07-22-2005, 11:45 AM
#21
2003 25' Safari
Kissimmee
I still believe the neutral and the ground are connected somewhere in the trailer - but not necessarily in the trailer's breaker box. For example, an appliance may have them common. You can check a trailer easily with an ohmmeter - check the resistance between neutral and ground on the main plug.
I realize this may not make sense why two wires are run that are connected together. Your home breaker box has neutral and ground connected in the box, yet all those redundant wires are run all the way back to it! The neutral goes to ground, and the ground is an alternate path to ground. The idea is to have conduit, appliance chassis, light fixture trim, etc grounded through a second path so if there is a short between hot and these parts the path is to ground and not to a person, and the breaker will overload and trip. The second path provides a level of redundancy to the system!
Dan
07-22-2005, 11:57 AM
#22
1967 26' Overlander
Huntsville
, Alabama
dmac,
I owe you an apology. I took your earlier post to mean that the Airstream came from the factory with the two wires twisted together. I now see that you meant someone else had done it.
Unfortunately, Fast Dan has not indicated he plans to fix his multi-position connector. An unsafe condition will exist in his Airstream until that occurs.
Tom
07-22-2005, 12:04 PM
#23
2003 25' Safari
Kissimmee
My faded memory recalls seeing appliances where neutral and ground are both attached to the appliance chassis, if correct then his trailer may have come from the factory this way. In any case, the plug on the main electrical cord must be replaced. That tingling sensation could be fatal with rain and bare feet!
Dan
07-22-2005, 01:30 PM
#24
1977 27' Overlander
1954 25' Cruiser
1990 34.5' Airstream 345
VC Highlands
, Nevada
Isolation transformer
You could use an isolation transformer which would eliminate the tingling problem completely. Problem is that they are expensive, heavy and finding a location to put the darn thing would be a problem. But it would guarantee that no matter where you were or what you plugged in to, you would be golden.
07-22-2005, 03:07 PM
#25
1967 26' Overlander
Huntsville
, Alabama
Originally Posted by dmac
My faded memory recalls seeing appliances where neutral and ground are both attached to the appliance chassis, if correct then his trailer may have come from the factory this way...
I believe what you are recalling applied to your home's 220 vac stove. If you had an oven light, which ran on 120 vac, the neutral leg was tied to ground. An electric dryer's motor was the same way.
For a purely 120 vac application such as an Airstream, there is no reason to tie neutral & ground together anywhere in the trailer.
Tom
07-22-2005, 09:51 PM
#26
1986 25' Sovereign
Southern Middle
, Tennessee
Believe me, connecting a ground and neutral together will trip the campground breaker. My incident 3 years ago where a short in the 30 amp plug kept tripping the campground breaker brought the services of a well meaning factory maintenance man to my trailer. When I wasn't looking, he ran a jumper wire from neutral to ground which is acceptable in the factory where he worked. Unfortunately this kept tripping the GFIC of the campground as well as the GFIC in my garage when I got home even after I replaced the offending plug. Only comparing the wiring in my breaker box to the wiring diagram in my manual revealed the culprit. As soon as it was removed everything was back to normal.
I don't think this is the same thing that you have going on but the ground/neutral caught my eye.
Craig
AIR #0078
3.73 rear end
Mag-Hytec rear diff cover
Amsoil synthetics all around
10-15-2005, 11:47 PM
#27
Dan,
I haven't checked my Airstream to see, but I suspect that the 120 volt system is wired the same as a house system. If that's the case, then the neutral wires and the ground wires are connected to each other in the main power distribution box. This is the only place where they are supposed to be interconnected.
Craig,
Connecting the neutral wire to ground outside the distribution box will not trip the circuit breaker, but it should trip a GFI (Ground Fault Interrupter). The GFI compares the current between the hot (black) and the neutral (white) wires. If this current is not equal, then current is leaking to ground somewhere and it will shut off the circuit. A straight circuit breaker will trip only when the current through the breaker exceeds its rating.
Rob,
Yes, you do understand it. I'm glad you got it all figured out before you or anyone else got hurt. I'm not an electrician by trade, but I know enough about it to understand that many people who think they can wire a circuit can't. One of the most common problems is that unknowing amateurs don't know that polarity matters on AC circuits.
Loren
2012 New Horizons Travel Trailer (formerly an Airstream owner)
2008 Dodge 2500 diesel with Equal-i-zer hitch.
10-16-2005, 05:04 AM
#28
Loren
Loren,
You should check, because an RV is not wired the same as your house. The ground and neutral should not be connected at the main power distribution box on your airstream.
The reason is that you do not have a real 'ground' at your campsite, unless you pound a 10 ft rod into the ground. The way you get to a real ground is through the power pedestal, which connects to ground through the park's power system.
Many residential electricians are caught unaware by this. If you have an electrician work on your trailer be sure he/she understands what a 'floating ground' is.