Old 07-24-2017, 02:17 PM   #1
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Is a rubber propane hose a viable option?

I'm turning to our community for some insight. I recently replaced the original Bowen? hot water tank in our 68 Sovereign with an Atwood 6 gal electric/propane model. Given what was there, I had to move stuff around. In running the new copper propane line from the shutoff under the trailer into the compartment where the hot water tank is located, I find that I have an approximate 8" - 12" distance from where the copper line comes out of the floor and the gas inlet valve on the hot water tank.

My issue is that this is a tight area to get into with at least one one 90 ( and possibly 45 ) degree bend involved. My question is given the short distance, are there any reasons why I could not use a Camco Propane Hose with the proper male end / female flare end to gap this last 8"-12" and connect the copper gas supply line coming out of the floor to the gas inlet on the hot water tank?

Any insight would be greatly appreciated!
cheetah1 is offline   Reply With Quote
Old 07-24-2017, 02:41 PM   #2
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by cheetah1 View Post
I'm turning to our community for some insight. I recently replaced the original Bowen? hot water tank in our 68 Sovereign with an Atwood 6 gal electric/propane model. Given what was there, I had to move stuff around. In running the new copper propane line from the shutoff under the trailer into the compartment where the hot water tank is located, I find that I have an approximate 8" - 12" distance from where the copper line comes out of the floor and the gas inlet valve on the hot water tank.

My issue is that this is a tight area to get into with at least one one 90 ( and possibly 45 ) degree bend involved. My question is given the short distance, are there any reasons why I could not use a Camco Propane Hose with the proper male end / female flare end to gap this last 8"-12" and connect the copper gas supply line coming out of the floor to the gas inlet on the hot water tank?

Any insight would be greatly appreciated!
Everything above the belly pan has to be copper until you reach the appliance. That's RVIA code. Rubber is not permitted.

Best option is drill a new floor penetration so you can come straight up to the new water heater instead of snaking the line around bends, relocate the portion of the propane line below the belly pan where it's readily accessible to be moved, and plug the old floor penetration.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 07-24-2017, 03:08 PM   #3
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Hi Protagonist! Thank you for your reply. I was really, really, really hoping I could get by with a rubber propane hose for these last few inches, but it seems like it is not meant to be. I appreciate your insight!
cheetah1 is offline   Reply With Quote
Old 07-25-2017, 11:11 AM   #4
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
The proper (small!) copper line should bend into tight corners really easily. You can use a brake line bending tool, available for a few dollars at any auto parts place, which will give you a bend radius of about 1".
__________________
To learn to see below the surface, you must adjust your altitude
Jammer is offline   Reply With Quote
Old 07-25-2017, 08:49 PM   #5
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Hi Jammer, - Thank you for your input. I am resigned that I have to use copper for this bit of install and appreciate your insight that this may be a bit easier than I am imagining!! The adventure continues!!
cheetah1 is offline   Reply With Quote
Old 07-25-2017, 10:14 PM   #6
Rivet Master
 
NevadaGeo's Avatar
 
1978 31' Excella 500
Genoa , Nevada
Join Date: Jul 2007
Posts: 1,554
Drilling the new hole might be an easier solution than the extra bends to make an old hole work in a tight corner. Perhaps working back from the water heater and make the last connection in the open.
__________________
I admit to being powerless over housecleaning and social niceities
Airforums 22655 and now, WBCCI 22655

NevadaGeo
NevadaGeo is offline   Reply With Quote
Old 07-26-2017, 01:38 PM   #7
Airstream Ambassador
 
AirstreamInc's Avatar
 
Jackson Center , Ohio
Join Date: Feb 2017
Posts: 742
Blog Entries: 1
Quote:
Originally Posted by cheetah1 View Post
I'm turning to our community for some insight. I recently replaced the original Bowen? hot water tank in our 68 Sovereign with an Atwood 6 gal electric/propane model. Given what was there, I had to move stuff around. In running the new copper propane line from the shutoff under the trailer into the compartment where the hot water tank is located, I find that I have an approximate 8" - 12" distance from where the copper line comes out of the floor and the gas inlet valve on the hot water tank.

My issue is that this is a tight area to get into with at least one one 90 ( and possibly 45 ) degree bend involved. My question is given the short distance, are there any reasons why I could not use a Camco Propane Hose with the proper male end / female flare end to gap this last 8"-12" and connect the copper gas supply line coming out of the floor to the gas inlet on the hot water tank?

Any insight would be greatly appreciated!

Hi cheetah1 -- the Camco Propane Hose you mentioned in your post is okay to use for the application you listed above.
__________________
Official account for Airstream, Inc.
Airstream Customer Service and Technical Support can be reached at 1 (877) 596-6111, option 1.
AirstreamInc is offline   Reply With Quote
Old 07-26-2017, 03:17 PM   #8
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 9,180
Just do NOT, under any circumstances, use the metal corrugated flex gas lines intended for home appliances. They are NOT rated for use in trailers or RVs. Guaranteed to vibrate, split, and thus leak propane. Not a good idea...
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 07-26-2017, 04:02 PM   #9
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Thank you NevadaGeo. In looking at what I have, your suggestion also popped into my mind as a more sane way to approach this. Additionally, since the copper tubing comes up through the flooring at a distance of about 12" from where the gas inlet is on the hot water tank, I'm thinking of putting at least one loop into that copper tubing to make it easier to move the connection around for when the time comes to replace that heater. Interestingly, I also received a reply from Airstream in Jackson Center telling me it is OK to use that flexible Camco rubber propane hose to make the connection from the copper tubing coming up in the floor to the hot water tank gas inlet. That surprised me - but if I can do that, this project just got a lot easier! What do you think?
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 04:20 PM   #10
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by cheetah1 View Post
Interestingly, I also received a reply from Airstream in Jackson Center telling me it is OK to use that flexible Camco rubber propane hose to make the connection from the copper tubing coming up in the floor to the hot water tank gas inlet. That surprised me - but if I can do that, this project just got a lot easier! What do you think?
I don't agree with them, but I'm not willing to say they're wrong— it might be me who's wrong.

But think of this: Rubber hoses degrade over time. They chafe against any sharp edge or corner in the area. The rubber gets old and cracks. If the hose isn't intact for whatever reason, you have propane leaking into your living spaces. That is a bad thing.

Something to consider, that most people don't know… Going "boom" isn't the main danger in having propane leak into your trailer. Long before there's enough propane to explode, there's enough to put you in the hospital, or the morgue. Propane becomes hazardous to breathe at just 10% of the lower explosive limit. That's the same concentration at which your propane detector goes off. So by the time the detector goes off, you're already in danger.

The folks at Airstream might be right, that you can use rubber propane hose inside the trailer. My memory might be faulty that it's against RVIA code. Personally I wouldn't take that chance. I'd use copper only inside the trailer, because I know what propane leaks can do to me. But I'm not the one who has to choose in this case.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 07-26-2017, 04:51 PM   #11
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Thank you Airstream! If I can use this, this project just got a lot easier. To confirm, the Camco hose I am talking about is the Heavy Duty 3' Propane Hose Assembly with 3/8" female flare X 3/8" female flare that Camco sells to go with the WAVE heaters. According to their direction for the WAVE heaters, this hose connects to the copper propane gas supply line and then connects to the WAVE heater.

My project is to connect to the copper gas supply tubing coming up through floor and connect that to the gas inlet of the Atwood water heater that is approximately 12" away. The 3' of the rubber hose is more than I need, BUT - it will allow me to leave the excess length coiled there for when the time comes to replace this water heater to make it easier to back out that connection when needed.

In your opinion, am I looking at using this 3' of Camco propane hose correctly?

Thank you!
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 05:34 PM   #12
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Protagonist, thank you for your input on this. Fortunately, or unfortunately - depending on your viewpoint, I'm one of those individuals that's extremely detail orientated. I can see myself putting a tag on this to replace it in 5 years. I am also putting in a WAVE 8 heater in the front of the trailer ( with the proper ventilation in mind) that uses this same heavy duty Camco propane hose from the copper supply line.
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 05:37 PM   #13
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Thanks rmkrum! I researched these as an option and was convinced they are NOT compatible with a travel trailer!
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 06:29 PM   #14
Rivet Master
 
BIGED52's Avatar
 
1967 22' Safari
MILAN , Illinois
Join Date: Dec 2004
Posts: 2,013
Propane line to water heater

cheetah1, You may want to check with a local Propane dealer on this project. If memory serves (and I think it does) you can have them make you a shorter version of the Camco hose at what will be a lower cost for sure. It will be just as safe as the Camco hose and fit into your available space better. My local dealer made my new hose and splitter hoses that go to the hard copper line at the A frame and to the tanks from the regulator. I am very impressed with the testing they did to assure no leaks and proper operation. I am currently having them make up a propane hose line for my furnace and stove to replace old (original) bent up lines to my appliances. I considered the Camco hoses but the length was just too long in the areas near the appliances. Hope this helps, Ed
__________________
1967 Safari Twin "Landshark" w/International trim package
2014 GMC Sierra 1500 Double Cab SLE
FORUMS MEMBER SINCE 12/16/2004AIR#7110
"My tire was thumping, I thought it was flat. When I looked at the tire, I noticed your CAT!" Burma Shave
BIGED52 is offline   Reply With Quote
Old 07-26-2017, 06:30 PM   #15
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by cheetah1 View Post
Protagonist, thank you for your input on this. Fortunately, or unfortunately - depending on your viewpoint, I'm one of those individuals that's extremely detail orientated.
No sweat. My opinion is only an opinion, not a mandate. I don't get upset if the advice I offer isn't taken.

My goal is to allow others to make an informed decision, which you are doing. So my work here is done.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 07-26-2017, 06:52 PM   #16
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
BIGED52, it definitely helps. I did not even think of that option and here I am in northern Wisconsin - home of propane dealers!
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 06:59 PM   #17
Rivet Master
 
AlinCal's Avatar
 
1991 25' Excella
2011 19' Flying Cloud
Santa Ynez , California
Join Date: Jan 2017
Posts: 1,185
I'm with Protagonist on this, why not just use copper anyway? Flairing tool cost?
__________________
Good judgment comes from experience, and a lot of that comes from bad judgment.
Will Rogers

Alan
AlinCal is offline   Reply With Quote
Old 07-26-2017, 07:12 PM   #18
3 Rivet Member
 
1968 30' Sovereign
New Richmond , Wisconsin
Join Date: Jul 2014
Posts: 137
Nope. Inexperience of trying to get that copper line to fit perfectly in a tight space (although I do have to buy the flaring tools). Second concern is having to replace that water tank in the future without having any "give" to that copper line in case it has to be removed. Third reason is not understanding why it is OK to use the Camco rubber propane hose to connect a free-standing WAVE 8 heater from an existing copper propane line - but - it is not OK to connect the water heater within a 12" space from an existing copper propane line. Hope that makes sense!
cheetah1 is offline   Reply With Quote
Old 07-26-2017, 07:50 PM   #19
Rivet Master
 
BIGED52's Avatar
 
1967 22' Safari
MILAN , Illinois
Join Date: Dec 2004
Posts: 2,013
Old School vs. new tech

This is the debate as the hoses these days are not as susceptible to age cracking and propane dry out as the old radiator hose lines on the past. The Techs from AirstreamInc. would never recommend the use of any product that could leave them open for a law suit due to a safety issue. These new hoses whether Camco or other provider are far and away better than previous hoses. Not having to deal with copper tubing.... PRICELESS! Ed
__________________
1967 Safari Twin "Landshark" w/International trim package
2014 GMC Sierra 1500 Double Cab SLE
FORUMS MEMBER SINCE 12/16/2004AIR#7110
"My tire was thumping, I thought it was flat. When I looked at the tire, I noticed your CAT!" Burma Shave
BIGED52 is offline   Reply With Quote
Old 07-26-2017, 09:28 PM   #20
Rivet Master
 
AlinCal's Avatar
 
1991 25' Excella
2011 19' Flying Cloud
Santa Ynez , California
Join Date: Jan 2017
Posts: 1,185
Quote:
Originally Posted by cheetah1 View Post
Nope. Inexperience of trying to get that copper line to fit perfectly in a tight space (although I do have to buy the flaring tools). Second concern is having to replace that water tank in the future without having any "give" to that copper line in case it has to be removed. Third reason is not understanding why it is OK to use the Camco rubber propane hose to connect a free-standing WAVE 8 heater from an existing copper propane line - but - it is not OK to connect the water heater within a 12" space from an existing copper propane line. Hope that makes sense!
OK sorry my ignorance I guess.
__________________
Good judgment comes from experience, and a lot of that comes from bad judgment.
Will Rogers

Alan
AlinCal is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
A hose is a hose is a hose Vitaver Plumbing - Systems & Fixtures 38 09-23-2020 10:41 AM
Is furnace duct hose the same as household dryer duct hose? Bearstream1 Furnaces, Heaters, Fireplaces & Air Conditioning 8 04-15-2020 12:46 AM
Anti-sway: truck option or hitch option or both? RubyDog Towing, Tow Vehicles & Hitches 27 12-27-2014 09:51 AM
ATV's are they a viable way to explore trails? LI Pets Off Topic Forum 5 09-25-2006 11:13 PM
Oil in the propane line and a connecting hose dbensen LP Gas, Piping, Tanks & Regulators 2 10-20-2005 07:50 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:44 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.