutral Kit be added to their panel to overcome the bonded neutral of the Yamaha inverter generator unless the owner removes a wire from the generator to create a floating neutral. The wire must be put back when the generator is being used as a portable generator.

Barry
pattonsr is offline   Reply With Quote
Old 03-16-2011, 03:43 PM   #14
3 Rivet Member
 
Currently Looking...
Austin , Texas
Join Date: Mar 2008
Posts: 213
I believe my previous post regarding a Yamaha EF6300iSDE is accurate. Other than that model, all bets are off as to Honda and Yamaha inverter generators.

I found the following information in a Yamaha document regarding Yamaha inverter generators. EF1000iS, EF3000iSE, EF3000iSEB have floating neutrals. EF2000iS, EF2400ISHC, EF4500iSE, EF6300iSDE have bonded neutrals. Very confusing information.

I have not found such a document for Honda inverters except that everyone says the EU2000 has a floating neutral. Other people say that to parallel two generators the neutral must be floating. But the Yamaha EF2000iS can be paralleled but the Yamaha document says it has a bonded neutral.

I think I will bow out now since my head is exploding.
pattonsr is offline   Reply With Quote
Old 03-16-2011, 05:01 PM   #15
4 Rivet Member
 
Zigidachs's Avatar
 
2017 23' International
Ridgefield , Washington
Join Date: Oct 2010
Posts: 306
Images: 1
Honda grounds

YOU GUYS ARE GOOD!!!!!!

I thought I knew a little about electricity, but I have been "schooled" well. I did not know the difference btwn a floating ground and a bonded ground till now. I found this comment on another site:

The question was about the need to "bond" the ground on a 2k gen set..and the answer was a resounding no----for these reasons:


"The reason it shows an open ground is because the 3 lamp testers use the ground/neutral bond at the service entrance to indicate that the ground is good. Most portable inverter 120v generators do not bond the neutral (code does not require it) so the tester indicates a problem that doesn't exist. The generator's receptacle ground terminal is attached to the frame of the generator so it still protects you from a failure within the generator that causes a fault to the case.

Some individuals have made adapters that bond the neutral (wide blade) to the ground so that their testers work or, more often, so their autoformer doesn't shut down the power because it detects an open ground, but this is not necessary for safety."

Thanks to all who responded to my question.....I'll buy the next round!!!! Zigi
Zigidachs is offline   Reply With Quote
Old 04-18-2011, 05:42 PM   #16
4 Rivet Member
 
fltlevel510's Avatar
 
2004 30' Classic Slideout
Between Here , And There
Join Date: Feb 2005
Posts: 379
Ryobi Generator

Was walking through the Home Depot today and noticed Ryobi now has a 2000w generator priced at $599. I tried to find out what the noise level was but had no luck. Here is a link.

fltlevel510 is offline   Reply With Quote
Old 04-18-2011, 07:04 PM   #17
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
Quieter the better, some of those units are flat-out obnoxious.
Mike Leary is offline   Reply With Quote
Old 04-18-2011, 07:18 PM   #18
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Ryobi 2000 Watt Inverter Generator - RYi2000T at The Home Depot

This link says 59dB. Who's gonna be the Guinea Pig on this one?
dznf0g is offline   Reply With Quote
Old 04-18-2011, 08:23 PM   #19
Rivet Master
 
DreamStreamr's Avatar
 
2005 25' International CCD
Fleetwood , North Carolina
Join Date: Aug 2005
Posts: 687
Images: 38
Send a message via Skype™ to DreamStreamr
Why buy a 2,000? It isn't enough to do more than charge the batteries and a 1,000 does this just fine for much less weight, lower fuel consumption, smaller storage space.

I wouldn't consider altering my Yamaha inverter generator's engineered design or safety features internally or externally. It is flirting with disaster to mess with good engineered designs on any listed assembly.

I cannot find it just now, but B Leipper did a superb job assessing the "need" and risks of altering the ground on portable generators. I'm pretty sure it is on this air forums. Here is a related post of his explaining well why not bond neutral and ground: http://www.airforums.com/forums/f37/...tml#post557206
__________________
Chasing 75 Degrees,

Jim N5RTG
dreamstreamr.com
DreamStreamr is offline   Reply With Quote
Old 04-18-2011, 09:00 PM   #20
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Quote:
Originally Posted by DreamStreamr View Post
Why buy a 2,000? It isn't enough to do more than charge the batteries and a 1,000 does this just fine for much less weight, lower fuel consumption, smaller storage space.

I wouldn't consider altering my Yamaha inverter generator's engineered design or safety features internally or externally. It is flirting with disaster to mess with good engineered designs on any listed assembly.

I cannot find it just now, but B Leipper did a superb job assessing the "need" and risks of altering the ground on portable generators. I'm pretty sure it is on this air forums. Here is a related post of his explaining well why not bond neutral and ground: http://www.airforums.com/forums/f37/...tml#post557206
Well, I'd prefer to use my 3 stage converter to charge the batteries and it draws 900 watts. Which 1000w gen are you suggesting and is it 1000w rated continuous or 800 watts/1000w?
dznf0g is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator Questions Mimimedia Generators & Solar Power 13 01-28-2010 02:35 PM
Generator Newbie Questions. ROBERTSUNRUS Generators & Solar Power 24 01-19-2010 01:21 PM
electrical, generator questions.... lvcat2004 Boondocking 5 07-28-2009 03:29 PM
Generator Questions .... again silverbambam Generators & Solar Power 9 04-02-2008 09:46 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:06 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.