New NT-30 Woes
Installed new Suburban Nt-30 over last winter. Used it on maybe 3 occasion this summer and it seemed to work fine, although it was never needed longer than a few minutes to take chill out in AM. Well over this weekend it was needed for longer. It seemed to work fine and brought space up to temp nicely. However, the next day when I turned up t-stat fan kicked on for maybe a minute but then shut off. No sound of ignitor. Turned t-state off and then back on and same senario. Thought maybe low voltage as we had no shore power. Well now home and shore power hooked up and same symptoms. Not sure what would prevent ignitor or valve from opening. Does high limit reset itself if tripped? Would fan still turn if high limit tripped. Bad board?? Dont know where to start?
|
|
|
09-21-2008, 07:53 PM
|
#2
|
Rivet Master
Currently Looking...
1984 31' Airstream310
Ajo
, Arizona
Join Date: Mar 2007
Posts: 7,649
|
The fan would still turn, though blow no heat should the board be bad. Hard to believe such a fresh unit would
fail. I would suspect the thermostat.
|
|
|
09-21-2008, 10:40 PM
|
#3
|
aluminauti
Where we
, Park it!
Join Date: Dec 2002
Posts: 316
|
We had a similar problem with a newly installed NT30 - we even de-installed it & had it bench tested. The unit ran fine on the bench. Turned out that we had a blockage in the propane line to the heater (spiders?) Anyway, we disconnected the propane line & used compressed air to blow out any obstructions. The heater has been working fine for the last 5 years.
|
|
|
09-22-2008, 07:14 AM
|
#4
|
2 Rivet Member
1965 22' Safari
lewisburg
, Pennsylvania
Join Date: Mar 2008
Posts: 22
|
Will bad t-stat allow fan to run? I can jump the t t-stat, but thought that bad t-stat would prevent even fan from kicking on. If there was a blockage wouldnt I still hear ignitor trying to fire before unti shut itself off?
|
|
|
09-22-2008, 07:23 AM
|
#5
|
Rivet Master
Currently Looking...
1984 31' Airstream310
Ajo
, Arizona
Join Date: Mar 2007
Posts: 7,649
|
Quote:
Originally Posted by PeteL
Will bad t-stat allow fan to run? I can jump the t t-stat, but thought that bad t-stat would prevent even fan from kicking on. If there was a blockage wouldnt I still hear ignitor trying to fire before unti shut itself off?
|
It's easy to test; I'd do that first.
|
|
|
09-22-2008, 08:24 AM
|
#6
|
2 Rivet Member
1965 22' Safari
lewisburg
, Pennsylvania
Join Date: Mar 2008
Posts: 22
|
Off to jump t-stat. On Suburban's website I noted a lockout mode on the SP. They do not explain how to get it out of lockout mode though. Says fan will run, but no heat in lockout mode.
|
|
|
09-22-2008, 08:48 AM
|
#7
|
2 Rivet Member
1965 22' Safari
lewisburg
, Pennsylvania
Join Date: Mar 2008
Posts: 22
|
Jumping Thermostat did not allow unit to ignite or even try to ignite. Recall the sp will try to ignite 3 times. It did not try even once. I am thinking unit went into lock out mode. I pulled power connector thinking it may reset itself. Anyone have any info on the lockout feature of the SPs
|
|
|
09-22-2008, 09:52 AM
|
#8
|
2 Rivet Member
1965 22' Safari
lewisburg
, Pennsylvania
Join Date: Mar 2008
Posts: 22
|
Spoke to tech at Suburban. Lock out mode just means 30 second shutdown because either sailswitch or limit switch (or both) is open. Knowing Sail switch test meant pulling unit I started with limit switch as it is easy to get to. Removed the two screws holding it in and noticed lower spade terminal came off by itself when pulling from panel. Tested switch and it was closed. Put the two spade connectors back on and reinstalled. Unit now works. I suspect lower spade connector worked itself loose and was cause of problem. Will run it and let it cycle all day to see if it reoccurs
|
|
|
11-14-2008, 02:45 PM
|
#9
|
WBCCI 8562
1975 31' Sovereign
Pelzer
, South Carolina
Join Date: Nov 2007
Posts: 225
|
I just installed at NT30 to replace the burned up NT32 in my 75 Sovereign, found that the exhaust was way too hot..I only had 2 heat outlets in the unit..so added (with a lot of trouble) a 3rd outlet, 3 inch duct. Cooled the unit alot. Should be able to hold hand near exhaust for a moment..if hotter then that something not right. In my case over temp kicked out. Fine now with the added register.
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
Bellypan Woes
|
Uncle Jack |
Belly Pans & Banana Wraps |
2 |
07-02-2007 03:10 PM |
12 volt woes
|
Tin Tortuga |
Electrical - Systems, Generators, Batteries & Solar |
5 |
02-03-2005 05:16 PM |
Leveler woes
|
guy99 |
Mechanics Corner - Engines, Transmission & More... |
9 |
10-20-2004 04:09 PM |
dometic woes
|
joel |
Refrigerators |
3 |
08-22-2004 12:09 PM |
Wiper Woes
|
smily |
Mechanics Corner - Engines, Transmission & More... |
5 |
02-13-2004 06:37 PM |
|
Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
Disclaimer:
This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.
All times are GMT -6. The time now is 03:31 AM.