I think I understand - but?

Quote:
Originally Posted by wmarsha View Post
Okay, look at the electrical system in its totality for a moment. each circuit in the AS is protected by a circuit breaker-if any individual load begins to draw more than the circuit breaker's rating-it will trip. Now, looking at the coach as a whole-it should never exceed 30 amps, right? well, no. If each of the individual circuits in your AS are drawing say 10 amps each, then if you have four circuits, you actually are drawing 40 amps. Now, knowing that is possible, if your umbilical is plugged into a 30 amp breaker, either in your surge protector, or in the circuit from home or rv camp or wherever then that breaker should operate. Now, you didn't say any circuit breaker operated-meaning the current flow through this umbilical never exceeded 30 amps. So what gives? Okay there is a mechanical connection that has begun to fail. that connection is/are the spades of the plug/receptacle. Those spades have introduced a resistance into the circuit and the result (energy usage) of that resistance is heat.

Okay, what is causing the resistance? Well, the physical connecting action of the plug/receptacle is supposed to "clean" the spades when inserted. However, the female receptacle's spring action of its contacts can become weakened over time, not cleaning the male spade's surface area, causing resistance. If the female end is "loose" (no offense intended), then it, too introduces resistance. Once the joint begins to heat, it becomes a heat sink, causing more and more heat until something oxidizes (burns) causing more resistance, and hence more heat.

Cure? keep contacts (male spades) clean, lubricate the receptacle with dielectric compound, insert the male plug straight into the female receptacle with as little side-to-side motion as is possible. Once a male end is heated like the one you have-time to cut it off and wire up a new one. When purchasing a new plug or receptacle, look at the construction of the piece-check out the "robustness" of the copper contacts-compare less expensive ones to more expensive ones-size does matter, here. a larger surface area (within the specifications of the plug/receptacle design) is better. Twist locks are probably better because of the physical twisting action of the contact connection. Plugs with the handle at the back may be better because they allow for straight pull apart action (no side-to-side). Once again, lubricate with dielectric compound.
Great explanation! But what about the Surge Guard? Shouldn't it have cut the power before melting? Or was it possibly malfunctioning.

Carol
__________________

__________________
tallytwo1994 is offline   Reply With Quote
Old 10-25-2009, 02:55 PM   #16
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 6,940
Images: 59
You don't need to have 30a to melt the plug. You only need a little resistance across a poorly made connection to generate 50 or 100 watts of power. More than enough power to start a fire inside the plug. I think most of the previous posters are right, it's a shoddy internal connection in the plug.
__________________

__________________
markdoane is offline   Reply With Quote
Old 10-25-2009, 04:24 PM   #17
banjobill
 
wmarsha's Avatar
 
2000 30' Limited
battle ground, , Washington
Join Date: Jun 2009
Posts: 510
surge guard cutting power before melting?

Carol's question is an excellent one. As long as the current flow through the surge guard does not exceed its capacity, then, no it will not cut the power. The "heating" of the mechanical connection looks just like an appliance to the surge guard-the heating is a relatively slow process, so there is no surge; and until the resistance reaches a point where it causes more current to flow than the surge guard will allow-the surge guard is happily doing its job-passing a maximum amount of current and not allowing any voltage spikes (surges). The "bad" mechanical connection looks just like a heater unit to the surge protector.

By the way, as long as we've reached this point let's talk about another interesting possibility: 1)Assume the RV park has 240VAC at 50 amps service for each camping spot. 2) we have the correct adapter to convert this to a 120VAC 30 amp female receptacle so that we can plug our AS umbilical into the RV park's power pedestal. In this scene, the adapter's connections can draw 50 amps of power before operating a breaker. The male end of your umbilical cord, if acting as a resistive fault (bad mechanical connection), can "see" 50 amps of 120VAC causing it to melt and possibly burn right at the connection-it would only pass as much current as your AS asked for (less than 30 amps, usually) but it could use the extra 20+amps right at the connection to cause it to melt into the adapter. So, using a device such as the surge guard when adapting from one type of AC service to another is always a good idea.

Upsizing the umbilical cord can carry the 50 amps further towards the AS, too, so make sure the 50 to 30 amp "adaptation" is outside of the coach-preferably in open air.

In a perfect world, there would be no need for adapters. But...
__________________
wmarsha is offline   Reply With Quote
Old 10-25-2009, 05:26 PM   #18
Rivet Master
 
Gene's Avatar
 
2008 25' Safari FB SE
Grand Junction , Colorado
Join Date: Sep 2007
Posts: 10,840
Here's another way to overload things: our trailer has 3 or 4 120 v. breakers—you could have the heat pump, a microwave and a toaster on separate circuits and that would add up to more than 30 amps. If there are 4 circuits, an electric heater can replace the heat pump in the overload situation. And you might be able to do it with two appliances if they each have more than 15 amps. I don't think there is main breaker to prevent that. If the surge protector isn't working, or it only prevents surges and not overamping, melting time has arrived.

Gene
__________________
Gene is offline   Reply With Quote
Old 10-25-2009, 05:39 PM   #19
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 6,940
Images: 59
Gene,

If you don't have a 30a main breaker you should probably add one. You need one if you have more than two circuits.
__________________
markdoane is offline   Reply With Quote
Old 10-25-2009, 07:47 PM   #20
Rivet Master
 
Gene's Avatar
 
2008 25' Safari FB SE
Grand Junction , Colorado
Join Date: Sep 2007
Posts: 10,840
I got down on the floor and actually looked at it. There are 4 20 amp breakers, one a GFCI. One is dedicated to the A/C, the others are branch circuits although one is labeled as a "microwave". It may not go anywhere. There is a 30 amp main breaker. Being used to household wiring, 4 20 amp circuits with a 30 amp main is strange to me although I did know this trailer's limit was 30 amps.

If the main is slow blow, you could use 2 high amp appliances with 17 or 18 amps and it might take a few minutes before the main flipped. I don't think that would be enough to melt anything the first time, but if you do it a lot, maybe so. But don't listen to me—I could have looked before, but didn't want to get on the floor.

Interestingly enough, I'm at the Terraport and hooked up to the 50 amp receptacle because it was the only one available. Maybe I'll see just what I can melt.

I think it wouldn't be too hard to upgrade the breaker panel with heavier wire for a 50 amp main and add a 50 amp plug on the exterior. Maybe two parallel mains, 30 and 50, with a switch, meters, lights, and I better stop coming up with fantasies.

Gene
__________________
Gene is offline   Reply With Quote
Old 10-26-2009, 12:51 AM   #21
4 Rivet Member
 
Alwhisman's Avatar
 
1978 Argosy Minuet 7.3 Metre
Dayton , Texas
Join Date: Aug 2008
Posts: 313
Images: 94
Blog Entries: 1
Send a message via Yahoo to Alwhisman
It's very common with molded plug heads. Thats the weak link. Just cut it off and replace it, should be fine.

Al
__________________
Alwhisman is offline   Reply With Quote
Old 10-26-2009, 01:10 AM   #22
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 7,266
Images: 18
Blog Entries: 51
Hi, melted connectors and/or plugs are caused by a loose/poor connection. A larger load will just make it happen quicker. An overload with proper connections will trip the circuit breaker, either in your trailer or at the power source. I have been to camp grounds where the plug slips in real easy; This is not good. I have not done this to my trailer and I hope I never have to, but you can bend your contact blades into a slight arch and this will make a tight fit in a loose receptical.
__________________
Bob

2005 Safari 25-B
"Le Petit Chateau Argent"
[ Small Silver Castle ]
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 10-26-2009, 08:32 AM   #23
4 Rivet Member
 
kennethowens's Avatar
 
1975 Argosy 24
Malakoff , Texas
Join Date: Apr 2009
Posts: 490
I looked at the 50-to-30 adapters. The wire size is small.
When they rate them at 30 amps...that is MAX amp draw
for a short "Duty Cycle". The modern Air Coditioner - by itself -
can strain(heat) the OEM 30 amp cord. Any added adapters
can make it worse because they are often of smaller wire size.
If a person wants to use All of the MAX 30 amps....then it seems
a larger supply cord(one that is capable of >30 amps) continuous
duty would work fine. I suggest an outdoor cable that is sunlight
and water resistant 6/3 with ground the entire distance. It seems
better to "over supply and under-use" than to "under supply and over-use".
These melted cords are evidence of "under supply and over-use".
__________________
kennethowens is offline   Reply With Quote
Old 03-13-2010, 11:00 PM   #24
Rivet Master
 
Melody Ranch's Avatar
 
1956 22' Flying Cloud
1953 32' Liner
1955 22' Safari
Valley View , Texas
Join Date: Jan 2006
Posts: 3,960
Images: 78
Send a message via Skype™ to Melody Ranch
Incineration???

I just had a handyman electrician install a 30 amp and a couple 15 amp outlets in a box outside my barn....making available power to any visiting Airstreamer.....and me when parked out under the trees. BUT, before I go any further with it...even test it...I have a nagging recollection that somewhere here in the Forum...a mention was made about being sure that the electrician knew that this was to be power for an RV...not a residence. 220 volts/240 volts something like that. I know nothing about it and and need to be sure about this....any input out there?
__________________
"If it can't be reduced, reused, repaired, rebuilt, refurbished, refinished, resold, recycled or composted
then it should be restricted, redesigned or removed from production."
Melody Ranch is offline   Reply With Quote
Old 03-13-2010, 11:21 PM   #25
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 7,266
Images: 18
Blog Entries: 51
Quote:
Originally Posted by CanoeStream View Post
Chuck has found a 20 amp outlet can be used if you aren't trying to run any other high-demand appliances on house current (eg, no microwave, put fridge on propane, etc) -- but most people don't even have 20 amp outlets in their home.
Hi, electrical code for my Lakewood house has 15 amp circuits for all ceiling lamps/porch lamps and wall mounted light switches; All recepticals are 20 amp. I would think that should be national standard, but maybe not. This may be a code upgrade from adding on and running new systems for remodeling our home. Our original wall plugs were two prong/non-grounded.
__________________
Bob

2005 Safari 25-B
"Le Petit Chateau Argent"
[ Small Silver Castle ]
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 03-14-2010, 12:19 PM   #26
More than one rivet loose
 
thecatsandi's Avatar

 
Currently Looking...
Keymar , Maryland
Join Date: Feb 2006
Posts: 3,754
Quote:
Originally Posted by CanoeStream View Post
Chuck has found a 20 amp outlet can be used if you aren't trying to run any other high-demand appliances on house current (eg, no microwave, put fridge on propane, etc) -- but most people don't even have 20 amp outlets in their home.
Depends on the age of your house. My house is full of 20A circuits. The addition in the 1990s has 15A outlets.
I added a 30A RV outlet by the street plus a 20A and an temp switched 15A. Total draw for all three is 40A.
I will be installing a 30A RV outlet where I park my trailer in the back yard. Just have to wait for the ground to thaw.

Both of the eletricians I have dealt with in Missoula will only install 12ga wire. Keeps problems to a minimum.
__________________
Michelle TAC MT-0
Sarah, Snowball

Looking for a 1962 Flying Cloud

thecatsandi is offline   Reply With Quote
Old 03-14-2010, 12:29 PM   #27
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
this might help
http://www.airforums.com/forums/f37/...ram-25523.html

Quote:
Originally Posted by Melody Ranch View Post
I just had a handyman electrician install a 30 amp and a couple 15 amp outlets in a box outside my barn....making available power to any visiting Airstreamer.....and me when parked out under the trees. BUT, before I go any further with it...even test it...I have a nagging recollection that somewhere here in the Forum...a mention was made about being sure that the electrician knew that this was to be power for an RV...not a residence. 220 volts/240 volts something like that. I know nothing about it and and need to be sure about this....any input out there?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 03-14-2010, 12:31 PM   #28
Don't forget your cat nap
 
Ag&Au's Avatar
 
Port Orchard , Washington
Join Date: May 2009
Posts: 4,464
Images: 1
Quote:
Originally Posted by Melody Ranch View Post
I just had a handyman electrician install a 30 amp and a couple 15 amp outlets in a box outside my barn....making available power to any visiting Airstreamer.....and me when parked out under the trees. BUT, before I go any further with it...even test it...I have a nagging recollection that somewhere here in the Forum...a mention was made about being sure that the electrician knew that this was to be power for an RV...not a residence. 220 volts/240 volts something like that. I know nothing about it and and need to be sure about this....any input out there?
Find someone who has a multimeter and can test it to see what voltage is on it. Also call the installer and ask him what he did. But, as you mentioned, until you know, don't plug anything into it.

Regards,
Ken
__________________

__________________
Ag&Au is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power surging from shore power in my Excella 500? NVDeputy Lights - Interior & Exterior 4 10-09-2009 12:52 PM
Accessing Shore Power Plug on '06 Safari Denis4x4 Batteries, Univolts, Converters & Inverters 5 03-09-2009 01:33 PM
Shore Power Again The Flintstones Batteries, Univolts, Converters & Inverters 13 10-09-2007 08:18 PM
Shore power and battery power problems jfremstad Electrical - Systems, Generators, Batteries & Solar 5 05-03-2007 09:23 AM
Shore power cord FreshAir Electrical - Systems, Generators, Batteries & Solar 18 02-21-2007 03:41 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:29 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.