Furnace stopped heat last nite

I'm looking for troubleshooting advice

Last night my 5 year old NT 30 furnace ran fine until the wee hours of the morning and then stopped heating. The blower kept running. Tried letting it sit and restart. Thermostat OK. Blower starts but furnace does not fire. Gas OK. Outside temp in the upper 20s. Any suggestions where to start?

Thanks,
Marshall
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-02-2010, 08:12 AM   #2
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Check the battery voltage.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 03-02-2010, 08:29 AM   #3
Single Slice
 
2004 28' Safari S/O
Livingston , Louisiana
Join Date: Oct 2009
Posts: 40
You might have a bad 'sail switch'. I had same trouble, 'gas level fine, blower starts, but does not light'. The sail switch is just an 'on/off' switch that measures the amount of air flow from the blower. Not enough flow, switch stays off and does not allow the gas to light: Or if switch is broken (like mine) it doesn't turn on and gas will not light. I found out about the sail switch in a recent issue of either "Trailer Life" or "Highways".
david686 is offline   Reply With Quote
Old 03-02-2010, 09:51 AM   #4
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
Given Suburban's reputation as "masters of the cold", I'm suprised your unit has lasted that long. The only thing you can check other than Terry's suggestion without pulling the furnace would be the electrode. If it's the ignitor board, replace it with a "Dinosaur".

Dinosaur Electronics Home. High quality circuit boards for RV appliances.
Mike Leary is offline   Reply With Quote
Old 03-02-2010, 11:11 AM   #5
Always Airstreaming!
 
rickandsandi's Avatar
 
2005 22' Safari
1960 24' Tradewind
Anytown , Connecticut
Join Date: Oct 2006
Posts: 3,115
Send a message via AIM to rickandsandi
We had the same problem with ours last fall. It is not the voltage because the fan is going on. Might be the paddle switch but have you tried pushing the reset button? We pushed it once and problem gone.
__________________
J. Rick Cipot
Sandi Gould
NEU New England Unit
Airstream Life Magazine
Proud Member of WBCCI
WBCCI #3411
AIR #17099
2009 Silverado 2500HD
2004 22' Safari
1960 24' Tradewind
rickandsandi is offline   Reply With Quote
Old 03-02-2010, 11:27 AM   #6
Rivet Master
 
1977 Argosy 24
Currently Looking...
Milltown , Wisconsin
Join Date: Mar 2006
Posts: 1,087
If the voltage is low, the fan can run slower then normal with out moving enough air to activate the sail switch, so the burner will not light. Charge the battery first and try the furnace. It's the easiest thing to do so do it first.
ventport is offline   Reply With Quote
Old 03-02-2010, 11:34 AM   #7
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
could moisture in the gas line frozen, blocking gas flow?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 03-02-2010, 01:15 PM   #8
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Update / follow up

I just disconnected the lead going to the electrode and checked for power with a test light with furnace running. No power to lead. Hooked up to shore power and have 13.3v.

I replaced the electrode about 3 years ago. I did not yet pull it out.

When I fired up the furnace last night I was hooked up to shore power. During the night shore power was turned off. When I found no heat the blower was on batt voltage was at 12.2. In the morning I hooked back up to shore power with no luck.

When the furnace failed I lit a stove burner with no problem. I also switched from a partial LP bottle to a full one.

I assume no power to the electrode points to one of the problems mentioned above. Anything else anybody can think of trying before I pull the furnace?

Any further recommendations on order of troubleshooting, or should I just take the furnace to someone who, hopefully, knows more than I do?

I don't see a reset button. There is a power switch on the furnace I turned off and on again.
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-02-2010, 01:37 PM   #9
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
If the furnace has to come out, you should replace the sail (limit) switch, card and motor; they will all fail, sooner than later. I'd be looking at the gas valve, too. Blow out all the feed lines with compressed air, also. Since misery loves company, I've, since 01, replaced the heater motor three times, the gas valve once, the electrode twice, the ignitor once and the limit switch three times. I think I've got another limit switch gone bad, the furnace will run for a few minutes then go into lockdown.
Mike Leary is offline   Reply With Quote
Old 03-02-2010, 05:46 PM   #10
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Update/ follow up #2

Quote:
Originally Posted by Mike Leary View Post
If the furnace has to come out, you should replace the sail (limit) switch, card and motor; they will all fail, sooner than later. I'd be looking at the gas valve, too. Blow out all the feed lines with compressed air, also. Since misery loves company, I've, since 01, replaced the heater motor three times, the gas valve once, the electrode twice, the ignitor once and the limit switch three times. I think I've got another limit switch gone bad, the furnace will run for a few minutes then go into lockdown.
Should I just get a new one? Can you still get them from Palomino? Anyone have the Palomino address.

I went to the local RV guy. He said the igniter wire was high voltage and testing it with a 12v tester will blow up the tester. It didn't, so I guess there was no power. It looks like it has to come out. He is willing to work on it.

Anyone know if a new NT 30 will slide into a 5 year old NT 30 cabinet?
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-02-2010, 06:02 PM   #11
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
Five years sucks; find someone who knows what's going on with that furnace, even though you've read my previous post about how I feel about Suburban products.
Mike Leary is offline   Reply With Quote
Old 03-02-2010, 06:28 PM   #12
Rivet Master
 
Lothlorian's Avatar
 
1973 27' Overlander
Loganville , Georgia
Join Date: Nov 2007
Posts: 1,741
This is where I bought my suburban furnace last fall. I paid 430.00 plus tax and shipping. LDV

Google Image Result for http://www.ldvusa.com/images/parts/small/22060021.jpg
__________________
Brian & Adrienne
Lothlorian is offline   Reply With Quote
Old 03-03-2010, 04:54 AM   #13
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
If I just buy a new NT30 will the inside components fit into the old cabinet. In other words, I don't want to remove the old cabinet if I don't have to. Can I just slide the new unit in the old NT30 cabinet?
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-03-2010, 07:25 AM   #14
Rivet Master
 
Lothlorian's Avatar
 
1973 27' Overlander
Loganville , Georgia
Join Date: Nov 2007
Posts: 1,741
Yes, There are several threads with photos on how to do it. It was easy. I followed Pizza chops directions and photos and somebody elses. It took me about 3 hours. If I did it again I bet I could knock it out in 1 hour. It all depends how old your orginal furnace it. Mine was a 70's Suburban furnace. It works great.

Brian
__________________
Brian & Adrienne
Lothlorian is offline   Reply With Quote
Old 03-03-2010, 08:10 AM   #15
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Quote:
Originally Posted by Mike Leary View Post
If the furnace has to come out, you should replace the sail (limit) switch, card and motor; they will all fail, sooner than later. I'd be looking at the gas valve, too. Blow out all the feed lines with compressed air, also. Since misery loves company, I've, since 01, replaced the heater motor three times, the gas valve once, the electrode twice, the ignitor once and the limit switch three times. I think I've got another limit switch gone bad, the furnace will run for a few minutes then go into lockdown.
Referring to the terms above and other posts:
1. Is the "sail", "paddle" and "limit switch" the same part with different names?
2. Is the "card" and "circuit board" the same part?
3. Is the "electrode" an "igniter" the same part?

Can someone advise me on my laundry list of parts to rebuild the NT 30SP. I'm thinking sail switch, circuit board, motor, electrode at minimum. What would the parts cost? I can get a new NT30SP from Palomino for less than $400 shipping included, so I'm wondering if a rebuild is worth it?
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-03-2010, 08:41 AM   #16
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
Quote:
Originally Posted by Lumatic View Post
Referring to the terms above and other posts:
1. Is the "sail", "paddle" and "limit switch" the same part with different names?
2. Is the "card" and "circuit board" the same part?
3. Is the "electrode" an "igniter" the same part?

Can someone advise me on my laundry list of parts to rebuild the NT 30SP. I'm thinking sail switch, circuit board, motor, electrode at minimum. What would the parts cost? I can get a new NT30SP from Palomino for less than $400 shipping included, so I'm wondering if a rebuild is worth it?
My guys call it a "limit switch", I'm not sure about the other two terms. Questions 2 & 3, the answer is "yes". A new motor is around $130.00, the limit switch is cheap, around $15.00, a gas valve is around $100.00, a card is $100, also. I think I'd buy a fresh furnace, that way you'll have warranty.
Mike Leary is offline   Reply With Quote
Old 03-03-2010, 09:51 AM   #17
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Quote:
Originally Posted by Mike Leary View Post
the limit switch is cheap, around $15.00,
If I am reading my diagram correctly the limit switch is in the front left lower corner of the furnace. If that is what I am looking at it is easily accessible. Do I have that right?

The electrode (igniter?) is also right in front.

I am thinking before I pull the furnace it may be worth dropping a new electrode and limit switch and see if that gets er goin. If I go through the work of pulling the furnace I will just drop a new one in.
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-03-2010, 09:55 AM   #18
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
I can't get to the limit switch in my configuration, but try that if you can get to it; like I said, I've gone through a lot of them. Be sure and replace the gasket on the electrode housing. You don't need to take the entire housing apart, only the center.
Mike Leary is offline   Reply With Quote
Old 03-03-2010, 01:34 PM   #19
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Bad Limit Switch

I took the limit switch out and tried to start the furnace, no heat. I connected the limit switch leads with a jumper wire and voila, heat. So I guess it's a bad $15 limit switch and I can postpone the inevitable a little longer.

By the way, you can still get a NT 30 SP from Palomino for $350.
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 03-03-2010, 01:57 PM   #20
Rivet Master
 
Mike Leary's Avatar
 
Currently Looking...
1984 31' Airstream310
Ajo , Arizona
Join Date: Mar 2007
Posts: 7,649
Images: 4
Well done!
Mike Leary is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 07:58 PM
heat pump & furnace problem al66pine Furnaces, Heaters, Fireplaces & Air Conditioning 0 10-07-2009 02:04 AM
Furnace on 72 Tradewind pilot lights but no heat RichHog Furnaces, Heaters, Fireplaces & Air Conditioning 10 05-16-2009 02:33 PM
The furnace stopped working ipso_facto Furnaces, Heaters, Fireplaces & Air Conditioning 13 02-24-2006 02:04 PM
Heat Pump and Furnace Operation Cracker Water Heaters, Filters & Pumps 21 12-10-2003 03:10 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 03:29 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.