Old 06-02-2019, 05:50 AM   #43
4 Rivet Member

 
2013 20' Flying Cloud
Westerly , Rhode Island
Join Date: Apr 2018
Posts: 377
Quote:
Originally Posted by turk123 View Post
For some reason, I didn't believe my 50 amp surge protector would work on 110 volts.
I noticed you said something similar above about not knowing your surge protector would work on the "lower" 110 voltage, but it's not designed to work on anything else is it? Trailers are not wired for 220 AFAIK. With the 50 amp are there two separate 110 lines?
__________________

smithcreek is offline   Reply With Quote
Old 06-02-2019, 05:58 AM   #44
Rivet Master
 
2014 20' Flying Cloud
Long Island , New York
Join Date: Jun 2015
Posts: 10,688
Quote:
Originally Posted by turk123 View Post
. . .
Let this be a lesson to all of us to take the precautions you all know you need to do to protect you and your trailer.
. . .
Amen to that!

Thank you for bringing this situation to our attention. Lots of good lessons here.

The one phrase I find the need to repeat to myself, over and over again during each waking hour, is this:

"Haste Makes Waste"

Rushing . . . . . NG!



Thanks again for all the details and suggestions from everyone.

Peter
__________________

OTRA15 is offline   Reply With Quote
Old 06-02-2019, 06:08 AM   #45
AirDreamer
 
turk123's Avatar

 
2019 30' Classic
Canfield , Ohio
Join Date: Jul 2015
Posts: 1,189
Quote:
Originally Posted by smithcreek View Post
I noticed you said something similar above about not knowing your surge protector would work on the "lower" 110 voltage, but it's not designed to work on anything else is it? Trailers are not wired for 220 AFAIK. With the 50 amp are there two separate 110 lines?
You are correct, and what I should have said was lower amp service.

http://www.myrv.us/electric/Pg/50amp_Service.htm
__________________
2017 Airstream International Signature 27FB Twin
2019 Airstream Classic 30 Twin

Got Connect? Turn off WiFi as WAN!!

Support Airstream Forum***
turk123 is offline   Reply With Quote
Old 06-02-2019, 06:31 AM   #46
Rivet Master
 
blkmagikca's Avatar

 
1987 32' Excella
Nepean , Ontario
Join Date: Mar 2006
Posts: 1,305
We tend to be complacent about campground electricity these days. When I first started RV'ing (some 38 years ago), many campgrounds used glass fuses at their pedestals, which made it mandatory to carry extra fuses. As well, many had reversed neutral/hot wiring. An article in the old Trailer Life magazine suggested carrying a plug/socket contraption with reversed wiring just to correct for those instances.

Some of my AS'er friends travelled down the Baja 2 years ago. They told me that they relied on their solar so charge their batteries, as the 110-v AC was very unreliable.

About 5 years ago I was camped at a white-water recreation area, and they told me that they had 30-amp service. All seemed OK, my surge protector indicated no faults, and the control panel for the Xantrex inverter/charger/converter showed 115-volts. When I switched on the a/c, everything bombed. I reset everything and watched the control panel while I switched on the a/c again; the votage dropped below 90-volts and then cut out. Obviously, there were issues with the campground wiring.

Lesson learned - never trust campground wiring. Always test before plugging in and always use a good surge protector. If in doubt, dry-camp.
__________________
VE3JDZ
AIR 12148
1987 Excella 32-foot
1999 Dodge Ram 2500HD Diesel
WBCCI 8080
blkmagikca is offline   Reply With Quote
Old 06-02-2019, 06:47 AM   #47
Half a Rivet Short
 
2017 30' Classic
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 6,786
Hi

Ok. to be very clear:

Your 50A surge protector is fine on 30A, 20A, 15A or 3A. Use it whenever you hook up your trailer. It will not protect you from everything and anything. It will take care of > 90% of what you will run into.

Extension cords come in a lot of flavors. Some have coper wire, some have aluminum wire. That makes the old "if it's 12 gauge it's good enough" stuff a bit tough these days. Best to *assume* it's aluminum and you need 10 gauge for a 20A circuit.

Normal wall plugs date back to a very different era. They wear out fairly quickly. The same is true of sockets. When they do, they get hot at high current. Cheap plastic melts when it gets hot. You don't run into it a lot because you pretty much never run them at full current.

=====

The generator bonding thing has been answered back a ways. Again to be clear:

Generators get used a lot of ways. If you are powering your house with one, you might not want neutral hooked to ground at the generator. If you are running your trailer off of one, you *do* want to tie neutral to ground at the generator. A shoring plug will do this just fine.

=====

The problems that occurred are *not* from the daisy chain setup. They are from some sort of wiring fault. That sort of thing can happen anywhere anytime. Campground power boxes lead a long hard life. They are at least as likely to do this to you as any rally setup.

Get a set of adapters for your plug setup. You need to get to 50A, 30A and 15 A plugs on the "input" side of your system. Surge protector at the post or built into the trailer, either way it always gets used.

Now (as if that wasn't enough) off to the deep end:

Technically a "surge protector" takes care of brief over voltage on the line. You can get then pretty cheap and they will help some. They will *not* help in the case of a wiring fault. Simply put a "surge protector" probably would not have protected the trailer in this case. What would protect it is a box like the EMS gizmos from Progressive. They are way more than just a surge protector. Don't cheap out ....

Bob
uncle_bob is offline   Reply With Quote
Old 06-02-2019, 06:57 AM   #48
Rivet Master
 
Ridgerunner3's Avatar
 
2002 25' Safari
Fountain Inn , South Carolina
Join Date: Sep 2011
Posts: 696
Images: 13
Quote:
Originally Posted by uncle_bob View Post
Hi




Generators get used a lot of ways. If you are powering your house with one, you might not want neutral hooked to ground at the generator. If you are running your trailer off of one, you *do* want to tie neutral to ground at the generator. A shoring plug will do this just fine.

Bob
Bob, I'm not sure what a shoring plug is. Can you explain?
__________________
Bud
Ridgerunner3 is offline   Reply With Quote
Old 06-02-2019, 09:41 AM   #49
geo
2 Rivet Member
 
2019 23' International
Vancouver , British Columbia
Join Date: Aug 2018
Posts: 28
Quote:
Originally Posted by Rainmaker View Post
Geo
Very interested in the lockbox. Can you show a picture or give some specs (ei. manufacture or dimensions). I would like to have something like that for when I have to use an extra 30 amp extension.
Itís a TRC Technology Research Corp 34590 Surge Guard Lock Hasp. Hereís a link to the product on Amazon:

https://www.amazon.com/dp/B002OUQI3W..._BU-8CbWCZTFWH
geo is offline   Reply With Quote
Old 06-02-2019, 11:00 AM   #50
3 Rivet Member
 
SilverWind's Avatar
 
2017 25' International
1968 17' Caravel
Los Osos , California
Join Date: Nov 2013
Posts: 243
Quote:
Originally Posted by uncle_bob View Post
Hi


=====

The generator bonding thing has been answered back a ways. Again to be clear:

Generators get used a lot of ways. If you are powering your house with one, you might not want neutral hooked to ground at the generator. If you are running your trailer off of one, you *do* want to tie neutral to ground at the generator. A shoring plug will do this just fine.

=====

Bob
Bob. To someone who owns an Airstream Trailer, a Honda 2000 Generator AND knows very little or nothing about electricity, your statement sounds very important but I really have no idea what you are talking about. Is there something that I need to be doing in addition to plugging the generator in and firing it up? Thanks
SilverWind is offline   Reply With Quote
Old 06-02-2019, 11:31 AM   #51
Rivet Master
 
SteveSueMac's Avatar

 
2012 27' Flying Cloud
W , New England
Join Date: Oct 2012
Posts: 6,895
Yeah. Iím confused about that advice as well.

For whatever itís worth, the Honda 2000 manual includes this statement below - meaning, I *should* be using a ďshoring plugĒ when connected to the trailer? Iíll google that now too....

GROUND SYSTEM
Honda portable generators have a system ground that connects generator frame components to the ground terminals in the AC output receptacles. The system ground is not connected to the AC neutral wire. If the generator is tested by a receptacle tester, it will not show the same ground circuit condition as for a home receptacle.
SteveSueMac is online now   Reply With Quote
Old 06-02-2019, 11:40 AM   #52
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 1,922
This

https://www.microair.net/products/ge...12272654155860

This is an example of what he is talking about.
Larry
lsbrodsky is offline   Reply With Quote
Old 06-02-2019, 11:58 AM   #53
Rivet Master
 
waninae39's Avatar

 
2017 22' Sport
NCR , Ontario
Join Date: Feb 2017
Posts: 1,338
uncle bob it correct

test any connection first. then fix it BEFORE connecting the AS
waninae39 is offline   Reply With Quote
Old 06-02-2019, 11:58 AM   #54
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 6,925
My trailer got fried!

A ďbonding plugĒ is a standard duplex plug with the neutral (white wire) connected to the U-ground (green or safety earth) lead. If you know what you are doing, itís easy to make one. If not, buy one already made.

When plugged into a ďfloating neutral ď generator it properly connects neutral and ground so EMS surge protectors see the right connections.

Normally, the neutral and ground are connected in a home service panel or in a campground pedestal. Itís a code requirement that ground and neutral NOT be connected in a trailer. The reason is that a hot-neutral wire swap could cause the trailer skin to have 120 volts on it in relation to ground, and touching the trailer could be fatal.

The separate ground lead ties the skin and frame of the trailer to ground, and would hopefully blow a breaker instead of killing someone in case of a hot-neutral swap condition.

In theory, a portable generatorís ground lug should be connected to a six foot long driven ground rod for safety. In practice, no one but the military and some commercial portable power providers actually ground mobile generators in the field.

Iíve seen the dirt smoking from bad wiring and lots of current going into a ground system in the field. It can cause a lot of trouble.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 06-02-2019, 12:03 PM   #55
Rivet Master
 
SteveSueMac's Avatar

 
2012 27' Flying Cloud
W , New England
Join Date: Oct 2012
Posts: 6,895
My trailer got fried!

Hmmm - so I never use my progressive EMS when powering the trailer on the Hondas. I always use it whenever plugged in to any other power source. I probably donít understand this well enough so appreciate the education....I thought I wasnít supposed to use the EMS with generators - and - it seems the main purpose of that plug is to help a surge protector bypass the condition that would halt your gennies...so - why do I actually need it?

And if I do need it - is it a matter of just plugging that piece in to one of the outlets in the generator or somewhere in the trailer?

Wide open to learning on this! Thanks!
SteveSueMac is online now   Reply With Quote
Old 06-02-2019, 12:06 PM   #56
3 Rivet Member
 
2018 27' Globetrotter
Mooresville , North Carolina
Join Date: Jan 2018
Posts: 163
Quote:
Originally Posted by SteveSueMac View Post
Yeah. Iím confused about that advice as well.

For whatever itís worth, the Honda 2000 manual includes this statement below - meaning, I *should* be using a ďshoring plugĒ when connected to the trailer? Iíll google that now too....

GROUND SYSTEM
Honda portable generators have a system ground that connects generator frame components to the ground terminals in the AC output receptacles. The system ground is not connected to the AC neutral wire. If the generator is tested by a receptacle tester, it will not show the same ground circuit condition as for a home receptacle.
I am in the same camp as these guys. I would like to know the answer re: the Honda 2000 as well. I thought I had read awhile back that Yamaha generators need the device you are talking about but the Honda does not. Based on all this discussion a definitive answer would be appreciated as my electrical knowledge is limited.
__________________

__________________
2018 GMC Sierra 2500HD Duramax
Equal-I-zer Hitch
"Roadrunner"
GOUSC is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No power to trailer from shore or batteries. Converter fried? MarkHB Batteries, Univolts, Converters & Inverters 7 07-09-2017 04:47 PM
Fried hot water heater diode jimlegs 2006 Safari SE 12 09-09-2012 10:36 AM
Fried trailer wires Monicaro Electrical - Systems, Generators, Batteries & Solar 3 06-28-2011 04:08 PM
Breaker for running lights got fried dickmfield Lights - Interior & Exterior 2 05-06-2010 02:05 PM
Power hitch jack - fried? Toasty's Dad Hitches, Couplers & Balls 9 02-06-2006 10:26 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.