Old 12-29-2015, 05:09 PM   #1
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Furnace will not shut off automatically.

Inside temp on the CCC 2 said that the inside temp was 32 degrees F. Out side temp was 54 degrees F. This was last night some where in West Virginia. Thermostat set at 68 degrees F. The furnace started and ran and ran and ran. Soon it was just like the sauna in Fort Lauderdale, about 90 degrees F inside. I shut off the furnace manually. Inside temp still showed that it was 32 degrees F. So this now does not seem to be related to the freeze sensor. Perhaps it is time for a new thermostat? Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 12-29-2015, 05:29 PM   #2
3 Rivet Member
 
Noggin's Avatar
 
1994 25' Excella
On the Lake , Georgia
Join Date: Feb 2011
Posts: 217
Jim
You are more than likely correct in getting a new thermostat but you might want to check you tube and see if they have anything on your brand.
Maybe a loose wire or tap with a hammer?
Happy New Year!
Joe
Noggin is offline   Reply With Quote
Old 01-01-2016, 02:13 PM   #3
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Today, the thermostat registered 33 degrees on the inside and 33 degrees f on the outside and performed as it should with the furnace starting and shutting down correctly. It seems to have reset itself overnight. The Airstream warmed up quickly and the furnace cycled properly. I hope the new thermostat, once installed, will do away with this inconsistent operational issue. Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-01-2016, 02:54 PM   #4
2 Rivet Member
 
Levelland , Texas
Join Date: Nov 2015
Posts: 24
Images: 1
I have the same exact problem it is not the thermostat it is the board on the air conditioner.I have had it worked on twice. Wish I did not have a Dometic.
Troy Tyson is offline   Reply With Quote
Old 01-01-2016, 05:03 PM   #5
Rivet Master
 
sgschwend's Avatar
 
1986 25' Sovereign
2008 F350, 6.4L diesel , Oak Harbor, WA
Join Date: Sep 2015
Posts: 605
Images: 13
A common thermostat is a two wire switch. To test these you can remove the front off the thermostat, then by shorting the two wires the heater should start, and it turns off when the two wires are open.

good luck,
sgschwend is offline   Reply With Quote
Old 01-01-2016, 05:17 PM   #6
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by sgschwend View Post
A common thermostat is a two wire switch. To test these you can remove the front off the thermostat, then by shorting the two wires the heater should start, and it turns off when the two wires are open.

good luck,
These are Dometic's digital Comfort Control Center II units (CCC-II), which are proprietary to Dometic and operate the A/C and or heat pump along with the furnace.


Jim,
Have you tried re-setting the CCC-II?
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 01-01-2016, 05:39 PM   #7
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Furnace will not shut off automatically.

Quote:
Originally Posted by lewster View Post
These are Dometic's digital Comfort Control Center II units (CCC-II), which are proprietary to Dometic and operate the A/C and or heat pump along with the furnace.





Jim,

Have you tried re-setting the CCC-II?
Yes, Lew, I have. The fact that it works periodically makes it quite confusing. The re-set had no effect. I did shut all power off over night and it operated normally the following day. Jim



Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-01-2016, 05:48 PM   #8
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Quote:
Originally Posted by Troy Tyson View Post
I have the same exact problem it is not the thermostat it is the board on the air conditioner.I have had it worked on twice. Wish I did not have a Dometic.

Sorry to hear that Troy. I do have a great dealer so I may end up there for a repair before I head out on my next trip. Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-01-2016, 06:29 PM   #9
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by Jim Flower View Post
Sorry to hear that Troy. I do have a great dealer so I may end up there for a repair before I head out on my next trip. Jim


Sent from my iPad using Airstream Forums
Before having the board checked, remove the air box below the A?C unit on your ceiling. You will find an RJ-45 phone plug union there. Remove both plugs (one should be black and the other grey) and use a hair dryer on the plugs and the union.

I have seen moisture in these and they are cheap Chinese components that have had many issues. You might be experiencing intermittent communication problems and this might help.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 01-01-2016, 07:30 PM   #10
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Quote:
Originally Posted by lewster View Post
Before having the board checked, remove the air box below the A?C unit on your ceiling. You will find an RJ-45 phone plug union there. Remove both plugs (one should be black and the other grey) and use a hair dryer on the plugs and the union.



I have seen moisture in these and they are cheap Chinese components that have had many issues. You might be experiencing intermittent communication problems and this might help.

I have one grey plug that is connected the other I think is a spare for an additional AC unit. That drying out process is my usual first step when the AC compressor will not start. Are you saying that it may also have an impact on the furnace operation by having the CCC2 default to a 32degree F setting for inside temperature? Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-01-2016, 07:54 PM   #11
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Doesn't hurt to try it. The default setting might be due to a comm. error. leave no stone unturned!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 01-02-2016, 05:56 AM   #12
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
True. I was looking for an excuse to visit the Airstream today although taking off the air box is getting a little old. I think I will spray that connector with a little ignition wire spray that I used on my old Morris. I wonder if the design was copied from something that Lucas built? Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-02-2016, 06:41 AM   #13
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by Jim Flower View Post
True. I was looking for an excuse to visit the Airstream today although taking off the air box is getting a little old. I think I will spray that connector with a little ignition wire spray that I used on my old Morris. I wonder if the design was copied from something that Lucas built? Jim


Sent from my iPad using Airstream Forums

Ahhhhh………Lukas….'Lord of Darkness' !!!!! I remember it well.

Either that, dielectric grease or a marine product called 'Corrosion Block' that I use almost by the case. Anything in that realm should help with reducing the potential of moisture in those connections.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 01-02-2016, 06:53 AM   #14
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Thanks for the memory jog Lew. Going to get some now. Jim


Sent from my iPad using Airstream Forums
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-02-2016, 07:57 AM   #15
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
You know why Brits drink warm beer? They have Lucas refrigerators! Groan.
idroba is offline   Reply With Quote
Old 01-02-2016, 11:16 AM   #16
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
Groan, but with a big smile. Jim
__________________
Jim
Jim Flower is offline   Reply With Quote
Old 01-03-2016, 11:25 AM   #17
Rivet Master
 
Jim Flower's Avatar
 
2012 30' International
1997 25' Safari
1967 20' Globetrotter
Burlington , Ontario
Join Date: Jul 2009
Posts: 1,499
The thermostat and furnace are operating properly today. I took off the air box and sprayed the connector with some Gunk that smelled like WD40. I am now ready for Florida humidity and Ontario winter and will have a spare CCC2 stashed away with an assortment of other spares. Feel like a sailor. Click image for larger version

Name:	ImageUploadedByAirstream Forums1451845522.692568.jpg
Views:	103
Size:	94.3 KB
ID:	255024
__________________
Jim
Jim Flower is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Automatically Fill Username/PW cwf Forum Admin, News and Member Account Info 6 03-04-2015 07:36 AM
Furnace won't shut off seismicfish Winter Living 2 03-04-2014 06:37 AM
furnace wont shut off! seismicfish Furnaces, Heaters, Fireplaces & Air Conditioning 0 08-31-2013 06:49 PM
Furnace blows cold and won't shut off svander Furnaces, Heaters, Fireplaces & Air Conditioning 13 01-08-2012 10:45 AM
Help Furnace Will not shut off Bruceh Furnaces, Heaters, Fireplaces & Air Conditioning 2 01-16-2008 05:47 AM