AC electrical question

I have a 98 Excella 1000 with 30amp service and one AC unit.

Should the AC have a GFCI breaker in the main panel box?

I think PO may have made some changes in the main box.
__________________

__________________
rdhoyum is offline   Reply With Quote
Old 04-16-2012, 08:35 PM   #2
Rivet Master
 
TouringDan's Avatar

 
1966 24' Tradewind
1995 34' Excella
Lynchburg , Virginia
Join Date: Sep 2009
Posts: 2,472
I believe that the AC should be on a dedicated 20 amp regular circuit breaker. It should not be a gfci type.

Dan
__________________

__________________
TouringDan is offline   Reply With Quote
Old 04-16-2012, 08:39 PM   #3
Rivet Master
 
Minno's Avatar

 
1972 31' Sovereign
Lexington , Minnesota
Join Date: Feb 2009
Posts: 3,323
No, the a/c should not be on a GFCI breaker. Probably won't hurt anything though. Might trip needlessly, which would be a nuisance.

Chris
__________________
Minno is offline   Reply With Quote
Old 04-16-2012, 08:48 PM   #4
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,813
Images: 12
No The starting capacitor on the compressor motor will most likely cause the breaker to trip more times than you will be willing to but up with.

GFIs are only used where an individual can get between the receptacle and a good ground, ie a water pipe.

They are grossly over rated and misunderstood by a governing bodies that has no knowledge of electricity.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 04-16-2012, 10:16 PM   #5
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 5,140
Images: 2
Blog Entries: 5
Here! Here! Howie!
__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 04-17-2012, 09:21 AM   #6
1 Rivet Member
 
Chandler , Arizona
Join Date: Sep 2011
Posts: 16
So consensus is regular breaker for the AC circuit. Which circuit should have the GFCI then? The main breaker??? or one of the other two. One of those is a 20 amp double pole...I'm guessing for the various wall outlets....then what would the other 30 amp be for?

I have the owners manual, but nothing technical for the trailer.
__________________
rdhoyum is offline   Reply With Quote
Old 04-17-2012, 10:01 AM   #7
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
in my '94 34' the main breaker was 30A and the air/microwave was on a 20A. the gfi was for the bath/galley/fridge/outside outlet circuit.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 04-17-2012, 10:27 AM   #8
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,813
Images: 12
The above description is correct for your trailer. There is NO REASON what so ever for a double pole breaker to be in an Airstream trailer with a 30 amp service. Double pole beakers are used with 220 volt single phase systems which in a trailer system would not be required until a 50 amp service.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 04-17-2012, 12:50 PM   #9
1 Rivet Member
 
Chandler , Arizona
Join Date: Sep 2011
Posts: 16
Ok, I got the circuit breakers all sorted. AC on its own 20amp, the working GFCI for bath and galley, the double 20 amp breaker is circuits 3&4 for b-room, converter and liv-rm.

Here's the problem. The AC controls are connected to 120 line. The control switch, rotary knob, six pin connector is disconnected. Upon connecting it the shore line outlet(a GFCI) trips instantly.

I can only conclude it onto the roof to diagnose an AC problem.
I'm doing all this while at storage. I'll bring it home tommorrow to connect to 30 amp RV pedestal and confirm the AC works like it did before last trip.

Any suggestions on what to check/test in AC would be very much appreciated.
__________________
rdhoyum is offline   Reply With Quote
Old 04-17-2012, 12:52 PM   #10
1 Rivet Member
 
Chandler , Arizona
Join Date: Sep 2011
Posts: 16
One note!!!!!! The AC is off when connecting the controls. I made no attempt to turn it on......of course I have no power to do so.
__________________
rdhoyum is offline   Reply With Quote
Old 04-17-2012, 01:05 PM   #11
Moderator
 
DKB_SATX's Avatar

 
2017 26' Flying Cloud
1976 Argosy 28
Alamo Heights , Texas
Join Date: Aug 2006
Posts: 6,401
Images: 1
Blog Entries: 7
So you're tripping a GFCI on the supply side of your shore-power receptacle, not one inside the Airstream?

Are you certain that shore-power receptacle just a mildly-annoying GFCI, or is it the REALLY frustrating arc-fault type that can trip when you're plugging in a perfectly safe appliance?
__________________
— David

Zero Gravitas — 2017 Flying Cloud 26U | Il Progetto — 1976 Argosy 28 Center Bath | WBCCI# 15566

He has all of the virtues I dislike and none of the vices I admire. — Sir Winston Churchill
DKB_SATX is offline   Reply With Quote
Old 04-17-2012, 01:56 PM   #12
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,813
Images: 12
If you are attempting to Plug Into a GFI as a source of power for the trailer and not talking of the GFI in the trailer you will never get power to the trailer unless you go in the trailer and turn off ALL the breakers.

What is happening there is as you plug into the GFI you are making contact with the receptacle in a sequence that is causing the GFI to see current across hot to ground before it sees hot to neutral. That will pop the breaker. The ground lug is longer than the hot and neutral and thus is the first to make contact.

Try turning off all the breakers inside the trailer and then plug into the GFI. Then you should be able to turn on the breakers inside. If at this point you still pop either the GFI inside the trailer or the one at the source you have a problem.

Report back if that is the case with details and we will go from there.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 04-17-2012, 02:05 PM   #13
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,316
It's usually considered unwise to plug a GFCI-protected circuit into another GFCI. The first GFCI sees the next one downstream as a ground fault. One reason why campground 30-amp and 50-amp pedestals are not protected by their own GFCI; since virtually all RVs have at least one GFCI breaker inside the unit.

Remember, only one GFCI per circuit! So, if your trailer has GFCI breakers, do not plug your trailer into a GFCI-protected home circuit. If you have nowhere else to plug in, you should turn off the GFCI breakers inside your trailer and do without them for as long as your shore power is plugged into a GFCI outside the trailer.

Coventional wisdom also says that you should not plug in appliances that have a permanently-installed self-starting motor (air conditioner or refrigerator with thermostat-controls) into a GFCI. The starter circuit typically registers as a ground fault as soon as the motor kicks in.
__________________
WBCCI #1105
TAC LA-4

My Google-Fu is strong today.
Protagonist is offline   Reply With Quote
Old 04-17-2012, 02:30 PM   #14
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,813
Images: 12
As long as we are talking the limitations of a GFI any system that has a filter cap across the input side of it's internal transformer will kick a GFI when plugged in. The charging current of the cap is enough to kick the GFI.

Lots of older audio/video equipment was so designed.

As a plant manager I had 15 steel work benches each with 12 AC receptacles mounted on them and test equipment that ranged as high a 80,000 volts. The local electrical inspector required that they each be on a GFI. They were till he left the building.
__________________

__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:56 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.