Odd behavior of AC condensation draining

I have installed a brand new dometic low profile AC on my trailer and used the "factory" condensate catch and drain pan. I installed the AC during the early stages of a full monty, so I am confident that there are no kinks, or other interesting features to my drain hose. This work was done a couple of years ago.

So when I was running my AC recently, I noticed that after running for a few hours, no water was coming out of my condensate hose. If I turned the AC off, water would literaly pour out of the drain hose in a steady stream for several minutes. As an experiment, I decided to not turn off the AC and see what would eventually happen, expecting the condensate water to eventually start dripping into the interior of the trailer, but instead it started running down the outside.

It appear that there is sufficient vacuum created by the moving air to keep the condensate from flowing down the drain tube. Anyone else experienced this? Any suggestions for a cure?

thanks in advance!
Belegedhel is offline   Reply With Quote
Old 06-22-2016, 09:59 AM   #2
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
Air flow is most likely the problem but I doubt it is vacuum. To create a vacuum that would hold a 7 ft column of water is extreme. More likely the air flow is holding the water back from getting to the drain, a wave.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 06-22-2016, 01:03 PM   #3
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 3,320
Hmmm...You might be on to something--does sound more plausible than a vacuum. Guess I'll have to drop the ceiling unit again and try to see where air might be getting into the drain channel.
Belegedhel is offline   Reply With Quote
Old 06-22-2016, 02:00 PM   #4
Rivet Master
 
HiHoAgRV's Avatar

 
1991 34' Excella
1963 26' Overlander
1961 26' Overlander
Central , Mississippi
Join Date: Nov 2006
Posts: 5,919
Images: 29
Blog Entries: 49
I have the same issue with the same AC unit I installed on the rear of my 34'. That's been 5? years ago? The original AC on the front of the trailer never has this issue.

As soon as the AC fan shuts off It makes a huge gusher of water, most of the time the hose will drain it all but on occasion it will spill inside the trailer. The gusher isn't random, its every cycle that has run enough to pull humidity out of the air.

At the time there were a number of threads regarding the same problem on New 'Streams and if I recall, the problem went away with a small redesign of the AC unit. I'm betting that the airflow keeps an extreme amount of water hung up in the system, when the fan stops it all dumps into the catch system at once.
__________________
Hi Ho Silver RV! Vernon, Sarah, Mac the Border Collie(RIP) -
A honkin' long 34' named AlumaTherapy https://www.airforums.com/forums/f20...num-54749.html
and a 26' '63 Overlander, Dolly https://www.airforums.com/forums/f10...ome-71609.html
HiHoAgRV is offline   Reply With Quote
Old 06-22-2016, 02:05 PM   #5
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 3,320
I was surprised that if I left it run long enough, the water would begin running down the outside of the trailer, suggesting that it was making it into the catch pan, but that something about the airflow was keeping it from going down the drain tube. I guess I should try my experiment again and ascertain exactly where it is coming from in order to get on the roof. I was just assuming it was coming out of the weep holes in the pan, but maybe it was draining from the AC itself.
Belegedhel is offline   Reply With Quote
Old 06-23-2016, 11:49 AM   #6
Rivet Master
 
kdickinson's Avatar
 
Currently Looking...
Taos , New Mexico
Join Date: Oct 2014
Posts: 566
If it's not too late there is an option on several newer A/C's in which you can add an active pump. I paid the extra $100 for the pump and it actively pumps the condensate out of the holding pan at start up. On average it seems to pump ~ 2-tablespoons and up to ~ 1/4 cup of water each time the A/C starts up through the day. The original A/C we had (Armstrong) used to leak into the trailer and of course the drain tube from which it leaked was directly above the bed. When we replaced the A/C last year I felt the additional cost of the pump was justified
kdickinson is offline   Reply With Quote
Old 06-23-2016, 01:51 PM   #7
4 Rivet Member
 
B00merang's Avatar
 
2010 20' Flying Cloud
Hailey , Idaho
Join Date: Nov 2014
Posts: 414
I had this problem a year ago...except my AC would discharge a lot of water into the camper. Turns out my (FC's) tubes were clogged. Used high pressure air to blow them out. The second thing I was told by my AS dealer is to leave the fan on "Auto"...I had it set on low and the unit's plumbing would freeze up. Maybe look whether either of these two issues could apply to your situation. jon
B00merang is offline   Reply With Quote
Old 06-23-2016, 02:44 PM   #8
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
Quote:
Originally Posted by B00merang View Post
The second thing I was told by my AS dealer is to leave the fan on "Auto"...I had it set on low and the unit's plumbing would freeze up. Maybe look whether either of these two issues could apply to your situation. jon
The position of the fan switch should not effect the unit freezing. ACs freeze up because of a low charge. A unit with a low charge will allow the suction pressure to drop below the freezing point on the coil and if the load is low across the coil it will freeze. Generally a unit is charged with enough refrigerant to keep the coil temperature around 40 degrees. This temperature is enough to cause condensation and thus humidity reduction while cooling the discharge air.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 06-23-2016, 08:02 PM   #9
Rivet Master
 
GammaDog's Avatar
 
2014 25' FB Eddie Bauer
Vero Beach , Florida
Join Date: Sep 2014
Posts: 695
Images: 26
I have precisely the same issue with water dripping (or streaming) into the trailer after long AC cycles in high humidity. It's always on the curb side of the AC unit. My condensate tube is not blocked because I also get drainage from the tube on the street side just in front of the front tire. I'm planning to have it looked into at my next service appointment.
GammaDog is offline   Reply With Quote
Old 06-23-2016, 08:34 PM   #10
Remember, Safety Third
 
Jim & Susan's Avatar

 
1973 27' Overlander
Catfish Corners , Georgia
Join Date: Oct 2004
Posts: 5,720
Images: 39
We've had the problem of the condensation running down the side of the Airstream a couple of times while out camping. Turns out we were just a little out of level, so the pan was "crooked" or "slanted" just enough to throw everything off. The original Armstrong is still working in ours, so no new items have been added. Got a few drips out of the line under the fridge, but the majority of the water ran down the side.

Jim
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 06-23-2016, 08:34 PM   #11
Rivet Master
 
HiHoAgRV's Avatar

 
1991 34' Excella
1963 26' Overlander
1961 26' Overlander
Central , Mississippi
Join Date: Nov 2006
Posts: 5,919
Images: 29
Blog Entries: 49
It's pretty common down here in the south for the units to freeze up in high humidity/low fan speed. Both of my trailers do it, my neighbors does it and a co-workers does it. High fan speed keeps the coils above freezing, low speed...well...not so much.

2 weeks back we had back to back nights of freeze up between 2 trailers, the common item was who ever cooked in the camper, had a freeze up. All it took to restore operation was flip from low-cool to hi-fan for :10.

I awoke to warm temps and a funny growling fan sound, knew instantly wuz up.

It's no fun at 2:00 am. Crawl out of bed, try to recall what knob does what, flip to high fan, wait for the fan to sound normal (air flow increases), once again try to recall what knob turns the unit back to "cool" and crawl back into bed..."Ouch"...sorry honey, didn't mean to awake you.
__________________
Hi Ho Silver RV! Vernon, Sarah, Mac the Border Collie(RIP) -
A honkin' long 34' named AlumaTherapy https://www.airforums.com/forums/f20...num-54749.html
and a 26' '63 Overlander, Dolly https://www.airforums.com/forums/f10...ome-71609.html
HiHoAgRV is offline   Reply With Quote
Old 06-24-2016, 06:13 AM   #12
4 Rivet Member
 
2011 30' Flying Cloud
Arvada , Colorado
Join Date: Feb 2008
Posts: 411
I written about this issue before, but we experienced condensation drip into our trailer from both heat pump units in heat mode, but not cool mode. We recently had the two units serviced at the Jackson Center plant during our relocation west. Result is that now only the rear unit leaks into the trailer in heat mode, the front unit seems fine. We now have an appointment this fall for the local Denver dealer to pick up in Airstream's warranty for the work.
Jack46 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic RM3862 Refrigerator Cooling Behavior nickmeloy Refrigerators 14 06-08-2013 08:32 PM
PD9260 strange behavior Skater Batteries, Univolts, Converters & Inverters 12 04-13-2012 11:44 PM
Strange Hot Water Behavior Jim Foster Water Heaters, Filters & Pumps 4 05-28-2010 08:43 PM
Strange 12v Behavior in '67 GT tphillips Electrical - Systems, Generators, Batteries & Solar 2 10-08-2009 05:58 PM
Explain this Dump Valve behavior..... Chuck Waste Systems, Tanks & Totes 2 08-28-2003 11:18 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:02 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.