Hi, totally confused here, we have a 2015 fb signature with 3-100 watt solar panels, wich takes care of some of the light stuff. We also have a silly micro wave, not my choice as I would have preferred having your standard gas stove. I purchased a new 3000e watt Honda, then was told I could not run my air conditioner, as it needs a 30 amp, and the 3000 watt generator would/could not be strong enough to do the job. I see here that people are using the 2000e generator to power the air con... what do I need to run the air con is what I'm asking, as the microwave will be chucked out soon and replaced
thanks
if you can shed some clear answers without amps or watt talk
cheers
Wakefield
__________________

__________________
wakefield is offline   Reply With Quote
Old 03-12-2016, 10:11 PM   #30
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Quote:
Originally Posted by wakefield View Post
Hi, totally confused here, we have a 2015 fb signature with 3-100 watt solar panels, wich takes care of some of the light stuff. We also have a silly micro wave, not my choice as I would have preferred having your standard gas stove. I purchased a new 3000e watt Honda, then was told I could not run my air conditioner, as it needs a 30 amp, and the 3000 watt generator would/could not be strong enough to do the job. I see here that people are using the 2000e generator to power the air con... what do I need to run the air con is what I'm asking, as the microwave will be chucked out soon and replaced
thanks
if you can shed some clear answers without amps or watt talk
cheers
Wakefield
This is as simple as it gets, as it IS all about watts and amps!

You have been given some erroneous information. I have folks running a 13.5K roof A/C with a Yamaha 2400 watt unit. Even a 15K unit will not draw over 15-16 amps @120VAC and ambient temperatures of 90ºF (check the data plate on your A/C unit if you need verification).

There should be no issues with a 3000 watt Honda and your roof air. You also have a 20 amp breaker on your A/C circuit….NOT A 30 A breaker.
__________________

__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 03-12-2016, 10:25 PM   #31
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 4,799
Images: 8
We have a Magnum MSH-3012 hybrid inverter in our 23D that can draw the additional power necessary to start the 13.5K BTU roof air conditioner from the 300 amp-hour lithium battery and then the Honda 2,000 watt generator can keep it running. This magic trick works if the batteries are close to fully charged as the Magnum will use the available AC power to charge the battery if the 500 watts of solar is not doing the job.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic model 30 twin beds, 50 amp service, 900 watt solar system, Centramatics, Dill TPMS, disc brakes, 16" tires & wheels
switz is online now   Reply With Quote
Old 03-13-2016, 09:00 AM   #32
4 Rivet Member
 
GammaDog's Avatar
 
2014 25' FB Eddie Bauer
Vero Beach , Florida
Join Date: Sep 2014
Posts: 353
Images: 26
Wakefield: Lewster has it right (as usual... thanks, Lewster for your many posts).

Let me add a couple of points. There is a key phrase in sizing generators for Airstreams or other RVs. It's "at the same time". Your 3000 watt Honda (sorry... I had to use 'watt' at least once) won't power everything in your trailer "at the same time". In my experience, even a 30 amp (oops... I did it again) shore power connection doesn't allow me to run everything onboard at the same time. As evidence, I occasionally trip a 30 amp breaker if I run AC, microwave, etc all at once.

However, your 3000 Honda should run the AC just fine provided you don't also run the microwave or other big loads which may even include your converter for battery charging.

How do you manage load you ask? The simple way is the mental manual method. For example, remember not to turn on the microwave while the AC is running on generator. The sure fire method is to use the breakers in your panel to actually disconnect loads you don't want to come on.

As for the solar capability you mentioned, it's a great tool to charge your batteries automagically from the sun, but the output of your three panels is only 10% of what your one generator can deliver. They are truly separate capabilities with the solar focused on keeping batteries topped off for the 12volt systems onboard while the generator can support the 120volt loads. There is a point of connection between these two systems. It's your inverter which can run light 120volt lads from your 12volt batteries for limited periods of time. The AC and microwave (and many portable appliances) are too much load for the typical inverter.

I hope that helps.
__________________
GammaDog is offline   Reply With Quote
Old 03-13-2016, 01:00 PM   #33
Rivet Master
 
tjdonahoe's Avatar
 
2013 31' Classic
billings , Montana
Join Date: Feb 2010
Posts: 1,843
The 3000 watt honda will be hard pressed to run the ac, especially on a hot day..best to use shore power for the ac......
__________________
tjdonahoe is offline   Reply With Quote
Old 03-13-2016, 04:09 PM   #34
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Quote:
Originally Posted by tjdonahoe View Post
The 3000 watt honda will be hard pressed to run the ac, especially on a hot day..best to use shore power for the ac......

Are you speaking from experience or pure conjecture????

A 3000 watt generator has a 25 amp output with a higher available transient amperage level. ANY RV air conditioner is wired to a 20 amp circuit breaker using 12AWG cable......... which is more than sufficient to start and run ANY rooftop RV unit.






Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 03-13-2016, 07:21 PM   #35
2 Rivet Member
 
Oak Harbor , wa
Join Date: Mar 2015
Posts: 42
We have a 2015 25FC, and use a single Honda 2000, even runs the air conditioning. Just remember to turn off battery charger and turn refer to gas. Otherwise the gen will attempt to run all these other loads and the AC and won't make it.
__________________
Stormalong is offline   Reply With Quote
Old 03-13-2016, 07:54 PM   #36
Rivet Master
 
kscherzi's Avatar
 
2013 27' FB International
El Dorado Hills , California
Join Date: Jan 2013
Posts: 1,136
Images: 24
I'm shocked. I've never heard of anyone running their AC off a 2,000 watt generator alone. Do you have the 13,500 or 15,000 BTU AC?
__________________
kscherzi is offline   Reply With Quote
Old 03-13-2016, 08:13 PM   #37
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
I've never seen that either. Not challenging the poster, but I have seen some very large transient loads when the compressor starts. When I set up a lithium battery and a Magnum 3000 watt hybrid inverter, the roof A/C will show a transient of 150 -165 amps coming from the batteries on start-up in addition to a Honda or Yamaha 2000 running and the trailer connected to it.

The hybrid inverter will add whatever amperage is necessary for 'load support' to allow the load (in this case, the compressor) to start. That translates to an additional 14-15 amps that is provided by the Magnum, added to the 16.7 amp maximum capacity of the Honda for a total of approx. 32 starting amps.

After the compressor has started, the load support from the Magnum diminishes to zero and the Honda takes over the operation of the A/C. I have seen the generator go into overload fault if the Magnum is not in load support mode, which is the equivalent of running the A/C on a 2000 watt generator alone.

Just my unbiased observations.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 03-14-2016, 07:08 AM   #38
Rivet Master
 
tjdonahoe's Avatar
 
2013 31' Classic
billings , Montana
Join Date: Feb 2010
Posts: 1,843
Quote:
Originally Posted by lewster View Post
Are you speaking from experience or pure conjecture????

A 3000 watt generator has a 25 amp output with a higher available transient amperage level. ANY RV air conditioner is wired to a 20 amp circuit breaker using 12AWG cable......... which is more than sufficient to start and run ANY rooftop RV unit.






Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
What I was trying to say is I thought the 3000 watt honda was working pretty hard running the ac, with everything switched to propane , I would rather have a 4500watt as it might not be working as hard....
__________________
tjdonahoe is offline   Reply With Quote
Old 03-15-2016, 10:13 AM   #39
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 4,799
Images: 8
The challenge with the larger Honda generators is the weighted keeps increasing with wattage output gets close to 300 pounds for the 7,500 watt unit. I can still slowly manhandle the 50 pounds of the 2,000 watt Hondas. Not interested in anything heavier.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic model 30 twin beds, 50 amp service, 900 watt solar system, Centramatics, Dill TPMS, disc brakes, 16" tires & wheels
switz is online now   Reply With Quote
Old 03-16-2016, 03:54 AM   #40
Rivet Master
 
tjdonahoe's Avatar
 
2013 31' Classic
billings , Montana
Join Date: Feb 2010
Posts: 1,843
Quote:
Originally Posted by switz View Post
The challenge with the larger Honda generators is the weighted keeps increasing with wattage output gets close to 300 pounds for the 7,500 watt unit. I can still slowly manhandle the 50 pounds of the 2,000 watt Hondas. Not interested in anything heavier.
I know you are right !
__________________

__________________
tjdonahoe is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Convert Frt Vent to Power on 2007 25FB 2dabeach Electrical - Systems, Generators, Batteries & Solar 3 10-10-2014 12:29 AM
2014 25FB FC Pioneer radio power off? btlayton 2009-2015 Flying Cloud 44 07-29-2014 11:52 AM
If I dont need a battery power can dispense with univolt? can I dispense fast fredy Batteries, Univolts, Converters & Inverters 7 04-14-2014 04:46 PM
The Can Can Can travelfables Member Introductions 3 02-01-2014 02:56 PM
"I think I can, I think I can, I think I can".... 2Rhinos Repairing/Replacing Floor &/or Frame 14 08-17-2011 02:39 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:24 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.