Quote:
Originally Posted by aftermath View Post
JimGolden has your solution. Take out the two circuit breakers that go to your garage and replace them with the slim line splits. They will go back into the box leaving you an open space. Use this to place a new 30 Amp breaker and run your line to where you want to install the new outlet.

Make sure you research the size of wire needed to carry the 30 amps through the distance you need. While reading all of this I was wondering how large is the wire that services the circuits in your garage? In home wiring, without special cases or distances, a 15 amp circuit is usually carried on a 14 gauge wire while a 20 amp on a 12 gauge wire. A 30 amp requires a heavier wire and even heavier if going a long distance.

My house was built in 1924 but it did have a "new" 200 amp box installed somewhere in the 70's. We have had a new kitchen done, a new furnace and two new air conditioners. Each time the electrician swapped out the old circuit breakers with the newer splits. Always done to code and always passed. No problems.
This. Use "mini" breakers for the smaller existing circuits to make room for a new single pole 30 amp breaker. Run proper sized conduit and wires. $1000.00 from a licensed electrician doesn't seem out of line, out here anyways.
__________________

__________________
909kenu is offline   Reply With Quote
Old 06-23-2016, 11:18 PM   #58
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 7,239
Images: 18
Blog Entries: 51
Quote:
Originally Posted by rodsterinfl View Post
There is a lot to AC power that many of us do not know. About two years ago someone shared an adapter that they had purchased to use on their generator on the forum. I found that the product had been removed from the market for safety reasons. I too was trying to use both outlets on the generator but my father, mr electric, laughed and talked about how you cannot always do that because of phase and other issues. Don't mix electrical sources he said just remember that ok? So, he started my generator and found that both were actually in phase but regardless he said, it isn't necessary as the generator will output the max to one plug anyway.

Houses are different as are circuits- like a different source. Anyway, I feel for you. Hope the best with the electrician.

Hi, I have one of those orange adapters on my Yamaha 2400 and it works great. If you have a duplex outlet that has one hot, one neutral, and one ground wire connected to it, this will work fine. The advantage that this adapter has is double the connections at the generator and a direct 30 amp connection for the RV cord. Not necessary, but a much better connection than a 30 amp to 15 amp reducer. [a reducer can shake loose, or fall out, due to the weight of the RV cord]

The problem with this adapter, and the reason it was discontinued, was because many contractor generators had separate phases, or separate wires to each outlet. And houses with duplex outlets wired for two different purposes. Common in some houses is a duplex with one outlet that is always hot and the other one is switched for a lamp. Also a duplex under the kitchen sink with one hot outlet for the dish washer and the other one switched for the garbage disposal. These would be very dangerous, but then again, why would anyone use this RV adapter on a inside of your house outlet?????
__________________

__________________
Bob

2005 Safari 25-B
"Le Petit Chateau Argent"
[ Small Silver Castle ]
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 06-24-2016, 09:03 AM   #59
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 1,994
Quote:
Originally Posted by Debit View Post
Here's an option to consider and one that at least has built-in breakers - just in case...

http://www.streambrite.com/images/in...r-power-I6.jpg
I guess my initial post was not thinking so far out of the box afterall...Looks like Steambrite already manufactures something that achieves a similar goal. Pricey though!

http://www.steam-brite.com/mytee-500...0-p-14192.html
__________________
Belegedhel is offline   Reply With Quote
Old 06-24-2016, 09:27 AM   #60
1 Rivet Member
 
1989 34' Excella
Olympia , Washington
Join Date: Mar 2016
Posts: 5
Steambrite does not tell enough about that unit to get me to drop $350.00 on it.

Interesting, the sticker on the thing sort of shows two of them going to one other device.

It may be intended for the pressure washer equipment they sell.
---------------------------------------------------------------
60 years ago my dad taught me;
Do it right, do it once. Do it wrong and you may do it many times before you get it right.

In this case, Please do it right. Then you can relax knowing all is well.
Electricity can be very dangerous, things can literally blow up in your face.
I hold a Federal license in industrial electronics, but I am still cautious inside power panels.
__________________
DaveR-WLYH is offline   Reply With Quote
Old 06-24-2016, 10:22 AM   #61
Overland Adventurer
 
AtomicNo13's Avatar
 
1991 34' Excella
2009 34' Panamerica
Telluride , Colorado
Join Date: May 2012
Posts: 1,718
With no extension cord use, I would be willing you can run your AC and nothing else safely and effectively on a 15 amp plug.
__________________
AtomicNo13 is offline   Reply With Quote
Old 06-24-2016, 10:26 AM   #62
Rivet Master

 
Vintage Kin Owner
Nowhere , Somewhere
Join Date: Jul 2005
Posts: 5,845
Not indefinitely if at all.
__________________
1984 Avion 30p 9.1 meter. 2006 Dodge 3500 cummins srw short bed crew cab.
avionstream is offline   Reply With Quote
Old 06-24-2016, 10:48 AM   #63
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 4,429
Images: 8
We have a 2,000 watt propane converted Honda generator. It has the power to run an air conditioner, but not the power to start it. So, we have a hybrid Magnum MSH-3012 inverter in the 2015 23D International Serenity attached to a 300 amp-hour lithium battery. When the air conditioner starts, the additional power necessary to cover the starting power surge comes from the battery. Pretty slick system.

If plugged into "shore" power, I always have a dedicated 30 amp 120Vac circuit breaker protected outlet to plug the trailer into.

A dryer outlet has two hot legs (thus the 240Vac) and a ground. There is no neutral to let one of the 120Vac legs power some other 120Vac device.

The 50 amp four wire power plug for the dual air conditioner Airstreams has two hot legs, a ground and a neutral. Thus one can have only 120Vac appliances inside the trailer and with careful pre-wiring study, connect the wires so the 120Vac load is close to balanced across the two hot legs.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic model 30 twin beds, 50 amp service, 900 watt solar system, Centramatics, Dill TPMS, disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 06-24-2016, 01:24 PM   #64
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 1,994
Quote:
Originally Posted by AtomicNo13 View Post
With no extension cord use, I would be willing you can run your AC and nothing else safely and effectively on a 15 amp plug.
Interestingly, last summer I plugged my power lead into the wall outlet in the garage with only a ~10" long adapter in the system. In my dim recollection, it seems like I could run the AC for a couple hours at a time before the little adapter plug would get rather warm and cause the 20A breaker to pop. This year, if I plug the trailer into that same outlet with same little adapter, it will trip the 20A breaker in a matter of a few minutes. I thought maybe my AC was getting sticky having not been run since last summer, so I ran it for a few hours on a pair of Honda eu2000i gennies. These gennies will run the AC just fine in "eco" mode, which sounds like they are at about half throttle--not sure how much the rated output is in this mode. Anyway, I tried plugging into the wall again after running on the gennies a while, but still no dice.

I noticed that the exhaust from the gennies killed some rather large patches of grass on my lawn, thus I started thinking of a jury-rig solution, and thus began this thread.
__________________
Belegedhel is offline   Reply With Quote
Old 06-24-2016, 01:43 PM   #65
3 Rivet Member
 
2015 25' FB Flying Cloud
Sandy , Utah
Join Date: May 2015
Posts: 107
I understand from some of the posts that you may be moving and are reluctant to spend the money. I understand that completely. I run my generators when I want to work inside the trailer in the summer. It seems the money may be better spent put toward buying generators which will go with you when you move.
__________________
rocco52 is offline   Reply With Quote
Old 06-24-2016, 01:56 PM   #66
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 1,994
My trailer is completely empty (as a result of a multi-year full-monty), and I am finally at the point of building out the cabinetry, running the pex, and so on. So being able to run the AC just for this summer, will help me to get a lot of work done. Once the rebuild is finished, I expect that it will be fairly rare that I want to run the AC for hours at a time at the house, in which case, the Honda gennies will be just fine.

With all the cash I have invested so far in the trailer, you wouldn't think that spending $1000 on electrical work would cause me to blink, but heck, if it were easy for me to part with my cash, I wouldn't be rebuilding a trailer from scratch in the first place!

Just when I thought the oilfield was a precarious enough industry to work in, it would appear that the global financial house of cards is collapsing due at least in part to a significant card removed from the middle of the deck (thank you, Brexit). So my penny-pinching nature makes it that much harder to invest very much cash in a feature that the next owner of my house may have no use for.
__________________
Belegedhel is offline   Reply With Quote
Old 06-24-2016, 02:15 PM   #67
Rivet Master
 
HowieE's Avatar

 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,522
Images: 12
Quote:
Originally Posted by Belegedhel View Post
Interestingly, last summer I plugged my power lead into the wall outlet in the garage with only a ~10" long adapter in the system. In my dim recollection, it seems like I could run the AC for a couple hours at a time before the little adapter plug would get rather warm and cause the 20A breaker to pop. This year, if I plug the trailer into that same outlet with same little adapter, it will trip the 20A breaker in a matter of a few minutes. I thought maybe my AC was getting sticky having not been run since last summer, so I ran it for a few hours on a pair of Honda eu2000i gennies. These gennies will run the AC just fine in "eco" mode, which sounds like they are at about half throttle--not sure how much the rated output is in this mode. Anyway, I tried plugging into the wall again after running on the gennies a while, but still no dice.

I noticed that the exhaust from the gennies killed some rather large patches of grass on my lawn, thus I started thinking of a jury-rig solution, and thus began this thread.
Running your AC on low voltage for a longer time, which you did, most likely did damage to the AC and likely the breaker also.

The older AC had a low voltage warning light to prevent this.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 06-24-2016, 02:20 PM   #68
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 1,994
Curses!
__________________
Belegedhel is offline   Reply With Quote
Old 06-24-2016, 09:07 PM   #69
Rivet Master
 
DavidsonOverlander's Avatar

 
1964 26' Overlander
1974 31' Sovereign
Milton , ON
Join Date: Oct 2002
Posts: 688
Images: 4
Quote:
Originally Posted by switz View Post
A dryer outlet has two hot legs (thus the 240Vac) and a ground. There is no neutral to let one of the 120Vac legs power some other 120Vac device.
I don't want to pull out my dryer to check, but I thought there were four connectors. Two hot, a neutral and a ground. Doesn't the dryer motor run on 120 volts? I think older dryers had three wires and newer ones have four.
__________________
Grant Davidson
Milton, ON

1946 Spartan Manor
1954 Va-Ka-Shun-Ette
1964 Overlander
1965 Avion C-10 Truck Camper
1974 Sovereign
2005 F-350 SRW 4x4 crew cab long box
TAC ON-5
DavidsonOverlander is online now   Reply With Quote
Old 06-24-2016, 09:18 PM   #70
Rivet Master
 
DavidsonOverlander's Avatar

 
1964 26' Overlander
1974 31' Sovereign
Milton , ON
Join Date: Oct 2002
Posts: 688
Images: 4
Quote:
Originally Posted by JimGolden View Post
Why not simply change a few of his regular sized breakers to slim line breakers? Then you free up room in the main panel to install a 30amp or 50amp breaker and run the appropriate sized wire to the new outlet.

Sub panel is nice, but I'd look at slim lines before I went to that trouble.
You'd need to check your panel to see how many circuits are allowed. Just because you can put in a slim line or tandem breaker doesn't mean that it's allowed within the capacity of your panel.
__________________

__________________
Grant Davidson
Milton, ON

1946 Spartan Manor
1954 Va-Ka-Shun-Ette
1964 Overlander
1965 Avion C-10 Truck Camper
1974 Sovereign
2005 F-350 SRW 4x4 crew cab long box
TAC ON-5
DavidsonOverlander is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rigging Up A Solar Trickle Charger Chuhhuniban Electrical - Systems, Generators, Batteries & Solar 1 03-28-2016 04:29 PM
Long Term Shore Power and House Battery cbrittan Batteries, Univolts, Converters & Inverters 30 11-02-2015 01:15 AM
jury duty mykabyka Full-Timing 10 09-15-2013 06:40 PM
Air Conditioner tripping breaker in my house while on shore power Wgbarrbevco General Repair Forum 10 08-16-2012 06:07 PM
Shore power and battery power problems jfremstad Electrical - Systems, Generators, Batteries & Solar 5 05-03-2007 08:23 AM


Virginia Campgrounds

Reviews provided by



Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.