Old 09-01-2013, 08:16 PM   #1
Rivet Master
 
Skater's Avatar
 
1995 30' Excella
Bowie , Maryland
Join Date: Apr 2005
Posts: 2,344
A/C woe - thermostat?

Our Dometic Penguin A/C has a problem where sometimes the compressor just doesn't start, although the fan runs. When the compressor does work, the A/C works beautifully. Adjusting the temperature seems to make it start working again. Do you think this is a sign of a bad thermostat or board or something else?

Model number is 620215.321; I'm pretty sure it's original to our '95. Thanks for any suggestions. Some of the parts look expensive so I'd like to be reasonbly sure it will fix the problem.
__________________

__________________
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel

Sold but not forgotten: 1991 Airstream B190
Sold: 2006 F-250 6.0L Powerstroke Supercab
Skater is offline   Reply With Quote
Old 09-01-2013, 08:45 PM   #2
Rivet Master
 
Skater's Avatar
 
1995 30' Excella
Bowie , Maryland
Join Date: Apr 2005
Posts: 2,344
Correction/update - it seems to be about 10 degrees (F) off. So the thermostat is set for 65 degrees, and it kicked on when the air going in was at about 75 degrees (using a laser thermometer to measure).
__________________

__________________
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel

Sold but not forgotten: 1991 Airstream B190
Sold: 2006 F-250 6.0L Powerstroke Supercab
Skater is offline   Reply With Quote
Old 09-05-2013, 06:52 AM   #3
Rivet Master
 
Skater's Avatar
 
1995 30' Excella
Bowie , Maryland
Join Date: Apr 2005
Posts: 2,344
Anyone have any suggestions or thoughts on this?
__________________
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel

Sold but not forgotten: 1991 Airstream B190
Sold: 2006 F-250 6.0L Powerstroke Supercab
Skater is offline   Reply With Quote
Old 09-05-2013, 06:56 AM   #4
3 Rivet Member
 
genearnold's Avatar
 
1992 34' Limited
Grand Island , Nebraska
Join Date: Feb 2005
Posts: 248
Are you using an extension cord? If so that may be the problem. If not, are you sure there is adequate power at the plug-in? I think one of these may me the most likely problem.
__________________
'92 Limited 34ft (now sold); '96 Dodge Cummins 4X2, 5speed
genearnold is offline   Reply With Quote
Old 09-05-2013, 07:21 AM   #5
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,300
My understanding— which becomes less certain with advancing age— is that the thermostat setting is a target value, not an absolute. When you set the thermostat to 75°, that does not mean that the A/C comes on when the temperature rises to 75°, or that the A/C shuts off when the temperature drops to 75°. What it means is the A/C will try to regulate the temperature so that the temperature range is centered on 75°. It will come on a certain number of degrees ABOVE 75°, and will shut off a certain number of degrees BELOW 75°.

Not sure how MANY degrees above or below, but ±10° from the setting for turning on or off seems excessive. I would expect something closer to ±3°~5° from the setting.

Having said all that, I think we've become too good at measuring temperature, and we become fixated on the numbers. Which is important for a refrigerator/freezer or when cooking meat, but not so much for an A/C. All we really need to know on the A/C thermostat is, push it up for warmer, down for colder, and fiddle with it until we're comfortable. Forget the numbers.
__________________
WBCCI #1105
TAC LA-4

My Google-Fu is strong today.
Protagonist is online now   Reply With Quote
Old 09-05-2013, 08:01 AM   #6
Site Team
 
Aage's Avatar
 
1974 31' Sovereign
Ottawa , ON
Join Date: May 2008
Posts: 11,204
Images: 25
There are two hefty capacitors in AC units, and they don't improve with age.

One is for the starting procedure and the other is used while running.

So...... replace the "start cap" and the "run cap". Not terribly difficult to do, nor expensive.
__________________
“Courage is being scared to death, but saddling up anyway.”
...John Wayne...........................
Aage is offline   Reply With Quote
Old 09-05-2013, 08:41 AM   #7
Moderator
 
DKB_SATX's Avatar

 
2017 26' Flying Cloud
1976 Argosy 28
Alamo Heights , Texas
Join Date: Aug 2006
Posts: 6,401
Images: 1
Blog Entries: 7
Quote:
Originally Posted by Protagonist View Post
~~
Having said all that, I think we've become too good at measuring temperature, and we become fixated on the numbers. Which is important for a refrigerator/freezer or when cooking meat, but not so much for an A/C. All we really need to know on the A/C thermostat is, push it up for warmer, down for colder, and fiddle with it until we're comfortable. Forget the numbers.
Heresy! What inoffensive thing could couples squabble about without numbers on the thermostat?!
__________________
— David

Zero Gravitas — 2017 Flying Cloud 26U | Il Progetto — 1976 Argosy 28 Center Bath | WBCCI# 15566

He has all of the virtues I dislike and none of the vices I admire. — Sir Winston Churchill
DKB_SATX is offline   Reply With Quote
Old 09-05-2013, 09:58 AM   #8
2 Rivet Member
 
tony6373's Avatar
 
2000 28' Excella
1994 31' Legacy 30
Hillsboro , Texas
Join Date: Jun 2007
Posts: 84
Thermostat problems

Thermostats do go bad but often they just need cleaning. Try blowing it out with contact cleaner like Radio Shack sells. Or in some cases you can take it apart and clean the contacts with a Q-tip and alcohol. TV remotes respond well to this kind of cleaning.

Interesting story, after buying my first Airstream (a well used '74 27') I ran into the previous owner at a rally. He asked if I had replaced the A/C yet? I said no it works just fine and he nearly had a stroke. Seems that was the main reason he had traded the trailer in on a Bvsn. The little bimetallic spring had let the contact get out of position. So I removed the t-stat cover and flipped the contact back where it belonged and all worked fine. Those old Armstrong A/C were built like a tank.

Tony
__________________
Tony T
2000 28' Classic TT
1994 30' Land Yacht M/H
tony6373 is offline   Reply With Quote
Old 09-05-2013, 11:01 AM   #9
Rivet Master
 
Skater's Avatar
 
1995 30' Excella
Bowie , Maryland
Join Date: Apr 2005
Posts: 2,344
Quote:
Originally Posted by Protagonist View Post
Having said all that, I think we've become too good at measuring temperature, and we become fixated on the numbers. Which is important for a refrigerator/freezer or when cooking meat, but not so much for an A/C. All we really need to know on the A/C thermostat is, push it up for warmer, down for colder, and fiddle with it until we're comfortable. Forget the numbers.
To be clear: I had it set to our usual 75-ish, and it just wasn't kicking on. The camper was extremely warm and stuffy - at least 85 degrees, with high humidity, and neither of us sleeps comfortably in those conditions. In fact, friends of ours were tent camping with us (fairly hardcore tent campers), and they gave up and found a hotel. Without the compressor running, there was no dehumidification, and it wasn't good in there at all. But once I adjusted the thermostat down to 65, the compressor started almost immediately and the camper was in great shape inside of an hour.

I'm not saying it was 77 when the thermostat should have meant it was 75. I'm saying it was frustratingly hot when it should have been comfortable.

Quote:
Originally Posted by Aage View Post
There are two hefty capacitors in AC units, and they don't improve with age.

One is for the starting procedure and the other is used while running.

So...... replace the "start cap" and the "run cap". Not terribly difficult to do, nor expensive.
Quote:
Originally Posted by genearnold View Post
Are you using an extension cord? If so that may be the problem. If not, are you sure there is adequate power at the plug-in? I think one of these may me the most likely problem.
My concern with both of these theories is that when I played with the thermostat, it started working perfectly, and worked perfectly for the entire night, cycling on and off - except it was set at 65 and cycling on and off around 75 degrees. (No extension cord, 30 amp connections.) I'd think if it was a cap or a power problem, it would be trying to cycle on at the correct temperature, and failing, rather than working perfectly at the "wrong" temperature setting.

Not to say that the caps shouldn't be replaced, or that we weren't having a power issue (at several different campgrounds - it's unusual for me to have an issue at any campground; I've ordered an AC volt meter to mount on a wall, though). But I'd think a power or cap problem would cause issues with the compressor starting and running, rather than the thermostat being off.

Quote:
Originally Posted by tony6373 View Post
Thermostats do go bad but often they just need cleaning. Try blowing it out with contact cleaner like Radio Shack sells. Or in some cases you can take it apart and clean the contacts with a Q-tip and alcohol. TV remotes respond well to this kind of cleaning.
Good idea - I'll pull it apart at some point and see what it looks like. The A/C in my B190 was pretty much all mechanical, and one night the thermostat went bad and froze me out. This one has at least some electronics.

Quote:
Interesting story, after buying my first Airstream (a well used '74 27') I ran into the previous owner at a rally. He asked if I had replaced the A/C yet? I said no it works just fine and he nearly had a stroke. Seems that was the main reason he had traded the trailer in on a Bvsn. The little bimetallic spring had let the contact get out of position. So I removed the t-stat cover and flipped the contact back where it belonged and all worked fine. Those old Armstrong A/C were built like a tank.
I've had that happen with other things, like an old monitor. "It goes dim and fuzzy!" "Never had that happen."
__________________
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel

Sold but not forgotten: 1991 Airstream B190
Sold: 2006 F-250 6.0L Powerstroke Supercab
Skater is offline   Reply With Quote
Old 09-05-2013, 11:59 AM   #10
Rivet Master
 
daveswenson's Avatar
 
2012 28' International
Issaquah , Washington
Join Date: Sep 2012
Posts: 767
What kind of thermostat do you have?
Here's a link to putting in an inexpensive digital replacement.

Mod #100: Honeywell, Dometic and Suburban Digitial Thermostat Install | ModMyRV
__________________
Dave

2014 Ram 2500 CTD
Pro Pride
Centramatics
daveswenson is offline   Reply With Quote
Old 09-05-2013, 02:55 PM   #11
Rivet Master
 
Skater's Avatar
 
1995 30' Excella
Bowie , Maryland
Join Date: Apr 2005
Posts: 2,344
Quote:
Originally Posted by daveswenson View Post
What kind of thermostat do you have?
Here's a link to putting in an inexpensive digital replacement.

Mod #100: Honeywell, Dometic and Suburban Digitial Thermostat Install | ModMyRV
Mine is mounted on the A/C itself. I understand newer setups have a separate thermostat, which sounds great, but I'd have to run the wires and all, which I'd rather not get into. Based on the owner's manual, apparently the separate thermostat was an option with my A/C, but Airstream didn't do it.
__________________
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel

Sold but not forgotten: 1991 Airstream B190
Sold: 2006 F-250 6.0L Powerstroke Supercab
Skater is offline   Reply With Quote
Old 09-05-2013, 05:47 PM   #12
Rivet Master
 
daveswenson's Avatar
 
2012 28' International
Issaquah , Washington
Join Date: Sep 2012
Posts: 767
Quote:
Originally Posted by Skater View Post
Mine is mounted on the A/C itself. I understand newer setups have a separate thermostat, which sounds great, but I'd have to run the wires and all, which I'd rather not get into. Based on the owner's manual, apparently the separate thermostat was an option with my A/C, but Airstream didn't do it.
Never mind.
__________________
Dave

2014 Ram 2500 CTD
Pro Pride
Centramatics
daveswenson is offline   Reply With Quote
Old 09-05-2013, 06:04 PM   #13
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
Quote:
Originally Posted by Skater View Post
Mine is mounted on the A/C itself. I understand newer setups have a separate thermostat, which sounds great, but I'd have to run the wires and all, which I'd rather not get into. Based on the owner's manual, apparently the separate thermostat was an option with my A/C, but Airstream didn't do it.
skater, if you have a slide switch for fhe temp setting the contacts may be worn or dirty. some electrical contact cleaner may help. if you take the control panel out, an electronics tech should be able to replace it. i had it done on my '94. think tv or ham radio repair shop.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 09-05-2013, 07:43 PM   #14
Rivet Master
 
Bigventure's Avatar
 
2016 30' Classic
Currently Looking...
Hinckley , Ohio
Join Date: Sep 2009
Posts: 571
Images: 4
What i'm gathering is it works fine, but is 10 degrees off.
So it may pay to look at the back of the knob. You may find a screw. That would be to adjust or calabrate the temp reading to the accual temp. This is the direction I would head first. Keep it simple. Road vibrations move things. It would help here if we had a photo.
__________________

__________________
If you could have a superpower, what would it be?

I chose America
Bigventure is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:45 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.