bigric,
If your meter measures capacitance, put one lead on the common terminal and get the microfarad readings from the others present. Also, this should be done with all of the terminals disconnected from the wiring.
Be careful about the possible charge stored in the caps. Before taking any readings, be sure that it is fully discharged. Put your meter on VAC and put the probes alternately across all of the terminals and you'll see the readings drop to almost nothing as you do this.
The rubber mallet trick might work if everything else is in good condition. Sometimes, the compressor just needs a 'little' shot to wake up.