50 Amp factory installed power service

I have a question for those folks with Airstream factory installed dual AC units and 50 amp service. The supplied 50 amp power cord is designed for a matching 50 amp power outlet. The information I have read is that the wire size (should be #6 copper for 50 amps) in the supplied cord is for 120VAC service even though there are four conductors and pins.

I searched the major portable generator brands 5000 to 6500 watt generators and none offered a 50 amp power outlet. They usually had a twist lock 30 Amp at 120Vac and a 30 Amp at 120/240Vac power outlet.

The 2013 Airstream parts book shows a 50 Amp Square D box that could support 8 wide breakers or 16 narrow breakers with a service rating of 100 Amps. The three connectors are for two 120 VAC legs and a neutral. I imagine there is a separate grounding bar as well.

The four wire power cord implies two 120vac legs, a neutral and a grounding conductor. I could understand the concept of bringing in two 120VAC lines and just putting the second AC on one leg by itself.

Then when plugged into a 30 amp 120VAC service, the second AC would not attempt to start as it lacks power. Simple, except the option to run either AC would be precluded. Also, if the park power outlet actually is wired with 50 amps on one leg, there would be no way to get power to the second AC.

The other option would be a voltage sensing switch that would send two 120vac input lines independently to the lugs of the power panel and if only a single line 120Vac power was sensed, it would cross connect and send the one leg power to both lugs in the panel.

Returning to the generator outlets I found. A 30 amp 120/240 twist lock would allow 30 amps on each 120VAC leg to the trailer. Since single AC trailers have 30 amp service, one leg would function as normal and the other leg could feed AC #2. There could be an imbalance on the neutral wire as the equipment load might not be evenly distributed in the panel.

Can anyone shed some light on the wiring in the 50 amp service coaches?
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 06-22-2013, 09:40 AM   #2
Rivet Master
 
m.hony's Avatar
 
2013 30' Classic
Greenwood , Mississippi
Join Date: Oct 2012
Posts: 12,111
There is no generator with 50 amp output as you have discovered. There is talk of pairing generators. You plug your 50 amp umbilical cord into the 30 amp generator output with an adapter. Don't try to run both air units.
__________________
2013 Classic 30 Limited
2007 Silver Toyota Tundra Crew Max Limited 5.7 iForce
2006 Vivid Black Harley-Davidson Road King Classic
1999 Black Nissan Pathfinder LE
TAC #MS-10
WBCCI #1811, Region 6, Unit 56
Airforums #70955
m.hony is offline   Reply With Quote
Old 06-22-2013, 10:38 AM   #3
Rivet Master
 
blkmagikca's Avatar

 
1987 32' Excella
Nepean , Ontario
Join Date: Mar 2006
Posts: 1,414
I previously had a 34-ft LY diesel pusher. It had a 6500-Watt LP-powered generator that had a 30-amp and a 20-amp output. (Nominally 30-amp at 240-volts) This setup powered both 13,500 BTU air-conditioners simultaneously - the rear one on the 20-amp circuit. The rig also came with 2 ATS (automatic transfer switches). One of the mods we made was to change the 30-amp shore line to a "50-amp" shore line, which meant going from a 120-volt 30-amp 3-wire cable to a 240-volt 30-amp 4-wire cable. We had to combine the two ATS switches into one (the original circuit had the neutrals being switched - advice received from CSA was that this was not necessary). The ATS switches have a built-in 60-second time delay relay to allow the generator to reach full potential before switching the load over to it.
__________________
VE3JDZ
AIR 12148
1987 Excella 32-foot
1999 Dodge Ram 2500HD Diesel
WBCCI 8080
blkmagikca is offline   Reply With Quote
Old 06-22-2013, 11:25 AM   #4
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by m.hony View Post
There is no generator with 50 amp output as you have discovered. There is talk of pairing generators. You plug your 50 amp umbilical cord into the 30 amp generator output with an adapter. Don't try to run both air units.
Champion 9500 Watt Portable Generator - Champion Generators 41534 - Portable Generators - Camping World
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 02:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.