Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 01-18-2005, 05:39 AM   #1
2 Rivet Member
 
Ga Pockets's Avatar
 
Join Date: Dec 2004
Posts: 52
Atwood HW ?

My unit has electronic ignition Atwood WH. I have gone through service manual and find no temp adjustment. It seems to be going through numerous cycles of firing up running for lest than a minute and shutting down. It almost seems like the set stemp is just above the 120 deg so that it comes on, raises the temp just enough to shut down and then when it drops below the 120 mark it starts all over again. Water does not seeem to be at 165 deg. I have to measure temp to verify that but past experience with regular Atwood tells me that water is not reaching high limit before shutting down. Is this temp controled with a circuit board? and is sthere anadjustment?
__________________
Ga Pockets
Ga Pockets is offline   Reply With Quote
Old 01-18-2005, 12:09 PM   #2
a.k.a. Ambassador Tim
 
Safari Tim's Avatar
 
1960 28' Ambassador
Northern , California
Join Date: Jun 2003
Posts: 1,921
Images: 35
It is my understanding that the DSI models do not have a temperature adjustment. It's a fixed temperature setpoint from the factory.

The pilot models do have an adjustment.

Hopefully others will chime in to help you with this one. All I can suggest is to recheck all your connections on the circuit board make sure they are clean and tight. That seems to be the most common failure.

Good luck!
__________________
-Tim
1960 International Ambassador 28'
2001 Silverado 2500HD CC 6.0L 4.10
Check out my book: Restoring a Dream
Check out my Airstream book for kids!: Airstream Adventures
theVAP - Airstream Podcast
Safari Tim is offline   Reply With Quote
Old 01-18-2005, 02:47 PM   #3
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 10,408
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
I don't think I saw an adjustment for ours. The water is "hot" though. Much hotter than I keep the home water heater set for. I normally use the electric side of the heater but based on my voltage gauge I know when the element is active. It doesn't take much water usage for the thermostat to call for heat. I only use the gas when we are showering.

Jack
__________________
Jack Canavera
STL Mo.
AIR #56 S/OS#15
'04 Classic 30' S.O.,'03 GMC Savana 2500
jcanavera is offline   Reply With Quote
Old 01-18-2005, 06:26 PM   #4
3 Rivet Member
 
mcneon's Avatar
 
Join Date: Jun 2003
Posts: 212
Images: 4
The thermostat on the Atwood DSI water heater is independent of the circuit board. It is not adjustable, and I believe it is factory set at 120 degrees. I have seen an adjustable replacement available for sale somewhere.

In any event, there's no way the thermostat could cause such rapid cycling unless the tank is empty. There must be some other safety device that is sensing an overheat or flameout condition and causing the on-off cycling.

Ga pockets, you mentioned 165 degrees water temp in your post. Water that hot creates a very serious scald hazard. Home water heaters years ago could be set up to about 140 degrees or higher, but even that is a potentially dangerous level.

Bob
mcneon is offline   Reply With Quote
Old 01-18-2005, 06:44 PM   #5
3 Rivet Member
 
mcneon's Avatar
 
Join Date: Jun 2003
Posts: 212
Images: 4
More info: from looking at the parts lists, there are major differences between the pilot and DSI water heater control systems. The pilot models use a gas valve very similar to the ones on home water heaters, with a rotary temperature control on the front.

The DSI models use a solenoid gas valve and a bimetal switch to control temperature. And there is an adjustable thermostat (110-150 degrees) available for these at Marks RV.

Don't know why the controls are so completely different on the two models, but they are.

Bob
mcneon is offline   Reply With Quote
Old 01-19-2005, 06:01 AM   #6
2 Rivet Member
 
Ga Pockets's Avatar
 
Join Date: Dec 2004
Posts: 52
I think I got the 165 deg from the service manual as a high limit shut down temp. I agree with you regarding scald potencial. thanks for the caution.
__________________
Ga Pockets
Ga Pockets is offline   Reply With Quote
Old 03-14-2005, 11:37 AM   #7
1 Rivet Member
 
Join Date: Mar 2005
Posts: 8
Images: 7
I can't seem to enter a new post so I'll take a shot at getting a reply here. I'm newly registered, but have been a viewer for over a year and now I have a request for help. My 6 gal Atwood DSI WH has had a problem for several seasons where it would start and then shut down after a few minutes. After turning the switch off and on it would restart and run again for a few minutes. Then after several recycles it would usually work for 3 - 4 days without problem. Last fall when I went to my site to winterize it would not work at all. I checked and cleaned all the electrical connections, but still it would not work. Is the circuit board the most likely culprit? Do they make replacements? Should I replace the board or the entire WH? Thanks for any and all help.
G-Daddy is offline   Reply With Quote
Old 03-14-2005, 04:35 PM   #8
Just a member
 
thenewkid64's Avatar
 
1978 28' Argosy 28
Lutz , Florida
Join Date: Mar 2002
Posts: 4,549
Images: 21
Send a message via AIM to thenewkid64 Send a message via Yahoo to thenewkid64
Quote:
Originally Posted by G-Daddy
Should I replace the board or the entire WH?
Yes.


One or the other is going to need to be replaced. The cost of the board is in the neighborhood of 183.00 OEM, a Dinosaur board is close to 100.00. A new heater is 350.00 form the web.

How old is the unit now? Has it been flushed each year to cut the sediment and scale? One of the issues with the Atwood heaters is the internal corrosion that eats the tank up. If the heater is more than 10 yrs old I would spend the extra and replace it.

KEEP THE OLD DOOR!

It will come with a white painted door. If you current heater is in that 10 year old range you should be able to transfer the old door.
__________________
Brett G
WBCCI #5501 AIR # 49
-------------------------
1978 Argosy 28 foot Motorhome

Wise men talk because they have something to say; fools, because they have to say something. -- Plato


thenewkid64 is offline   Reply With Quote
Old 03-14-2005, 07:52 PM   #9
2 Rivet Member
 
Join Date: Jan 2004
Posts: 36
I have an '84 Atwood water heater. I'm trying to get it running after replacing gas lines and a long period of inactivity. It clicks and sparks but no flame. I've bled line, replaced connections etc. Probably no PM by PO. Should I just replace it? Will the current 6 Gal heaters fit OK? Is it hard to replace? Thanks.
jperryfly is offline   Reply With Quote
Old 06-05-2005, 08:36 AM   #10
Rivet Master
 
LuminumTraila's Avatar
 
2006 19' Safari SE
NW of Boston , Massachusetts
Join Date: Aug 2002
Posts: 987
Images: 3
Atwood Water Heater Operation

We have an Atwood water heater, model G6A2 with ITT General Control, and we're using the following instructions in the manual to try to light it:

a. Turn Lighting Control dial to "Pilot" position and hold against stop while lighting pilot burner. Allow pilot to burn approximately one half minute before releasing dial.
b. Turn knob to "ON" position. If pilot does not remain lit, repeat operation allowing longer period before releasing button or knob.

We can't get it to light. Can anyone tell us what the trick is?
Attached Thumbnails
Click image for larger version

Name:	waterheater.JPG
Views:	737
Size:	62.6 KB
ID:	12606  
__________________
Doug & Jamie, AIR #650
LuminumTraila is offline   Reply With Quote
Old 06-05-2005, 09:10 AM   #11
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Bad thermocouple?

You may have a bad thermocouple. But see if this thread will help you get it lit.

Tom
TomW is offline   Reply With Quote
Old 06-05-2005, 11:55 AM   #12
Rivet Master
 
Over59's Avatar
 
1959 26' Overlander
Putnam , Connecticut
Join Date: Sep 2003
Posts: 3,064
Images: 37
The pilot disc on my 68 was rusted and was hard to light. I replace the pilot with a kit from the SOB RV place. Took a little adjusting at the originatation of the heat sensor was different but it now light easily.
Over59 is offline   Reply With Quote
Old 06-06-2005, 12:06 AM   #13
Rivet Master
 
Tinsel Loaf's Avatar
 
Join Date: Jan 2003
Posts: 790
Our 2003 Atwood puts out 165 degree water with the electronic board and I see no adjustment of temperature setpoint on it. Ii will blow through a lot of propane so we mainly use it on electric.
Tinsel Loaf is offline   Reply With Quote
Old 06-06-2005, 06:42 AM   #14
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,477
No temp control on our unit either FWIW.
Silvertwinkie is offline   Reply With Quote
Old 06-06-2005, 10:34 AM   #15
a.k.a. Ambassador Tim
 
Safari Tim's Avatar
 
1960 28' Ambassador
Northern , California
Join Date: Jun 2003
Posts: 1,921
Images: 35
My understanding is the DSI (auto lighting) water heaters do not have a temperature adjustment. The pilot models do have temperature adjustment.
__________________
-Tim
1960 International Ambassador 28'
2001 Silverado 2500HD CC 6.0L 4.10
Check out my book: Restoring a Dream
Check out my Airstream book for kids!: Airstream Adventures
theVAP - Airstream Podcast
Safari Tim is offline   Reply With Quote
Old 06-06-2005, 12:06 PM   #16
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,477
Yup...ours is a DSI unit.
Silvertwinkie is offline   Reply With Quote
Old 06-19-2005, 11:44 AM   #17
Rivet Master
 
LuminumTraila's Avatar
 
2006 19' Safari SE
NW of Boston , Massachusetts
Join Date: Aug 2002
Posts: 987
Images: 3
Followup

Quote:
Originally Posted by dougjamie
We can't get it to light. Can anyone tell us what the trick is?
We took our trailer to an RV service place this week to have the new furnace put in and while it was there we asked them to look at the water heater and do some troubleshooting for us. We weren't comfortable messing with it ourselves since we're new to all this kind of stuff and we still have a healthy fear of propane appliances. Anyway, they got it fired up just by cleaning it up and blowing the old dust and spider webs out of it. It's working great for us now.

-J
__________________
Doug & Jamie, AIR #650
LuminumTraila is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot water Heater DClark Water Heaters, Filters & Pumps 15 08-25-2017 02:35 AM
Atwood water heater uwe Water Heaters, Filters & Pumps 5 10-03-2009 01:58 AM
Atwood Question ALANSD Water Heaters, Filters & Pumps 2 04-14-2004 09:54 AM
Atwood 7916-II furnace Silvertwinkie Furnaces, Heaters, Fireplaces & Air Conditioning 0 05-17-2003 11:05 PM
Atwood Water Heater Parts? ViewRVs Water Heaters, Filters & Pumps 1 04-08-2003 08:13 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 01:47 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.