I have a problem with my air conditioning and heat pump functions from my Dometic Penguin HVAC unit.

I had thought that the reversing valve normally allowed cooling, and was energized to reverse refrigerant flow to the coils thereby providing the heat pump function. This appears not to be the case.

When I replaced the thermostat with a Comfort Control Center, I also had to replace the control board (with p/n 3312227.000) in the rooftop A/C unit.

After install, I was getting hot air from my cooling cycle, and cold air from my heat pump function. I thought my re-wiring was suspect, so a Dometic email got a response with schematics, and I found no issues.

The diagnostic mode (press Program, Fan and F/C button while off) allows step by step function cycling. When I turn the Reversing Valve on, I get a nominal 120v sent to the reversing valve (verified by meter).

When I disconnect the reversing valve wire harness, I get hot air in all modes, which tells me that the reversing valve is normally in heat pump mode, and requires power to get to (what I thought would be normal) cooling mode. Seems odd to me, but maybe the old control board took care of that.

Maybe the dipswitches need to be different than what I did (only Heat Pump and Furnace switches are on).

I have sent a message to OutofDoorsMart (where I bought the parts), but maybe someone else has experience with this.

Any thoughts would be appreciated.

Phil
__________________

__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Old 10-07-2015, 09:07 PM   #2
Rivet Master
 
1974 31' Sovereign
1979 23' Safari
Wayland , New York
Join Date: Jan 2012
Posts: 1,627
Images: 3
What wire did you run from the unit to the CCC. Wasn't by chance regular phone line? I think you would have had to run something since the SZLCD and CCC use different wires. If you used regular phone line, that's probably the problem. In their infinite quest for a buck dometic uses a phone line with phone jacks on the ends, but to keep people from simply being able to go buy phone line in store they require one end to be reverse wired. If it's not that may be what's causing the unit to essentially run backwards.
Hope that makes sense and helps.
__________________

__________________
HiJoeSilver is offline   Reply With Quote
Old 10-07-2015, 09:25 PM   #3
Rivet Master
 
Phil and/or Sue's Avatar
 
1997 34' Limited
Young Harris , Georgia
Join Date: Feb 2003
Posts: 857
Images: 40
The wire from the CCC to the rooftop is good (6 wire, correctly oriented).

As I boil this down, it seems to be a question of how the reversing valve is supposed to work. When completely isolated electrically, it appears to be reversed. That is, when I pulled the electrical plug off the terminals so it was unpowered, I got heat in the Heat Pump mode, as well as heat when I tried the Cooling mode.

I was wondering if the old tstat/control board kept the reversing valve off for Heat Pump, and powered it for Cooling. I still have them (packed somewhere in our move), but I'm hoping to find out about what I have installed, and whether I need to change settings on the board. Maybe it's the wrong board for a/c...
__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Old 10-07-2015, 09:26 PM   #4
Rivet Master
 
Phil and/or Sue's Avatar
 
1997 34' Limited
Young Harris , Georgia
Join Date: Feb 2003
Posts: 857
Images: 40
By the way, thanks for your thought and time.

Phil
__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Old 10-07-2015, 09:33 PM   #5
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
But it worked normal before replacing the thermostat ...?
__________________
nrgtrakr is offline   Reply With Quote
Old 10-07-2015, 09:37 PM   #6
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Dometic's reversing valves are always on heat pump mode in resting state unless energized by the t/stat when it calls for call for cooling, so your last diagnosis is correct! Heat in resting state, cooling in energized state.

The next thing you have to look at is the compatibility of the board to the CCC-II and your specific upper unit. Call Dometic and give them the part numbers to be certain that you have the correct board.

Also, depending on which board you have, you might have to set the DIP switch for 'heat pump' if it's present in the DIP switch line. If you ran your furnace lines (should be 2 blue wires) into the board, you will also need to activate the 'furnace' DIP switch.

As I recall, the communication cable is a 4 wire phone cable with one R-11 reversed from the other. You might try 2 things: use a 4 conductor cable and try placing it into the second RJ-11 union at the base of the upper unit.

Keep us posted on your progress.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 10-08-2015, 01:13 PM   #7
Rivet Master
 
Phil and/or Sue's Avatar
 
1997 34' Limited
Young Harris , Georgia
Join Date: Feb 2003
Posts: 857
Images: 40
Thanks for your message. My reply got lost this morning.

I am going to talk to Out Of Doors Mart to see how they determined the control board they sold me. I presume I gave them my rooftop info, but I'll find out. Maybe there's a dipswitch setting I can manipulate (although it doesn't look like it).

Phil
__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Old 10-17-2015, 06:30 PM   #8
Rivet Master
 
Phil and/or Sue's Avatar
 
1997 34' Limited
Young Harris , Georgia
Join Date: Feb 2003
Posts: 857
Images: 40
Out of Doors Mart has been talking with Dometic. No answer yet, but hopeful that either already - installed board can be configured to support my A/C, or some other simple fix can be found.
__________________

__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 08:58 PM
To heat pump, or not to heat pump, that is the ?? MacDad Furnaces, Heaters, Fireplaces & Air Conditioning 16 09-06-2014 10:58 PM
Early penquin a/c verus newer penquin II safari25-05 Furnaces, Heaters, Fireplaces & Air Conditioning 8 06-01-2013 06:36 PM
Heat Pump/Air Condition Blowing Hot Air Safari-Rick Furnaces, Heaters, Fireplaces & Air Conditioning 1 04-24-2012 09:30 PM
Small or Large Penquin GoldFever Furnaces, Heaters, Fireplaces & Air Conditioning 9 07-16-2003 10:30 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:28 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.