Old 06-28-2009, 11:33 AM   #15
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,499
Images: 1
Quote:
Originally Posted by Gael79 View Post
Hello All,

Even though the start Cap "tests" O.K., The relief hole in the top is open, so I will replace it with a like capacitor from Grainger ($8.00). I'll post P/N when I purchase and check to see if actually works.

I was getting goofy continuity readings on the start relay, so I decided to open it up. Check out the relay that I am the proud owner of...

The Service manual, (yes I have a copy PM me if interested) shows the relay as P/N 1890A13. The relay has General Electric and 3ARR3 K3S2 marked on it.

Has anyone changed this relay out with success, and do you have a good P/N and source?
I'll take it with me when I go to Grainger tomorrow. Once again, if I have any luck, will post results.

Thanks again to all who have got me this far. If this fixes the problem, and the a/c works, I'll have about $40.00 invested, and that includes a moisture proof enclosure to place these two components in.

Best to all,
Grainger also has the relay.

Andy
__________________

__________________
Inland RV Center, In is offline   Reply With Quote
Old 06-28-2009, 02:27 PM   #16
2 Rivet Member
 
Gael79's Avatar
 
1970 31' Sovereign
Lombard , Illinois
Join Date: Apr 2008
Posts: 93
Hello Andy,

Thanks a million! Do you happen to know what the current p/n is, or do they have the cross reference manuals on site?

Thanks again,
__________________

__________________
Scott

I have a picture of my Airstream in my wallet, and I'm sitting on it...

...If that's not love, I don't know what is!
Gael79 is offline   Reply With Quote
Old 06-28-2009, 02:51 PM   #17
4 Rivet Member
 
Distantdrummer's Avatar
 
1975 31' Sovereign
Houston , Texas
Join Date: Nov 2003
Posts: 494
Scott where did you get the manual?
Why not scan and post it (or link) here on site like someone was good enough to do with the later model manual.
Keep us posted with your results. Sure hope it works.
Armstrongs are awesome for their duration. Just think what other item could set up there in the elements for 40 years and keep on tickin. Not even a Timex.
__________________
__________________________
____ d'drummer ____

...aahh..rumm..pu..tum..tummm...
Distantdrummer is offline   Reply With Quote
Old 06-28-2009, 09:18 PM   #18
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,499
Images: 1
Quote:
Originally Posted by Gael79 View Post
Hello Andy,

Thanks a million! Do you happen to know what the current p/n is, or do they have the cross reference manuals on site?

Thanks again,
There are several different relay's that you can use.

Basically the start relay is a SP normally off device. (single pole)

The two big factors is the coil voltage, which in your case is 24 volts AC, and the currect carrying capacity of the relay terminals. As I recall it's something like 18 amps.

Andy
__________________
Inland RV Center, In is offline   Reply With Quote
Old 06-28-2009, 11:36 PM   #19
2 Rivet Member
 
Potters , Idaho
Join Date: Jun 2007
Posts: 97
Scott,
From the picture your relay got wet and shorted out and that's what cooked it. It took less than 30 seconds to fry it probably.
Continuity is a goofy thing with relays. When your Thermostat calls for air it puts 24V to your relay and it snaps, which then makes connection to start your AC and you will have voltage across two contacts. . So when you do continuity on a dead (no volt) you should have continuity across the other side only. Going from memory now. It is easy to test with VOM. Disconnect the wires going to the AC and turn the thermostat and find the 24v from Thermostat. Hook the wires to the relay and you should have 24v going to the AC unit.
The relay part number I have is 1890A13 from the Armstrong Service guide. The fan relays (2) is part 237-07. One for low speed and one for high speed.
I believe you can use any relay with the correct number of terminals and as long as it is rated for 24v and as Andy states heavy current draw. The Granger catalog shows a bunch with descriptions and the part number may not be the same.
I would be interested in the service manual if you can PM it too me.
Good luck,
Gary
__________________
phoney is offline   Reply With Quote
Old 06-29-2009, 05:43 AM   #20
2 Rivet Member
 
Gael79's Avatar
 
1970 31' Sovereign
Lombard , Illinois
Join Date: Apr 2008
Posts: 93
Manuals Coming...

Hello Gary,

Give me a day or two, and I'll post it on this thread. That way as suggested, all will have access.

This relay is not a contactor relay, it is a potential relay. It is a separate relay, not the low 24vac relay. I believe it is designed to engage when there is no (low) voltage across it, and disengage, based on the back voltage (EMF) that the compressor coils generate when spooling up to speed. There are only 3 wires going to this relay. It removes the start capacitor from the circuit, when the motor in the compressor is at about 3/4 of full speed. Most motors today have centrifugal switches that open up when the armature spins so fast to do the same thing.

I know of an appliance store in town that does A/C and heating work. I will try to get there today, and see if they have any insight.

Thanks to all,
__________________
Scott

I have a picture of my Airstream in my wallet, and I'm sitting on it...

...If that's not love, I don't know what is!
Gael79 is offline   Reply With Quote
Old 07-01-2009, 09:23 PM   #21
2 Rivet Member
 
Gael79's Avatar
 
1970 31' Sovereign
Lombard , Illinois
Join Date: Apr 2008
Posts: 93
Replacement Parts

Hello All,

The Replacement Start Capacitor was purchased at Grainger. The capacitor is P/N 2MEP1, Dayton is the manufacturer. It is the same physical size as the old cap, but this one is rated for 330 volts, rater than 220 volts, which was the original one. I could have had them order a 220 volt, and saved about $3.00, but they had this one in stock,and for those of you that want to use the same enclosure, the new 220 volt one is a bit smaller in diameter than the original. If you buy the one I did, it fits in the stock bracket, being the same diameter as the original. This is O.K., you can go higher with the voltage, but don't go lower than the rated voltage. The original cap was 130-156mf and the new one is 130-158mf, also within allowable tolerances.

Now for the potential relay. I searched high and low, several hours, over a couple of days, to no avail. I finally ended up in a A/C wholesaler supply warehouse (G.W. Berkheimer Co., actually a big chain of stores in the Chicago area). I told my tale of woe to an older guy behind the counter, and he had the answer. The relay I was given is close if not the exact same physical size as the original. The manufacturer of this relay is "SUPCO". It is called a "Universal Potential Relay". Manufacturer's P/N SUPR 418-146-0242. Berkheimer's P/N 94847. This relay wires exactly, wire for wire, the same as the old relay, so it is a easy install. Where the original relay uses back EMF (tastes the voltage level of the compressor windings) this new Universal relay has a timing circuit that disengages the capacitor after a given time, to do the same function as the original.

I have attached a couple of pictures to show what the install looks like. It is, I believe as close to original as you can get today. Like I said, mine was damage due to moisture. This is only a temporary install for me. I am going to replace the enclosure, with a weatherproof one in the next couple of weeks, but this will get me through the holiday weekend, and was good enough to test the circuit with. Now, it was only in the mid sixties today, but I did hear the compressor kick in, and ran it long enough to feel the lines at the compressor feel hot and cold, so I believe I can report that the new parts do the job. If not, I'll report back after this weekend at the campground.

Bottom Line: New Capacitor, $14.03. New Relay, $16.96. A working A/C on a mid 90's day at the campground, Priceless.

Note: At least in Illinois, Both of these places I went to, Grainger and Berkheimer, are "wholesalers" and you have to have access to a commercial account to purchase from them. As practice, they do not sell to the general public. I was able to puchase these items through my employer's account. Get creative... ... as long as they have a valid business address, they will sell you the parts.

I know I promised a copy of the service manual for a TR21-12. Bear with me. I'll post it next week, as soon as I can get time to figure out how to do it.

Best to all,
Attached Thumbnails
Click image for larger version

Name:	Picture051_01Jul09.jpg
Views:	201
Size:	209.7 KB
ID:	83265   Click image for larger version

Name:	Picture052_01Jul09.jpg
Views:	246
Size:	200.3 KB
ID:	83266  

__________________
Scott

I have a picture of my Airstream in my wallet, and I'm sitting on it...

...If that's not love, I don't know what is!
Gael79 is offline   Reply With Quote
Old 06-29-2010, 02:05 PM   #22
3 Rivet Member
 
1972 27' Overlander
Saline , Michigan
Join Date: Oct 2002
Posts: 178
Same AC much different start cap

My start capacitor looked much like the one in Scott's picture, the wires were connected, but when I touched, they fell off.

My Capacitor looks like his, in the box with the relay, but it is much lower MFD. Mine is 21-25 MFD
250 VAC 60 CPS
GE part# 35F241BA8.

the one scott used is 130 to 158 MFD.

I suppose one of our units may have had the fan replaced.

I could not make out all the number on my Condenser fan.
It is a 1/6 HP rotates CC and has two speeds. After it runs a while it gets stiff, I have oiled it, I might need to replace. Anyone have more specs for an apporpriate condensor fan motor. like RPM, Volts, etc. The guy at Granger, said if I do replace the motor I would need a new, different capacitor.



Quote:
Originally Posted by Gael79 View Post
Hello All,

The Replacement Start Capacitor was purchased at Grainger. The capacitor is P/N 2MEP1, Dayton is the manufacturer. It is the same physical size as the old cap, but this one is rated for 330 volts, rater than 220 volts, which was the original one. I could have had them order a 220 volt, and saved about $3.00, but they had this one in stock,and for those of you that want to use the same enclosure, the new 220 volt one is a bit smaller in diameter than the original. If you buy the one I did, it fits in the stock bracket, being the same diameter as the original. This is O.K., you can go higher with the voltage, but don't go lower than the rated voltage. The original cap was 130-156mf and the new one is 130-158mf, also within allowable tolerances.

Now for the potential relay. I searched high and low, several hours, over a couple of days, to no avail. I finally ended up in a A/C wholesaler supply warehouse (G.W. Berkheimer Co., actually a big chain of stores in the Chicago area). I told my tale of woe to an older guy behind the counter, and he had the answer. The relay I was given is close if not the exact same physical size as the original. The manufacturer of this relay is "SUPCO". It is called a "Universal Potential Relay". Manufacturer's P/N SUPR 418-146-0242. Berkheimer's P/N 94847. This relay wires exactly, wire for wire, the same as the old relay, so it is a easy install. Where the original relay uses back EMF (tastes the voltage level of the compressor windings) this new Universal relay has a timing circuit that disengages the capacitor after a given time, to do the same function as the original.

I have attached a couple of pictures to show what the install looks like. It is, I believe as close to original as you can get today. Like I said, mine was damage due to moisture. This is only a temporary install for me. I am going to replace the enclosure, with a weatherproof one in the next couple of weeks, but this will get me through the holiday weekend, and was good enough to test the circuit with. Now, it was only in the mid sixties today, but I did hear the compressor kick in, and ran it long enough to feel the lines at the compressor feel hot and cold, so I believe I can report that the new parts do the job. If not, I'll report back after this weekend at the campground.

Bottom Line: New Capacitor, $14.03. New Relay, $16.96. A working A/C on a mid 90's day at the campground, Priceless.

Note: At least in Illinois, Both of these places I went to, Grainger and Berkheimer, are "wholesalers" and you have to have access to a commercial account to purchase from them. As practice, they do not sell to the general public. I was able to puchase these items through my employer's account. Get creative... ... as long as they have a valid business address, they will sell you the parts.

I know I promised a copy of the service manual for a TR21-12. Bear with me. I'll post it next week, as soon as I can get time to figure out how to do it.

Best to all,
__________________
loechli is offline   Reply With Quote
Old 06-29-2010, 06:48 PM   #23
3 Rivet Member
 
1972 27' Overlander
Saline , Michigan
Join Date: Oct 2002
Posts: 178
Just got off the trailer,

The Condensor motor is a GE
I see the following number on the bottom of the motor.
9397
5KGP39EG 9397s
According to my manual it is a 2 speed 1/6 HP motor and it spins CCW

I did a bunch of google searches and can not find these part numbers or any cross references.

I also want to know if it is ok to use a start capacitor with larger MFD than mine.

My Capacitor looks like his, in the box with the relay, but it is much lower MFD. Mine is 21-25 MFD
250 VAC 60 CPS
GE part# 35F241BA8.

the one scott used is 130 to 158 MFD.
__________________
loechli is offline   Reply With Quote
Old 06-29-2010, 07:49 PM   #24
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,119
Strange. There shouldn't be that much of a difference, unless you're looking at the fan capacitor rather than the compressor capacitor.
__________________
Jammer is offline   Reply With Quote
Old 06-30-2010, 07:33 PM   #25
3 Rivet Member
 
1972 27' Overlander
Saline , Michigan
Join Date: Oct 2002
Posts: 178
Granger can not find a start capacitor for me

The start capacitor currently on my 72 armstrong ac is
21-25 MFD 250 VAC
Granger can not find a match.
How high can I go on the MFD before i should be concerned about damaging my compressor.

Has anyone used a supco spp6e, it sounds like it can replace both the start capacitor as well as the Start relay, I am not sure my start relay is bad, but for the price I will probably replace, it would be nice if the spp6e could do both, not sure if this is a good idea and how to wire.

Steve
__________________
loechli is offline   Reply With Quote
Old 08-10-2011, 02:39 PM   #26
3 Rivet Member
 
1972 27' Overlander
Saline , Michigan
Join Date: Oct 2002
Posts: 178
I have a 72 international with orniginal Armstrong Air conditioner TR 21-12.

Last year I replaced a very stiff condenser fan, start relay and start capacitor, AC worked very well, but then it started shutting down the compressor in hot temps over 90 degrees.

Just had the condenser coils acid cleaned in hopes that it was just dirty.
That did not solve problem.

Currently the AC works almost always on "low", and often on high, but when it gets in the high 80's or hotter and I am running on high the Compressor will often cycle off. If I shut the unit off, wait 2 or 3 minutes it will start and run fine, then after 10 min or so, compressor will shut off again.

Anyone have any ideas?
__________________
loechli is offline   Reply With Quote
Old 08-10-2011, 03:55 PM   #27
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,499
Images: 1
Quote:
Originally Posted by loechli View Post
I have a 72 international with orniginal Armstrong Air conditioner TR 21-12.

Last year I replaced a very stiff condenser fan, start relay and start capacitor, AC worked very well, but then it started shutting down the compressor in hot temps over 90 degrees.

Just had the condenser coils acid cleaned in hopes that it was just dirty.
That did not solve problem.

Currently the AC works almost always on "low", and often on high, but when it gets in the high 80's or hotter and I am running on high the Compressor will often cycle off. If I shut the unit off, wait 2 or 3 minutes it will start and run fine, then after 10 min or so, compressor will shut off again.

Anyone have any ideas?
Either your using an extension cord that's too small, or, the AC is low on Freon.

Check the temperature as close to the AC outlet as possible. That temperature should be 15 to 18 degrees cooler than the inside of the trailer.

If less than that, low Freon is the problem.

Andy
__________________
Inland RV Center, In is offline   Reply With Quote
Old 08-10-2011, 09:20 PM   #28
3 Rivet Member
 
1972 27' Overlander
Saline , Michigan
Join Date: Oct 2002
Posts: 178
No extension cord is being used,
I will check the temperature.

Andy do you mean to check the temp inside trailer then run air and check temp coming out of vent?
__________________

__________________
loechli is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Armstrong TR21-12 gonna fixey ??? pansy Furnaces, Heaters, Fireplaces & Air Conditioning 1 05-08-2008 08:08 AM
Schematic wiring diagram for Armstrong AC TR21-12, GO7series DMC Furnaces, Heaters, Fireplaces & Air Conditioning 4 10-06-2007 01:01 PM
Hello, looking for a schematic of the wiring in my Armstrong AC model TR21-12, DMC Member Introductions 1 07-10-2007 07:11 AM
armstrong a/c mike beech Furnaces, Heaters, Fireplaces & Air Conditioning 16 01-06-2007 06:31 PM