Dometic Brisk Air II Condensation Leak?

We recently installed a new Dometic B59516.XX1C0 Brisk II in our '79 AS Excella (ground-up renovation) and today when we turned the unit off, then back on 5 minutes later water came out of the ceiling vent holes. I am assuming this is built-up condensation because there has been no rain since we installed the unit here in Nashville (though it has been very humid).

My question: how to avoid this condensation coming through the ceiling vents? It was quite a bit of water, enough that I had to mop it off the floor.

The previous A/C unit (and Armstrong TR24) had a hose that connected to it that drained the condensation down below the trailer. I wonder if this dometic A/C unit has a similar "bleed" nozzle that I could connect this existing pipe to?
__________________

__________________
trekerboy is offline   Reply With Quote
Old 09-01-2016, 01:49 PM   #2
Rivet Master
 
DFlores's Avatar
 
1968 22' Safari
Austin , Texas
Join Date: Sep 2011
Posts: 555
Images: 3
Yes, there is a kit with two cups to catch condensate that then flows thru plastic tube into the return box, then out the side into the ceiling where the tubing connects to down pipe headed thru floor


Sent from my iPhone
David & Diane
__________________

__________________
DFlores
David & Diana
DFlores is offline   Reply With Quote
Old 09-02-2016, 07:52 AM   #3
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 2,058
If you installed the new Air conditioner without any after-market condensate capture device, then the condensate should be draining out of a hole on either side of the unit and running down the outside of your trailer. The way that both of the condensate capture systems (the older "pan" and the more modern "cups") work is they catch the condensate that drips out of the afore mentioned holes, and then funnel it inside the trailer and down the condensate drain tube that was originally installed inside the wall.

I have some theories as to what is going on, but need more information...

Who did the installation (was it you, or someone else)?

Was a condensate catch pan or condensate capture cups used?

Do you see water dripping down the outside of the trailer after the unit has been run for a while?

When you say a lot of water was released, can you be more specific, ie., half a cup, a full cup, a liter? Did the water drip out of the unit, or did it pour?

How long has it been since the unit was installed?

Was this your first time running it since the install?

Are you sure the unit was only shut off for 5 minutes?

Did the water start to drip immediately after the unit was shut off, or only after it was turned back on again?

Did anyone go in and out of the door?
__________________
Belegedhel is offline   Reply With Quote
Old 09-03-2016, 07:06 AM   #4
4 Rivet Member
 
trekerboy's Avatar
 
1979 31' Excella 500
Charlevoix , Michigan
Join Date: Aug 2014
Posts: 286
Quote:
Originally Posted by Belegedhel View Post
If you installed the new Air conditioner without any after-market condensate capture device, then the condensate should be draining out of a hole on either side of the unit and running down the outside of your trailer. The way that both of the condensate capture systems (the older "pan" and the more modern "cups") work is they catch the condensate that drips out of the afore mentioned holes, and then funnel it inside the trailer and down the condensate drain tube that was originally installed inside the wall.

I have some theories as to what is going on, but need more information...
Thank you for your help!

Quote:
Originally Posted by Belegedhel View Post
Who did the installation (was it you, or someone else)?
It was myself and my brother (we are the ones that renovated the entire trailer over the past two years)

Quote:
Originally Posted by Belegedhel View Post
Was a condensate catch pan or condensate capture cups used?
We haven't used any aftermarket solution to capture the condensation, so it's just dripping out as it normally would, down the side of the AS.

Quote:
Originally Posted by Belegedhel View Post
Do you see water dripping down the outside of the trailer after the unit has been run for a while?
I haven't seen water dripping down the side after the unit has been shut off for a while, but the very first time we turned the unit on after installing it, after a while there was a pretty constant stream of water running down the side of the AS. Enough for a trip down to the ground (off the shell) once every few seconds.

Quote:
Originally Posted by Belegedhel View Post
When you say a lot of water was released, can you be more specific, ie., half a cup, a full cup, a liter? Did the water drip out of the unit, or did it pour?
It was probably a 1/2 cup, and it poured.

Quote:
Originally Posted by Belegedhel View Post
How long has it been since the unit was installed?
About 6 days since the initial install.

Quote:
Originally Posted by Belegedhel View Post
Was this your first time running it since the install?
No, it had been continually running since we got here to Nashville (very hot here right now).


Quote:
Originally Posted by Belegedhel View Post
Are you sure the unit was only shut off for 5 minutes?
It may have been less than 5 minutes.

Quote:
Originally Posted by Belegedhel View Post
Did the water start to drip immediately after the unit was shut off, or only after it was turned back on again?
Only after it was turned back on again?

Quote:
Originally Posted by Belegedhel View Post
Did anyone go in and out of the door?
It's possible, but honestly I can't say for certain. Are you thinking there might have been some interaction between extreme temperature differentials?
__________________
trekerboy is offline   Reply With Quote
Old 09-03-2016, 11:15 AM   #5
1 Rivet Member
 
2014 31' Classic
Hot Springs , Arkansas
Join Date: Jan 2016
Posts: 16
If the blower vent on the bottom of our unit is not completely open ours will dispense water into the floor.
__________________
Gigi1957 is offline   Reply With Quote
Old 09-04-2016, 09:44 AM   #6
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 2,058
One of two things seems to be happening (both problems many other owners have experienced).

Many of us have experienced the issue where the unit seems to retain condensate, and then when the unit is turned off, it is suddenly released. In some cases it is released to the condensate drainage system, in others it drips into the interior as well. Typically if you can find the right combination of fan speed and vent openings/directions, you will see that you get a steady drip from your condensate capture hose, or in your case down the outside of the trailer, and you won't have any drip to the inside, or any burst of drainage when you turn off the AC. I don't run my fan on max anymore, and no longer have this problem.

If it is just dripping to the inside, not streaming, then I would suggest that what is happening is the plastic duct in the AC that is used to draw in air is getting cooler and cooler the longer you run the system. In theory, if you have your trailer fairly well sealed up, then the air in the trailer should become less and less humid as it gets passed through the AC unit.

Now, if you walk out of the front door, a volume of nice humid air enters your trailer. When this air gets sucked into your AC intake, it is going to encounter that cold plastic, and some of that humidity is going to condense in the intake. Perhaps if the AC is kept running the constant rush of air keeps those drops of condensate stuck to the plastic intake duct, so when you turn it off, the water is then able to drip down. It is unexpected that you would see the drips only after turning the AC back on again, though.

My AC unit is only a couple of years old. I recently pulled the shroud off of it, and observed that on each side of the unit, there are coolant lines or wires that penetrate from the outside into the air intake side of the AC unit. The factory used some kind of very mobile butyl to seal the hole around the penetrations, and in only a couple years' time, that butyl had sagged enough to allow outside air to get sucked directly into my AC. I got rid of a lot of my dripping when I sealed these up.

So next time you experience this bit of dripping, try to identify exactly where it is coming from, and whether it corresponds to the intake side of the AC or not.

good luck!
__________________
Belegedhel is offline   Reply With Quote
Old 09-10-2016, 11:10 AM   #7
4 Rivet Member
 
trekerboy's Avatar
 
1979 31' Excella 500
Charlevoix , Michigan
Join Date: Aug 2014
Posts: 286
Well, I did a bit of detective work and am no closer to figuring out why the condensation leaked in from the vents that one time, but I did learn a lot about where the condensate congregates in the AC unit!

Click image for larger version

Name:	ImageUploadedByAirstream Forums1473527292.438401.jpg
Views:	21
Size:	62.0 KB
ID:	271375Click image for larger version

Name:	ImageUploadedByAirstream Forums1473527311.507420.jpg
Views:	23
Size:	73.6 KB
ID:	271376
Click image for larger version

Name:	ImageUploadedByAirstream Forums1473527324.170796.jpg
Views:	20
Size:	68.3 KB
ID:	271377

And this seems to be the "cup" where it all congregates and drips out the outside:

Click image for larger version

Name:	ImageUploadedByAirstream Forums1473527333.256872.jpg
Views:	23
Size:	65.2 KB
ID:	271378

While I was up there I did find a missing rivet hole that perhaps some water was leaking into, I plugged that up.

Thanks for your help everyone, case closed for now.
__________________

__________________
trekerboy is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic Brisk II install adonh Furnaces, Heaters, Fireplaces & Air Conditioning 14 09-26-2015 03:25 PM
Dometic Brisk II Air Conditioner adonh Furnaces, Heaters, Fireplaces & Air Conditioning 4 06-25-2013 10:59 AM
Duotherm Brisk Air texascanuk Furnaces, Heaters, Fireplaces & Air Conditioning 1 04-07-2011 08:36 PM
Brisk Air New Style Shroud seawaatty Furnaces, Heaters, Fireplaces & Air Conditioning 0 03-25-2010 12:27 PM
Duo Therm Brisk Air JAG Furnaces, Heaters, Fireplaces & Air Conditioning 6 06-06-2002 08:29 PM


Virginia Campgrounds

Reviews provided by



Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:26 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.