20 amp Air conditioner

Why can't or don't they make an RV air conditioner that works off of a 20 amp outlet? I have one in my house.
__________________

__________________
mandolindave is offline   Reply With Quote
Old 11-18-2004, 05:25 PM   #2
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 9,002
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
Quote:
Originally Posted by mandolindave
Why can't or don't they make an RV air conditioner that works off of a 20 amp outlet? I have one in my house.
It's not that there aren't any, its just a matter of all the other stuff you run inside that trailer. A 13.5K Duo-Therm can run on less than 20 amps. The problem is that the entire trailer runs off one line to one plug and to one outlet.

In your house you probably have the A/C on a dedicated circuit. Your TV, Microwave, lights and other items run off many different circuits to the breaker box which probably has 200 amp service or so, and the wiring to support it.

Jack
__________________

__________________
Jack Canavera
STL Mo.
AIR #56
'04 Classic 30' S.O.,'03 GMC Savana 2500,'14 Honda CTX 700
jcanavera is offline   Reply With Quote
Old 11-18-2004, 06:28 PM   #3
Rivet Master
 
Join Date: Mar 2002
Posts: 1,482
Images: 19
The other problem is getting an actual 20 amp feed to the coach. Standard household plugs and receptacles are 15 amp. There are true 20 amp plugs and receptacles but they are seldom seen.

Mark
__________________
j54mark is offline   Reply With Quote
Old 11-18-2004, 08:50 PM   #4
Rivet Master
 
mandolindave's Avatar
 
Join Date: Jan 2004
Posts: 2,116
Images: 4
Those are good points.......

I thought one of the weak links was the nature of the AC unit itself.
The compressor uses a lot of energy when it is cycling on, and not
enough juice destroys the compressor motor prematurely. I learned
from this forum that some people set their AC units to full blast
so it wouldn't cycle off and on. So why..... don't they use smaller units
that use less power and are designed not to cycle off and on?????????
It might take longer to cool down a trailer but you could use the AC
in a lot more places.
__________________
mandolindave is offline   Reply With Quote
Old 11-18-2004, 09:35 PM   #5
Rivet Master
 
RoadKingMoe's Avatar
 
2001 34' Limited
The State of , Ohio
Join Date: Sep 2002
Posts: 1,605
Images: 23
We have a 20 amp outlet in our garage. That's one that the left slot is a sideways T not just a vertical I (as with a 15A outlet), and comes from a 20A breaker in the main panel. We've run the 13,500 btu air-conditoner in our trailer off it many times, using a 30 female to 15A male (two vertical prongs) adapter on the end of the plug. Yeah, we should technically have a 20A male (right prong vertical, left prong horizontal), but the 15A works fine and doesn't get hot.

When we do, however, we switch the refrigerator over to gas and the batteries are charged, so the converter is drawing very little 120VAC, just powering the lights and radio. Obviously, using the electric water heater element is out of the question, and we switch the air conditioner to fan-only when using the microwave.

Works just fine. The breaker in the Airstream main panel that feeds the AC is only 20A.
__________________
Maurice
RoadKingMoe is offline   Reply With Quote
Old 11-19-2004, 08:02 AM   #6
Rivet Master
 
mandolindave's Avatar
 
Join Date: Jan 2004
Posts: 2,116
Images: 4
Hey Moe,
I am using a 20 amp circuit. It works fine for me too. But because
I read here on the forum about eventually ruining the AC unit, I plan to
beef up the wiring and extension cable.
But ....the point of this thread is to complain about not having
an AC unit that will work on a 15 or 20 amp service.
__________________
mandolindave is offline   Reply With Quote
Old 11-19-2004, 08:40 AM   #7
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,334
It'll work, but it isn't suggested that it be done. This also depends on how far you are from the main panel, how long of an ext cord you're using, what gauge house wiring is going to the outlet the Stream is connected to, etc.

I tested our 15k unit off the 15a plug, though the breaker is a 20a breaker. The unit appeared to work just fine, however, the 15a outlet did get a warm, not hot, just warm. The 20a breaker wasn't even warm. It was the same cold temp as the other breakers. When we had an 11k unit last year, the same results happened, only the 15a plug was less warm.

I don't run the A/C really when it's in the drive, but if I ever do, I'll be upgrading the outlets and breaker since in my book there is plenty of time to do it right the first time than plenty of time to fix what I broke by cutting corners. I recently upgraded the wiring from the house to the garage so that I just need a few things to get to the correct 30a circuit and connectors and not have to deal with a warm 15a plug.
__________________
Computers manufactured by companies such as IBM, Compaq and millions of others are by far the most popular with about 70 million machines in use worldwide. Macintosh fans note that cockroaches are far more numerous than humans and that numbers alone do not denote a higher life form. -NY Times 11/91
Silvertwinkie is offline   Reply With Quote
Old 11-19-2004, 08:47 AM   #8
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 9,002
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
Quote:
Originally Posted by mandolindave
I thought one of the weak links was the nature of the AC unit itself.
The compressor uses a lot of energy when it is cycling on, and not
enough juice destroys the compressor motor prematurely. I learned
from this forum that some people set their AC units to full blast
so it wouldn't cycle off and on. So why..... don't they use smaller units
that use less power and are designed not to cycle off and on?????????
It might take longer to cool down a trailer but you could use the AC
in a lot more places.
Most A/C units have a heavy startup draw. That startup could be in excess of the rating of the circuit. Most can handle that short spike. Where you ruin an AC unit is when you run it in a continual low voltage situation. So those who set their units to full blast aren't helping themselves if their circuit cannot handle the load.

Using a smaller AC unit is just not a longer cool down situation. An AC unit has to carry the load that a hot summer day puts upon it. One of the reasons I upgraded my AC on my Classic to the 15K Penguin was a terrible experience with my 13.5K Penguin on my 27' Safari. It was 100 degrees and we were in full sun. The unit couldn't keep the trailer below 85 degrees. My dealer and Jackson Center folks checked it out and said it was working within specs. So consider the fact that an 11K unit would draw less power but in the conditions I was in, would be functionally useless.

Jack
__________________

__________________
Jack Canavera
STL Mo.
AIR #56
'04 Classic 30' S.O.,'03 GMC Savana 2500,'14 Honda CTX 700
jcanavera is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to install a new air conditioner? Steve Wong Furnaces, Heaters, Fireplaces & Air Conditioning 30 05-02-2017 04:12 PM
Armstrong Air Conditioner Kurt & Eve Furnaces, Heaters, Fireplaces & Air Conditioning 23 09-21-2004 08:00 AM
Rear Air Conditioner Wiring cooperhawk General Motorhome Topics 3 07-11-2004 10:00 AM
Air conditioner thermostat working? nickcrowhurst Furnaces, Heaters, Fireplaces & Air Conditioning 7 03-18-2004 08:37 PM
Air Conditioner Question/Problem??? pscottn Furnaces, Heaters, Fireplaces & Air Conditioning 6 08-23-2003 11:21 AM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:36 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.