Old 09-25-2016, 12:13 PM   #1
1 Rivet Member
 
Washington , Washington, D.C.
Join Date: Mar 2014
Posts: 18
Converting 50amp power source to 30 amp trailer

Hi,

We have a 2015 23' FC, which has a 30 amp receiver. We are traveling next weekend to a campground where we will have to use a 50 amp hookup. To convert the power source for our trailer, we purchased a Camco 55175 18" PowerGrip Dogbone Electrical Adapter with Handle.

I've read the forums on this topic, and I believe this should be fine. When we arrive at the campsite, I'll double check with the office that the 50 amp hookup is only 110volts -- as I understand we might fry our electrical equipment if the hookup is 220v. But, this might not be the case if we have a breaker -- which i believe is standard for late model airstreams?

However, because it's our first time hooking into 50 amp, can someone please confirm if we are doing this right, or if there's anything else we should be doing?

Thanks so much in advance!!

Mimi and Dan
danandmimi is offline   Reply With Quote
Old 09-25-2016, 12:26 PM   #2
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,668
You will be fine as long as what they have is a 50 amp RV connection. Often campgrounds say they have 50 amp but most also have 30 amp so you may not need the adapter. I carry one just because I have read, and then it happened, that the 30 amp receptacle in the pedestal was corroded or loose and wouldn't work. I plugged into the 50 amp side with my adapter and everything was fine.

The talk about 220 volt was, I think, related to getting an electrician to wire up a 30 amp receptacle at home. Apparently some have had that done and the electrician wired it up like a dryer. The 50 amp RV service is in fact 240 volts line to line and 120 volts line to neutral. It should have a four-pin connector like your adapter. Everything in your trailer is wired line to neutral, so it will only see 120 volts.

I carry a 50-30 adapter, a 30-15 adapter, and an outlet checker. I will plug the outlet checker into the 30-15 adapter and plug that into the pedestal 30 amp receptacle or plug the pair into the 50-30 adapter and plug that into the 50 amp receptacle prior to hooking up. That way I know that it is all wired up correctly. I also have a plug-in voltmeter in an outlet in the trailer and I look at that before turning on the air conditioner or any sensitive equipment like televisions.

Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 09-25-2016, 12:28 PM   #3
Rivet Master
 
2015 30' Classic
Pleasanton , California
Join Date: Jan 2015
Posts: 745
You have the correct plug and you will not have any issues regarding incorrect voltages. The 50A pedestal provides two independent 120 V, 50A circuits so you can easily power your trailer without concern.
__________________
Al, K6IV
2015 30' Classic, "Chez Nu"
2014 RAM 2500 w/Cummins Diesel
ProPride Hitch, 400 W Solar
alano is offline   Reply With Quote
Old 09-25-2016, 12:37 PM   #4
3 Rivet Member
 
Al Boondy's Avatar
 
1973 31' Excella 500
Vicksburg , Mississippi
Join Date: Jul 2016
Posts: 164
Images: 1
A 50 amp hookup IS 240v, a 30 amp is 120v.
The 50 amp is 2 120v legs that are 180 degrees out of phase. Most campers that have 50amp hookup use each leg independently. They don't "combine" them for 240 volts unless they have standard clothes dryer.
Your adapter simply takes one of the 120v legs out of the picture and converts the other to a 30 amp camper plug.
You've got what you need, happy camping!
Al Boondy is offline   Reply With Quote
Old 09-25-2016, 08:39 PM   #5
Vintage Kin
 
Fort Worth , Texas
Join Date: Nov 2006
Posts: 8,014
Images: 1
I've run my 30A service trailer exclusively with the dogbone for the last four years.
slowmover is offline   Reply With Quote
Old 09-26-2016, 12:59 PM   #6
1 Rivet Member
 
2016 Interstate Grand Tour Ext
Park City , Utah
Join Date: Jun 2016
Posts: 8
I too have used the adapter -- 50 to 30 --- with NO problem...
Ramjet48 is offline   Reply With Quote
Old 09-26-2016, 01:06 PM   #7
4 Rivet Member
 
2017 27' Flying Cloud
London , Ontario
Join Date: Jul 2016
Posts: 250
I highly recommend this book on RV electrical safety - a great $10 investment.

https://www.amazon.com/No~Shock~Zone.../dp/B00L2DWBD8
Philip Jones is offline   Reply With Quote
Old 09-26-2016, 01:09 PM   #8
Vintage Kin
 
Fort Worth , Texas
Join Date: Nov 2006
Posts: 8,014
Images: 1
Forgot to add above that on dual service pedestals the 50A is often in better shape than the 30A. Less wear and tear on outlet.
slowmover is offline   Reply With Quote
Old 09-26-2016, 05:09 PM   #9
Rivet Master
 
2015 25' Flying Cloud
2016 30' Flying Cloud
Blenheim Ontario , Ontario
Join Date: May 2015
Posts: 1,263
The question is:

Preamble;
Many so called 30 Amp plugs seem to deliver much less than that.
I was just at a 'campground' this last weekend with '30 Amp' service, but even just turning on the hot water heater, and coffee pot (fridge running on AC) brought the voltage way down.
Using the Airconditioner only with fridge on, brought it down to 108 Volts. but with fridge only, the meter showed 120-122 VAC. (Shurlite plug in.) The 'grunt' just wasn't there.
This happens a number of times, yet other sites show great voltage, when loaded.

Would using a 50-30 dogbone make more amperage available?
MelGoddard is offline   Reply With Quote
Old 09-26-2016, 05:19 PM   #10
Rivet Master
 
2014 27' Flying Cloud
Wenatchee , Washington
Join Date: May 2014
Posts: 512
I've been wondering the same thing.


Sent from my iPhone using Airstream Forums
__________________
2018 Ram 3500 SLT CTD 4X4 pickup
2014 Airstream Flying Cloud 27FB
WBCCI #7180
21Airstream is offline   Reply With Quote
Old 09-26-2016, 06:20 PM   #11
4 Rivet Member
 
2003 31' Classic
Terra Alta , West Virginia
Join Date: Jan 2015
Posts: 274
I was told that it would help give your full 30 amps by using the 50 to 30 pigtail. I got mine on that advice and use it frequently with no issues. Seems logical especially on those days when useage is high in the campground such as a hot day. The guy who suggested it is really sharp so ...
Dave
wvstreamer is offline   Reply With Quote
Old 09-26-2016, 06:48 PM   #12
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,668
Quote:
Originally Posted by MelGoddard View Post
The question is:

Preamble;
Many so called 30 Amp plugs seem to deliver much less than that.
I was just at a 'campground' this last weekend with '30 Amp' service, but even just turning on the hot water heater, and coffee pot (fridge running on AC) brought the voltage way down.
Using the Airconditioner only with fridge on, brought it down to 108 Volts. but with fridge only, the meter showed 120-122 VAC. (Shurlite plug in.) The 'grunt' just wasn't there.
This happens a number of times, yet other sites show great voltage, when loaded.

Would using a 50-30 dogbone make more amperage available?
It won't make more amperage available, but it might well reduce the voltage drop in the lines and equipment.

Air conditioner - 15.1 amps (13,500 BTU)
Water heater - 12.7 amps
Microwave - 12.5 amps
Refrigerator - 2.7 amps
Converter - hard to say, could be up to 7 amps depending on charging and 12V load
Depending on what is on, it could be pushing the limits of, or even tripping a 30A circuit.

The wire for a 50A circuit would likely be a larger gauge than for a 30A circuit of the same length. The wire gauge as required by code is based on voltage drop, so the 50A circuit and the 30A circuit will have similar voltage drops at full load. But running a 30A load on a 50A circuit would have around 30/50 or 60% of the voltage drop compared to running a 30A load on a 30A circuit, assuming the 30A circuit was wired with the smaller gauge wire. So if you dropped 10 volts on a 30A circuit you might expect only 6 volts drop on a 50A circuit assuming everything else was up to snuff.



Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 09-26-2016, 08:06 PM   #13
Rivet Master
 
2015 25' Flying Cloud
2016 30' Flying Cloud
Blenheim Ontario , Ontario
Join Date: May 2015
Posts: 1,263
Quote:
Originally Posted by Al and Missy View Post
It won't make more amperage available, but it might well reduce the voltage drop in the lines and equipment.

Air conditioner - 15.1 amps (13,500 BTU)
Water heater - 12.7 amps
Microwave - 12.5 amps
Refrigerator - 2.7 amps
Converter - hard to say, could be up to 7 amps depending on charging and 12V load
Depending on what is on, it could be pushing the limits of, or even tripping a 30A circuit.

The wire for a 50A circuit would likely be a larger gauge than for a 30A circuit of the same length. The wire gauge as required by code is based on voltage drop, so the 50A circuit and the 30A circuit will have similar voltage drops at full load. But running a 30A load on a 50A circuit would have around 30/50 or 60% of the voltage drop compared to running a 30A load on a 30A circuit, assuming the 30A circuit was wired with the smaller gauge wire. So if you dropped 10 volts on a 30A circuit you might expect only 6 volts drop on a 50A circuit assuming everything else was up to snuff.



Al
"It might well reduce the voltage drop......."

So, using Mike Socol's analogy of water flow, if the voltage, (electrical pressure) is reduced, then the current flow, (electron volume) must greatly reduced. Conversely, more current avail, less voltage drop.
Meaning that perhaps my services would run better using a 50 amp service, (10 ga. wire still feeding my AS's 12 ga. wire, instead of the campground 12 ga. feeding my 12 ga.)
I can live with that.
Maintaining voltage is dependent upon delivering the 'grunt' to power the services.
It seems that others, above, get the same benefit.
MelGoddard is offline   Reply With Quote
Old 09-26-2016, 11:47 PM   #14
Vintage Kin
 
Fort Worth , Texas
Join Date: Nov 2006
Posts: 8,014
Images: 1
AC use in summer is what overloads park electric. Besides the dogbone, switch the reefer and water heater over to propane. The former will cool better as a result. The latter will perform as it should.
slowmover is offline   Reply With Quote
Old 09-28-2016, 06:05 AM   #15
Olroy
 
1976 29' Ambassador
1986 34.5' Airstream 345
Barbourville , Kentucky
Join Date: Aug 2007
Posts: 14
Good info here. Some real elect. In this out fit. Be kind of foolish if you have an old 30A not to run yo a 50 A cable. Split the 2 hot wires and add a little panel run you a super power strip on extra phase to kitchen for appliances,or portable a/c if needed..no more problems with overloaded recut. In kitchen.. Easy DIY just use stranded #10 for power strip..worked for me. Carry a 30 amp adapter. ( I'm electrician)
Olroy is offline   Reply With Quote
Old 09-29-2016, 06:20 AM   #16
Rivet Master
 
2015 25' Flying Cloud
2016 30' Flying Cloud
Blenheim Ontario , Ontario
Join Date: May 2015
Posts: 1,263
Quote:
Originally Posted by Olroy View Post
Good info here. Some real elect. In this out fit. Be kind of foolish if you have an old 30A not to run yo a 50 A cable. Split the 2 hot wires and add a little panel run you a super power strip on extra phase to kitchen for appliances,or portable a/c if needed..no more problems with overloaded recut. In kitchen.. Easy DIY just use stranded #10 for power strip..worked for me. Carry a 30 amp adapter. ( I'm electrician)
Whatever are you 'talking' about?
MelGoddard is offline   Reply With Quote
Old 09-29-2016, 07:19 AM   #17
3 Rivet Member
 
Al Boondy's Avatar
 
1973 31' Excella 500
Vicksburg , Mississippi
Join Date: Jul 2016
Posts: 164
Images: 1
Quote:
Originally Posted by MelGoddard View Post
Whatever are you 'talking' about?
I think that he is pointing out the foolishness of struggling with power management on a 30 amp outlet when there is usually 100 amps(2 50amp 120v legs) available just inches away.
Even on 50 amp trailers they usually only use second leg for 2nd AC.
There are much better ways to do it.
Al Boondy is offline   Reply With Quote
Old 09-29-2016, 07:17 PM   #18
Rivet Master
 
2015 25' Flying Cloud
2016 30' Flying Cloud
Blenheim Ontario , Ontario
Join Date: May 2015
Posts: 1,263
Quote:
Originally Posted by Al Boondy View Post
I think that he is pointing out the foolishness of struggling with power management on a 30 amp outlet when there is usually 100 amps(2 50amp 120v legs) available just inches away.
Even on 50 amp trailers they usually only use second leg for 2nd AC.
There are much better ways to do it.
Perhaps you're right.
You pointed out earlier that the legs were 180 out of phase; so I gather that Olroy is suggesting running a separate circuit for the one leg, to handle the 'heavy grunt' and using the other leg for 'normal' services.

I only have one A/C so that would be a lot of work to get the results I need.
Suppose that if I use a 50-30 adapter, that would give me a full 30 amps for the services that I use????
My meter showing an abnormal voltage drop, indicates to me that the 'delivery' is not sufficient at some campsites. (like this last one in Wheatley, Ontario.)
Other campsites give me the 'full Monty'.
MelGoddard is offline   Reply With Quote
Old 09-29-2016, 08:13 PM   #19
3 Rivet Member
 
Al Boondy's Avatar
 
1973 31' Excella 500
Vicksburg , Mississippi
Join Date: Jul 2016
Posts: 164
Images: 1
Quote:
Originally Posted by MelGoddard View Post
Perhaps you're right.
You pointed out earlier that the legs were 180 out of phase; so I gather that Olroy is suggesting running a separate circuit for the one leg, to handle the 'heavy grunt' and using the other leg for 'normal' services.

I only have one A/C so that would be a lot of work to get the results I need.
Suppose that if I use a 50-30 adapter, that would give me a full 30 amps for the services that I use????
My meter showing an abnormal voltage drop, indicates to me that the 'delivery' is not sufficient at some campsites. (like this last one in Wheatley, Ontario.)
Other campsites give me the 'full Monty'.
I've seen campgrounds with a 10v difference between the 2 legs because all the 30 amp outlets were on the same leg and all the campers were using 30 amp service. I switched mine.
This could have been the problem.

Retrofitting an Airstream wouldn't be easy but if you have the inside skins off it's a no brainer. Wire it with residential load center for 240v 50amp service and balance the loads. If you only have 30 amp service at campground a 30 to 50 amp adapter with jumper will allow everything to work as normal 30 amp. This also allows conventional clothes dryers, induction stove top and wall mount 240v electric heaters to be installed. No worries about water heater, refrigerator microwave blow dryer and ACs on at the same time.
High end coaches are wired this way don't know why more travel trailers aren't.
Al Boondy is offline   Reply With Quote
Old 09-29-2016, 10:30 PM   #20
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,215
Images: 9
Older parks with just a 30 amp RV and 20 amp standard duplex at each site are typically sharing 50 amp 240Vac service with the other side. Thus the 30 amp on side one and the 20 amp on side two are on one leg and the 20 amp on side one is paired to the 30 amp on side two. The entire park is underpowered for the loads presented by today's trailers even with 30 amp service as the incoming power of the time did not contemplate air conditioning.

Having a surge and low voltage device like this 30A Portable Model 34830 with LCD Display - http://www.trci.net/products/surge-g...-w-lcd-display) will help protect all of your trailer 120Vac equipment.

If the issue of maintaining proper voltage is a big concern, one can carry a voltage regulator as well (http://www.trci.net/products/surge-g...tage-regulator) as the surge protection to cover all the bases. The 50 amp version is quite heavy.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What power supply to replace with on 50amp 2016 classic Clozzzer Electrical - Systems, Generators, Batteries & Solar 45 08-29-2016 11:56 PM
Changing 30 amp to 50amp Fortiz Electrical - Systems, Generators, Batteries & Solar 3 06-21-2013 07:30 AM
50amp for 30amp trailer? racoco Electrical - Systems, Generators, Batteries & Solar 15 08-24-2007 07:43 PM
Converting from 30 amp to 50 amp shore power blkmagikca General Motorhome Topics 8 03-28-2006 01:20 PM
Power Inlet 50amp markdoane Electrical - Systems, Generators, Batteries & Solar 4 10-14-2005 08:25 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.