Heat pump no longer heating air?? Help!

Hi everyone,
I've been following the forums for the past 6 months or so but haven't posted much but thanks for the great forum and information!
I have a 2015 International Signature 25 purchased new in September and departed on my current trip 10/15(~4 months). I have the Dometic Penguin II AC with heat pump which worked flawlessly until a few days ago when I noticed the heat pump was constantly running but the air felt cold and it couldn't keep the interior temperature warm at all, it had dropped to about 43 at night here in LA with a few days only getting into the mid 50s, previously this was fine for the heat pump but I've since had to rely only on the furnace for heat. While it's annoying to burn propane when my new trailer should be in proper working order, my bigger concern is making sure I have AC for the summer as I'm in the San Fernando Valley and it can get warm here in the summer.
I've thoroughly tested both the heat pump and AC, neither works properly providing only air within a few degrees of the interior temperature. With the thermostat AND fan set to auto, I've set the thermostat temp to 80, the compressor comes on then 15 seconds later the fan kicks in, normal per Dometic, but the air coming out is not heated at all, similarly when I set the temp to 60 to force the AC on, the fan first comes on then the compressor about 15 seconds later, normal per Dometic, but the air is the same temperature coming out, no cooling provided.
I checked the return intake registers and the filters were dirty but not to the point where air would not pass through, I washed them in warm soapy water, thoroughly dried them and put them back in but no change in heating/cooling provided and the internal components I could see with the return register covers removed did not look very dirty. I was hoping there's another filter but per Colonial where I purchased, those are the only filters.
I found a guide on troubleshooting via the CCC II, with the thermostat Off, hold the "Program","Fan", and "F/C" buttons simultaneously, then use the up/down to test various components, verify dip switch settings etc and everything appears to be ok so now I'm stumped, any suggestions on next steps?
I have not yet climbed on the roof to check the unit and with ducted air, there's not too much you can do from inside the trailer so obviously that's my next step but nothing else happened from when AC/HP worked, I've been in the same location for a month so I haven't moved the trailer, we did get some rain and lots of wind right around when I noticed I was cold but I suspect that's just a coincidence. Colonial suggests I may have lost all my refrigerant and while I can understand the logic, it seems unlikely to me since I've not been traveling or putting any stress on the unit aside from regular use while stationary. I am still under warranty but it's difficult for me to take the trailer to a dealer right now as this where I'm currently living and I'm stopped here in LA because my best friend, Gizmo (3 legged boxer mix) is sick and getting regular chemo so I don't want to make any big changes right now, plus i have to cook for him regularly since he has special dietary needs so this situation kinda sucks but I have some time to figure things out.
I've read the other similar threads but haven't found any answers, I noticed some people disconnected power and reconnected and everything worked, I tried that by disconnecting power for 10-15 mins with no luck, then just tried flipping the breaker off but no luck again.

So, I apologize for the lengthy post but I'm trying to describe everything I can think of. I did recently removed the plastic shroud for the Fantastic fan in the bedroom to get an idea of where some wiring is (before I noticed any hp/AC issues) and I know there's thermostat wires up there but I didn't touch a thing, just took pics and replaced the cover.

Any help/suggestions are much appreciated as I'd really like to fix this on my own, too bad the dealer or my insurance can't provide me with a rental Airstream while it's being repaired, that would be convenient.

Looking forward to all you brilliant minds getting back to me with some ideas!
Thanks everyone!

Zach/Gizmo
deadlock is offline   Reply With Quote
Old 02-03-2016, 05:29 PM   #2
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
If you are not getting the proper performance from either your A/C or heat pump, there is a very good chance that you have experienced a leak in your system.

Have your unit checked by a competent professional. If you are within your Dometic 2year warranty, be certain they they are also an authorized Dometic service center as well.

A simple amp draw test on the compressor's 120 VAC wires will provide definitive proof.


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-03-2016, 05:58 PM   #3
Rivet Master
 
Mrjkq's Avatar
 
2016 25' Flying Cloud
Venice , Florida
Join Date: Apr 2015
Posts: 1,024
I thought I read a post on this forum something to the effect that if the cold temp gets below a certain degree the heat pump will not heat, that could be the issue.
__________________
Joe
Venice, FL
2016 FC 25RTB
TAC FL-47
2018 Nissan Titan XD Cummins Diesel
Mrjkq is offline   Reply With Quote
Old 02-03-2016, 06:09 PM   #4
Rivet Master
 
AWCHIEF's Avatar
 
2006 23' Safari SE
Biloxi , Mississippi
Join Date: Nov 2011
Posts: 8,278
Images: 33
My heat pump seems to work to about 35 degrees and then only blows out cool air.
__________________
MICHAEL

Do you know what a learning experience is? A learning experience is one of those things that says "You know that thing that you just did? Don't do that."
AWCHIEF is offline   Reply With Quote
Old 02-03-2016, 06:18 PM   #5
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
"I've thoroughly tested both the heat pump and AC, neither works properly providing only air within a few degrees of the interior temperature."

If neither the heat pump or A/C are working as the OP stated in his post, There is a very strong probability that he has a refrigerant leak and the unit must be replaced.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-03-2016, 06:27 PM   #6
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
That rather wretched thermostat can be programmed to automatically shift from heatpump to furnace when it gets too cold for the heatpump to work. Getting it right? - well read the instructions and pray. My newer heatpump works into the high 30's - older one was ineffective below 40-45 degrees.

I hesitate to even suggest this but - have you cleaned out the filters lately? It's a good idea to do it once a month but it's easy to let it slip. There are dozens of little peculiarities about RV's and Airstreams in particular that you don't know as a newbie - so if you are going "what filters" you're just where I was not that many years ago. (Two small plastic screens that pull out of the A/C. Vacuum them, wash, rinse, dry and reinsert - voila!)

Just a few weeks ago, there was a thread about bathroom fans - and a newbie who had been using his for several weeks suddenly learned that you push UP on the handle to open the fan before turning it on. He'd been running the fan with the lid down and wondered why it did such a poor job of clearing the steam out of his shower.!)

I - the experienced owner - bought a slightly used Eddie Bauer and didn't realize that the stove vent was still packed for shipping.... I turned on the fan and spit styrofoam all over the place. Made a noise like a cat with it's tail in the fan!

Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 02-03-2016, 06:43 PM   #7
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
Thanks everyone. As lewster suggested, i probably have a refrigerant leak. I'll do a current draw test in the compressor, I assume it's only accessible from the roof?
Not a big deal but I'll have to find a decent ladder. At least I'll get a chance to inspect the roof and see how much room I have to upgrade my solar.
I've owned many window AC units but never experienced a refrigerant leak, it still seems odd to me that my unit would lose all refrigerant while stationary and being used regularly but it sounds like AS cheaper out on the AC/HP units, this would be surprising if I hadn't already learned they use a single stage charger EVEN with the solar package, pretty lame and unacceptable considering what these trailers cost.

And yes I'm aware that in auto it will switch from HP to furnace around 38 degrees, my unit did that flawlessly until this week.

Any guesses on how long a dealer will need to keep my trailer to diagnose and replace the entire AC/HP unit? It's really a headache to find somewhere else to stay for however long but I'm definitely going to make sure I leverage my warranty, still have 20 months left on it.

I'll update everyone once I get in touch with Airstream LA, missed their call back this morning and they were impossible to get in touch with all day, hopefully they're competent.

Thanks again!
deadlock is offline   Reply With Quote
Old 02-03-2016, 06:45 PM   #8
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
Hey Paula, cleaning the filters was the first thing I tried. They were dirty but not so much to prevent air padding through, I was hoping it was a filter issue as well.
Ugh
deadlock is offline   Reply With Quote
Old 02-03-2016, 08:15 PM   #9
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
If you have access to a clamp on ammeter, you could easily measure the current flow at the circuit breaker for the AC in the main box. No need to climb onto the roof.
idroba is offline   Reply With Quote
Old 02-03-2016, 08:40 PM   #10
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by idroba View Post
If you have access to a clamp on ammeter, you could easily measure the current flow at the circuit breaker for the AC in the main box. No need to climb onto the roof.
Ahhh, but you will also have the amperage draw for the blower motor included into that breaker's circuit. Best to do it on the roof to isolate the compressor draw. For Dometic units, it is usually the black wire going from the relay board into the compressor.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-04-2016, 12:06 AM   #11
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
Hmm. As suspected, I figured I wouldn't be so lucky as to be able to isolate the compressor and get the current draw without getting on the roof.
Thanks for the info!
deadlock is offline   Reply With Quote
Old 02-04-2016, 08:35 AM   #12
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
But the fan draw is constant, and could be measured first at the panel by setting the AC on Fan only, then recording the measurement. Then put the unit in heat or cool and measure the current. Subtract the fan current and you have the compressor current.

Anything to keep from getting on the roof and into the unit is good.... grin.
idroba is offline   Reply With Quote
Old 02-04-2016, 10:06 AM   #13
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
True! When I'm on a client's clock, it's just much easier ( and quicker) for me to hop on the roof to check it. That also gives me an opportunity to check other areas of the system. :-))


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-04-2016, 12:00 PM   #14
3 Rivet Member
 
2002 25' Classic
Kalama , Washington
Join Date: Feb 2003
Posts: 189
Hey Zach -- Is a service call out of the question? Must be a dealer/service center within reach. Once diagnosed and recorded, you could make your way there at your convenience without wasting time while they order parts. Can't imagine Angelinos will get uncomfortable for a couple of months.
Good luck. I'll be interested to hear its conclusion. We gave up on our heat pump some time ago (besides, they're noisy).
nwclassic is offline   Reply With Quote
Old 02-04-2016, 04:31 PM   #15
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
When measuring the compressor current, what result am I looking for to determine if I lost refrigerant or not?
deadlock is offline   Reply With Quote
Old 02-04-2016, 04:34 PM   #16
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
It's a pain to take it to the dealer since I'm currently staying in it but if they can do it all in a day then I'm fine with that.
I spoke with Airstream Los Angeles earlier and they said if it needs replacement, the paperwork with Airstream/Dometic can take a few days but the actual work is only a few hours so I'm a bit more optimist.

My heat pump isn't that noisy, I have ducted air which helps quite a bit.
deadlock is offline   Reply With Quote
Old 02-04-2016, 05:59 PM   #17
4 Rivet Member
 
1973 31' Sovereign
Middletown , California
Join Date: Oct 2013
Posts: 424
I'd ask the dealer where you will take it for warranty service if they can send the tech out to look at it. Or perhaps they work with a mobile RV service person they trust to diagnose the problem. If you have good air flow through the outside and inside of the unit a situation like this requires a look under the shroud to see what went wrong. If the dealer has determined the unit is bad and has a unit in stock they can change it out in a few hours. Maybe if you explain your situation the dealer will work with you to minimize the disruption of your routine. Good luck.
ijustlee is offline   Reply With Quote
Old 02-04-2016, 06:59 PM   #18
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
I did check with Airstream LA if they provide mobile service but they do not. Still waiting for a call back from one of their techs. I also reached out to a Dometic authorized mobile RV shop but they haven't called back, the lack of urgency or just normal priority is quite frustrating. I don't need AC/HP as I can get by with the furnace but I want to take care of the problem now before I need to use the unit.
deadlock is offline   Reply With Quote
Old 02-05-2016, 05:44 AM   #19
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by deadlock View Post
When measuring the compressor current, what result am I looking for to determine if I lost refrigerant or not?

Using an amp clamp type meter, look at the black or blue wire going from the relay board directly into the compressor.

Remove the shroud, go back inside and turn the unit on. Climb back on the roof and take the measurement. This allows the compressor to start up and settle down a bit before taking the readings.

The compressor FLA or RLA (full load amps or running load amps) for a Dometic 15K unit is around 13 amps at 95 degrees. Depending on the ambient temps, you should see 11-13 amps.

If you have lost refrigerant, your readings will be less than half of the operational rating.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-05-2016, 12:45 PM   #20
2 Rivet Member
 
2015 25' International
Southern CA , California
Join Date: Sep 2015
Posts: 25
Lewster- Thanks! Exactly what I needed. I'm gonna grab a ladder from the maintenance crew and get to the bottom of this.

Are you ever out in Southern CA? I've been wanting to upgrade the factory solar and max out my solar capacity, upgrade my charger and solar charge controller. I'd love to work with you on getting this done.
If not, when things calm down I'm a few months, I can head up north, when are you in Oregon?
deadlock is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 07:58 PM
Heat Pump - Replace with an AC or Heat Pump? A W Warn General Repair Forum 32 10-12-2015 02:18 PM
To heat pump, or not to heat pump, that is the ?? MacDad Furnaces, Heaters, Fireplaces & Air Conditioning 16 09-06-2014 09:58 PM
Heat Pump/Air Condition Blowing Hot Air Safari-Rick Furnaces, Heaters, Fireplaces & Air Conditioning 1 04-24-2012 08:30 PM
New AC, Heat Pump or Heat strip? firedog 1990 - 1993 Excella 3 01-22-2010 04:23 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:29 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.