Quote:
Originally Posted by jmsokol View Post
You all have to understand that I get calls and emails from reporters, sheriffs offices and lawyers every time thereís an electrocution death involving an RV. The most heartbreaking ones are the little children who are killed by their parentís negligence. Iím doing all I can to educate manufacturers, dealerships, campgrounds and owners how to manage electricity safely. But itís a big job, and Iím only one guy with zero budget to do it. Please invite me to any regional rallies you might have, and help me find a budget. Thanks... Mike Sokol
Hi Mike

Your seminar was the one I wanted to go to at Alumapoloza. I had to stay at the trailer (Holloway) as the maintenance guys from Airstream were coming to check my trailer for damage. I missed it! Darn!
__________________

__________________
2017 Airstream International Signature 27FB Twin
2019 Airstream Classic 30 Twin

Support Airstream Forum***
turk123 is online now   Reply With Quote
Old 06-15-2019, 07:18 AM   #170
Half a Rivet Short
 
2017 30' Classic
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 7,218
Hi

Hang on a second here.... we toss "code" around like it's some sort of magic single piece of regulation that covers everything and anything you might ever wonder about. There are multiple regulatory agencies out there. They each put out their own rules. If you are hard wired into the electric grid, one set of rules applies. If you connect with a plug ... geee ... I wonder what happens then (rule wise) ...???? .... oh, look, those rules don't apply any more.

Bob
__________________

uncle_bob is offline   Reply With Quote
Old 06-15-2019, 08:13 AM   #171
3 Rivet Member

 
2019 30' Classic
Belen , New Mexico
Join Date: Apr 2011
Posts: 153
Quote:
Originally Posted by uncle_bob View Post
Hi

Hang on a second here.... we toss "code" around like it's some sort of magic single piece of regulation that covers everything and anything you might ever wonder about. There are multiple regulatory agencies out there. They each put out their own rules. If you are hard wired into the electric grid, one set of rules applies. If you connect with a plug ... geee ... I wonder what happens then (rule wise) ...???? .... oh, look, those rules don't apply any more.

Bob
Not to mention that short-term temporary conditions often have exclusions from code (i.e. - construction power at a home being built vs. the power distribution in a home.) I have no idea what codes apply in that jurisdiction, but using non-UV, non-armored cable in a power situation that only lasts a couple of days may not be a code violation even if it would be on a long-term installation.

I suspect, because of the short-term nature of the event, that the code stopped at the main supply panel. Everything after that is up to the event.

I know I attend an event in Oklahoma every year that has special needs for power. The City owned park just mandates that a qualified electrician make all of the changes and that the power is put back in it's original condition afterwards. There is no code that applies, no inspections and no government oversight. They use bare romex zip-tied to support structures for the temporary power runs. The event lasts a week, but the setup team is there three weeks prior. The city officials visit regularly and nary a word is said.
Ephraim is offline   Reply With Quote
Old 06-15-2019, 09:06 AM   #172
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
Quote:
Originally Posted by Ephraim View Post
Not to mention that short-term temporary conditions often have exclusions from code (i.e. - construction power at a home being built vs. the power distribution in a home.) I have no idea what codes apply in that jurisdiction, but using non-UV, non-armored cable in a power situation that only lasts a couple of days may not be a code violation even if it would be on a long-term installation.

I suspect, because of the short-term nature of the event, that the code stopped at the main supply panel. Everything after that is up to the event.

I know I attend an event in Oklahoma every year that has special needs for power. The City owned park just mandates that a qualified electrician make all of the changes and that the power is put back in it's original condition afterwards. There is no code that applies, no inspections and no government oversight. They use bare romex zip-tied to support structures for the temporary power runs. The event lasts a week, but the setup team is there three weeks prior. The city officials visit regularly and nary a word is said.

So the interesting thing is that the National Electrical Code is not an actual law at all. In fact, it's just a really good set of suggestions that can be accepted or rejected by each state. Then each county in a state can choose what parts of the code to accept. And each city can do the same thing. This works all the way down to the local AHJ (Authority Having Jurisdiction) who is your local inspector. He or she has ultimate control over what they will or will not allow to happen in their jurisdiction. But they can be held legally liable is they allow something dangerous in their jurisdiction to occur that results in a loss of life or property. So yes, there are specific sections of code that specify temporary wiring for constructions sites. Also, there are tons of other agencies such as UL who control how generators work, the DOT who controls how big your RV can be on the road, etc... But your local inspector can choose to allow nearly anything to happen temporarily. However, this can have dangerous and deadly consequences if not carefully managed. It sounds like the Alumapalooza event had some dangerous consequences simply because wiring best practices were not followed. For example, you never want to build a power distro system that can become dangerous if someone draws too much amperage. That's what circuit breakers and wire gauge is all about.
jmsokol is offline   Reply With Quote
Old 06-15-2019, 10:55 AM   #173
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,777
Images: 11
Quote:
Originally Posted by OTRA15 View Post
Portable generators connected only to a single RV are generally not grounded.

Any more analysis than that is "analysis paralysis" to this brain.



FWIW


IMHO, when running on a generator, the safety reason for grounding the trailer, and even for bonding the neutral and ground at the source, is for all practical purposes eliminated.
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 06-15-2019, 11:11 AM   #174
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 7,141
My trailer got fried!

Quote:
Originally Posted by J. Morgan View Post
IMHO, when running on a generator, the safety reason for grounding the trailer, and even for bonding the neutral and ground at the source, is for all practical purposes eliminated.


Respectfully disagree from the point of view that Ďfield expedientí power supply setups for events such as Ham Radio Field Day have to be set up for safety. That includes grounding, bonding and proper wiring and circuit protection to generators and loads. Mickey Mousing it is an easy way to kill people.

That said, on a single generator to a single trailer, the main reason I use a bonding plug is to make sure a hot line shorted to trailer shell fault will blow the breaker somewhere instead of potentially zapping me or my family or bystanders.

If I was out for an extended period on generator power, or using my radios a lot, a driven ground to tie down AC power and RF would be the way to go. That gives you safety on the AC power, RF to the antennas, and some electrostatic discharge (read lightning) protection in a field situation.

Iíve also used, seen, and documented how the military does it, and a driven ground rod is part and parcel of Ďdoing it rightí. It saves you from miswired stuff, and trust me, it happens all the time in the field.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 06-15-2019, 11:42 AM   #175
AirDreamer
 
turk123's Avatar
 
2019 30' Classic
Canfield , Ohio
Join Date: Jul 2015
Posts: 1,355
I think what it boils down to is the wiring at Holloway field was not safe. They eventually corrected it, but due to a mishandled hair dryer, the wire nut melted and the box became live. I guess the breaker didn't trip as the hair dryer did not pull over the 20 amp. The short made it trip! Why the wiring smoked is beyond my knowledge, but it did and it damaged 5 trailers. It could have caused more issues.

We were in tornado warnings the first part of the event week and the fields were soggy with rain. The rain was pooling in all the ruts and everywhere you walked it was wet. Not a great scenario for 20 amps laying on the ground.

I sometimes see temporary feeds at festivals and fairs. They use pretty bulky cable most of the time and you don't see Romex on the ground to be tripped on.

I also construct buildings as a land developer. One temp service pole can run $2800 to set up and they have to be inspected when they go up and when they come down. They are up high away from the public, have sealed boxes, and are installed by the electrician. He is responsible for all the issues. Heavy duty extension cords are typically used to run to the building. It cannot be overloaded as each run has a twenty amp circuit. This is much safer than what we saw at JC.
__________________
2017 Airstream International Signature 27FB Twin
2019 Airstream Classic 30 Twin

Support Airstream Forum***
turk123 is online now   Reply With Quote
Old 06-15-2019, 11:48 AM   #176
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
Quote:
Originally Posted by J. Morgan View Post
IMHO, when running on a generator, the safety reason for grounding the trailer, and even for bonding the neutral and ground at the source, is for all practical purposes eliminated.
Correct... thereís no need to earth ground the generator or the RV, and G/N bonding the generator is optional. However electronics like EMS units, some refrigerators and an occasional furnace wonít operate properly with an unbonded neutral. Plus, GFCIís wonít trip without a neutral bond, and testing the 120-volt circuits becomes complicated. Since all RVs with an on-board generator have a G-N bond created by the transfer switch when in generator mode, this is the normal state of operation, and my G-N bonding plug isnít there to fool the EMS, only create the wiring condition itís expecting.
jmsokol is offline   Reply With Quote
Old 06-15-2019, 12:13 PM   #177
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
Quote:
Originally Posted by turk123 View Post
I think what it boils down to is the wiring at Holloway field was not safe. They eventually corrected it, but due to a mishandled hair dryer, the wire nut melted and the box became live. I guess the breaker didn't trip as the hair dryer did not pull over the 20 amp. The short made it trip! Why the wiring smoked is beyond my knowledge, but it did and it damaged 5 trailers.
If there was a proper EGC (ground) in place, then the breaker should have tripped immediately and prevented a hot-skin/contact-voltage. Was this all powered by a big generator or connected to a service panel from the building?
jmsokol is offline   Reply With Quote
Old 06-15-2019, 12:23 PM   #178
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
Quote:
Originally Posted by rmkrum View Post
Respectfully disagree from the point of view that Ďfield expedientí power supply setups for events such as Ham Radio Field Day have to be set up for safety. That includes grounding, bonding and proper wiring and circuit protection to generators and loads. Mickey Mousing it is an easy way to kill people.

That said, on a single generator to a single trailer, the main reason I use a bonding plug is to make sure a hot line shorted to trailer shell fault will blow the breaker somewhere instead of potentially zapping me or my family or bystanders.

If I was out for an extended period on generator power, or using my radios a lot, a driven ground to tie down AC power and RF would be the way to go. That gives you safety on the AC power, RF to the antennas, and some electrostatic discharge (read lightning) protection in a field situation.

Iíve also used, seen, and documented how the military does it, and a driven ground rod is part and parcel of Ďdoing it rightí. It saves you from miswired stuff, and trust me, it happens all the time in the field.
Remember that you donít want to drive a grounding rod anywhere there could be underground wires or plumbing. Iíve heard of a few deaths from that sort of thing. Also, the military didnít earth-ground the shower generator properly at a base in Iraq about 10 years ago, so at least 18 servicemen were electrocuted. Gotta be safe around power. https://www.huffpost.com/entry/toll-rises--at-least-18-u_b_124863
jmsokol is offline   Reply With Quote
Old 06-15-2019, 12:26 PM   #179
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,777
Images: 11
Quote:
Originally Posted by jmsokol View Post
Correct... thereís no need to earth ground the generator or the RV, and G/N bonding the generator is optional. However electronics like EMS units, some refrigerators and an occasional furnace wonít operate properly with an unbonded neutral. Plus, GFCIís wonít trip without a neutral bond, and testing the 120-volt circuits becomes complicated. Since all RVs with an on-board generator have a G-N bond created by the transfer switch when in generator mode, this is the normal state of operation, and my G-N bonding plug isnít there to fool the EMS, only create the wiring condition itís expecting.


It's my understanding that GFI outlets work independent of the ground circuit.

https://www.ecmweb.com/basics/how-gfcis-work

I get that there may be some devices that may want to see the bond, but my trailer uses none of these.

In my thoughts, a trailer running an unbonded generator is actually overall safer than a bonded generator of on bonded shore power, as the chance of the trailer shell completing a circuit (on purpose or by accident) is MUCH reduced.
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 06-15-2019, 12:57 PM   #180
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
Quote:
Originally Posted by J. Morgan View Post
It's my understanding that GFI outlets work independent of the ground circuit.
Yes, if you mean the EGC ground wire which they donít need at all to operate. But a GFCI does need an earth referenced power system to trip. On the other hand a fully floated neutral system like your RV on generator power is really quite safe. But once you distribute power to a second RV or even an electric drill or saw outside of the RV then all kinds of dangerous scenarios are possible.
jmsokol is offline   Reply With Quote
Old 06-15-2019, 01:10 PM   #181
2 Rivet Member
 
Currently Looking...
Hagerstown , Maryland
Join Date: Sep 2010
Posts: 35
FYI here’s something I wrote about GFCI theory which includes some simple diagrams. They’re really very simple once you understand the basics of operation. https://www.rvtravel.com/rv-electric...g-gfci-part-i/
jmsokol is offline   Reply With Quote
Old 06-15-2019, 07:01 PM   #182
AirDreamer
 
turk123's Avatar
 
2019 30' Classic
Canfield , Ohio
Join Date: Jul 2015
Posts: 1,355
I donít have all the details yet, but another Airstream has burned. Seems as if it was in storage and caught on fire. Completely melted.

Sorry for highjacking my own thread, but can this be electrical?
__________________

__________________
2017 Airstream International Signature 27FB Twin
2019 Airstream Classic 30 Twin

Support Airstream Forum***
turk123 is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No power to trailer from shore or batteries. Converter fried? MarkHB Batteries, Univolts, Converters & Inverters 7 07-09-2017 04:47 PM
Fried hot water heater diode jimlegs 2006 Safari SE 12 09-09-2012 10:36 AM
Fried trailer wires Monicaro Electrical - Systems, Generators, Batteries & Solar 3 06-28-2011 04:08 PM
Breaker for running lights got fried dickmfield Lights - Interior & Exterior 2 05-06-2010 02:05 PM
Power hitch jack - fried? Toasty's Dad Hitches, Couplers & Balls 9 02-06-2006 10:26 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:10 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.