I seem to have some issues with keeping my pilot lit. The unit lights ok, but frequently extinguishes itself after heating the water tank. I have checked and adjusted both the pilot flame and air shutter adjustment...both appear to be correct but still don't like to consistantly work unattended.
The unit appears to be the original equip. (I am the second owner, and the AS was always serviced by dealer) Bowen heater and Robertshaw control, but I'm reluctant to R&R if all I need is a cleaning, etc.
Thanks in advance
Sometimes the pilot flame gets pulled off the thermocouple. This may happen right when the water gets hot and the main jet goes off. On a prior trailer, I had to bend the thermocouple bracket a bit to keep it in the pilot flame when this happened. I had a similar problem with a prior refrigerator where the flame wasn't quite on the thermocouple at all times.
__________________
John W. Irwin
2005 Classic 28 "Sabre-Dog III"
2004 Silverado 2500HD Duramax/Allison
WBCCI Region 9 Webmaster, #9632
Wow! thanks for the prompt reply!
At the risk of sounding ignorant (a risk I hope I don't run too often ;-) ), is the thermocouple the small tubular unit w/ the other lead into the control unit and directly above the pilot flame?
Originally posted by Marko69AS Wow! thanks for the prompt reply!
At the risk of sounding ignorant (a risk I hope I don't run too often ;-) ), is the thermocouple the small tubular unit w/ the other lead into the control unit and directly above the pilot flame?
Correct. The thermocouple has to stay in the flame at all times to generate the small electrical potential that keeps the gas valve actuated. If the flame is pulled off, even momentarily, the valve will shut off.
Here in Texas. a lot of folks have problems with high winds pulling the flame away and the WH going off. My old Scamp did that sometimes until I did some bending to keep the flame playing on the thermocouple better.
__________________
John W. Irwin
2005 Classic 28 "Sabre-Dog III"
2004 Silverado 2500HD Duramax/Allison
WBCCI Region 9 Webmaster, #9632
I should have mentioned that sometimes thermocouples do get weak and sometimes totally fail. Years of being in the flame and long periods of exposure to the elements will ultimately eat away the metal sheath. They only cost a few dollars to replace.
__________________
John W. Irwin
2005 Classic 28 "Sabre-Dog III"
2004 Silverado 2500HD Duramax/Allison
WBCCI Region 9 Webmaster, #9632
This sounds like good advise...thanks. Not only is the thermocouple farther away from the pilot flame than the recommended pilot flame height, the water heater is on the windy side of the trailer.
I went out a few weeks back with my newly installed atwood water heater.
I blew out 3 times in four days.
I called atwood and they acted like that was normal.
They have an optional pilot relight module that runs off a 9 volt battery so it needs no other wiring. It senses the flame and when it is not there it creates a spark to ignite it.
I assume you could also light it then w/o a match this way but I am not sure.
Thanks Pahaska!
Just a little bending and adjusting and wallah, I seem to have the issue fixed (at least all day yesterday and through a windy evening and a couple of cycles this morning)...at least greatly improved.
Thanks again,
Marko