I will be trying to set up electrical service for my trailer at the place I park it. This location is about 150' from the main breaker in the house. I would like to install underground wiring enclosed in PVC from the parking area to the house breaker box. The parking area would include a plug for my 31'1983 excella,and two lights overhead and plugs for my boat charger and a extra one for whatever. I have a air conditioner and the normal appliances in the trailer. What size breaker in the breaker box would I use? What size wire to run the distance from the house to insure proper current. Any input would be appreciated.
__________________

__________________
Tom C.
Okiegent is offline   Reply With Quote
Old 06-14-2010, 02:22 PM   #2
3 Rivet Member
 
1986 25' Sovereign
Plant City , Florida
Join Date: Mar 2010
Posts: 225
I have done this exact same thing. I ran a 220 50amp sub panel to the parking barn and then ran all of my power out of this to my 30amp rv plug as well as over head lights and convenience outlets. With 150' run you have to account for voltage drop. If you decide to to run 220, then you can use #4 wire. For this you will need two hots a neutral and a ground. (2 black, 1 white, 1 green)

If you decide to only run 110volts you will need to upsize the wire to #2 for the run. Keep in mind that you can derate the neutral to one size smaller #4 and the ground to #10.

You will need to use carlon (the gray pvc).
__________________

__________________
ck21084 is offline   Reply With Quote
Old 06-14-2010, 02:33 PM   #3
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
ck21084 - I assume you ran copper wire? Regardless, I agree that voltage drop has to be accounted for.

Here's a voltage drop calculator which may help the effort.

Okiegent - be advised that the materials alone (with the price of metal) is going to make this an expensive project.

Tom
TomW is offline   Reply With Quote
Old 06-14-2010, 02:40 PM   #4
3 Rivet Member
 
1986 25' Sovereign
Plant City , Florida
Join Date: Mar 2010
Posts: 225
Quote:
Originally Posted by TomW View Post
ck21084 - I assume you ran copper wire? Regardless, I agree that voltage drop has to be accounted for.

Here's a voltage drop calculator which may help the effort.

Okiegent - be advised that the materials alone (with the price of metal) is going to make this an expensive project.

Tom
Correct! Copper only!

I think #2 is around $1.30~$2.00 a foot. depending on how you go it could be $757.50 just for wire ( these prices are from my local lowes) an electric supply house is cheaper.
__________________
ck21084 is offline   Reply With Quote
Old 06-14-2010, 03:03 PM   #5
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,119
You may find that aluminum cable is cheaper, even though you have to go up a size.
__________________
Jammer is offline   Reply With Quote
Old 06-14-2010, 03:55 PM   #6
3 Rivet Member
 
Okiegent's Avatar
 
1983 31' Excella
Choctaw , Oklahoma
Join Date: Dec 2009
Posts: 156
Images: 14
I appreciate your quick reply. Your answers have got my mind to thinking here. We have a local supply house who has wire it would seem a little cheaper. Copper 2 hot and a neutral would run me around 250.00 for 150' Aluminum would be around 1.20 a foot x 3 The copper would come as a package so I would not have to buy three wires.I still do not know what I am doing here just yet. I will do some more home work. I will get back to you all.
__________________
Tom C.
Okiegent is offline   Reply With Quote
Old 06-14-2010, 04:12 PM   #7
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
We're creeping up on a little pucker factor here.

Quote:
Originally Posted by Okiegent View Post
... The copper would come as a package so I would not have to buy three wires..
Be careful. Packaged wire gets tough to fish through a PVC pipe over long distances. Nothing sux worse than not being able to fish wire through pre-laid conduit.

Another option your may want to consider is buying "packaged" wire suitable for burying instead of fishing through electrical PVC.

Tom
TomW is offline   Reply With Quote
Old 06-15-2010, 05:04 AM   #8
3 Rivet Member
 
Okiegent's Avatar
 
1983 31' Excella
Choctaw , Oklahoma
Join Date: Dec 2009
Posts: 156
Images: 14
Quote:
Originally Posted by TomW View Post
Be careful. Packaged wire gets tough to fish through a PVC pipe over long distances. Nothing sux worse than not being able to fish wire through pre-laid conduit.

Another option your may want to consider is buying "packaged" wire suitable for burying instead of fishing through electrical PVC.

Tom
Yes I had thought of that Tom. I wanted to try and save as much as possible on the project and romax #8 in the carbon PVC seemed reasonable at this point . I am thinking I will also do as CK recommended and run 110 and do a 30 amp service instead of a 50 amp.I will mull it over some more though. We are leaving Friday for ten days. When we get back I am sure I will have more questions. Thanks for all the information at this point. Have a great day all.
__________________
Tom C.
Okiegent is offline   Reply With Quote
Old 06-15-2010, 08:01 AM   #9
3 Rivet Member
 
1986 25' Sovereign
Plant City , Florida
Join Date: Mar 2010
Posts: 225
Quote:
Originally Posted by Okiegent View Post
Yes I had thought of that Tom. I wanted to try and save as much as possible on the project and romax #8 in the carbon PVC seemed reasonable at this point . I am thinking I will also do as CK recommended and run 110 and do a 30 amp service instead of a 50 amp.I will mull it over some more though. We are leaving Friday for ten days. When we get back I am sure I will have more questions. Thanks for all the information at this point. Have a great day all.
I know that money can be tight but, you mentioned that you wanted to run a boat charger, a few outlets and a couple of lights. These items could pull more than the service would allow with the RV plug at 30 amps you could burn the wire up, esp with #8 and a 30amp circuit.

As for direct burial cable, it has always been more expensive and much harder to service if there ever is an issue. Ask me how i know. (conduit would have kept the shovel from being blown out of my hand.)
__________________
ck21084 is offline   Reply With Quote
Old 06-15-2010, 03:22 PM   #10
3 Rivet Member
 
Okiegent's Avatar
 
1983 31' Excella
Choctaw , Oklahoma
Join Date: Dec 2009
Posts: 156
Images: 14
CK My thought was. That an air conditioner only requires around 30 amp's to get started. Once started and cycling it would probably pull 15 to 20 amp's. Now I know the boat charger want pull more than say 15 amp's, probably 3 amp's to be real. Then two lights and a convenience plug 20 amp's. I don't think I will ever have my air conditioner running and both outside lights on and the receptacles all utilized at the same time. So I figured that 30 amp service would work. #8 would be plenty for 30 amp service. Now like I said I am mulling all the great advice over though. I have not made a decision yet.
__________________
Tom C.
Okiegent is offline   Reply With Quote
Old 06-15-2010, 03:35 PM   #11
Rivet Master
 
clancy_boy's Avatar
 
2003 22' International CCD
Kiln , Mississippi
Join Date: Dec 2005
Posts: 2,780
Images: 8
It might be much easier to lay all of your wire out and slide the PVC conduit over it and glue together, then roll it into the trench and do the short connections on each end to fit. I realize this is not the pro method but it works for the DIY types like me that have little experience pulling cables in conduit. 150 feet, it's only 6 pieces of 20 foot conduit.

Never short change yourself on the wire size - always go bigger. The tools and equipment you burn up over the years will cost alot more than the pennies difference in cable costs. Think of it this way, if you do it yourself - you are already saving the cost of an electrician - that's alot of savings verses the cost of materials alone.

Aluminum wire requires special connectors and if your house power box is not rated for aluminum wire you cannot use it. Go copper and save yourself the headache.
__________________
Michael & Tina with Layla and Preston BZ
The family has grown.
2003 22' INTERNATIONAL CCD
clancy_boy is offline   Reply With Quote
Old 06-15-2010, 05:51 PM   #12
Rivet Master
 
Smartstream's Avatar

 
1982 28' Airstream 280
Port Angeles , Washington
Join Date: Aug 2008
Posts: 1,371
I don't want to beat a dead horse but go bigger. When you spend a few bucks for a job like this you only want to do it once. What you want to run today, battery charger and a few lights may change in the future if you get new, bigger or more toys.

I agree with ck21084 go for 50 amp 220. You never know what you might need in the future. A simple weld repair will make it worthwhile. You may not have a welder but needing a job done gets easier if you rent a welder or if a friend brings his welder or other tools over. A compressor to inflate a flat tire, it all takes power.

If you run direct burial cable and bury it 24" I hope you never need to dig that deep that you would hit it with a shovel. Also take pictures and make a sketch of where your wire is buried in case you do have to work around it in the future. Who knows you may sell the place some day and the buyer will have a big Moho with a 50 amp service and that plug will make the sale.

Good luck, Dan
__________________
Smartstream is offline   Reply With Quote
Old 06-15-2010, 10:31 PM   #13
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 5,139
Images: 2
Blog Entries: 5
If you are running that far, I would slide the conduit over the wire one stick at a time, then just be carefull not to over do it with the glue. Once all the pipe is assembled , then just slide it in the trench. I'm not sure but I don't think your trailer requires 220 volts. Make sure you know the requirement and that you have met it before turning on the power. If it is wrong you will probably let the smoke out of some stuff. Since electrical devices work on smoke, if the smoke is released, they won't work any more. LOL.
__________________
TG Twinkie is offline   Reply With Quote
Old 06-16-2010, 06:54 AM   #14
3 Rivet Member
 
Okiegent's Avatar
 
1983 31' Excella
Choctaw , Oklahoma
Join Date: Dec 2009
Posts: 156
Images: 14
It is great to hear so many genuine responses to the post. That was what I was needing and looking for. I wanted to be sure that the job was done right and I would have no trouble. All of the post have been on target in my thinking. As well as enlightening me on what size of wire and service to run. All of this has been very helpful. Thanks to all of you for your advice. I will keep you posted when I start the project.
__________________

__________________
Tom C.
Okiegent is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service RedSHED Off Topic Forum 0 11-09-2007 07:08 PM
For electric for genration hase to be oun for electric RichardT Electrical - Systems, Generators, Batteries & Solar 7 12-05-2005 09:05 PM
Service Scott Hopkin Commercial Listings 6 04-07-2005 08:08 AM
Electric or Gas electric fridge replacement?? tin can luv Refrigerators 26 03-22-2004 10:50 AM
service... canny_banjo_man Airstream Motorhome Forums 6 11-12-2002 06:52 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.