Not Getting Sufficient Heat From Furnace

Question for you more experienced DYI folks:

The furnace in our 25' 07 Safari is working but putting out insufficient heat.
The unit starts fine and provides heat, just seems not near as much heat as I recall last season.

Using my IR Thermometer, I measure exhaust temp at unit outside about 125 degrees, inside at the register closest to the furnace about 115 after the unit has been running a few minutes. Would anyone know what the normal temps should be at these locations?

We had the LP gas regulator replaced about two months ago, so I assume it is receiving sufficient gas.

Any thoughts appreciated.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 10-23-2016, 09:26 AM   #2
Rivet Master
 
2019 27' Globetrotter
Missouri Valley , Iowa
Join Date: Sep 2008
Posts: 512
This is unlikely to be your problem, but could be something to check. On my '89 Excella, I had been working on the flexible furnace ducts last season. For some reason I did not hook the 2 flex hoses up that run to the bathroom and bedroom areas. I checked the furnace a couple of weeks ago before going to the installation rally for our unit. It was toasty under the sink area but chilly in the rest of the trailer!! A simple fix. Maybe you have a similar problem with the ductwork for your furnace.

Dan
Farmer Dan is offline   Reply With Quote
Old 10-23-2016, 09:34 AM   #3
Rivet Master
 
dkottum's Avatar
 
2012 25' Flying Cloud
Battle Lake , Minnesota
Join Date: Jun 2009
Posts: 7,714
The output air temp would be somewhat dependent on it's temp going in, so could this be different than before? Do you think the fan is running at the same speed, is there a voltage drop (other stuff plugged in or on and drawing down the voltage, it doesn't take much with a 30 amp supply). Was the regulator set for the correct pressure when installed?
__________________
Doug and Cheryl
2012 FC RB, Michelin 16, ProPride 1400
2016 Ram 1500 Laramie Crew Cab 4X4 Ecodiesel 3.92 axles

The Truth is More Important Than the Facts
dkottum is offline   Reply With Quote
Old 10-24-2016, 06:35 AM   #4
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
Thanks for the responses so far.......

1. We are getting great airflow and the ducts all appear to be connected properly.
2. And outside air temps pretty consistent.
3. I do not own a gauge to measure the gas pressure, so need to check that. The tech that installed it seemed really competent, so I would be surprised if that is the issue....and he took a measurement after installation to make sure it was correct.

Still would be interested in what a normal exhaust temp might be and what temp you should read at the inside heat register closest to the furnace.

My best guess is perhaps the burner needs cleaning or servicing to ensure proper flame....but that is a guess at this point.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 10-24-2016, 02:48 PM   #5
2 Rivet Member
 
Runnells , IA
Join Date: Jul 2012
Posts: 29
Would you post your solution if/when you find one please? We have a similar problem. Furnace worked fine last winter. Air coming out of vents is hardly above room temp but the exhaust is HOT. Air flow seems normal.

Thanks for any help.
sid42 is offline   Reply With Quote
Old 10-24-2016, 02:55 PM   #6
4 Rivet Member
 
2016 30' International
Florence , Alabama
Join Date: Oct 2016
Posts: 493
Just my two $0.02, but that exhaust temp sounds way low. I have nothing to base this on, but is would expect closer to 200.
joshjack is offline   Reply With Quote
Old 10-25-2016, 06:11 AM   #7
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
Quote:
Originally Posted by sid42 View Post
Would you post your solution if/when you find one please? We have a similar problem. Furnace worked fine last winter. Air coming out of vents is hardly above room temp but the exhaust is HOT. Air flow seems normal.

Thanks for any help.
Sure will!
Thanks for responding.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 10-25-2016, 06:28 AM   #8
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
The air temp coming out of the supply side should be roughly 80-ish degrees F above the return intake air temp. Not sure what the AS design calls for. Thus the temps in Post #1 seem low. Can you remove one of the ducts at the furnace and measure the temp being discharged, vs. the interior temp of the trailer? Not sure if you have access to do this. If not, letting it run for a few minutes and measuring the discharge at the supply register is more or less the same, so taking the duct off is not that crucial.

Burner servicing/cleaning sounds like a good plan, as they can get really rusty especially if you travel in humid or foggy areas, in particular near salt water IMO, like Spanish Fort AL for instance!

Once disassembled, a new burner might be a good investment for a 10-year old trailer +/-. Other nearby parts would be candidates for new replacements also IMO, like the pilot light assembly or Piezo etc. sparker/igniter, depending on what you have.

Good luck!

Peter
OTRA15 is offline   Reply With Quote
Old 10-25-2016, 10:47 AM   #9
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Quote:
Originally Posted by Alumitater View Post
Using my IR Thermometer, I measure exhaust temp at unit outside about 125 degrees, inside at the register closest to the furnace about 115 after the unit has been running a few minutes. Would anyone know what the normal temps should be at these locations?
Typically 140 at the register and a little higher at the exhaust.

Quote:
We had the LP gas regulator replaced about two months ago, so I assume it is receiving sufficient gas.
Only way to tell for sure is to measure the gas pressure while the furnace is running.

Be sure your propane bottles are reasonably full. It's easy to fool yourself if they don't have float gauges. Best thing to do if there is any doubt is remove them from the trailer and weigh them on a bathroom scale.
__________________
To learn to see below the surface, you must adjust your altitude
Jammer is offline   Reply With Quote
Old 10-26-2016, 06:17 AM   #10
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
Peter and Jammer:

Just the kind of information I was hoping for.
Thanks for passing along.

Sounds like a trip to the dealership is the best resolve....I undertake many repairs, but gas issues....now that's different!
I will post the results, my be a couple of weeks.

Thanks again to all who contributed.
Tom
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 10-26-2016, 08:05 AM   #11
2020 Classic 33
 
Box Elder , South Dakota
Join Date: Oct 2013
Posts: 1,731
Images: 1
I checked my 2015 Classic, larger furnace, but getting 160-175 out of the primary vent by the door and 130-145 in the rear of the trailer. Exterior exhaust about 185.
__________________
Gary
2020 Classic 33 Twin, 2019 Ram 3500 Longhorn, ProPride
NØVPN
ghaynes755 is offline   Reply With Quote
Old 10-26-2016, 09:49 AM   #12
Rivet Master
 
jdalrymple's Avatar
 
2009 27' FB Flying Cloud
1982 31' International
1991 35' Airstream 350
Jay , Oklahoma
Join Date: Oct 2006
Posts: 1,706
Dirt daubers in the the burner/exhaust tube?



Regards,

JD
__________________
Jeff & Cindy
'09 27FB Flying Cloud;'82 31 International
'91 350 LE MH; '21 Interstate 24GT


jdalrymple is offline   Reply With Quote
Old 10-26-2016, 11:36 AM   #13
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
Thanks Alumitater, good luck at the dealer!

Peter
OTRA15 is offline   Reply With Quote
Old 10-27-2016, 05:51 AM   #14
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
Quote:
Originally Posted by ghaynes755 View Post
I checked my 2015 Classic, larger furnace, but getting 160-175 out of the primary vent by the door and 130-145 in the rear of the trailer. Exterior exhaust about 185.
Thanks! That sounds more like it.
We have Foley Airstream nearby in Gulfport....good folks.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 10-27-2016, 06:41 AM   #15
2 Rivet Member
 
h2ocoolerman's Avatar
 
2017 27' International
Graham , Washington
Join Date: Sep 2016
Posts: 38
Definitely would recommend a inspection. One common issue I have seen is partial obstruction of the burner orifice. Usually by spider nests. The normal heat rise across the heat exchanger should be listed somewhere on the unit or literature. The two main factors are the temp of the flame and the airflow across the heat exchanger.
h2ocoolerman is offline   Reply With Quote
Old 10-28-2016, 06:35 AM   #16
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
Quote:
Originally Posted by h2ocoolerman View Post
Definitely would recommend a inspection. One common issue I have seen is partial obstruction of the burner orifice. Usually by spider nests. The normal heat rise across the heat exchanger should be listed somewhere on the unit or literature. The two main factors are the temp of the flame and the airflow across the heat exchanger.
Thanks, good guidance. I suspect a spider may be my issue. Just a gut feeling.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Old 11-14-2016, 07:54 PM   #17
4 Rivet Member
 
Alumitater's Avatar
 
2007 25' Safari
Fairhope , Alabama
Join Date: Jul 2011
Posts: 302
update on issue

Thought I would report I took some time and my air compressor and gave the furnace cabinet and outlet areas a good blowing out. Then cranked up the furnace and after a few minutes was reading 140+ at register closest to furnace and 180+ at exhaust.

Cautiously optimistic that may have been spider web issue or some other obstruction. Will continue to test and monitor as our temps begin to drop here in LA (Lower Alabama).

Thanks for all your suggestions and information.
__________________
Tom and Robin
2007 Safari 25' FB Twin
"If you have to go through a minefield....follow somebody"
Alumitater is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 07:58 PM
Sufficient Sway Bar Tension? Frank&Mike Hitches, Couplers & Balls 7 10-29-2012 04:37 AM
Is my GMC sufficient? macstrange Tow Vehicles 8 12-06-2011 02:59 AM
New 2008 airstream *dwr* ccd * fully self sufficient * eBay Watch Airstreams on eBay 0 06-15-2009 01:30 PM
New 2008 airstream *dwr* ccd * fully self sufficient * eBay Watch Airstreams on eBay 0 05-21-2009 12:00 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 01:24 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.