Old 12-14-2010, 06:31 PM   #81
Rivet Master
 
Jim Foster's Avatar
 
1965 17' Caravel
1983 27' Excella
Walnut Grove/Laguna Woods , California
Join Date: Jun 2004
Posts: 1,635
Send a message via Yahoo to Jim Foster
Quote:
Originally Posted by dznf0g View Post
I'm not sure if the heat will hurt the bilge blower, or computer fan like in another post, but let us know how it works out.
I really don't think heat will be an issue. We boated in the Sacramento Delta for thirty years. The engine compartment on a run-a bout boat can get very warm sitting in the sun in the summer.

If I do this, we'll all find out. I will certainly post my findings. Won't happen until after the first of the year, as we will be on the road until then. I really don't like to get into projects, even small ones, on the road if I can help it. It always seems that the one tool that will make the job easier has not made the trip.
__________________
Past President, El Camino Real Unit WBCCI#6620
Street Rod Builder (see avatar)
Kite flier (check out links below)
https://www.youtube.com/watch?v=Bp3nuNtlZcA&t=331s
https://www.youtube.com/my_videos?feature=mhee
Jim Foster is offline   Reply With Quote
Old 12-14-2010, 10:49 PM   #82
3 Rivet Member
 
Whirlaway's Avatar
 
2008 27' Classic FB
Anytown , Massachusetts
Join Date: Feb 2007
Posts: 249
Well you all inspired me to pull my AS apart to find out why I had very little heat

After spending the weekend on my side, back and belly trying to figure out this heating, I am more confused now. There seems no reasoning why the heat blasts the living space then there's no or little heat in the fb and bath.

I have a little more than a ten (10) degree difference between the two (2) areas. Nothing new everyone is reporting these numbers. However the FB has the thermostat and it's calling for heat and not getting it. Can we trick the thermostat somehow?

When the heat is running it's roaring in the galley area.

Lin.
__________________
Life Is Not A Dress Rehersal
It's okay to have too much fun
WBCCI #8701* TAC MA-1 * NEU UNIT
Gracie...A Liver & White GSP
Get busy livin', or get busy dyin'." - The Shawshank Redemption
Whirlaway is offline   Reply With Quote
Old 12-19-2010, 08:12 PM   #83
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
OK gang another night for carving up a perfectly good new trailer. You folks with the 1975 Sovereigns who are wishing you had just bought a new traylah that didn't need any work... it's not like that...


The supplies showed up quickly from DWI and one other source. Pictured are the two sizes of duct, a 4x4x2 tee, a 4" Atwood duct adapter, and a 4x2 reducer. The Atwood duct adapter had to be ordered from another place because DWI doesn't sell them. In the end I did not need use the T. In addition to these materials I needed a 4" stainless steel clamp and a 2" stainless steel clamp, and a couple of sheet metal screws.

Tools required were a 2 5/8" hole saw, cordless drill, drill bits, a hammer and punch, and screwdrivers.
Attached Thumbnails
Click image for larger version

Name:	parts.jpg
Views:	148
Size:	86.9 KB
ID:	117360  
Jammer is offline   Reply With Quote
Old 12-19-2010, 08:19 PM   #84
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
It turned out there wasn't enough clearance for two Ts so I ended up moving the 2" outlet on the furnace to the next position forward. This required punching out the knockout with a hammer and drift, fiddly to do with the furnace installed, but possible with perseverance. The 2" outlet was moved to this opening and the new 4" outlet installed in the aftward one from which the 2" outlet had been removed.

The outlets attach using a clever sort of bayonet arrangement but the mother ship put in a couple of screws in each one, too, just to be sure. In true mother ship fashion one of them didn't actually hit the furnace and so served no purpose. Start using a jig and predrilling them before assembly in a more controlled environment, guys. But I digress.

I followed the mother ship's lead and used a screw in each one in addition to the retention provided by the bayonet.

The completed shot does not show a 4" clamp because I was one short in my planning. Some other day.

The existing 2" duct that disappears into the floor is then reattached to the front outlet, and a new piece of 4" duct is attached and run aftward.
Attached Thumbnails
Click image for larger version

Name:	furn-b4.jpeg
Views:	125
Size:	56.4 KB
ID:	117361   Click image for larger version

Name:	furn-z.jpeg
Views:	171
Size:	62.1 KB
ID:	117362  

Jammer is offline   Reply With Quote
Old 12-19-2010, 08:24 PM   #85
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Moving aftward the next shots show the T and reducer installed under the drawers under the microwave. First I assembled the T and reducer using sheet metal screws. They fit snugly so no tape or sealant is required. Then the new 4" duct from the furnace is cut to fit the large end of the T, and two pieces of 2" duct are attached to the outlets. The whole thing fits under the drawers.
Attached Thumbnails
Click image for larger version

Name:	t begin.jpg
Views:	125
Size:	45.8 KB
ID:	117363   Click image for larger version

Name:	t complete.jpeg
Views:	103
Size:	34.2 KB
ID:	117364  

Click image for larger version

Name:	drawers-b4.jpg
Views:	123
Size:	59.1 KB
ID:	117365   Click image for larger version

Name:	drawers-z.jpg
Views:	111
Size:	87.7 KB
ID:	117366  

Jammer is offline   Reply With Quote
Old 12-19-2010, 08:29 PM   #86
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
The two new 2" ducts proceed under the range, where I couldn't get a photo, and then emerge under the false floor in the coat closet. I had to use the hole saw to drill a hole for one of them because there is some excess internal wall that blocks access.

These next shots are looking down into the coat closet. In the bottom of the photo (toward the center of the trailer) you can see the wall box for the pic-a-watt heater I installed previously. I removed the existing 4x4x2 T and the short section of 2" duct that went down to the fresh water tank. I was able to splice the two existing pieces of 4" ductwork together by hand and will run some tape over them at some point. This is what the mother ship does (see downthread). The other piece of 2" duct continues to the shower area aft of the closet.

The changes leave this area no more or less cluttered than before, since the T is gone, but there's one more duct.
Attached Thumbnails
Click image for larger version

Name:	closet-b4.jpeg
Views:	106
Size:	51.9 KB
ID:	117367   Click image for larger version

Name:	closet-z.jpeg
Views:	112
Size:	46.7 KB
ID:	117368  

Jammer is offline   Reply With Quote
Old 12-19-2010, 08:37 PM   #87
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
My original plan had been to run one of the 2" ducts to the carpeted box at the head of the curbside bed (I have a twin) where the existing 4" duct emerges in a register.

It turns out that the way Airstream builds these, the bulkhead between the shower and the bedroom is the same for twins and queens, so there's only a 4" hole. Airstream spliced a couple feet onto the duct using clear packing tape. Jackson Center, meet duct tape; despite widespread misuse it is in fact the proper product for joining ductwork.

Anyway, the only access into this area is through the 4" hole at the front of the carpeted box, and the box is assembled and attached to the underbed cabinetry and the bulkhead using staples. Experience has shown that it is nearly impossible to disassemble stuff like this without damaging it.

I've decided to just let the 2" duct terminate behind the shower, for now. At some point I may try to get a right angle drill and a hole saw inside the duct outlet but that's going to be a time-consuming ship-in-a-bottle type of project and great care will be required to be sure the hole doesn't end up going through the fiberglass shower stall or some other equally critical component.
Attached Thumbnails
Click image for larger version

Name:	bedroom.jpeg
Views:	101
Size:	55.3 KB
ID:	117369  
Jammer is offline   Reply With Quote
Old 12-19-2010, 08:42 PM   #88
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Here's a shot of the bottom of the closet with the ducts removed. It's hard to see what's what but the short of it is that the loose duct that terminates in this area is warming one end of the fresh water tank. You can see the tank sensor near the center of the photo, and the PEX tank outlet that goes to the water pump at left center. I don't know whether the sheet metal at the top of the photo is double wall or is the same piece that you can see under the trailer from the outside. I believe the vertical line to the right is one of the low point drains.
Attached Thumbnails
Click image for larger version

Name:	freshtank.jpeg
Views:	127
Size:	67.9 KB
ID:	117370  
Jammer is offline   Reply With Quote
Old 12-19-2010, 09:08 PM   #89
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
I blocked off half of one of the front heat outlets temporarily with some foam to take measurements. I have some 1/4" flame retardant foam sheeting on order. When it arrives I'm going to wrap into a cylindrical shape and put inside the very short section of ducts coming forward from the furnace, both for noise control and to reduce the airflow by an equivalent amount.

I'll copy my earlier observations from upthread, and add the difference between the gaucho and the other locations in brackets.

Quote:
Originally Posted by Jammer View Post
In 15 degree outside temps, running the furnace (only, not any of my electric heat), I recorded these temperatures:

Gaucho 69
Dinette 66 [-3]
Head 61 [-8]
Bed 58 [-11]
Tonight it is a little cooler, around 11 degrees. The measurements now:

Gaucho 68
Dinette 66 [-2]
Head 65 [-3]
Bed 59 [-9]

The cold weather makes this a somewhat more demanding test, and I estimate a 5% reduction in the bracketed values if I were to retest in 15 degree conditions.

I'm pleased with the improvement in the head. The temperature measured at the bed, while better, is still a disappointment.
Attached Thumbnails
Click image for larger version

Name:	partclosed.jpeg
Views:	152
Size:	39.6 KB
ID:	117371  
Jammer is offline   Reply With Quote
Old 12-19-2010, 09:28 PM   #90
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Looking at the duct temperatures, upthread we had:

Quote:
Originally Posted by Jammer View Post
Galley outlets - 160 degrees
Head - 134 degrees
Bedroom - 104 degrees
With the front outlet half blocked off as shown above I measured these values after the modifications:

Galley outlets - 162
Head - 137
Bedroom - 112

I'm not sure where to go from here. While the logical next step would be to insulate the ducts, clearance is tight.
Jammer is offline   Reply With Quote
Old 12-19-2010, 10:18 PM   #91
Rivet Master
 
Westfalia's Avatar
 
Some Place with a German Name , Texas
Join Date: Jun 2005
Posts: 908
Images: 35
Send a message via AIM to Westfalia
Have you considered using some reflectix wrap for some of the straight runs of ducting? its not high r value but is better than what is there now and is thin enough to work with in tight spaces. I also ended up wrapping some of the enclosed compartments in reflectix on exterior surfaces to slow the heat transfer.
Westfalia is offline   Reply With Quote
Old 12-19-2010, 10:30 PM   #92
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
That's the sort of thing I'll have to consider. I'm going to have to measure and figure out how much clearance there really is to work with. Part of the problem is that, to insulate enough of the run, the range will have to come out, which will be a bigger project than what I've done so far.

Another possibility might be to better insulate the exterior compartment doors. The twin layout has three large externally accessible storage lockers. The queen only has one. It's one of the advantage of the twin layout. But perhaps that contributes to the heat loss.
Jammer is offline   Reply With Quote
Old 12-19-2010, 10:46 PM   #93
Rivet Master
 
Dave Park's Avatar
 
2005 22' Safari
Hyde Park Place , Ohio
Join Date: Jul 2010
Posts: 973
You can also apply a layer of reflectix or similar to the inside walls of the cabinets, especially around that run. That will raise the ambient temperature in those spaces a bit, and as we were taught in school, heat likes to travel down a gradient and does so faster on a steeper gradient. It will also help with condensation (or move it somewhere better ventilated.)
__________________
TX-16
Dave Park is offline   Reply With Quote
Old 12-19-2010, 11:47 PM   #94
Rivet Master
 
Westfalia's Avatar
 
Some Place with a German Name , Texas
Join Date: Jun 2005
Posts: 908
Images: 35
Send a message via AIM to Westfalia
Dave , that is exactly what I had done. While I have no quantative data on temperature increases, i do feel that this has helped duct temp to the front bedroom and reduced drafts.
Westfalia is offline   Reply With Quote
Old 12-20-2010, 07:32 AM   #95
Site Team
 
Aage's Avatar
 
1974 31' Sovereign
Ottawa , ON
Join Date: May 2008
Posts: 11,219
Images: 25
It's a pity that AS decided to go with that plastic over spring "cheap dryer vent" design of supply tube for the hot air.

The added resistance due to the turbulence the grooves create costs you a lot of air pressure on long runs, plus encourages dust to collect fast, as anyone with one of those tubes on their dryer already knows.

As I previously stated, on mine they still used a mini version of what tin-whackers still put in new homes (steel). And just re-sealing the joints with duct tape improved the heat and airflow on the long runs (like to the bathroom in the rear) on my '74 Sov.

Question: in the photo showing two vents (one is half plugged), are they both hot air supply vents?
__________________
“Courage is being scared to death, but saddling up anyway.”
...John Wayne...........................
Aage is offline   Reply With Quote
Old 12-20-2010, 10:11 AM   #96
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
The two vents are both hot air supplies. They are within inches of the furnace and emit a good deal of heat and noise.
Jammer is offline   Reply With Quote
Old 12-20-2010, 12:22 PM   #97
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 8,377
Images: 18
Blog Entries: 55
Quote:
Originally Posted by Jammer View Post
The two vents are both hot air supplies. They are within inches of the furnace and emit a good deal of heat and noise.
Hi, your trailer and your furnace are larger than mine, but my furnace only has three vents. One in the bedroom, one in the bathroom, and one in the livingroom. The one in the livingroom is located under my oven, by my entrance door, and only inches away from the actual furnace; Could you block one of the close ones off so you can get better circulation on the other ones? With two vents that close to the furnace, I can't believe that there would be much pressure or heat left for the vents 15' to 20' away.
__________________
Bob 2005 Safari 25-B
"Le Petit Chateau Argent" Small Silver Castle
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 12-20-2010, 12:38 PM   #98
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Quote:
Originally Posted by ROBERTSUNRUS View Post
Hi, your trailer and your furnace are larger than mine, but my furnace only has three vents. One in the bedroom, one in the bathroom, and one in the livingroom. The one in the livingroom is located under my oven, by my entrance door, and only inches away from the actual furnace; Could you block one of the close ones off so you can get better circulation on the other ones? With two vents that close to the furnace, I can't believe that there would be much pressure or heat left for the vents 15' to 20' away.
Robert,

I'll bet, if you look in your furnace installation materials, it will say that a minimum of three 4" ducts are required for proper airflow volume and heat removal from furnace box. I know the larger furnace in mine requires four 4" exits. Blocking off one of the vents may raise the furnace plenum temperature to a level unacceptable from a durability and safety standpoint.
dznf0g is offline   Reply With Quote
Old 12-20-2010, 12:59 PM   #99
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Robert,

It has been suggested. The Atwood installation guide for this furnace says that a minimum of four, 4" diameter ducts leading to nonadjustable (that is, always fully open) registers are required. Blocking off one of the front outlets, completely, would leave only three 4" diameter ducts plus the three 2" outlets, somewhat less than the total area Atwood says is required. In measuring the outlet temperature, it's 170 degrees once the trailer is warm. The high limit trip point for the furnace is 190 so there's not much blocking off of the outlets that I can do without getting close to the trip point.

The furnace is more or less in the center of the trailer and so the idea of having two forward vents and two aft vents makes sense except for the fact, as you point out, that the two forward vents emit far more heat due to their proximity to the furnace.
Jammer is offline   Reply With Quote
Old 12-20-2010, 01:11 PM   #100
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 8,377
Images: 18
Blog Entries: 55
Hi, then what if we block off one of the front vents and run a new one to the bedroom instead? [two in the bedroom and one in the living room]
__________________
Bob 2005 Safari 25-B
"Le Petit Chateau Argent" Small Silver Castle
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Reply

Tags
furnace tuning


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 07:58 PM
New AC, Heat Pump or Heat strip? firedog 1990 - 1993 Excella 3 01-22-2010 04:23 PM
The Heat is ON!! GlenCoombe Mechanics Corner - Engines, Transmission & More... 5 10-09-2005 03:48 PM
Odd back-to-back eBay auctions .... summerkid Trailer Values 5 09-12-2005 12:34 PM
need heat whistler Furnaces, Heaters, Fireplaces & Air Conditioning 3 06-07-2004 01:32 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 02:45 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.