Old 08-29-2016, 10:38 PM   #1
2 Rivet Member
 
1976 Argosy 26
Henderson , Kentucky
Join Date: Jul 2016
Posts: 48
Images: 14
How to configure 30 amp service?

Ok 30 amp service in 76 Argosy and want to update water heater to add comfort of electric igniter and electric/gas water heater so with electric. Also have electric/gas refrigerator; heater fan; AC (without heat); heater fan; water pump; vent fan; 20 interior (1156) bulbs in variety of lights and 2 exterior (1141) lights. And not counting electric draw from temp switches or possible outlet usage for tv, radio, computer, or chargers. Electric panel has 4 breakers. So 4 breaker slots. I understand a 20 amp breaker dedicated to AC. 1) So how can you run most efficiently? 2) can you change or use double breakers and put a 15 amp side for electric water heater and turn off when not in use or when AC is in use? 3) How do you manage this concern? Thanks for you advice and experience.
__________________

__________________
Ky76Argosy is offline   Reply With Quote
Old 08-29-2016, 11:57 PM   #2
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,196
Images: 21
I'd break that down a little bit friend. I think you might be asking how to better organize your AC circuits.
__________________

__________________
Randy 208-514-8950
www.bestconverter.com
Converters, Inverters, Trimetric, EMS, Zamp Solar, Lifeline Batteries
68 Overlander is offline   Reply With Quote
Old 08-30-2016, 12:54 AM   #3
4 Rivet Member
 
DryFly's Avatar
 
1972 Argosy 20
Snoqualmie , Washington
Join Date: Sep 2012
Posts: 388
Quote:
Originally Posted by Ky76Argosy View Post
Ok 30 amp service in 76 Argosy and want to update water heater to add comfort of electric igniter and electric/gas water heater so with electric. Also have electric/gas refrigerator; heater fan; AC (without heat); heater fan; water pump; vent fan; 20 interior (1156) bulbs in variety of lights and 2 exterior (1141) lights. And not counting electric draw from temp switches or possible outlet usage for tv, radio, computer, or chargers. Electric panel has 4 breakers. So 4 breaker slots. I understand a 20 amp breaker dedicated to AC. 1) So how can you run most efficiently? 2) can you change or use double breakers and put a 15 amp side for electric water heater and turn off when not in use or when AC is in use? 3) How do you manage this concern? Thanks for you advice and experience.
Why do you want to convert your water heater to electric? if you want electric ignition then your circuitry should be ok, but is it that big of a deal to manually light the water heater? I can't think of a good reason to convert it over. Is it toasted and do you need to replace it? If you leave it as propane then all your circuits are adequate to run everything. You may want to change out your fuse box to a modern blade style, and definitely get rid of the Univolt if it's still there, but the original wiring/circuitry should be plenty adequate for all your systems.
__________________
DryFly is offline   Reply With Quote
Old 08-30-2016, 08:04 PM   #4
Rivet Master
 
1974 31' Sovereign
1979 23' Safari
Wayland , New York
Join Date: Jan 2012
Posts: 1,232
Images: 3
Quote:
Originally Posted by Ky76Argosy View Post
Ok 30 amp service in 76 Argosy and want to update water heater to add comfort of electric igniter and electric/gas water heater so with electric. Also have electric/gas refrigerator; heater fan; AC (without heat); heater fan; water pump; vent fan; 20 interior (1156) bulbs in variety of lights and 2 exterior (1141) lights. And not counting electric draw from temp switches or possible outlet usage for tv, radio, computer, or chargers. Electric panel has 4 breakers. So 4 breaker slots. I understand a 20 amp breaker dedicated to AC. 1) So how can you run most efficiently? 2) can you change or use double breakers and put a 15 amp side for electric water heater and turn off when not in use or when AC is in use? 3) How do you manage this concern? Thanks for you advice and experience.
Crossing your 12vdc and 120vac a little on the list but no biggy.
How close is the circuit breaker panel to the water heater? how easy would it be to run a wire from the panel to the water heater? Those are the big questions.
I've been using a SOB for the summer, it has a electric ignition electric/propane water heater and I wish I had put one in my safari instead of the manual pilot propane /electric I did use. I usually just leave the electric switch on then when I plug in I don't have to worry about it. When I boondock I turn on the propane switch. Have used both at the same time as it increases the recovery time essentially meaning more hot water quicker.
If the breaker panel is close and easy to run a wire to the water heater you can easily add a slim line circuit breaker, which is 2 breakers in one slot. Just be sure you get one compatible with the panel, there are different breaker types. Either a sticker on the panel will tell you what type to use, or you can pull one out to determine the type.
You'll also have to run 12vdc to the water heater but there's usually something near by to tap off of, it doesn't use much 12vdc.
I thought running the AC and water heater on electric might be a problem initially, but in the SOB I've had both running at the same time and haven't had any issues with the 30 amps. If I ran the microwave at the same time, I would expect I'd be tripping a breaker. Let me go try it, oh wait just kidding.
Hope this helps.
Joe
__________________
HiJoeSilver is offline   Reply With Quote
Old 08-31-2016, 08:53 AM   #5
2 Rivet Member
 
1976 Argosy 26
Henderson , Kentucky
Join Date: Jul 2016
Posts: 48
Images: 14
Thanks to all providing pertinent info on questions and here is additional info - the water heater is max 3-4' from breaker box on same wall to left

Why response.
Easy access helped my decision.
Old heater had floor rot under and my finger could poke through bottom of housing, with igniter, heater element in questionable condition. I had no prior history with trailer just bought, so why spend money to fix and find not what want.
Friend has 2004 Bambi with this gas/electric type water heater.
I wanted electric igniter.
New Atwood costs reasonable (steal) at $375 and would have electric if could work out connection and amps. $90 so more got with electric.

I am new to forum and read many threads. I do not know propriety of responding to responders. But if responder posts is it impolite not to respond? I often find responders ask questions about why changing to what, is not providing constructive info, only comments critical to a decision, wasting time and providing little. I guess that is the purist inquiry Why? Why? But why not add constructive info?

I am limited in ability or experience in these matters. And thanks to all who provide info germane to questions. I did not ask for critique of decision already made. That's like asking me why pick my wife. Many decisions have a self explanatory reason, I just did.

The response about improved question form (I had expected more from a responder with such insight and history, and I often read your posts for on point info or great ideas) - but to respond to that response - after "how to" I used 4 words/number to ask question which does describe my service. Not 5 words, but who is counting, and no description. So, I thought mine proper and accurate. But will definitely try hard to think on form of my question next time. Also now do I repost in new post changing the question as corrected. Paralyzed with indecision. But if you understand my question, please provide info for solution.

Response may intimidate or cause hesitation to post again. But thanks again for all info and interest.
__________________
Ky76Argosy is offline   Reply With Quote
Old 08-31-2016, 09:03 AM   #6
2 Rivet Member
 
1976 Argosy 26
Henderson , Kentucky
Join Date: Jul 2016
Posts: 48
Images: 14
Thanks for post. In response - I wanted to upgrade my Argosy 26, new to me, old heater removed to fix floor rot and looked deficient. New Atwood($375) has electric igniter, both electric and gas. Yes probably will use gas generally, but if have electric need to work out bugs so works. As for electric igniter, why not. If friends use turn on easier or easier for novice? Turn on gas, flip switch. Why not, or do you have any real issue? Mitch
__________________
Ky76Argosy is offline   Reply With Quote
Old 08-31-2016, 09:35 AM   #7
Rivet Master
 
A W Warn's Avatar

 
2000 25' Safari
1999 34' Excella
Davidson County, NC , Highlands County, FL
Join Date: Aug 2006
Posts: 2,134
You will be happy with the propane/electric water heater. You will need to wire for 120v for the heating element and 12v for the control module.

All lights and the furnace are 12v, no 120v required except the receptacle for the converter. My fridge (newer than yours ?) takes both 120 and 12v, not sure about yours.

If you will go to Airstream's website, to the "Service" tab then to "Manuals" tab, and look through some of the owner's manuals for newer trailers you can find electrical drawings that show the circuits as they are wired on later years. My 99 34' only has the 4 breakers, same as your Argosy, and manages a microwave and a combo water heater in addition to all of those things you have.
__________________
Alan
2014 Silverado 1500 Crew Cab 5.3L maximum trailering package (yes, I'm towing the 34')
A W Warn is online now   Reply With Quote
Old 08-31-2016, 09:46 AM   #8
Rivet Master
 
A W Warn's Avatar

 
2000 25' Safari
1999 34' Excella
Davidson County, NC , Highlands County, FL
Join Date: Aug 2006
Posts: 2,134
Quote:
Originally Posted by Ky76Argosy View Post
Ok 30 amp service in 76 Argosy and want to update water heater to add comfort of electric igniter and electric/gas water heater so with electric. Also have electric/gas refrigerator; heater fan; AC (without heat); heater fan; water pump; vent fan; 20 interior (1156) bulbs in variety of lights and 2 exterior (1141) lights. And not counting electric draw from temp switches or possible outlet usage for tv, radio, computer, or chargers. Electric panel has 4 breakers. So 4 breaker slots. I understand a 20 amp breaker dedicated to AC. 1) So how can you run most efficiently? 2) can you change or use double breakers and put a 15 amp side for electric water heater and turn off when not in use or when AC is in use? 3) How do you manage this concern? Thanks for you advice and experience.
1) Load management - you will learn quickly to not run the microwave, coffee pot, water heater, etc. at the same time. Breaker trips, you reset, you learn.
2) Probably not, but maybe - you should not use different type breakers. If you can find an exact match (brand and type), maybe. But unless you change out the whole panel I doubt you can find the correct breaker. If you use different brands it could create a fire hazard and might void your insurance. I suggest you tie into an existing circuit. It is acceptable to have two load wires connected to one breaker. If you find a thin line double single pole breaker get one that has 2 - 20 amp and wire the WH with 12 ga wire.
3) see 1 & 2
__________________
Alan
2014 Silverado 1500 Crew Cab 5.3L maximum trailering package (yes, I'm towing the 34')
A W Warn is online now   Reply With Quote
Old 08-31-2016, 10:30 AM   #9
4 Rivet Member
 
youngpeck's Avatar

 
1976 25' Caravanner
Salt Lake City , Utah
Join Date: Oct 2013
Posts: 304
Here's an excellent book on the subject:

https://www.amazon.com/Electrical-Sy...trical+systems
__________________
youngpeck is offline   Reply With Quote
Old 08-31-2016, 05:22 PM   #10
2 Rivet Member
 
1976 Argosy 26
Henderson , Kentucky
Join Date: Jul 2016
Posts: 48
Images: 14
Thanks all. I thought a good upgrade just not able to wrap my head round amps and tripping breakers. I am hanging out LED lights, and Dometic RM76D which worked off LP/120; unsure if 12v. I removed for flooring and new pex water line, I never operated electric side without shoreline, so fingers crossed, I hope will work when replaced.
__________________
Ky76Argosy is offline   Reply With Quote
Old 08-31-2016, 06:40 PM   #11
Rivet Master
 
1974 31' Sovereign
1979 23' Safari
Wayland , New York
Join Date: Jan 2012
Posts: 1,232
Images: 3
"Thanks to all providing pertinent info on questions and here is additional info - the water heater is max 3-4' from breaker box on same wall to left "

Easy right there!
Pop in a slim line breaker that gives you 2 circuits in one space. Try to match the original breaker amperage so you don't up rate the original 15a circuit to 20a. 15a is enough for the water heater. Stop at big blue or orange or menards, get 7-8 feet of metal conduit shielded electrical wire. Run it along the wall and or floor to the new water heater. There are plastic chafing plugs that go in the end of the metal to protect wires from metal edges.
Being close, easy peasy.
Think you're making a good choice upgrading to the propane/electric, it's so convenient.
__________________
HiJoeSilver is offline   Reply With Quote
Old 09-01-2016, 08:05 AM   #12
1 Rivet Member
 
1976 31' Sovereign
Apache Junction , Arizona
Join Date: May 2012
Posts: 14
How to configure 30 amp service... try a load shed.

http://www.parallaxpower.com/als20-accessory-als20

This load shed automatically switches between a main and a secondary load, such as between a microwave and a water heater. It is specifically designed for your exact needs. Check out the parallax power link. They even include a video.

Have fun,
Pete
__________________
plbalza54 is offline   Reply With Quote
Old 09-01-2016, 08:38 AM   #13
3 Rivet Member

 
1964 24' Tradewind
Lawrence , Kansas
Join Date: Oct 2012
Posts: 165
When I had to replace my water heater the repair guy suggested we put on its own pigtail which I plug in separately to power. This has worked out great. When the water heater is running on electric it is not putting extra load on my 30 amps.
__________________
ttbikes is offline   Reply With Quote
Old 09-01-2016, 09:23 AM   #14
Rivet Master

 
Vintage Kin Owner
Nowhere , Somewhere
Join Date: Jul 2005
Posts: 5,687
I think the newer fridges cool on 120 or lp, but need 12 volt for the electronics.
__________________

__________________
1984 Avion 30p 9.1 meter. 2006 Dodge 3500 cummins srw short bed crew cab.
avionstream is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Carefree Roadside & Rear Window Awning Arms & Rollers For 1976 31' Airstream Sovereign mrnos44 Airstream Classifieds 0 08-23-2016 08:08 PM
Service snafu $&!&& and which battery is which amirm Sprinter and B-van Forum 25 07-04-2016 10:19 PM
Goucho couch,original am/fm 8 track & lots of wood & aluminum from interior remodel gquailhunter Airstream Classifieds 0 09-19-2015 05:25 PM
50 amp to 30 amp only service Pearson422 Electrical - Systems, Generators, Batteries & Solar 13 10-08-2013 09:01 AM


Virginia Campgrounds

Reviews provided by



Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:24 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.