If the supply fan is not delivering the right volume of air the discharge temp could still be in the range you describe (46 to 49), and the AS would still be warm.

A dirty filter would certainly cause the supply air to be reduced, but I am sure you have already checked that, and besides the evaporator would ice up if the supply volume was severely reduced.

The condenser should generally feel hot to the touch not warm, low refrigerant is certainly a possibility.

I would call Dometic and describe the symptoms. The problem of course will be getting it to a place that has the techs to work on the unit.


SRW is offline   Reply With Quote
Old 06-20-2009, 04:32 AM   #16
Rivet Master
ZoominC6's Avatar
2004 30' Classic Slideout
College Town USA , Virginia
Join Date: May 2005
Posts: 1,500
Kevin, One little thing that may help is to insulate the skylights above the shade. I read that you've closed the shade. I purchased some foil backed styrofoam commonly used in the construction industry as exterior sheathing on some homes. I cut pieces to fit and taped two back to back with foil duct tape, placed them in the skylight and pulled the shade over them. This helps in hot weather although I doubt it will be a final solution for you. Good luck and please keep us posted.

In dog years, I'm dead!
ZoominC6 is offline   Reply With Quote
Old 06-20-2009, 06:23 AM   #17
2 Rivet Member
1992 29' Excella
DFW , Texas
Join Date: Oct 2008
Posts: 23
Images: 2
Originally Posted by omnistream View Post
I am having the same issue with my 32 excella that has a penguin 13.5 a/c. I think I need to recharge the system.

Omnistream, I had thought the same thing. A friend who is well versed and licensed on ACs came out and read the intake and outflow temps. It was around 10-15 degrees. He removed the bottom AC cover and immediately found that the lower coils were completely clogged. We were also troubleshooting a water pan leak so we ended up removing the AC to clean the coils with the acids that he had. These cleared the gunk out such that you could actually see through the fins of the coils. It took several applications of the cleaning acid. It made a world of difference taking 17+ years of gunk off of the coils. We now have a differential of 30+ degrees. It is very cold air coming out. That said, it still isn't sufficient to cool the trailer down in the heat of a Texas summer day. I can also feel the heat through the top of my trailer.
TxToaster is offline   Reply With Quote
Old 06-23-2009, 08:06 AM   #18
4 Rivet Member
Davis's Avatar
1996 34' Excella
Americus , Georgia
Join Date: May 2004
Posts: 292
Originally Posted by omnistream View Post
I am having the same issue with my 32 excella that has a penguin 13.5 a/c. I think I need to recharge the system.

Please tell me where I can get instruction to recharge my duotherm penguin 13,500 btu unit. Does it have to have R-22 coolant? How do I install the valves to recharge or are there not couplings like in an automobile a/c system?
Bottom line though! (I realize I may be commiting blasphemy here) I don't think the Airstream is insulated well, PERIOD! I mean one inch of fiberglass batting has no functional R-factor. I can feel the heat just radiating through the wall! I have seriously considered trying to remove the cheap fiberglass and carefully filling the wall sections with injectable low-expansion foam. Anyone else feel the same? Have any experience in this regard? Airstream could make these things like ice chest if they chose too! I am quite disappointed in this aspect of the Airstream.

Kevin, I may be wrong but I would have to say that the temps you are experiencing are normal compared to the many Airstreams I have owned with Dometic and Coleman units they all suffered when ambient temps were above 95 deg.I also have 52 deg air from the a/c vent with interior trailer temps around 83 deg . A few years ago I looked at a brand new 30ft trailer in 100 deg temps with the a/c on and it was blowing 52 deg air with interior temps around 85 deg and so I figured that was normal for an Airstream.

Omnistream I would have to agree that the Airstreams suffer from insulation. When I contacted the factory they told me that they use a R14 fiberglass insulation but when is packed in between the walls so tightly it looses it efficiency and is actually around a R 7.

I have seen many SOB trailers parked next to me and I can hear their units compressor cycle on and off where mine would run all day in the real hot temps.

I have placed two different fans in front and back of my trailer to help circulate the air and it helps a little.
1991 Airstream Excella 1000 34ft (SOLD)
1994 Chevrolet Crew Cab dually 2WD 6.5td
2005 Chevrolet Suburban LT 1500 2WD 5.3
WBCCI # 10219 Georgia Unit
AIR # 5131
Davis is offline   Reply With Quote
Old 06-28-2009, 09:08 AM   #19
3 Rivet Member
Silvertherapy's Avatar
2008 27' International FB
Shoreacres , Texas
Join Date: Jan 2008
Posts: 109

I also have the 27 ft FB with the 15K unit. Last Week we were up at Inks Lake and during the hottest part of the 100 degree days, our inside got no hotter than 78-80 and we did not have any of the insulating panels up that you have. However, for some immediate relief for a full timer, I would suggest that you did what my neighbor across the street is doing. He lives full time in his 31 ft 5th wheel while he is re-building his house from Ike. He added a portable AC from Sam's and ducted the exhaust out of one of his slide outs,However, that still did not get his temps down! What did work was a $30.00 misting hose strung across the top of his trailer during the day creating an evaporative cooling effect on the top of the trailer. This alone dropped the inside temperature at least 10-15 degrees and he is no longer even trying to use the portable he bought. (and regrets cutting the hole!)
The misting hose is just 3/8" tubing with atomizing nozzles. I got one for my next trip to Lake Livingston next weekend. It is made by Mistymate. (
This does not answer whether or not there is a problem with your AC, but it will give you some immediate relief!

Good luck,

Johnny and Connie Hill
Silvertherapy is offline   Reply With Quote
Old 06-28-2009, 11:03 AM   #20
Rivet Master
Crusty's Avatar
1992 34' Excella
Austin , Texas
Join Date: Mar 2007
Posts: 562
Images: 10
It's HOT in Austin!

Hey folks - this is 105-108 daily high temps (with high relative humidity) and it it HOT here in central Texas. When a native Texan says it's hot that's probably a quantum step above what most people think is hot.

My 13.5k Penguin is working properly and my 34' Excella is getting up to around 90 during the hottest part of the day (no shade), and down to the high 60's setpoint overnight when the outside air temp may drop to 75.

I may go buy some Reflectix insulation to block some of the heat entry from windows and the FF's but the heat gain through the walls is incredible. You can put your hand on the interior walls and feel the heat that is being radiated through them, so I think your a/c is doing the best that it can under these circumstances.

Keep lots of ice handy and drink iced tea (the house wine of the south), wear light and skimpy clothes, and stay in the shade.
"If you come to a fork in the road, take it."
Austin, TX "Rancho Deluxe"
Crusty is offline   Reply With Quote
Old 06-29-2009, 11:35 AM   #21
1 Rivet Member
camphost's Avatar
Join Date: Oct 2002
Posts: 11
Thumbs up Foam Insulation

I just have to agree. I think foam would be a much better choice.
camphost is offline   Reply With Quote
Old 06-29-2009, 11:46 AM   #22
4 Rivet Member
1971 29' Ambassador
Leonardtown , Maryland
Join Date: Oct 2004
Posts: 262
Images: 3

I have a similar problem with the AC in my classic. I talked with my AC expert he advised me "do not" break the lines and add any fittings.
Under normal conditions a sealed system does not leak and the freon does not deterioate. He did suggest checking the inside vents to ensure they are clear of any obstructions such as insulation and trim material, then remove the cover on the roof and using a cleaner like Spray Nine, 409 or a "coil cleaner" and spray the coils, then rinse with a garden hose. He indicated dirt will build up on the coils, you can not see it but it does restrict the cooling ability.


Rebee - WBCCI #1325
2002 Classic Ltd 30'
2007 Dodge 2500, 6.7 Cummins
Rebee is offline   Reply With Quote
Old 07-06-2009, 11:06 AM   #23
4 Rivet Member
dstalzer's Avatar
2005 25' Classic
Austin , Texas
Join Date: Jun 2008
Posts: 346
We camped at Lake Georgetown the past 4 days and had similar problems with our 25' Classic and Dometic Penguin 15K A/C. We were in a partial shaded site keeping the night shades drawn and with the awning out. The breaker for the A/C tripped 2 times and had to be reset. At first I thought this happened because of the fan setting was on low. It did help by setting the fan to high and setting the thermostat up around 77 so the unit would cycle (when set at 77 the temp was around 79 - 80, maybe not calibrated correctly). After using the high fan setting, we were able to keep the temp no higher than 80 during the 100+ outside temperature. I was wondering if low freon could be causing the A/C to draw too much current which was making the breaker trip. Does anyone have an idea about this.

dstalzer is offline   Reply With Quote
Old 07-06-2009, 11:39 AM   #24
3 Rivet Member
2008 28' Safari SE
winter garden , Florida
Join Date: Mar 2009
Posts: 210
I would more suspect low current at the campsite during peak demand. My 08 28' with the 15,000 heat pump had no problems two weeks ago during temps approaching 100 here in florida. My wife was actually very cold and had to wear a hooded sweatshirt in the trailer. I keep the temp at 68 and fan on high to keep my two snow dogs cool.
bob34787 is offline   Reply With Quote
Old 07-06-2009, 11:42 AM   #25
4 Rivet Member
dstalzer's Avatar
2005 25' Classic
Austin , Texas
Join Date: Jun 2008
Posts: 346
Immediately after the breaker tripped, I went out and checked the voltage at the power post I was plugged into and it was reading 125V, so I think low voltage was not the problem.

dstalzer is offline   Reply With Quote
Old 07-07-2009, 09:35 PM   #26
Streamer Jabe
Jabreyd13's Avatar
1978 31' Excella 500
Edmond , Oklahoma
Join Date: Jun 2009
Posts: 28
Super Hot Walls!

It got up to 105 today and I am in full sun and my Penguin 13.5 unit is killing me. Literally. The walls were 93 degrees and radiating heat like and oven. I thought these things were insulated better. I am in for a long summer since temps are going to be this way for the next couple of weeks at least. Oklahoma Summers are hot! I need two units, and I only have a 31 footer. I am not going to damage my original interior trying to reinsulate. I wish I was a heat and air guy!
Jabreyd13 is offline   Reply With Quote
Old 07-08-2009, 09:55 PM   #27
E Pluribus Aluminus
Jaxon's Avatar

2008 34' Classic S/O
1967 22' Safari
2005 30' Classic
Rockport , Texas
Join Date: Aug 2005
Posts: 1,159
Images: 10
Send a message via AIM to Jaxon Send a message via Yahoo to Jaxon
Same temps here in Austin, Okie... We just changed out our Dometic 13.5 for a Carrier 15, low profile. Made a significant difference. Back in the clover...

Anybody want to buy a used Dometic 13.5 A/C with heat strip? Needs a circuit board but other than that, works great for under 100 degree temps...
Bill & Kim
34 Classic Limited w/slideout (Anabelle)
Chevy Silverado * 2500HD Duramax * LTZ
WBCCI 7005 * AIR 9218

The trouble with trouble is it always starts out as fun...
Jaxon is online now   Reply With Quote
Old 07-08-2009, 10:21 PM   #28
Streamer Jabe
Jabreyd13's Avatar
1978 31' Excella 500
Edmond , Oklahoma
Join Date: Jun 2009
Posts: 28
15K A/C Needed

It looks like I too have a 13.5K Dometic Penguin for sale with a heat strip. It works great in 100 degree heat, but only at night.

Jabreyd13 is offline   Reply With Quote

Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic Duo Therm Penguin gloran Furnaces, Heaters, Fireplaces & Air Conditioning 3 01-20-2007 11:06 AM
Dometic penguin logic board 0557 Furnaces, Heaters, Fireplaces & Air Conditioning 3 10-10-2005 09:47 AM
how to trouble shoot a dometic penguin AC unit 0557 Furnaces, Heaters, Fireplaces & Air Conditioning 1 08-18-2004 05:26 PM
Dometic Penguin A/C Control Panel Board Saigon Furnaces, Heaters, Fireplaces & Air Conditioning 1 06-05-2004 10:55 AM
Dometic Penguin for '66 Safari? markh8624 Furnaces, Heaters, Fireplaces & Air Conditioning 21 02-24-2004 05:30 PM

Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:01 PM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.