Another consideration that no one has mentioned is, assuming you actually do have two outlets on two separate breakers in the garage, they may be on different legs of the 120/240 service. Are the breakers in the same vertical row in the breaker box? If not they are different phases and connecting them together will short your 240 volts and blow both breakers (if you are lucky).

While what you have suggested is unconventional, and may violate the building code, I'm not sure there is any particular risk. This is not unlike connecting the output of two Honda (or Yamaha) generators in parallel to get twice the capacity. Each generator has an output breaker, connecting the two in parallel gives twice the capacity. The special circuitry in the generators synchronizes the two, but that is not required in this case because the two breaker outputs are in phase (if they are on the same side of the breaker panel as mentioned above). The only problem is that the two circuits may not equally share the load and you could pop the breaker in the circuit that is carrying more load and then guarantee that the other breaker would pop.

That said, your safest option is to have a licensed electrician hook up something for you. The suggestion to add a sub-panel would be the least expensive. You could save some more money by renting a trencher and digging the ditch for burial of the cable yourself.

Al
__________________

__________________

"You cannot reason someone out of a position they have not been reasoned into"

Al, K5TAN and Missy, N4RGO
2002 Classic 30 Slideout
S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
2001 Safari 25 RB Twin (Gone, but not forgotten)
WBCCI 1322, TAC FL-39, AIR 82265

Al and Missy is offline   Reply With Quote
Old 06-22-2016, 09:15 PM   #16
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 2,608
When it's electrical power, it's far safer to do it right. Jury-rigging stuff with AC power can bite hard, or burn your house down.

Better to bite the bullet and do it right.


Sent from my pocket Internet using Airstream Forums
__________________

__________________
KE4GNK/AE
'The Silver HamShack' (2007 International 22FB CCD 75th Aniversary model)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch
2012 shortbed crewcab 4x4 Toyota Taco TV with more antennae on it
rmkrum is offline   Reply With Quote
Old 06-22-2016, 09:42 PM   #17
Agent 86
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 4,368
Images: 11
Jury-rigging shore power at the house

The sub panel idea mentioned above is what I would do.

Simple, easy, cheap, safe, DONE.


Superat stultitia.
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 06-23-2016, 07:26 AM   #18
Zil
3 Rivet Member
 
Vintage Kin Owner
Currently Looking...
egg harbor city , South Jersey
Join Date: Apr 2014
Posts: 200
Quote:
Originally Posted by markdoane View Post
I guess I would rate this the #1 idea of the month. At least OP asked the question.

Use Aerowood's method.
A sub panel would be next best to larger main panel. How ever, in my service, I have three light circuits that could be safely combined. In any case, a knowledge of electricity is required. Ask another electrician about your case.
__________________
Zil is offline   Reply With Quote
Old 06-23-2016, 08:20 AM   #19
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 7,239
Images: 18
Blog Entries: 51
Quote:
Originally Posted by kokopat View Post
Have you utility company put in another service with meter at the garage. I'm sure they want it done correctly.


Hi, in the long run this would be the best idea. At 50 yards, that's just too much wire for a heavy load. [move the garage closer to the house]
__________________
Bob

2005 Safari 25-B
"Le Petit Chateau Argent"
[ Small Silver Castle ]
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 06-23-2016, 08:46 AM   #20
Rivet Master
 
AWCHIEF's Avatar
 
2006 23' Safari SE
Biloxi , Mississippi
Join Date: Nov 2011
Posts: 7,805
Images: 33
I had my exterior 30 amp outlets built to code. Not worth chancing the wrath of the gods.
__________________
MICHAEL

Do you know what a learning experience is? A learning experience is one of those things that says "You know that thing that you just did? Don't do that."
AWCHIEF is offline   Reply With Quote
Old 06-23-2016, 09:24 AM   #21
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 2,108
Thanks all for your feedback. I had another look at my breaker box last night, and it turns out that both breakers for the two circuits going to the garage are located on the same breaker "block" (ie., there is a single breaker unit that has two breaker switches on it), so there should be no worries about phases, etc.. I thought it was two 15A breakers, but in fact they are 20A each. I thought about it some more, and think I have found the real danger in the plan.

As a thought experiment, lets take the jury rigged pigtail arrangement out of the equation and imagine just hard-wiring a female 30 amp plug where the two sets of wires for the two circuits enter the garage, combining the inputs as described earlier. If I plug my trailer into this plug, theoretically the two circuits will share the 30A load, roughly equally assuming wire lengths are the same and overall resistances are the same. The problem is that those circuits will continue out of the 30A plug (where they are joined), one of them supplying lights, and the other supplying outlets in the garage. If I plug my mal-functioning circular saw into an outlet and the motor windings are in a dead short, it will try and pull all the current it can through the circuit. Since the outlet circuit combines with the light circuit at the 30A plug, the breakers won't pop until they see a combined 40A load. This 40A dead-short max load will be seen by the 20A max capacity wiring that goes from the 30A plug to the outlet that the saw is plugged into, and here is where the fire danger lies, when that wiring melts. I could defeat this by installing a secondary set of breakers within the garage, in between the 30A plug and the two garage circuits, but it is still a jury rig, definitely wouldn't meet code.

Another option might be to replace my garage circuit breaker with a 50A breaker, wire that to a sub-breaker box, and then put the two 20A circuits and the 30A circuit breakers in that box. This would still require running the additional 30A wiring out to the garage, though. I guess I'll see if I can find an electrician with a more creative/cost effective solution than the first one I consulted.
__________________
Belegedhel is offline   Reply With Quote
Old 06-23-2016, 09:34 AM   #22
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 6,680
Images: 12
Quote:
Originally Posted by Belegedhel View Post
Thanks all for your feedback. I had another look at my breaker box last night, and it turns out that both breakers for the two circuits going to the garage are located on the same breaker "block" (ie., there is a single breaker unit that has two breaker switches on it), so there should be no worries about phases, etc.. I thought it was two 15A breakers, but in fact they are 20A each. I thought about it some more, and think I have found the real danger in the plan.

As a thought experiment, lets take the jury rigged pigtail arrangement out of the equation and imagine just hard-wiring a female 30 amp plug where the two sets of wires for the two circuits enter the garage, combining the inputs as described earlier. If I plug my trailer into this plug, theoretically the two circuits will share the 30A load, roughly equally assuming wire lengths are the same and overall resistances are the same. The problem is that those circuits will continue out of the 30A plug (where they are joined), one of them supplying lights, and the other supplying outlets in the garage. If I plug my mal-functioning circular saw into an outlet and the motor windings are in a dead short, it will try and pull all the current it can through the circuit. Since the outlet circuit combines with the light circuit at the 30A plug, the breakers won't pop until they see a combined 40A load. This 40A dead-short max load will be seen by the 20A max capacity wiring that goes from the 30A plug to the outlet that the saw is plugged into, and here is where the fire danger lies, when that wiring melts. I could defeat this by installing a secondary set of breakers within the garage, in between the 30A plug and the two garage circuits, but it is still a jury rig, definitely wouldn't meet code.

Another option might be to replace my garage circuit breaker with a 50A breaker, wire that to a sub-breaker box, and then put the two 20A circuits and the 30A circuit breakers in that box. This would still require running the additional 30A wiring out to the garage, though. I guess I'll see if I can find an electrician with a more creative/cost effective solution than the first one I consulted.
I am going to assume you are attempting to create a fictional episode for a comedy TV show here. If so please sign your comments with a disclaimer, or as Rube Goldberg, as there may be some readers that may see this as possible and follow suit.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 06-23-2016, 09:41 AM   #23
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 6,756
Images: 59
The option in your last paragraph may be feasible, but you should get an electrician to calculate the wire size for the 30a run out to the garage.
Also check with your local building inspector. You will need a permit and they will be able to tell you any local requirements and maybe a cheaper alternative.
__________________
markdoane is offline   Reply With Quote
Old 06-23-2016, 11:29 AM   #24
2 Rivet Member
 
1968 22' Safari
Tulsa , Oklahoma
Join Date: Oct 2015
Posts: 80
Terminology

BTW, jerry-rigging is an approach. Jury-rigging is a crime.

I'm just saying'...

Jay and Lisa
__________________
splyb is offline   Reply With Quote
Old 06-23-2016, 11:52 AM   #25
4 Rivet Member
 
1973 31' Sovereign
Middletown , California
Join Date: Oct 2015
Posts: 400
I always say living in a trailer is life at the end of an extension cord. Getting enough power for me to stay comfortable is a bit of an art form as the 15A to 30A adapters melt if you look at them hard. It's hard to say much about your situation without knowing exactly what is there because details count when dealing with electricity. From what you have shared so far it seems like you have 2 hots and maybe 2 neutrals running to the garage. How do the wires enter the garage, is there a junction box that you can look into? What do you see in there? How much would you spend to have AC? Breakers are sized to protect the wires and usually 20A breakers go with # 12 wire and for a long run like you have I wouldn't try to pull more than 15A per hot wire. There is hope but meeting code could be tricky so you need an electrician that knows what they are doing. Maybe send 220 to a transformer and sub panel in the garage? A sub panel with breakers for the garage circuits? There is probably a way to get the job done safely.
__________________
ijustlee is offline   Reply With Quote
Old 06-23-2016, 11:58 AM   #26
2 Rivet Member

 
2004 30' Land Yacht 30 SL
Surprise , Arizona
Join Date: Feb 2016
Posts: 23
I had the same problem and fixed it with adjusting the breakers in the box so that I could open up 30 amp service. I had the installer put an outside 30 amp plug just below the box and then bought a 50ft male to female 30amp extension to go to my RV which has to be in the street (driveway to short). This has worked very well except for 1 day when the outside weather was at 120deg (AZ). The cord got so hot in the sun it tripped the coach breaker for the ac unit. I kill the breaker at the box when not in use (I have an outside box so it is a weather protected outlet). This was a lot cheaper than having the installer run conduit. Just a note, I also looked at trying to use something makeshift and was quickly talked out of it. If you can move some loads around in your box and not create a fire hazard I think this is a great solution.
__________________
C21Tiger is offline   Reply With Quote
Old 06-23-2016, 12:07 PM   #27
Rivet Master
 
jdalrymple's Avatar
 
2009 27' FB Flying Cloud
1991 35' Airstream 350
Jay , Oklahoma
Join Date: Oct 2006
Posts: 1,541
A quick wire calculation says 30 amps of single phase 120 volt AC at 150' requires 4 gauge wire.

150' seems like a long measurement, even for a long, skinny home.

Measure and make sure that the 50 yard estimate is correct. The re-arrangement of breakers and/or the addition of a sub panel are acceptable methods to add circuits.

The combining of receptacles via extension cords is not.


Regards,

JD
__________________
Jeff & Cindy
'09 27FB Flying Cloud
'91 350 LE MH
jdalrymple is offline   Reply With Quote
Old 06-23-2016, 12:11 PM   #28
Agent 86
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 4,368
Images: 11
http://www.ecmag.com/section/systems...ected-parallel


Superat stultitia.
__________________

__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rigging Up A Solar Trickle Charger Chuhhuniban Electrical - Systems, Generators, Batteries & Solar 1 03-28-2016 04:29 PM
Long Term Shore Power and House Battery cbrittan Batteries, Univolts, Converters & Inverters 30 11-02-2015 01:15 AM
jury duty mykabyka Full-Timing 10 09-15-2013 06:40 PM
Air Conditioner tripping breaker in my house while on shore power Wgbarrbevco General Repair Forum 10 08-16-2012 06:07 PM
Shore power and battery power problems jfremstad Electrical - Systems, Generators, Batteries & Solar 5 05-03-2007 08:23 AM


Virginia Campgrounds

Reviews provided by



Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:52 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.