First, what led me to using the 50 amp service was the fact that at some SP, I was tripping the 30 amp outlet outside more than once while camping. So I figured, why not get an adapter and start using the 50 amp one where available This seamed to work till this past winter.
We were up in northern GA using a space heater most of the time for about 2 wks. I went to unplug it and found the male plug from the trailer had melted to the female adapter plug Now I'm trying to understand what caused it. The breakers inside never tripped. So why would it have a melt down at the plug? Is it that the load going through the wiring is to much for the size power cable of the trailer? or is it that the load was to much for the plug itself? Since I need to replace the plug, my thinking (I know, Bad idea) why not use a 50 amp plug and get an adapter to go to 30 amp when needed. This might solve a melt down?? Any input on this would really be great
__________________

__________________
Julia & Bob
W/ Deedee & Boo
AIR #30685
RLS is offline   Reply With Quote
Old 02-01-2011, 07:31 PM   #2
Rivet Master
 
Dwight's Avatar
 
1999 34' Excella
Joshua , Texas
Join Date: Apr 2002
Posts: 548
Images: 2
Just to clarify, your trailer is 30amp and you are connecting to a 50amp receptacle (shore power)?

try this link....http://www.airforums.com/forums/f37/...ted-57807.html
__________________

__________________
History doesn't repeat itself, people do!
Dwight is offline   Reply With Quote
Old 02-01-2011, 07:35 PM   #3
Rivet Master
 
TBRich's Avatar

 
2006 19' Safari SE
Tucson , Arizona
Join Date: Jun 2007
Posts: 4,483
Images: 64
I believe that if you are using an adaptor from 50 service to a 30-amp cord and circuit (your AS) that you are only getting 30 amps in the translation...I am pretty sure you are not getting more power.

It sounds to me like there was an issue with the source rather than your unit that caused the melt-down.
__________________
TB & Greg and Abbey Schnauzer
AirForums #21900 . Membership Chair, 4C
Unit #3954
Travel Log: AZBambi...On the Road Again
TBRich is offline   Reply With Quote
Old 02-01-2011, 07:50 PM   #4
Rivet Master
 
Dwight's Avatar
 
1999 34' Excella
Joshua , Texas
Join Date: Apr 2002
Posts: 548
Images: 2
The 50amp plug has 4 prongs. There is one ground, one neutral, and two hot wires. The Airstream should never have to be hooked up to one of these simply because the internal wiring of the Airstream is rated at only 30-amps. unless you change your breaker box.

If you use as 50-amp to 30-amp adapter, it will work just fine as long as you never attach any additional heavy load electrical items to the Airstream's duplex outlets. If you attempt to do so, the 50-amp service will be more than happy to send all that power to your vehicle but you better hope that the 30-amp breaker on the Airstream will trip otherwise you could be looking at melted wires or a vehicle fire.
__________________
History doesn't repeat itself, people do!
Dwight is offline   Reply With Quote
Old 02-01-2011, 08:04 PM   #5
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,362
Images: 7
A "LOT" of power outlets at campgrounds have pitted and corroded 30 amp outlets causing resistance that in turn leads to heating at the connector eventually destroying the CG outlet and the RV plug.

Your 30amp male plug could have been pitted and had a high resistance causing excessive heat.
This is mostly caused by campers plugging in and unplugging their power cords without turning off the breaker.

Another problem is the 50amp outlet is protected by a 50 map breaker so your breaker box in the RV is the only protection from overloading and I have seen more than one wired with out the 30 amp main.
__________________
Garry
garry is offline   Reply With Quote
Old 02-01-2011, 08:04 PM   #6
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
A 50-to-30 amp connector simply uses one of the 120VAC hot legs in the 50 amp receptacle and the neutral and ground. You don't really gain anything over the straight 30 amp outlet, and in some cases, you actually limit yourself to 25 amps.........or half of the 50 amps available.

You seem to be over-drawing the rated capacity of the wire in your shore cord, resulting in excessive heat and melting. I would add up the appliances that you are using, and I bet you are way over 30 amps (360 watts).
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 02-01-2011, 08:25 PM   #7
4 Rivet Member
 
withidl's Avatar
 
2002 31' Classic
Houston , Texas
Join Date: Oct 2004
Posts: 440
Images: 1
Sand Connector Prongs

Quote:
Originally Posted by garry View Post
A "LOT" of power outlets at campgrounds have pitted and corroded 30 amp outlets causing resistance that in turn leads to heating at the connector eventually destroying the CG outlet and the RV plug.

Your 30amp male plug could have been pitted and had a high resistance causing excessive heat.
This is mostly caused by campers plugging in and unplugging their power cords without turning off the breaker.
=================================================

Agreed. I will add that you can sand (400 grit) the 30 amp connector "prongs" till they shine to remove pitting/corrosion for better contact AND inserting/removing the 30 amp connector numerous time (without load) will also remove some of the pitting/corrosion in the campsite recepticle.
__________________
withidl is offline   Reply With Quote
Old 02-01-2011, 08:51 PM   #8
RLS
Rivet Master
 
RLS's Avatar

 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 608
Thanks everyone First, The trailer is set up for 30 amp service. Second,from what little I know, I think there is 50 amps going to each prong of the 50 amp service outlet, not 25 amp. This was why I started using the 50 amp in the first place. Third, the plug being pitted I guess could be the culprit. That sounds like it would cause it, not the wiring size being to small for the load. I'm sure we were at the limits of what could be used. I got a feeling what might have put it over the top for the melt down was when the electric hot water heater would kick on. Next time in cold weather like that I will be using the gas for the hot water heater.
I like how much bulk and tight fitting the 50 amp plug is, so that is what I am going to use with an adapter to go down to 30 amp service when needed. I will be using just one side of the 2 prongs. Hopefully this is OK?? Thanks again, this forum is the best
__________________
Julia & Bob
W/ Deedee & Boo
AIR #30685
RLS is offline   Reply With Quote
Old 02-01-2011, 10:22 PM   #9
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,362
Images: 7
Wrong info here........

The 220V outlet is no different than what is used in your 220 at home the difference is it is wired in the load center of the RV so you have 2 separate 120VAC sources each one at 50 amps for a total of 100 amps or 12000 watts total.

On a 30 amp RV you only have one 120VAC line from the pedestal into the RV with a 30 amp main breaker.

What you plan to do is fine you will only be using one side of the 50 amps the only down side is you have a 50 amp breaker at the CG pedestal and hopefully a 30 amp main in the RV so you can only draw 30 amps.

Running a 1500W heater =12 or 13 amps HW heater kicks on and you are now pulling around 27 amps add the converter and you are maxed out close to tripping the 30 amp breaker. Running the HW heater on gas solves the problem.
__________________
Garry
garry is offline   Reply With Quote
Old 02-01-2011, 10:38 PM   #10
RLS
Rivet Master
 
RLS's Avatar

 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 608
Garry, Thanks for the info. Here is what I was putting up to show why I thought it was 50 amp each leg.
Quote:
From this common service we can draw 120 or 240 volts. Each leg is 50 amps @ 120 volts. 50-amp X 120-volt = 6000 watts. But since there are 2 HOT 120-volt legs at 6000 + 6000 = 12,000 watts to use in the RV or 50-amp X 240-volt = 12,000 watts when used as a 240-volt service.
This is for RV service. and yes, I do have a main 30 amp breaker inside plus 4 (I think) 15 amp ones.
__________________
Julia & Bob
W/ Deedee & Boo
AIR #30685
RLS is offline   Reply With Quote
Old 02-01-2011, 10:43 PM   #11
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,119
Quote:
Originally Posted by RLS View Post
We were up in northern GA using a space heater most of the time for about 2 wks. I went to unplug it and found the male plug from the trailer had melted to the female adapter plug Now I'm trying to understand what caused it.
In general, the plugs on 30 amp shore power cords eventually fail and melt even if they aren't overloaded.

This can be caused by any combination of: corroded and worn campground shore power receptacles, corrosion on the blades of the plug, or corrosion or fatigue on the clamp connection between the blades of the plug and the shore power cable.

While in theory overloading can cause it too, most plugs that fail don't fail because of an overload. You should have a 30 amp main breaker that will trip in the event of an overload. If not, add one.
Since you have a 30 amp main breaker, overloading isn't the problem, because the breaker would have tripped.

The molded-on plugs don't always last for the life of the cord. At the first sign of overheating, unless the problem is with the campground receptacle, the plug should be cut off and replaced.
__________________
Jammer is offline   Reply With Quote
Old 02-02-2011, 12:38 AM   #12
Rivet Master
 
NevadaGeo's Avatar
 
1978 31' Excella 500
Genoa , Nevada
Join Date: Jul 2007
Posts: 1,305
An infrared temperature gun could tell you where the cord or plug is getting hot. I use one a lot, check the disc brake temperatures, check temperatures in the engine, check if the freezer is getting colder, lots of uses.
__________________
I admit to being powerless over housecleaning and social niceities
Airforums 22655 and now, WBCCI 22655

NevadaGeo
NevadaGeo is offline   Reply With Quote
Old 02-02-2011, 02:58 AM   #13
Be Calm, Have a Cupcake
 
Secguru's Avatar
 
Vintage Kin Owner
Houston , Texas
Join Date: Nov 2007
Posts: 223
Images: 1
Just for the record

30 Amp 120 Volt service is 3,600 Watts, not 360 Watts.
__________________
Secguru

Would you rather have a mansion full of money or a trailer full of love?
Secguru is offline   Reply With Quote
Old 02-03-2011, 10:15 PM   #14
4 Rivet Member
 
Hodum's Avatar
 
1995 34' Excella
Corinth , Mississippi
Join Date: Dec 2010
Posts: 304
There was probably a loose connection where the melting took place. The spring tension of the female plug was more than likely weak and allowed heat build up. The thirty amp adapter only connects to one leg of the 240 volt plug and that will only alow 120 volts to the main in the RV. The main will limit the amperage to 30 amps therefore under normal circumstances no problems. Usually when there is heat there is a loose connection or an overload. In this case the main 30 amp breaker in the RV would have prevented an overload.
__________________

__________________
Hodum is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
'67 Caravel Door lock Question vonzellen Doors & Locks 14 11-29-2011 02:26 PM
LP regulator question GAT LP Gas, Piping, Tanks & Regulators 17 05-09-2011 08:09 AM
Polishing Question NicheVintage Cleaning, Stripping & Polishing 48 02-08-2011 01:04 PM
'67 Caravel Restoration Electrical question vonzellen 1966-68 Caravel 1 01-15-2011 08:25 AM
Trailering Question Cracker Jacks, Stabilizers, Lifting and Leveling 14 01-02-2011 03:55 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.