Need advice on 30 amp outlet box

I am in the process of installing a 30 amp outlet box on the outside of the garage and really could use some input on this.
I have a 50 amp plug now for the welder that has not been used on the other side of the garage. My thinking is to splice into one side of this 50 amp plug (to get 120 volts) and run 10 ga. Romex to the 30 amp outlet. Is this OK? and is 10 ga OK with a distance of 60 ft.? Also, should I change the breakers to 30 amp?

Thanks, Bob
RLS is offline   Reply With Quote
Old 05-29-2009, 12:16 AM   #2
Rivet Master
 
3 Dog Nite's Avatar
 
Currently Looking...
1989 34.5' Airstream 345
Cleveland , Tennessee
Join Date: Jul 2007
Posts: 787
Your thinking is OK. Be sure to put a blank cover on the box where the 50 amp outlet used to be. 10 ga wire is OK for 30 amps for a short run of 60'. I'm assuming that the 50 amp was run with 8 ga. Be sure to put a wire nut on both ends of the unused wire from the 50 amp circuit. No unnecessary sparks allowed. Is Romex code for exterior where you live? You didn't say if it was going outside or staying in. Make sure it burial type if using outside. Run it in a short peice of conduit from the box to underground for protection. Use a 2nd piece to bring it up to the 30 amp outlet box.

Ricky
__________________
"Sometimes I wonder if the world is being run by smart people who are putting us on, or by imbeciles who really mean it." Mark Twain

AIR 22749 WBCCI 2349 NOVA TAC TN-6
1989 345 LE Classic Motorhome
3 Dog Nite is offline   Reply With Quote
Old 05-29-2009, 03:29 AM   #3
4 Rivet Member
 
1977 31' Sovereign
Manchester , New Hampshire
Join Date: May 2006
Posts: 347
Images: 33
Blog Entries: 1
Quote:
Originally Posted by 3 Dog Nite View Post
Your thinking is OK. Be sure to put a blank cover on the box where the 50 amp outlet used to be. 10 ga wire is OK for 30 amps for a short run of 60'. I'm assuming that the 50 amp was run with 8 ga. Be sure to put a wire nut on both ends of the unused wire from the 50 amp circuit. No unnecessary sparks allowed. Is Romex code for exterior where you live? You didn't say if it was going outside or staying in. Make sure it burial type if using outside. Run it in a short peice of conduit from the box to underground for protection. Use a 2nd piece to bring it up to the 30 amp outlet box.

Ricky
Could he use the same plug but switch out circuit breaker with a 30 amp and use only one of the legs of the 220 volt. That way he would not have to do all kinds of installation stuff . He could even since I believe it usually is a dual pole circuit breaker for his 220 volt welder use a duel pole 30 amp and just end cap one lead at distribution panel . Any electricians have any advice out there on this I dont want to mislead anyone?.
__________________
1976 Airstream Sovereign International Landyacht (renovating)(found DOM plate said 1976)
1968 Airstream Caravel 17 footer

2004 Nissan Titan with BT package
K/N Cool intake air
Duel power exhaust
Mrcrowley is offline   Reply With Quote
Old 05-29-2009, 07:13 AM   #4
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
will you ever use the welder again? if you might i'd look to see if it is possible to run a line from the welding outlet to a 30a fused 120v line to an outlet for the trailer. that way you'd get to have both.

i wouldn't weld with the trailer plugged in even if you don't trip a breaker. the voltage spikes would not be a good thing.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 05-29-2009, 07:14 AM   #5
RLS
Rivet Master
 
RLS's Avatar
 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 623
Quote:
Originally Posted by 3 Dog Nite View Post
Your thinking is OK. Be sure to put a blank cover on the box where the 50 amp outlet used to be. 10 ga wire is OK for 30 amps for a short run of 60'. I'm assuming that the 50 amp was run with 8 ga. Be sure to put a wire nut on both ends of the unused wire from the 50 amp circuit. No unnecessary sparks allowed. Is Romex code for exterior where you live? You didn't say if it was going outside or staying in. Make sure it burial type if using outside. Run it in a short peice of conduit from the box to underground for protection. Use a 2nd piece to bring it up to the 30 amp outlet box.

Ricky
Thanks for the advice. The 50 amp one is on the inside wall of the garage. My thinking is to fish the new 10 amp wire down the wall from the attic and connect it, run it across the attic above the garage and come down the outside wall in a conduit to the new box. Hmm, do not know about Romex possibly not being up to code. What should be used?

Bob
RLS is offline   Reply With Quote
Old 05-29-2009, 07:15 AM   #6
Rivet Master
 
easyride's Avatar
 
1977 27' Overlander
1973 27' Overlander
1963 19' Globetrotter
Naples , Florida
Join Date: Nov 2007
Posts: 1,259
Images: 1
? do you have 4 wires coming to 50 amp box? You need a 120 v leg,a ground,and a neutral.Even though the neutral and the ground go to the same place in the box ,an electrician told me I need both. How far is panel,might be better to go to panel and keep your welder outlet.Dave
Just saw the other posts, romex is legal in residential housing. Are you planning on keeping the 50 amp,if so I believe it is illegal to tap in in the ceiling,where are you going to get the slack to make a junction box.also breaker must be installed between 8ga and 10 ga. My opinion,Dave
easyride is offline   Reply With Quote
Old 05-29-2009, 07:46 AM   #7
RLS
Rivet Master
 
RLS's Avatar
 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 623
Quote:
Originally Posted by easyride View Post
? do you have 4 wires coming to 50 amp box? You need a 120 v leg,a ground,and a neutral.Even though the neutral and the ground go to the same place in the box ,an electrician told me I need both. How far is panel,might be better to go to panel and keep your welder outlet.Dave
Just saw the other posts, romex is legal in residential housing. Are you planning on keeping the 50 amp,if so I believe it is illegal to tap in in the ceiling,where are you going to get the slack to make a junction box.also breaker must be installed between 8ga and 10 ga. My opinion,Dave
OK, I just went out and opened up the 50 amp outlet. Those wires are HUGE! and only 3 of them. I thought there would be a separate ground wire but like you say, the neutral and ground are one. I guess my best bet is to go to the panel and put in a new 30 amp breaker. I've just never opened up one of those!

Thank you, Bob
RLS is offline   Reply With Quote
Old 05-29-2009, 08:08 AM   #8
4 Rivet Member
 
1977 31' Sovereign
Manchester , New Hampshire
Join Date: May 2006
Posts: 347
Images: 33
Blog Entries: 1
Quote:
Originally Posted by RLS View Post
OK, I just went out and opened up the 50 amp outlet. Those wires are HUGE! and only 3 of them. I thought there would be a separate ground wire but like you say, the neutral and ground are one. I guess my best bet is to go to the panel and put in a new 30 amp breaker. I've just never opened up one of those!

Thank you, Bob
Ok just so I understand you want to run a line from the welders plug to the other side of garage closer to where you trailer is ? . I would If I were you add a 30 amp breaker to your breaker box and run a 10/3 wire from there to where you want it near your trailer.

1) When opening a breaker box think saftey first..Use gloves..
2) Use insulated tools (short screw drivers )Manipulate wires with pliers not hands.
3) When you run wires in box tape off the ends so no wire is exposed
4) DO it slow and easy
5) Strip wires one at a time and make sure you have wires away from breaker box.
6) Wire up the neutral and ground wire first
7) Wire line to circuit breaker before you pop in circuit breaker(live wire is black)make sure breaker is off.
__________________
1976 Airstream Sovereign International Landyacht (renovating)(found DOM plate said 1976)
1968 Airstream Caravel 17 footer

2004 Nissan Titan with BT package
K/N Cool intake air
Duel power exhaust
Mrcrowley is offline   Reply With Quote
Old 05-29-2009, 08:12 AM   #9
Rivet Master
 
3 Dog Nite's Avatar
 
Currently Looking...
1989 34.5' Airstream 345
Cleveland , Tennessee
Join Date: Jul 2007
Posts: 787
I was questioning the Romex alone being code for exterior use. It's OK when run inside conduit. make sure you have a large diameter conduit as romex won't pull as easy as 3 loose wires.

Ricky
__________________
"Sometimes I wonder if the world is being run by smart people who are putting us on, or by imbeciles who really mean it." Mark Twain

AIR 22749 WBCCI 2349 NOVA TAC TN-6
1989 345 LE Classic Motorhome
3 Dog Nite is offline   Reply With Quote
Old 05-29-2009, 08:32 AM   #10
RLS
Rivet Master
 
RLS's Avatar
 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 623
Thanks

Just want to say thank you for the great input on this. The 50 amp welding plug idea is out! I will attempt to open up the breaker panel box and wire in a new 30 amp line with breaker.
Since this will be my first time with opening up one of these, I think it best to have the main power OFF!

Bob
RLS is offline   Reply With Quote
Old 05-29-2009, 08:35 AM   #11
Rivet Master
 
easyride's Avatar
 
1977 27' Overlander
1973 27' Overlander
1963 19' Globetrotter
Naples , Florida
Join Date: Nov 2007
Posts: 1,259
Images: 1
Hopefully your panel is not full,if it is you need a piggy back breaker,get the brand name of your panel, and purchase a 30 amp single pole breaker,should be an open knockout on panel.make sure you use a romex connector.Also make sure yoy turn off the main breaker usually a 200 amp breaker,do not touch top lugs,they are still hot.Better yet get a licenced electrician,then if the house burns down it is his insurance paying for it.Dave
easyride is offline   Reply With Quote
Old 05-29-2009, 09:18 AM   #12
RLS
Rivet Master
 
RLS's Avatar
 
2004 25' Classic
Prescott , Arizona
Join Date: Jul 2008
Posts: 623
One more question?

OK, I'm thinking (that's bad I know!) but how about wiring straight from the panel ( no breaker ) to an outlet panel that has a 30 amp breaker like this B001813YG2 | Conibear RV Center

Bob
RLS is offline   Reply With Quote
Old 05-29-2009, 09:56 AM   #13
4 Rivet Member
 
1977 31' Sovereign
Manchester , New Hampshire
Join Date: May 2006
Posts: 347
Images: 33
Blog Entries: 1
Quote:
Originally Posted by RLS View Post
OK, I'm thinking (that's bad I know!) but how about wiring straight from the panel ( no breaker ) to an outlet panel that has a 30 amp breaker like this B001813YG2 | Conibear RV Center

Bob
Well you need a breaker from the breaker box there is no other way to connect to main bus . There is one more way to do this you could turn the welding plug int a fuse panel with a 30 amp circuit breaker in it but you would need to run a ground rod to that panel .How far is the Welding Plug from the trailer?
__________________
1976 Airstream Sovereign International Landyacht (renovating)(found DOM plate said 1976)
1968 Airstream Caravel 17 footer

2004 Nissan Titan with BT package
K/N Cool intake air
Duel power exhaust
Mrcrowley is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
wiring a new 30 amp outlet gparker Electrical - Systems, Generators, Batteries & Solar 22 03-25-2010 08:07 PM
outlet box depth tinbender Batteries, Univolts, Converters & Inverters 10 02-27-2008 07:04 PM
'05 Safari: More amp-hours in stock battery box tpi Batteries, Univolts, Converters & Inverters 15 09-17-2007 11:39 AM
30 amp box davidz71 Electrical - Systems, Generators, Batteries & Solar 10 10-23-2005 09:38 AM
30 amp outlet john hd Electrical - Systems, Generators, Batteries & Solar 20 02-26-2003 01:54 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:26 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.