Question 1972 31' w/Propane Furnace "no heat all fan"

I have a 72 31' with the original Suburban Propane Furnace. The thermostat works, but no flame and no gas. The propane top burners work and I noticed there is what looks like some sort of tank in the middle of the furnace, I opened it up...tried to manually light pilot with the push pilot mech. no good. No gas present it seems. Any advice?
FarHarley is offline   Reply With Quote
Old 11-24-2004, 11:28 PM   #2
Rivet Master
 
Janets Husband's Avatar
 
1977 Argosy Minuet 6.0 Metre
1964 26' Overlander
1977 25' Tradewind
Eastern , Washington
Join Date: Jan 2004
Posts: 865
Images: 6
Quote:
Originally Posted by FarHarley
I have a 72 31' with the original Suburban Propane Furnace. The thermostat works, but no flame and no gas. The propane top burners work and I noticed there is what looks like some sort of tank in the middle of the furnace, I opened it up...tried to manually light pilot with the push pilot mech. no good. No gas present it seems. Any advice?
Welcome to the forum from the far reaches of the Tri-Cities.
I would check a few things to start with.
1.) Take a look under the trailer and see if there is a shutoff valve on the furnace line. Make sure it is open.
2.) Try heating the thermal couple before you try and light the furnace.
3.) Make sure you have the thermostat in the on position before lighting.
__________________
Peace
Gary
Janets Husband is offline   Reply With Quote
Old 11-24-2004, 11:33 PM   #3
New Member
 
Join Date: Oct 2004
Posts: 3
Thanks Gary,
Happy Thanksgiving!
I will do that, Turkey Day morning. I'm new to all this, so where is the thermocoupler located?
Thanks again....
Quote:
Originally Posted by Janet's Husband
Welcome to the forum from the far reaches of the Tri-Cities.
I would check a few things to start with.
1.) Take a look under the trailer and see if there is a shutoff valve on the furnace line. Make sure it is open.
2.) Try heating the thermal couple before you try and light the furnace.
3.) Make sure you have the thermostat in the on position before lighting.
FarHarley is offline   Reply With Quote
Old 11-25-2004, 07:44 AM   #4
Rivet Master
 
eubank's Avatar

 
Airstream - Other
2016 Interstate Grand Tour Ext
Bosque Farms , New Mexico
Join Date: Jan 2004
Posts: 7,030
These heaters have what's called a "sail switch," which basically gates the flow of propane to the burner. What you don't want is a situation in which propane is burning, but the fan quits. The switch is set right in front of the fan and has a little sail-like arm that effectively blows over if the fan works. If the switch is blown over, the propane is ON. If the switch is not blown over, then it assumes no fan, and the propane won't flow.

Now, sail switches are a darned good idea, but the sail-like arm must necessarily move easily (because mere movement of air must be able to move it). Alas, this is also a fairly dusty environment, so sometimes the sail switch gets bits of dust in it and won't blow over.

Last time ours went dead, I ordered a new switch (not that expensive). However, in the meantime I took out the old one and gave it a good blow-off with compressed air. Put it back in, and all has been well ever since. Now we have the old switch still installed (three years), and the new one still in its sealed package.

Anyway, it kind of sounds to me like you've got the symptoms of sail-switchitis: Fan works, no flame. As others have pointed out, check to make sure that the propane is on and making it to the heater. If it is, then maybe it's time to clean the switch with the air compressor.


Lynn
__________________
ACI Big Red Number 21043
eubank is offline   Reply With Quote
Old 11-25-2004, 08:34 AM   #5
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
lynn and gary hit on some good points.

in addition, make sure your battery is fully charged or the trailer is plugged in with the univolt running. a low battery voltage will not spin the fan fast enough to trip the sail switch.

if you 73 is like my buddys 74, the gas valve for the furnace is inside, next to it on the right, getting a pilot lit can take a while. lighting the stove certainly helps purge the lines faster.

good luck and welcome to the forum!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
72 Airstream International Furnace parts loechli Furnaces, Heaters, Fireplaces & Air Conditioning 7 08-20-2008 07:17 PM
Furnace stuff... Chuck Furnaces, Heaters, Fireplaces & Air Conditioning 11 12-02-2002 05:36 PM
Jingle Bell Furnace Fix Pahaska Furnaces, Heaters, Fireplaces & Air Conditioning 5 11-19-2002 09:59 PM
Heat protection ALANSD Airstream Motorhome Forums 14 11-03-2002 02:55 PM
Heat Riser ALANSD Airstream Motorhome Forums 7 09-11-2002 03:38 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:39 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.