Old 03-08-2008, 04:52 PM   #43
Rivet Master
Commercial Member
 
lewster's Avatar
 
Currently Looking...
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 4,749
Just found this info that might affect your decision to resurrect your NT-22:

"Suburban initiated a recall for all furnaces made from 1966 through 1977:

Campaign : 77E-012 initiated summer of 77
Campaign : 81E-015 initiated winter 81-82

The furnaces were models NT-17, NT-20, NT-22 and NT-30 manufactured between 1966 & 1970 The serial numbers were 0064881 and lower. Also furnaces made between 1970 & 1977 except those with an "M" suffix, The serial numbers are: 0064881 through 0715865. The recall specifies:" if the model and serial number of your furnace falls within those noted, have it inspected unless you are VERY SURE the Suburban recall has already been completed on your unit. The furnaces in question have a rubber-like crossover tube that could crack. Extremely dangerous carbon monoxide would then be expelled into the interior.”

From your description, your cross-over tube IS CRACKED and while it probably is not the source of your non-ignition problem, I would highly recommend replacing your NT-22 with a new unit completely! I strongly feel that comparing the costs of repairing/restoring a 35+ year old furnace of questionable safety vs. replacing with a new unit is a no brainer at this point......................REPLACE IT!

Thanks!
__________________

__________________
Lew Farber-RVIA Certified Master Tech.... MASTER TECH ENERGY SYSTEMS, INC.
AM SOLAR FACTORY AUTHORIZED SALES & INSTALLATIONS ...MAGNUM INVERTERS ...LIFELINE BATTERIES.... ELECTRICAL COMPONENT UPGRADES
NO MORE AIRSTREAM.... NO MORE MEMBERSHIPS....BUT I'M STILL AROUND!
lewster is offline   Reply With Quote
Old 03-08-2008, 09:06 PM   #44
2 Rivet Member
 
1971 23' Safari
taylorsville , Utah
Join Date: Nov 2007
Posts: 21
Thank you very much for that info. Apparently my unit was NOT ever taken in to get a new cross-over tube! But, as you say, this does make my decision simple. Now I just hope that the new unit doesn't offer me too much grief. Thanks again, I really appreciate you saving me some cash!
__________________

__________________
canine camp is offline   Reply With Quote
Old 03-09-2008, 11:31 AM   #45
Moderator
Commercial Member
 
eubank's Avatar
 
1967 30' Sovereign
Angel Fire , New Mexico
Join Date: Jan 2004
Posts: 5,853
Durn. I was really hoping to see a solution here.

Lynn
__________________
WBCCI 21043
eubank is offline   Reply With Quote
Old 03-09-2008, 05:26 PM   #46
Rivet Master
Commercial Member
 
lewster's Avatar
 
Currently Looking...
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 4,749
Quote:
Originally Posted by eubank
Durn. I was really hoping to see a solution here.

Lynn
This is a solution Lynn. I can get behind the restoration of many items on vintage Airstreams, but when it comes to LP and your safety, furnaces, water heaters and other LP appliances that can rust and degrade over time (especially 35+ years) just do not qualify as suitable candidates for restoration in my book.
__________________
Lew Farber-RVIA Certified Master Tech.... MASTER TECH ENERGY SYSTEMS, INC.
AM SOLAR FACTORY AUTHORIZED SALES & INSTALLATIONS ...MAGNUM INVERTERS ...LIFELINE BATTERIES.... ELECTRICAL COMPONENT UPGRADES
NO MORE AIRSTREAM.... NO MORE MEMBERSHIPS....BUT I'M STILL AROUND!
lewster is offline   Reply With Quote
Old 02-10-2010, 10:53 AM   #47
New Member
 
1973 31' Sovereign
1973 31' Sovereign
Hurricane and Park City , Utah
Join Date: Jul 2008
Posts: 3
Replacement Furnace for 1973 31' Soverign

I just purchased my second 31' 1973 Soverign sans the furnance. I bought my first 1973 31' soverign two years ago, in great shape, so I have some experience with vintage airstreams. The new rig has a univolt that was been by passed, plus an Onan generator. The generator is foreign to me. There is a control in the front console next to the radio/tape deck. NO manual, or reference in the AS shop manual.

The previous owner used only 110v shore power, which is my intention also, yet I am somewhat of a purist, so would like to restore to original for resale. Questions are; 1. What is best replacement furnace and btu sizing for 31'? The ducting is in place for the rear bath and bedroom., as is the external vent and cover. Would it be better to go 110 v? furnance? If the univolt is bad, what is the best replacement?. Any suggestions would be appreciated. Thanks
__________________
charles12 is offline   Reply With Quote
Old 02-10-2010, 11:41 AM   #48
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 15,748
Images: 1
Quote:
Originally Posted by charles12 View Post
I just purchased my second 31' 1973 Soverign sans the furnance. I bought my first 1973 31' soverign two years ago, in great shape, so I have some experience with vintage airstreams. The new rig has a univolt that was been by passed, plus an Onan generator. The generator is foreign to me. There is a control in the front console next to the radio/tape deck. NO manual, or reference in the AS shop manual.

The previous owner used only 110v shore power, which is my intention also, yet I am somewhat of a purist, so would like to restore to original for resale. Questions are; 1. What is best replacement furnace and btu sizing for 31'? The ducting is in place for the rear bath and bedroom., as is the external vent and cover. Would it be better to go 110 v? furnance? If the univolt is bad, what is the best replacement?. Any suggestions would be appreciated. Thanks
Charles.

The correct replacement furnace is a Suburban NT-30SP.

Airstream has used a solid state 55 amp Univolt for several years, with excellent results.

Pure electric heat is not efficient and along with the fact that the heat must be circulated thru the ducts, so that the tanks are protected in freezing weather.

Andy
__________________
Andy Rogozinski
Inland RV Center
Corona, CA
Inland RV Center, In is offline   Reply With Quote
Old 02-10-2010, 10:19 PM   #49
Kmpro
 
kmpro's Avatar
 
Currently Looking...
1984 31' Airstream310
Lubbock , Texas
Join Date: Feb 2010
Posts: 301
Blog Entries: 2
I just recently purchased a 1984 AS model 310 Limited M/H. This is my 13th RV since 1969, so, even though I am new to this forum"this ain't my first rodeo." My furnace too was like the thread here blowing cold air and no burner. After pulling the furnace, I decided it was foolish to risk being carbon monoxided by a 25 year old furnace. My solution? Replace the 30K BTU with a new 34K unit(same size physically) and don't worry about dying in my sleep.
__________________
kmpro is offline   Reply With Quote
Old 02-26-2010, 10:38 PM   #50
3 Rivet Member
 
GoldFever's Avatar
 
2007 23' International CCD
Hemet , California
Join Date: May 2002
Posts: 106
Images: 2
NT30K Replacement?

We've got a 1992 25ft Excella with an NT30K furnace. I've had the furnace out before to get it to work...blew it out, made sure sail switch worked, etc.
It started 3 weeks ago after I put in a new thermostat but now the blower goes on strongly but the pilot won't light. Thinking about removing it again and trying to figure out what's wrong this time. However, I'm not exactly thrilled with doing this again. It is a 6.5amp, 1988 model furnace. I'm inclined to go with a new unit but here is my problem: There are three (3) exhaust openings for this unit, two stacked on the right, one even with the other side top tube. There are two mud dauber screens covering these openings to the outside world.
The Suburban NT-30SP has two exhaust openings and they seem to be near the center of the back of the unit and would not fit in the space because of plumbing behind the cabinet wall next to the door.
So my question is what unit can I use to exactly replace the old unit? So far I have not been able to find one that wouldn't require lots of work to move pipes, ducting, and cutting more holes in the aluminum skin (which I will not do).
Sure wish there was an "exact" replacement so I could pull out the old big amperage and noisy unit and put in a low amperage and quieter unit.
Suggestions welcome. Finding a solution priceless....
Gary in Hemet, CA
__________________
Gary & Susan Norgan
2007 International 23ft Ocean Breeze
Hemet, CA
"The key to flexibility is indecision"
GoldFever is offline   Reply With Quote
Old 03-09-2010, 09:40 AM   #51
3 Rivet Member
 
GoldFever's Avatar
 
2007 23' International CCD
Hemet , California
Join Date: May 2002
Posts: 106
Images: 2
Update: Solution Found

Removed the old controller board and had it tested. Result: Not sending a signal to the ignitor so I bought a Dinosaur Electronics Universal Ignitor Board, Model UIB S.
Installed it and still no flame.
Pulled the sail switch out (previously just blew it out with high pressure air) and noticed that the push pin switch was not springing back out so was not making a clicking noise...as it should. Voila!! Go buy new switch. Installed this new switch and it now works every time. Over the last few days I take a detour to the trailer and jump in and push the lever over on the thermostat. Sort of sneak up on the furnace at random times to see if it works. It has worked each time. I think the problem is solved.
__________________
Gary & Susan Norgan
2007 International 23ft Ocean Breeze
Hemet, CA
"The key to flexibility is indecision"
GoldFever is offline   Reply With Quote
Old 03-09-2010, 10:06 AM   #52
Full Timers/Diesel power.
 
Mike Leary's Avatar

 
1983 31' Airstream310
Winnemucca , Nevada
Join Date: Mar 2007
Posts: 2,517
Images: 11
Quote:
Originally Posted by GoldFever View Post
Removed the old controller board and had it tested. Result: Not sending a signal to the ignitor so I bought a Dinosaur Electronics Universal Ignitor Board, Model UIB S.
Installed it and still no flame.
Pulled the sail switch out (previously just blew it out with high pressure air) and noticed that the push pin switch was not springing back out so was not making a clicking noise...as it should. Voila!! Go buy new switch. Installed this new switch and it now works every time. Over the last few days I take a detour to the trailer and jump in and push the lever over on the thermostat. Sort of sneak up on the furnace at random times to see if it works. It has worked each time. I think the problem is solved.
What is a "push pin switch", I'm having similiar problems. Got a part #?
__________________
"A settled wisdom, plus the itch to be elsewhere"
Mike Leary is offline   Reply With Quote
Old 03-09-2010, 10:08 PM   #53
3 Rivet Member
 
GoldFever's Avatar
 
2007 23' International CCD
Hemet , California
Join Date: May 2002
Posts: 106
Images: 2
Whoops!! Part named by me

Actually I was referring to the little pin that gets shoved into the body of the sail switch. The new sail switch I bought makes a click when the metal "sail" moves toward the switch body. The "push pin switch" is supposed to have a spring action, pushing it back out and at the same time makes the clicking sound when you release the sail. Mine did not click and usually just got stuck in the "in" position.
Sorry for the misunderstanding here

Part number? The guy at the trailer supply nearby went over to the wall with all the Suburban parts hanging on it and found the one that looked just like the old one except it was white not black like the old one. He said if just needs to be the exact same size and design as the old one....which it was...and it works perfectly.

Hope this helps.
__________________
Gary & Susan Norgan
2007 International 23ft Ocean Breeze
Hemet, CA
"The key to flexibility is indecision"
GoldFever is offline   Reply With Quote
Old 07-25-2013, 08:01 PM   #54
1 Rivet Member
 
Patricia720's Avatar
 
2003 25' Safari
Prescott Valley , Arizona
Join Date: Dec 2012
Posts: 8
I've referred to this string several times and it has been very helpful. I was having the same problem with the furnace in my 2003 Safari and it proved to be the sail switch. I had it replaced by a mobile RV repair guy, since I was on the road and did not have the time to wait for a part in the mail. The furnace worked well for about two weeks and then the same thing started yet again. By "same thing," I mean the blower motor comes on and runs for awhile but there is no ignition. I'm in Arizona all summer so it hasn't been a big deal but the problem is rising to the top of my To Do list. Any ideas as to what is damaging the sail switches? Or do you think it's a coincidence that two died in span of two weeks?
__________________
Patricia720 is offline   Reply With Quote
Old 07-26-2013, 08:14 AM   #55
Moderator
Commercial Member
 
eubank's Avatar
 
1967 30' Sovereign
Angel Fire , New Mexico
Join Date: Jan 2004
Posts: 5,853
Dust is the enemy of a sail switch. I've fixed or replaced ours on a number of occasions, several times by simply taking it out (no easy task) and giving it a good blow-out with compressed air.

On the most recent occasion, I replaced with a new one that had been sitting in its shipping box for several years. Interestingly, the manufacturer had slightly redesigned the switch so that the sail is slightly larger, making it easier for the blower to move.


Lynn
__________________
WBCCI 21043
eubank is offline   Reply With Quote
Old 07-26-2013, 11:14 PM   #56
1 Rivet Member
 
Patricia720's Avatar
 
2003 25' Safari
Prescott Valley , Arizona
Join Date: Dec 2012
Posts: 8
Dust eh? That makes sense. Thanks for the input. When I dig the bugger out I'll try to figure out how the dust is making its way in and if I can prevent it.

Patricia
__________________

__________________
Patricia720 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
A/C not blowing cold anymore hollandranch Furnaces, Heaters, Fireplaces & Air Conditioning 17 09-26-2007 10:44 AM
Furnace blows cold air guy99 Furnaces, Heaters, Fireplaces & Air Conditioning 37 04-06-2007 10:26 PM
New Airstream - Air conditioner/Furnace problem mariffe Electrical - Systems, Generators, Batteries & Solar 12 04-16-2003 04:26 PM
Forced Air furnace Joan D'Andrea Furnaces, Heaters, Fireplaces & Air Conditioning 16 11-02-2002 09:41 PM
cold weather how do air streams do? overlander Our Community 2 10-02-2002 05:10 AM




Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.

Airstream News Delivered to your Email!

Stay up-to-date with Airstream news in your inbox!

unsusbcribe at anytime with one click

Close [X]