The major function of AC is to remove humidity. The human body can tolerate and feel more comfortable in higher temperatures if the humidity is low.

Many people will try to cool a home or trailer after leaving the unit off for a period of time to save money. Economically, you are better off leaving the AC on all the time, on a thermostat. This will draw the humidity in the space out of the wood, furniture and other belongings and allow you to be comfortable at a higher temperature setting.

When I rebuilt my toybox I sprayed 2"-3" of structural foam into all the wall and ceiling cavaties and now it's like a Thermos.

BTW, your circuit breaker could be defective. They are simply a electro-mechanical device that can become sensetive after being tripped a couple of times. CB replacement resolves most AC issues. If the new CB trips, look further. Never install a CB that is higher in ampacity than the wre size will allow. 15-amps for 14-gauge, 20-amps for 12-gauge and 30-amps for 10-gauge. The allowable wattages are 1320, 2000 and 3000 respectively.
__________________

__________________
Barry2952 is offline   Reply With Quote
Old 07-04-2006, 11:09 AM   #16
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,282
Quote:
Originally Posted by Barry2952
The major function of AC is to remove humidity. The human body can tolerate and feel more comfortable in higher temperatures if the humidity is low.

Many people will try to cool a home or trailer after leaving the unit off for a period of time to save money. Economically, you are better off leaving the AC on all the time, on a thermostat. This will draw the humidity in the space out of the wood, furniture and other belongings and allow you to be comfortable at a higher temperature setting.

When I rebuilt my toybox I sprayed 2"-3" of structural foam into all the wall and ceiling cavaties and now it's like a Thermos.

BTW, your circuit breaker could be defective. They are simply a electro-mechanical device that can become sensetive after being tripped a couple of times. CB replacement resolves most AC issues. If the new CB trips, look further. Never install a CB that is higher in ampacity than the wre size will allow. 15-amps for 14-gauge, 20-amps for 12-gauge and 30-amps for 10-gauge. The allowable wattages are 1320, 2000 and 3000 respectively.
Not to be a 'nit-pick' here, but wattage is figured as P=IE, so you multiply volts (120) X amps to get the allowable wattage for a circuit. 15 amp lines allow 1800 watts, 20 amp lines allow 2400 watts and 30 amp lines allow 3600 watts.
__________________

__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 07-04-2006, 11:34 AM   #17
Rivet Master
 
2006 30' Classic
Farmington , New Mexico
Join Date: Feb 2005
Posts: 822
Images: 14
Quote:
Originally Posted by Jim Clark
I believe freezing up is a sign of a unit which is short on gas or dirty. You want a good sweat back on the suction line, which is the bigger one also called the low pressure line. I know my unit is working great when I seen the condensation coming down the drain tube and pooling on the ground. Same for my home unit.

Jim
Freezing ocurs when the moist air passes through an evaporator that has below freezing temps. The moisture freezes to the evap. and blocks air flow. This condition is common when the thermostate is set to low and operating in very humid conditions.The easiest way to prevent freezing is to raise the thermostate setting.---pieman
__________________
Mike Lewis is offline   Reply With Quote
Old 07-04-2006, 01:35 PM   #18
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 9,002
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
Quote:
Originally Posted by Mike Lewis
Freezing ocurs when the moist air passes through an evaporator that has below freezing temps. The moisture freezes to the evap. and blocks air flow. This condition is common when the thermostate is set to low and operating in very humid conditions.The easiest way to prevent freezing is to raise the thermostate setting.---pieman

....and make sure that fan speed is up. Dirty air filters or too slow an air speed will tend to allow ice to form.

Jack
__________________
Jack Canavera
STL Mo.
AIR #56
'04 Classic 30' S.O.,'03 GMC Savana 2500,'14 Honda CTX 700
jcanavera is offline   Reply With Quote
Old 07-04-2006, 03:00 PM   #19
3 Rivet Member
 
Join Date: Jan 2004
Posts: 126
Quote:
Originally Posted by lewster
Not to be a 'nit-pick' here, but wattage is figured as P=IE, so you multiply volts (120) X amps to get the allowable wattage for a circuit. 15 amp lines allow 1800 watts, 20 amp lines allow 2400 watts and 30 amp lines allow 3600 watts.
That would be true, if you were not an electrician, which I am. The rule of thumb is that you should never load a circuit in excess of 80% of its capacity. I like to use 75%, but then I'm a cautious person.

In addition, should voltage be 110 volts there is a proportional decrease in the capacity of the circuit. Your formula does not allow for voltage fluctuations, which I'm sure we've all experienced.
__________________
Barry2952 is offline   Reply With Quote
Old 07-04-2006, 03:43 PM   #20
2 Rivet Member
 
firefly007's Avatar
 
1964 17' Bambi II
longwood , Florida
Join Date: Jun 2006
Posts: 76
Quote:
Originally Posted by Barry2952
That would be true, if you were not an electrician, which I am. The rule of thumb is that you should never load a circuit in excess of 80% of its capacity. I like to use 75%, but then I'm a cautious person.

In addition, should voltage be 110 volts there is a proportional decrease in the capacity of the circuit. Your formula does not allow for voltage fluctuations, which I'm sure we've all experienced.
Hey Guys, I'll have to crack the books to be sure but I think when dealing with inductance devices like ac motors the formula is P=IE times the cosine of Theta which would be the phase angle of the windings.

Whew, I usually just tear about 10 percent off the top of the P=IE formula or measure the actual current in amps. There are several small inline Amp/Watt gauges that look like a short extension cord. I like to keep one in the trailer to keep an eye on Watt (sorry) is going on. If anyone needs one I will post the source.

Steve
__________________
firefly007 is offline   Reply With Quote
Old 07-04-2006, 04:08 PM   #21
3 Rivet Member
 
Join Date: Jan 2004
Posts: 126
Yes, if you tear off 10% from the formula using 110-volts our answers come very close together. Do you concur?
__________________
Barry2952 is offline   Reply With Quote
Old 07-04-2006, 05:42 PM   #22
2 Rivet Member
 
firefly007's Avatar
 
1964 17' Bambi II
longwood , Florida
Join Date: Jun 2006
Posts: 76
Yup, I agree. Sorry for tryin to show off. Just tring to stretch my brain a little. The best answer was your idea on low voltage. Usually when someone ask me about this situation I will find about 105 volts. It makes ac motors mad and draws more current.

steve
__________________
firefly007 is offline   Reply With Quote
Old 07-04-2006, 05:56 PM   #23
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
Quote:
Originally Posted by Barry2952
That would be true, if you were not an electrician, which I am. The rule of thumb is that you should never load a circuit in excess of 80% of its capacity. I like to use 75%, but then I'm a cautious person.

In addition, should voltage be 110 volts there is a proportional decrease in the capacity of the circuit. Your formula does not allow for voltage fluctuations, which I'm sure we've all experienced.
hey barry, don't you suppose the capacitors in the airconditioner would bring the power factor to unity?

or are they just for starting the unit?

it would be interesting to put a var meter on a running unit and see what ya get!

i certainly do not disagree about the 80% rule. at the power company we have tried to run lines in emergencies at 110% with bad results!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 07-04-2006, 06:23 PM   #24
3 Rivet Member
 
Join Date: Jan 2004
Posts: 126
Quote:
Originally Posted by firefly007
Yup, I agree. Sorry for tryin to show off.

steve
No problem, I was just trying to help. I reread my post and I guess I sounded a little snotty.

I'm just concerned when people believe they can put full wattage on a residential electrical circuit. Yes, the wire can take the full wattage but the devices can't, especially with the inherent vibration of a motor home or trailer. Couple that with typical overloading from use of all the appliances available today and it gets pretty scary.
__________________
Barry2952 is offline   Reply With Quote
Old 07-04-2006, 06:50 PM   #25
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,282
What power utility do you guys use? I haven't seen 110 VAC for years. The last time I plugged in my Fluke RMS multimeter, it read between 119-121 VAC .
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 07-04-2006, 07:00 PM   #26
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
when i hook up a new residential customer i like to see 125volts at the transformer.

when you calculate line loss in the service you should be 120/123v at the meter.

tip of the day: buy 130v light bulbs! they last longer!

john

ps, lew fluke meters are iffy at best, my shop meter is a good old simpson!
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 07-04-2006, 08:07 PM   #27
2 Rivet Member
 
firefly007's Avatar
 
1964 17' Bambi II
longwood , Florida
Join Date: Jun 2006
Posts: 76
Quote:
Originally Posted by lewster
What power utility do you guys use? I haven't seen 110 VAC for years. The last time I plugged in my Fluke RMS multimeter, it read between 119-121 VAC .
Most of my experiance is at marinas. Poor grounding and moisture damage along with overloading is probably worse there
__________________
firefly007 is offline   Reply With Quote
Old 07-09-2006, 10:55 PM   #28
Rivet Master
 
silverback's Avatar
 
2006 28' Safari SE
Currently Looking...
Sierra Vista , United States
Join Date: Jun 2003
Posts: 702
Back home again and catching up on posts. We lost WiFi access so I wasn't able to report on the campground voltage. It stayed a steady 110 VAC everytime I measured it. Are you guys saying that is marginal? I was beginning to think we may have a bad breaker. If I tried Auto fan while the outside temps were high (even after the humidity dropped) it would consistently trip after a while (hour?). It worked fine in the evening. So it was High fan and high noise levels during the day. Once we moved up to 7k feet and the SW monsoon kicked in the AC was no longer an issue (lighting strikes and flooding took over). And I am happy to say the Safari SE remained leak proof.
Thanks,
Ken
__________________

__________________
4CU Charter Member
silverback is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
frig and a/c suggestions Neenm General Appliance Topics 6 04-08-2007 08:42 PM
A/C replacement? VWMARTINEZ Furnaces, Heaters, Fireplaces & Air Conditioning 6 03-09-2007 03:14 AM
Converter Breaker? Sav'h Steve Electrical - Systems, Generators, Batteries & Solar 7 11-18-2002 09:45 AM
1971 Armstrog A/C uwe Furnaces, Heaters, Fireplaces & Air Conditioning 2 08-06-2002 06:08 PM
Mediocre A/C Chuck Furnaces, Heaters, Fireplaces & Air Conditioning 4 07-07-2002 08:52 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:32 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.