Old 07-04-2007, 05:22 PM   #1
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet Coleman AC Problems

My old Coleman AC on my 83 Excella has developed a problem. After running fine for extended periods, days even, it will emit a shuddering “Brrrrrgh!” and shut down. Checking the voltage at the unit reveals 122 volts. Even jumping around the switch accomplishes nothing. Not anything works, not the fan, the heater, or the compressor. After sitting twenty minutes or so, it will come back to life. This has happened a couple of times (that I know of). Has anyone else experienced anything like this?

Thanks

Vaughan
__________________

__________________
vswingfield is offline   Reply With Quote
Old 07-04-2007, 05:29 PM   #2
Desert Fox
 
1985 31' Sovereign
Tucson , Arizona
Join Date: Jan 2004
Posts: 250
Smile Hi,

You may have a termal swich on your compresor that is defective or the compresor may be bad. Normaly on a cooling unit there is a termal swich which keeps the defective motor from caching fire or blowing out your breakers. You schould check your voltage when the unit is running and if you have a amp meter measure the current draw.
Good luck Russell in hot Tucson Az. Wating for the monsoon.
__________________

__________________
RUSSELL is offline   Reply With Quote
Old 07-04-2007, 05:34 PM   #3
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
The compressor is protecting itself

Quote:
Originally Posted by vswingfield
... After running fine for extended periods, days even, it will emit a shuddering “Brrrrrgh!” and shut down. ...
Sounds like the overtemp sensor mounted on the compressor shut down your party. I think you're running low on freon.

The compressor's load will vary with respect to the outside temperature. If the day, in itself, is somewhat comfortable, the compressor does not have a hard time keeping your Airstream's interior cooled to your liking. But if the day is a bit on the hot side, the compressor will not be cooled by the return of "not real hot" freon.

I think you need freon. The problem is that very few people will service RV air conditioners. Unless you're lucky to find someone like Johnny, you may have to replace your AC.

Tom
TomW is offline   Reply With Quote
Old 07-04-2007, 05:44 PM   #4
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet Runnin Hot in Arkansas

Quote:
Originally Posted by TomW
Sounds like the overtemp sensor mounted on the compressor shut down your party. I think you're running low on freon.

The compressor's load will vary with respect to the outside temperature. If the day, in itself, is somewhat comfortable, the compressor does not have a hard time keeping your Airstream's interior cooled to your liking. But if the day is a bit on the hot side, the compressor will not be cooled by the return of "not real hot" freon.

I think you need freon. The problem is that very few people will service RV air conditioners. Unless you're lucky to find someone like Johnny, you may have to replace your AC.

Tom
Thanks Russell and Tom,

That’s about what I thought. I want it gone, I want it gone, but it’s also time to pay the car insurance. On hot sunny days, the interior is the same temp as outside. I want to replace it with a 15,000 btu Carrier heat pump, but finances dictate otherwise, at least for the short run. My brother and I could service the unit, he even has a bottle of Freon in reserve, but I really don’t want to go to the trouble of adding taps to the lines. I just don’t think it’s big enough for my Airstream.

Vaughan
__________________
vswingfield is offline   Reply With Quote
Old 07-04-2007, 06:13 PM   #5
Well Preserved

 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 20,190
Quote:
Originally Posted by vswingfield
I want to replace it with a 15,000 btu Carrier heat pump, but finances dictate otherwise,
Vaughan
A similar sized non-heat pump Carrier is several hundred dollars cheaper.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 07-04-2007, 07:02 PM   #6
Rivet Master
 
Ganglin's Avatar
 
1971 27' Overlander
Central , Ohio
Join Date: Jun 2006
Posts: 2,365
Images: 13
Vaughan,

I have an old Coleman also that does some similar things. Lucky to find a guy in a nearby small town that has worked on them for years. He advised that before I bring it in (and spend money on it) we should take the cover off and clean everything throughly. Said even a few leaves in the wrong spot can cause enough of a hot spot to shut the unit down. His next thought (as mentioned above) was - low on freon.
__________________
Ganglin is offline   Reply With Quote
Old 07-05-2007, 06:33 PM   #7
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet Thanks Guys

Quote:
Originally Posted by overlander63
A similar sized non-heat pump Carrier is several hundred dollars cheaper.
Hi Terry,

I looked at those too. Here in Arkansas, the heat pump would take care of most of my heating needs. For colder nights, I have a stand up electric heater. Given the price of propane, I really try to avoid burning it.
Quote:
Originally Posted by Ganglin
Vaughan,

I have an old Coleman also that does some similar things. Lucky to find a guy in a nearby small town that has worked on them for years. He advised that before I bring it in (and spend money on it) we should take the cover off and clean everything throughly. Said even a few leaves in the wrong spot can cause enough of a hot spot to shut the unit down. His next thought (as mentioned above) was - low on freon.
Hi Gary,

Excellent point. I have “fixed” more than one home refrigerator by vacuuming the coils.

Vaughan
__________________
vswingfield is offline   Reply With Quote
Old 07-06-2007, 01:22 PM   #8
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,499
Images: 1
Quote:
Originally Posted by vswingfield
My old Coleman AC on my 83 Excella has developed a problem. After running fine for extended periods, days even, it will emit a shuddering “Brrrrrgh!” and shut down. Checking the voltage at the unit reveals 122 volts. Even jumping around the switch accomplishes nothing. Not anything works, not the fan, the heater, or the compressor. After sitting twenty minutes or so, it will come back to life. This has happened a couple of times (that I know of). Has anyone else experienced anything like this?

Thanks

Vaughan

An AC compressor, if low on freon, will overheat, causing the shut down.

I would suggest that you have someone that is familiar with RV AC';s, put some gauges to it.

They will know what the proper pressures should be, which is a function of the ambient temperature as well.

Andy
__________________
Inland RV Center, In is offline   Reply With Quote
Old 07-06-2007, 03:40 PM   #9
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet First Step

Thanks Andy,

Tomorrow, if not raining, I will pull the cover and do the general cleaning. I'll get my special custom Airstream ladder (extension ladder with two old bath towels duct taped on each side) and get to work. I’ve done automotive AC work, and own two sets of gauges. I am familiar with the process and the ambient air conditions. Do you know which refrigerant Coleman used in them?

I will keep everyone updated on this. Maybe I’ll get lucky and there will be a big nest blocking the flow.

Vaughan
__________________
vswingfield is offline   Reply With Quote
Old 07-07-2007, 03:24 PM   #10
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet Step 1, No Luck

Quote:
Originally Posted by vswingfield
Maybe I’ll get lucky and there will be a big nest blocking the flow.
Well, just finished removing the cover and checking for obstructions. Only 1 small dirt dauber nest on the very top of the compressor. Washed everything anyway.

It did give me a chance to oil the fan. The plastic plugs in the oil lines broke and fell away, so I decided to make replacements by squirting a tiny amount of silicone seal on the top. Ordinarily I would never put silicone seal where it would be potentially difficult to remove, but hey, I just flooded the things with 20 weight Mobile 1. There’s no way it’s going to stick. I kind of smeared it off to the side to create little pull handles.

The nests I did discover was a big nest of the large red wasps in my front vent and a nest of the smaller, less aggressive, red and black wasps in the belly pan by the steps. After dealing with them, there are still a few survivors buzzing by. I decided that replacing the cover could wait till tomorrow when things calm down a bit.

I think the next step will be replacement with a 15,000 btu heat pump as soon as financially possible.

Vaughan
__________________
vswingfield is offline   Reply With Quote
Old 07-07-2007, 05:35 PM   #11
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,809
Images: 12
A simple overload cutoff at the compressor would not effect the fan.

After the unit shuts down and the fan will not work will the fan work an hour after the AC has shut down. I ask this because if a unit is low on gas and in high humidity it will freeze over the coils and if this ice gets enough it could touch the fan and thus the noise you hear. Once the fan stops the compressor would soon go out on overload. If the unit sits for an hour and then the fan will run I would look for ice on the face of the coils the next time you run it. Just remove the filter and look up at the coils.

As long as you have the cover off you can do a simple check as to the charge. Start the unit and after a few minuits touch the larger of the 2 lines at the compressor. This line should be cold and if the humidity is high it may be wet. If not cold or wet but warm you have a problem, low charge or leaking valve in the compressor. Don't touch that small line. It will be hot.

That old a unit most likely has a piston compressor. The newer units a rotory and much quiter. That is it's self may be a good reason to upgrade.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is online now   Reply With Quote
Old 07-07-2007, 06:10 PM   #12
Rivet Master
 
vswingfield's Avatar
 
1983 34' Excella
1967 24' Tradewind
Little Rock , Arkansas
Join Date: Nov 2006
Posts: 3,771
Images: 32
Rivet Cool Rig, HowieE!

Quote:
Originally Posted by HowieE
A simple overload cutoff at the compressor would not effect the fan.

After the unit shuts down and the fan will not work will the fan work an hour after the AC has shut down. I ask this because if a unit is low on gas and in high humidity it will freeze over the coils and if this ice gets enough it could touch the fan and thus the noise you hear. Once the fan stops the compressor would soon go out on overload. If the unit sits for an hour and then the fan will run I would look for ice on the face of the coils the next time you run it. Just remove the filter and look up at the coils.

As long as you have the cover off you can do a simple check as to the charge. Start the unit and after a few minuits touch the larger of the 2 lines at the compressor. This line should be cold and if the humidity is high it may be wet. If not cold or wet but warm you have a problem, low charge or leaking valve in the compressor. Don't touch that small line. It will be hot.

That old a unit most likely has a piston compressor. The newer units a rotory and much quiter. That is it's self may be a good reason to upgrade.
Hi HowieE,

Good suggestions, but it’s not like an ice buildup. The sound to shutoff is only a couple of seconds. Coil freeze over is an excellent indicator of low Freon since the low size pressure of R12 almost exactly coincides with Fahrenheit temperature of the resulting gas in the evaporator. You usually fill till the low side is 30 or 31 degrees to prevent freezing condensation. I am not getting freeze up, so I am a little skeptical of the low Freon guesses. Could be wrong, though. I was also concerned about the fan being shut off by a compressor shutoff. Didn’t make sense.

Great looking rig! I looked at your website. Dual fuel, huh, cool beans! Haven’t seen anything like that in years! Back in the 80s I rebuild irrigation engines in the Texas panhandle. Most of the stuff was Minneapolis Moline HD 800s, 800 CID natural gas burning 6 cylinders. We were also an Allis Chalmers dealership. Many of the Allis diesels were fitted with propane carbs and connected to natural gas or propane. You don’t have to even readjust the carb to switch from one to the other. They made tremendous power. A legendary embarrassing event occurred before I started there. They had completed a dual fuel conversion on a new Allis engine and a factor rep was there taking photos. The engine was hooked to a 600 hp tractor dyno. One of the shop owners richened the natural gas mixture, and the engine ran away-pegging the dyno and even flattening the tire on one side and lifting the other off the shop floor on the other. Just as it appeared that the engine was going to start spinning the dyno, someone stomped on the natural gas line and got things under control.

I think I need a bigger, newer unit anyway. Since you have a properly sized unit, how does your AC cool your AS? It really gets hot here, and I’m thinking a 15,000 btu AC is what I need anyway.

Vaughan
__________________
vswingfield is offline   Reply With Quote
Old 07-07-2007, 08:27 PM   #13
Well Preserved

 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 20,190
Vaughan, it's a little late to tell you now, but the older a/c units used R22 freon.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 07-07-2007, 08:34 PM   #14
Moderator
 
HiHoAgRV's Avatar

 
1991 34' Excella
1963 26' Overlander
1961 26' Overlander
Central , Mississippi
Join Date: Nov 2006
Posts: 5,325
Images: 29
Blog Entries: 49
I tend to agree with Howie, all of the units I have messed with have the thermal shutoff at the compressor, it wont shut down the fans. Mine had a bad circuit breaker and did the unpredictable so I would swap a $5 breaker and see where it went.
Then again, I can see that your are looking for the forum to support the purchase of a new larger AC, go for it. Your old one is probably on it's last leg
__________________

__________________
Hi Ho Silver RV! Vernon, Sarah, Mac the Border Collie -
A honkin' long 34' named AlumaTherapy http://www.airforums.com/forums/f205...num-54749.html
and a 26' '63 Overlander, Dolly http://www.airforums.com/forums/f109...ome-71609.html
HiHoAgRV is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water problems Dbraw Fresh Water Systems 14 10-03-2009 03:15 AM
Generator Problems thenewkid64 General Motorhome Topics 27 05-07-2003 10:36 PM
Auto Battery problems.... kzener40 Airstream Motorhome Forums 10 08-05-2002 07:37 PM
Fridge Cooling Problems 68International Refrigerators 6 07-10-2002 04:53 PM
Lighting problems ramoore53 Electrical - Systems, Generators, Batteries & Solar 1 05-08-2002 11:02 AM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:32 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.