Old 07-22-2015, 10:01 AM   #15
Rivet Master
 
Ahab's Avatar
 
2008 22' Safari
Oracle , Arizona
Join Date: Oct 2007
Posts: 1,174
When using my SS as a guest room it's plugged into a 20amp circuit. AC runs fine and has been doing this for 8 years in 100º+ temps.
__________________

__________________
Ahab is offline   Reply With Quote
Old 07-22-2015, 10:04 AM   #16
Rivet Master
 
J. Morgan's Avatar

 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,045
Images: 11
I was just through Oracle weekend before last. It was pretty hot....
__________________

__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 07-22-2015, 10:23 AM   #17
2 Rivet Member
 
jdlimages's Avatar
 
1961 22' Flying Cloud
Oklahoma City , Oklahoma
Join Date: Oct 2014
Posts: 29
Sounds like I'm gonna be OK...the 20 amp breaker is seperate (nothing else running on it) and I won't have to use an extension cord. I'll just keep an eye on the temperature of the cord and plug. Thanks!
__________________
jdlimages is offline   Reply With Quote
Old 07-22-2015, 10:33 AM   #18
Rivet Master
 
J. Morgan's Avatar

 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,045
Images: 11
What I will say is that I would use it.

I put a new outlet in my garage for my trailer. I could have wired in a 30 amp, I chose to wire in a 20 amp.
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 07-22-2015, 10:57 AM   #19
Rivet Master
 
NevadaGeo's Avatar
 
1978 31' Excella 500
Genoa , Nevada
Join Date: Jul 2007
Posts: 1,305
If your compressor stalls on start up, unplug it before you let the smoke out. If the compressor don't like the electricity you are feeding it, it'll stall and fume and smoke about it. It don't care what others here are saying about it. Mine, likes 30 amps to start. Won't start on 20 amp. Doesn't matter if it would "run" on 20 amp if it won't start.
__________________
I admit to being powerless over housecleaning and social niceities
Airforums 22655 and now, WBCCI 22655

NevadaGeo
NevadaGeo is offline   Reply With Quote
Old 07-22-2015, 11:49 AM   #20
Overland Adventurer
 
AtomicNo13's Avatar
 
1991 34' Excella
2009 34' Panamerica
Telluride , Colorado
Join Date: May 2012
Posts: 1,885
I'm currently stopped at courtesy parking for the hot day.
I have been using 20 amp service on and off for years. I'll intermittently use this to run the AC. My 24 year old Penguin 1 will start and run happily like this as long as the voltage stays above 105 volts. The key to success is the proper wire, and as few connections as possible. I clean the pins on all my cords with a dremel and brasso once a year.
I think the older units start and run easier than the newer units. For my dometic I also have installed an extreme duty start kit which is a much beefier starting cap. Any appliance ship can spec a good cap for you to replace yours. Money well spent!
__________________
AtomicNo13 is offline   Reply With Quote
Old 07-22-2015, 12:34 PM   #21
3 Rivet Member
 
c177tx's Avatar
 
2008 19' Bambi
Austin , Texas
Join Date: Feb 2006
Posts: 112
Images: 20
I have been full timing in my 2008 Bambi for 6 years. Texas heat, 13.5 AC. On a 20 amp using an adapter, No problems.
__________________
c177tx is offline   Reply With Quote
Old 07-23-2015, 09:18 AM   #22
2 Rivet Member
 
2012 25' FB Eddie Bauer
Virginia Beach , Virginia
Join Date: Apr 2015
Posts: 43
Have been running my AC off a 20 amp circuit all summer with no problem. It is a dedicated circuit with only the AC and a other AS light running....
__________________
Crabpot is offline   Reply With Quote
Old 07-23-2015, 11:07 AM   #23
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Quote:
Originally Posted by wxbuoy View Post
Start up is where the damage to the A/C is going to occur. The sell what is called hard start capacitors to replace the one currently installed. Basically it is a larger voltage storage device so when the compressor kicks in it gets the initial load from it vice dropping the current and doing damage. It then " recharges" while running at normal wattage draw.


Sent from my iPhone using Airstream Forums
If the engineers that design the electrical systems of these A/C units felt that they required capacitors of different ratings, they would have called for them in the original designs.

Using ANY electrical device that deviates from the original specifications in a rated (UL or CE) appliance is not only asking for future problems, but will also de-rate the unit. In a new unit, it will void the warranty and in an older unit, should use of said appliance be the cause of a fire, you can be sure that the insurance company's fire inspectors will be looking very closely for any modifications like this to the appliance.

I have been involved in more than one instance of this and in each case, the unauthorized modifications that the owner performed on an appliance that was determined to be the cause of damage to the RV totally absolved the insurance company of any payment requirement.

JUST USE THE PROPER SIZE CABLES AND OUTLETS!!!!!! It's really very simple.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 07-23-2015, 12:24 PM   #24
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,811
Images: 12
You have pretty much answered what you have to look after within the trailer. Now look at his house.

When we say NOTHING ELSE we mean nothing else on that circuit. No clock in the bathroom or light in some remote room. After the AC has run for an hour or so feel the wires as the enter the panel box. If one is warm you are running above the limit.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 07-23-2015, 12:48 PM   #25
Rivet Master
 
mandolindave's Avatar
 
Join Date: Jan 2004
Posts: 2,115
Images: 4
I did it before I knew it was an issue.

I read somewhere here that, if you going to use an AC with a 20 breaker, that you should turn it on full blast and leave it there, or turn it off.

You are not doing the unit any favors as the cycling off and ON is when the damage is done. Maybe leave a window open so the unit has to keep working. Maybe use open windows as a temp control if it gets a little to cold.

DISCLAIMER….I AM NOT AN ELECTRICIAN
__________________
mandolindave is offline   Reply With Quote
Old 07-23-2015, 02:09 PM   #26
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,811
Images: 12
In general the starting function of any motor does more damage per unit time than running time. That is a fact but not one that should come into the consideration of running an AC unit, especially if you are going to run the unit at a 100% duty cycle by causing a fake load by leaving the windows open.

Most miss the fact that more than half of the function of an AC is to reduce the humidity level in a space. Leaving the windows open you will never achieve anything relating to comfort.

Smaller motors, the fan motor, that can be run at different speeds do this by putting a load resistor in series with the motor windings. That load resistor produces heat while slowing the fan motor. So under this consideration I would suggest running the fan at high speed, no useless heat, and let the AC cycle against the thermostat.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 07-24-2015, 02:23 AM   #27
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Quote:
Originally Posted by NevadaGeo View Post
If your compressor stalls on start up, unplug it before you let the smoke out. If the compressor don't like the electricity you are feeding it, it'll stall and fume and smoke about it. It don't care what others here are saying about it. Mine, likes 30 amps to start. Won't start on 20 amp. Doesn't matter if it would "run" on 20 amp if it won't start.
Since the compressor is hermetically sealed with the motor totally inside the refrigeration shell it will not smoke. If it becomes overheated, the internal thermal cut off will open the circuit, and reset when it cools down. But no smoke.
__________________
idroba is offline   Reply With Quote
Old 07-26-2015, 05:58 PM   #28
Rivet Master
 
J. Morgan's Avatar

 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,045
Images: 11
I bet near everyones RV air conditioner runs on a 20 amp circuit breaker.....

The breaker in the trailer is 99% going to be 20 amp.
__________________

__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker, Breaker!! Bing-Bing Generators & Solar Power 25 09-24-2013 09:25 PM
breaker breaker project66 Batteries, Univolts, Converters & Inverters 4 05-29-2012 09:37 PM
PO rewired my 12V to run only 110V AirSpleen Electrical - Systems, Generators, Batteries & Solar 3 04-06-2007 02:26 PM
Rust: Red Flag? Deal-breaker? Run away? j_c_c Buyer Guidelines 4 08-24-2006 08:10 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:32 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.