Melted Plugs Due to Hot Generator?

My wife has a mobile business out of a '76 Sovereign. Last week we were running the lights and A/C off of our Champion 4750 generator (using propane). The husband of the person running the show thought it would be a good idea to throw a blanket and boxes on top of our generator to muffle the sound. Within an hour, the electricity to the trailer cut off. I went outside to discover the situation. The generator was still running. Luckily nothing caught fire, but it did scorch the plugs where an 30amp extension met the trailer plug. We had to finish the show without lights or A/C. I ended up replacing the plugs this past weekend. The generator is usually running at about 118v under load. Would this have changed due to the heat and caused the current to melt the plugs? I didn't think to check the voltage on the generator when I uncovered it, I was too angry.
__________________

Kevio is offline   Reply With Quote
Old 03-25-2019, 10:03 AM   #2
Rivet Master
 
Al and Missy's Avatar

 
2002 30' Classic S/O
Melbourne Beach , Florida
Join Date: Nov 2013
Posts: 3,275
What was "scorched", the extension cord plug, the generator receptacle, or both? Were the blades of the plug discolored? What do you mean by "scorched"? Were there burn marks, of just melted plastic?

According to the manual for the generator, the 30A receptacles are protected by circuit breakers. Unless the one feeding your cable failed, it seems unlikely that the current exceeded the rating of the plug/receptacle. If the plug/receptacle has burn marks, my suspicion is the plug blades or the receptacle mating parts were corroded, resulting in higher resistance and generating excessive heat at the connection points.

The generator heat might have simply melted the plastic parts, or caused the voltage to go up or down. The voltage is the determining factor. The trailer will draw current that is dependent on the voltage supplied. If the voltage went down, the AC unit would draw more current, but again, the circuit breaker should have tripped to protect the 30A rated wiring. If the voltage went up, the current drawn by the AC would go down until some failure point was reached but it doesn't sound like that was your problem.

A common problem is voltage drop in the extension cable if the wire size is inadequate. This would cause the AC to draw more current, but again the breaker should have tripped.

The only time I have had scorched, as in burned, connectors water got into the junction between the trailer plug and the extension receptacle and shorted hot to neutral. Enough heat was generated without exceeding 30A (in that small space, a few amps of current, 200-300 watts, would have been enough) to heat up and discolor the plastic.

Al
__________________

__________________

"You cannot reason someone out of a position they have not been reasoned into"

Al, K5TAN and Missy, N4RGO
2002 Classic 30 Slideout
S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
2001 Safari 25 RB Twin (Gone, but not forgotten)
WBCCI 1322, TAC FL-39, AIR 82265

Al and Missy is offline   Reply With Quote
Old 03-25-2019, 10:23 AM   #3
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
Thanks for the detailed response! The black wire blade is where the plugs melted. The plug at the generator was fine. It was just where the extension mated. The extension is a 30amp extension cable that is the same thickness as the trailer cable.
Attached Thumbnails
Click image for larger version

Name:	CablesBurned.jpg
Views:	47
Size:	248.1 KB
ID:	336525   Click image for larger version

Name:	PlugsRepaired.jpg
Views:	53
Size:	235.0 KB
ID:	336526  

Kevio is offline   Reply With Quote
Old 03-25-2019, 10:28 AM   #4
Well Preserved
 
overlander63's Avatar

 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 20,812
Quote:
Originally Posted by Kevio View Post
Thanks for the detailed response! The black wire blade is where the plugs melted. The plug at the generator was fine. It was just where the extension mated. The extension is a 30amp extension cable that is the same thickness as the trailer cable.
You had a bad connection at that plug.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 03-25-2019, 10:36 AM   #5
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
But wouldn't it have been the generator that caused it? It seems coincidental that it was fine at the previous show but melted within an hour of this incident.
Kevio is offline   Reply With Quote
Old 03-25-2019, 10:51 AM   #6
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 6,441
Melted Plugs Due to Hot Generator?

Possibly the blankets and other stuff overheated the generator and reduced the output voltage, which led to excess current. However, the damage you showed is most likely to be from an overheated, bad connection. Iíd say time to replace the toasted parts and drive on. Iíd also have a few rather strong words with the bozo that darn near fried your generator by covering it up. His actions could have caused a bad fire.

Also, just because a breaker is marked 30 amps does not mean it will open at exactly 30 amps. They are rated at 30, but it may take a lot more to trip it. They have manufacturing tolerances and are not that precise. The extension cord and plug overheated, yes. But didnít draw enough current to open the breaker. That to me says the connection was marginal. Replace with a heavy duty set is your best bet. If you can get the bozo to pay for the toasted parts, that would be nicer, but highly unlikely IMHO.

Molded plugs and sockets tend to be a bit marginal at best. Your new ones, properly installed, are more likely to survive better. The fact that the generator end isnít toasted points real strong to just the molded connectors that melted being at fault. Also says your generator is rather well built...and any third party that messes with your generator needs to be stopped. I wouldnít put up with that at all.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 03-25-2019, 11:04 AM   #7
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
Great, thanks. That's what I was thinking but since this is all new to me, I wasn't sure. I don't think the plugs were corroded, as the extension was fairly new and the trailer plug was in good shape. I definitely had a few words with the guy but tempered myself out of consideration for my wife's business. He offered to fix it but I wasn't about to let him touch anything considering he didn't know that you shouldn't cover a generator. It could have been a lot worse. Needless to say, we aren't going back to that show.

Would something like this prevent this kind of thing in the future (excluding corroded plugs)?
https://www.amazon.com/Progressive-I.../dp/B015Y9MX38
Kevio is offline   Reply With Quote
Old 03-25-2019, 11:58 AM   #8
Overkill Specialist
 
GMFL's Avatar

 
2014 23' International
Dadeville , Alabama
Join Date: Oct 2015
Posts: 2,511
Images: 4
Blog Entries: 36
It was a bad connection in the cord plugs. Not the generator. Low voltage or high voltage would not be the cause. Loose connections cause arcing of the contacts which work like a welder and burn the contacts up. Covering the generator would not have caused damage to the cord. It might have caused the generator to overheat if not vented damaging the generator, but not the cable. You were pulling around 18 amps and with a loose connection it could easily burn up the plugs.
__________________
Dept of ďOverKillĒ
GMFL is offline   Reply With Quote
Old 03-25-2019, 12:06 PM   #9
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 6,441
Melted Plugs Due to Hot Generator?

A Progressive industries surge protector alone will not do the job. You need a surge protector and EMS combination to monitor for low voltage or excess voltage. They are a bit more expensive than a simple surge protector alone. Highly recommended by the way. Itís a lot safer and detects midwifed connections and kills power to protect trailer and people.

Note that an EMS used with a portable generator needs a jumper plug to connect ground and neutral at the generator to make the EMS protection circuitry work properly.

Most all generators have ground and neutral (green and white wires, usually) floating, and the EMS does not like that and will not pass power on to the trailer. Thatís what itís supposed to do. The bonding plug solves that minor issue.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 03-25-2019, 12:16 PM   #10
CLOUDSPLITTER "Tahawus"
 
ROBERT CROSS's Avatar

 
2003 25' Classic
Zanadude Nebula , Milky Way
Join Date: Jun 2007
Posts: 13,216
Images: 1
I would....

...accept the $$$ offer of the box and blanket guy🥴, buy new quality cords, plugs and never again consider such a noise abatement solution.🤔

Bob
🇺🇸
__________________
"We are all here on earth to help others; what on earth the others are here for I don't know."
W. H. Auden


"The hardest thing about Airstreaming, clearing your head and accepting how others feel itís supposed to be done"Ö..
Amanamus


"Tahawus"
ROBERT CROSS is offline   Reply With Quote
Old 03-25-2019, 12:19 PM   #11
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
So something like this?
https://www.amazon.com/Progressive-I...dp/B01N0W4CZ8/

Are you saying to use a jumper wire from the ground plug of the EMS to the frame or ground wire on the generator?
Kevio is offline   Reply With Quote
Old 03-25-2019, 12:54 PM   #12
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 6,441
Melted Plugs Due to Hot Generator?

Thatís the portable version of the EMS I use. Mine is hardwired in the trailer behind the power panel.

The jumper plug Iím talking about is a standard three prong household plug that fits into a standard duplex outlet.

It has a wire (14-gauge is big enough) inside it jumped from the U-ground (green screw) to the neutral (wide flat prong usually) silver screw. That ties neutral and ground together.

To use it, you merely plug it into any available standard 3-prong plug on the generator. Then neutral and ground are tied together on all the generator connections including the RV-30 socket and the EMS will work right.

If you are not certain how to build one, they can be purchased. I think Camco also sells a pre-built one.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 03-25-2019, 01:04 PM   #13
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
Ah, ok. Thanks for the additional info!
Kevio is offline   Reply With Quote
Old 03-25-2019, 01:07 PM   #14
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 6,441
My pleasure.
__________________

__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot hot hot aluminum! 58cruzer General Repair Forum 23 06-24-2013 01:08 AM
AC just quit working and it's Hot Hot Hot!!! SaabLover Furnaces, Heaters, Fireplaces & Air Conditioning 9 07-27-2010 09:03 PM
How Can it Be? 2 Plugs work, 2 Plugs dont Aluminumb Electrical - Systems, Generators, Batteries & Solar 10 07-27-2009 07:44 PM
Alternator wire melted airstream963 Mechanics Corner - Engines, Transmission & More... 5 05-07-2005 06:46 PM
Melted lens? Rickj Electrical - Systems, Generators, Batteries & Solar 3 01-02-2004 11:17 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:58 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.