Old 10-15-2016, 05:44 AM   #1
2 Rivet Member
 
1994 34' Excella
Kalamazoo , Michigan
Join Date: Mar 2014
Posts: 72
Furnace Won't stay lit...

We have an Atwood 8535 III in our 94 Excella . When heat is requested, it goes through the normal starting cycle, and lights off, but the flame goes out after about 20 seconds or so. Then goes through attempted restart several times, with the same result.

I've pulled and cleaned the exhaust tube, checked and cleaned all the connections.

What's next, folks? We are leaving soon for a fall trip, and I'm imagining we are going to want heat.

Thanks in advance!


Sent from my iPad using Airstream Forums
__________________

__________________
TomS is offline   Reply With Quote
Old 10-15-2016, 06:30 AM   #2
Rivet Master

 
2014 20' Flying Cloud
Long Island , New York
Join Date: Jun 2015
Posts: 3,023
Just a guess from a lay person, but the "sail switch" in the furnace may have gone bad? This switch depends on the air flowing correctly inside the furnace, to prevent overheating in case there might be an obstruction preventing air flow. With your furnace being over 20 years old, this is a likely candidate IMO. Or the furnace's home circuit board may have gone bad? Not sure how easy either is to replace, but a mobile RV tech or a good RV shop could probably diagnose correctly.

Hopefully someone more knowledgeable will show up here soon.

We had a 25' AS in the 90's which needed a new furnace home circuit board when we sold her (at 13 years of age +/-).

Good luck!

Peter
__________________

__________________
OTRA15 is offline   Reply With Quote
Old 10-15-2016, 06:37 AM   #3
2 Rivet Member
 
1994 34' Excella
Kalamazoo , Michigan
Join Date: Mar 2014
Posts: 72
I may be wrong, but I don't think the burner will ignite at all if the sail switch is bad. I had the blower assembly apart a year ago, and the sail switch seemed to be operating normally then. The furnace functioned fine then, too.

You could be right about the board, tho.

Thanks...

Any other thoughts?

What is the best way to get the burner assembly dismounted for inspection?


Sent from my iPad using Airstream Forums
__________________
TomS is offline   Reply With Quote
Old 10-15-2016, 06:43 AM   #4
Rivet Master

 
2014 20' Flying Cloud
Long Island , New York
Join Date: Jun 2015
Posts: 3,023
I believe that some circuits allow the furnace to ignite, even with a bad sail switch, and then shut things down after a time delay. If you take things apart enough to expose the sail switch, I would put a new one in anyway maybe. No clue on dis-assembly.
__________________
OTRA15 is offline   Reply With Quote
Old 10-15-2016, 06:45 AM   #5
2 Rivet Member
 
1994 34' Excella
Kalamazoo , Michigan
Join Date: Mar 2014
Posts: 72
Good point..Will check that out...


Sent from my iPad using Airstream Forums
__________________
TomS is offline   Reply With Quote
Old 10-15-2016, 07:09 AM   #6
Rivet Master
 
paiceman's Avatar

 
2017 30' Classic
Upper St Clair , Pennsylvania
Join Date: Aug 2011
Posts: 1,605
Images: 1
Could be your in furnace of external flow control for the propane. Had the same issue with our previous AS. We enlarged the opening of the internal and changed out the external, worked fine after that. I just can't recall the exact name of either control valve. Could look it up, but gave all the books away when we sold it and bought a 2017 Classic with a TOTALLY different baseboard hot water system. Now have to relearn everything.

Bud
__________________
SAFE TRAVELS

Bud & Alice (Bud posts)
Abby- Black Lab-TDI Certified
Hopey-Yellow Lab-TDI Certified
2017 30' Classic
2015 F350 6.7 Diesel Crew Cab
USAF - Military Training Instructor (TI) - 68-72
paiceman is offline   Reply With Quote
Old 10-15-2016, 08:14 AM   #7
Rivet Master

 
2014 20' Flying Cloud
Long Island , New York
Join Date: Jun 2015
Posts: 3,023
PS Tom, is your battery voltage OK? If the furnace has been working well for a while, Bud's suggestion about the propane valve sizing is less likely IMO.

For a 20-year-old trailer, I would consider replacing both the board and the sail switch, and get an extra sail switch as well.

A good investment for cold weather travels . . .

Happy Trails.

Peter
__________________
OTRA15 is offline   Reply With Quote
Old 10-15-2016, 08:26 AM   #8
2 Rivet Member
 
2010 23' International
Joliet , Illinois
Join Date: Nov 2013
Posts: 53
If the flame lights then goes out it will probably be the flame sensor. If it was the sail switch you would not (better not) get a flame. It should only run for just a few seconds. If it really does run for 20 seconds or longer it could also be the over temp (high limit) switch. That would be easy to check with a meter.
__________________
bel73 is offline   Reply With Quote
Old 10-15-2016, 12:20 PM   #9
2 Rivet Member
 
1994 34' Excella
Kalamazoo , Michigan
Join Date: Mar 2014
Posts: 72
I'm on shore power, but I will check the voltage.

Pulled the cover, cleaned and checked the sail switch with a multimeter. Seems ok.

After all this, it now shuts off the gas after about 5-7 seconds...

Should the over temp switch be normally closed or normally open?

The flame sensor is part of the igniter assembly, right? Is there an easy way to remove the igniter/burner Assyrian for visual check?

Thanks!


Sent from my iPad using Airstream Forums
__________________
TomS is offline   Reply With Quote
Old 10-15-2016, 12:57 PM   #10
2 Rivet Member
 
1994 34' Excella
Kalamazoo , Michigan
Join Date: Mar 2014
Posts: 72
Checked the voltage at the furnace...12.5v. The limit switch and the sail switch both check ok.

I'm down to board or flame sensor.

Thanks for all the help!


Sent from my iPad using Airstream Forums
__________________
TomS is offline   Reply With Quote
Old 10-15-2016, 01:09 PM   #11
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 4,691
Images: 2
Blog Entries: 5
Temp switch should be closed unless the plenum overheats. Normally closed; opens on over temp. You may have an obstruction in the intake or exhaust plenum causing the plenum to over heat. A temporary jumper on the temp switch and sail switch should eliminate or at least ID which, if any are the culprit.
I would suspect the flame rod or control board.
Have you checked the gas pressure?
__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 10-15-2016, 01:44 PM   #12
2 Rivet Member
 
1998 34' Limited
Buford , Georgia
Join Date: Jul 2008
Posts: 66
Almost certainly NOT the sail switch or the board. I believe you said it goes into a relight mode on its own? When it does that, does the igniter spark appropriately? Do you also hear the gas valve open?
Our 34 footer has two furnaces. I had to replace the gas valves in both of them. Sometimes they would light, sometimes not. Even when they did, they would occasionally drop out after a bit.

I also thought about the limit switch, but you've checked that now. Depending on your access, you may have to get the guts out of the furnace to diagnose. They're not too hard to remove. You need to be able to see what's happening first. My guess is that either the gas valve is weak or the flame sensor drops when it gets really hot.(I've never seen this) Pulling ours out was the only way to accurately diagnose. I fully expected two different problems in each furnace. I was wrong. They both needed the valve, although they were different valves/different sized furnaces. Wishing you quick success.
__________________
fwjumper is offline   Reply With Quote
Old 10-15-2016, 01:57 PM   #13
2 Rivet Member
 
2010 23' International
Joliet , Illinois
Join Date: Nov 2013
Posts: 53
If it shuts off within 5-7 seconds my guess is the flame sensor. If you can get to it take a look to see if it has some corrosion on it. If it seems to, take some emory paper steel wool or something to clean it up with. That will sometimes get you by in a pinch.

Good luck
__________________
bel73 is offline   Reply With Quote
Old 10-15-2016, 03:25 PM   #14
4 Rivet Member
 
1973 31' Sovereign
Middletown , California
Join Date: Oct 2015
Posts: 304
It seems like the circuit board thinks there is no burner flame. Try cleaning the sensing rod with abrasive cloth and make sure that the flame is touching the rod. A lot of furnaces have a port or window so you can look at the flame and see what it's doing. Sometimes having the inspection port open changes the conditions around the sensor or the flame burns your eyebrow so you might have to hold a glass bottom up to the port and look through that. The flame should be blue with just the tips orange and the sensing rod, which is sometimes the spark electrode, needs to touch the flame. Because the rod glows red hot while the burner is on it can get a coating of oxidation which needs to be removed. If the sensing rod is clean and in the right place and the ground wire allows a good low resistance connection to the circuit board, the board might be bad.
__________________

__________________
ijustlee is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace won't stay lit JBBeaubeaux Water Heaters, Filters & Pumps 1 05-04-2016 08:02 PM
Pilot light won't stay lit abridges01 Refrigerators 5 09-25-2006 12:01 AM
Water heater prob, pilot won't stay lit & heater won't fire. johnboy Water Heaters, Filters & Pumps 1 06-20-2006 05:24 PM
Pilot Light won't stay lit Mike Callaha Water Heaters, Filters & Pumps 15 03-26-2005 01:56 PM
Furnace won't light /stay lit Don Furnaces, Heaters, Fireplaces & Air Conditioning 9 06-29-2002 04:37 AM


Virginia Campgrounds

Reviews provided by



Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.