Installing an outdoor outlet

not really for the "trailer", but I know that some of you have installed 30-amp to your trailer's parking spot. So I thought I'd ask the collective:

I want to run a wire to my tool shed. standard 110/120 volt 15 or 20 amp outlet so that I can have an overhead light/plug in a power tool occasionally...and use the electric start on my snowblower. the shed is about 80 feet away from my foundation. I have an outlet in mind into which I can tie this circuit. what do I need to do?

bury a wire from the house to the shed: how deep does it need to be? what kind of wire? 12/2? does it need to be in a conduit? if so, what kind?

I'm thinking I'll install a single weather-proof outlet on the oustide of the shed; then run the wire inside for a single outlet, then to a switch, and to an overhead light. Should this shed be grounded separately from the house's grounding system?

I may want to run 30 amps to the trailer's parking spot, too (also about 80 feet away), but that would require a sub-panel and so forth. But If I have to rent an expensive trenching tool for the shed project...might as well bury a wire for the trailer, too, even if I don't actually connect anything until a later date.
__________________

__________________
Air:291
Wbcci: 3752
'73 Safari 23'
'00 Dodge Ram 1500 4x4 QC
Chuck is offline   Reply With Quote
Old 11-08-2004, 02:49 PM   #2
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
Around here, utilities are buried 18 inches below ground. I believe that is also the frost line.

For a simple outlet, home improvement stores sell wire rated to be buried without having to be encased in conduit. Your trailer's shore power might be a different story.

Here's one idea: Rent the trencher, and dig both trenches. Bury the outlet wire in one trench, and bury the right size conduit in the shore power trench. Finishing the project can be done at a later date.

Tom
__________________

__________________
TomW is offline   Reply With Quote
Old 11-08-2004, 03:44 PM   #3
Patriotic
 
Chuck's Avatar

 
1973 23' Safari
North of Boston , Massachusetts
Join Date: May 2002
Posts: 4,533
Images: 260
Quote:
Originally Posted by tcwilliams
Around here, utilities are buried 18 inches below ground. I believe that is also the frost line.

For a simple outlet, home improvement stores sell wire rated to be buried without having to be encased in conduit. Your trailer's shore power might be a different story.

Here's one idea: Rent the trencher, and dig both trenches. Bury the outlet wire in one trench, and bury the right size conduit in the shore power trench. Finishing the project can be done at a later date.

Tom
yeah, that's just what I was thinking. rent a trencher, do both, hook up the other one later. but I need to know the right kind of wire, and how deep, first.
18"?? frost line is 4 FEET here. I don't think we have to dig that deep. at least, I hope not.

(we DO have to dig that deep to put in a deck, or other outside structure requireing a footing or foundation. mighty big PITA.)
__________________
Air:291
Wbcci: 3752
'73 Safari 23'
'00 Dodge Ram 1500 4x4 QC
Chuck is offline   Reply With Quote
Old 11-08-2004, 05:45 PM   #4
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
chuck,

here is a wire size calculator http://www.pljohnson.com/electrical/...voltdrop.shtml

as you will see you want #6 awg for the 30 amp circuit and # 8 for the 20 amp circuit. assuming both runs are 80 feet one way, from the breaker box.

direct bury romex is o.k. unless you have rocky soil, then you should use conduit. tip, a cheap way is to put the wire inside black courragated drain tube for most of the run. it is cheap and is what we do at the power company when we install a service to a house in rocky soil. otherwise backfill the trench with screened sand. believe me you don't want to try to dig up a faulted cable because a rock severed it due to frost heave!

primary conductors (over 480 volts) are installed at 30 inches, secondary conductors (0 to 480 volts) are installed at 24 inches in depth.

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 11-08-2004, 05:56 PM   #5
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 6,940
Images: 59
Chuck,

I think you can go shallower if you use rigid conduit. Where I live, the rules are:
24" for UF rated wire
18" for PVC conduit
6" for rigid conduit

You should place a warning tape 12" above the feeder. You also need to switch to rigid conduit where the feeder comes out of the ground.
__________________
markdoane is offline   Reply With Quote
Old 11-08-2004, 06:36 PM   #6
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
Quote:
Originally Posted by john hd
...primary conductors (over 480 volts) are installed at 30 inches, secondary conductors (0 to 480 volts) are installed at 24 inches in depth...
Chuck,

I have no doubt that John is right, but I can almost guarantee (99.99%) that there is no more than 240 vac running to your house. And you only need 120 vac for either of your intended goals.

Also, bear in mind that voltage drops (see John's table link) are with respect to the main breaker box, not where you tie into an exisiting circuit.


Tom
__________________
TomW is offline   Reply With Quote
Old 11-08-2004, 09:44 PM   #7
4 Rivet Member
 
Join Date: Jan 2004
Posts: 472
Images: 17
Send a message via Yahoo to silver suz
I do reccommed putting the wire in pvc pipe so you don't cut it with a shovel some years later. We learned that the hard way. silver suz
__________________
silver suz is offline   Reply With Quote
Old 11-09-2004, 08:53 AM   #8
Patriotic
 
Chuck's Avatar

 
1973 23' Safari
North of Boston , Massachusetts
Join Date: May 2002
Posts: 4,533
Images: 260
Quote:
Originally Posted by markdoane
Chuck,

You should place a warning tape 12" above the feeder.
What's that mean?

Quote:
Originally Posted by markdoane
You also need to switch to rigid conduit where the feeder comes out of the ground.
I'm assuming that "rigid" means "metal"? pvc pipe seems pretty "rigid", to me.

Thanks for all the other tips, folks. yes, there is 240v service to the house. and I DO have very rocky soil. hadn't thought of that issue, so I'd better plan on using conduit.

I'll double check the measurements, too. probably closer to 100' away from the breaker box.

I'll of course, consult a local electrician before I do anything, just to make sure I don't do anything that's way out of code. But at this point, I'm just kicking the idea around.....gotta find out what it'll cost me, etc, etc.
__________________
Air:291
Wbcci: 3752
'73 Safari 23'
'00 Dodge Ram 1500 4x4 QC
Chuck is offline   Reply With Quote
Old 11-09-2004, 09:43 AM   #9
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 2,918
Images: 2
Warning tape, available at home centers, is colored plastic tape with no adhesive with the words "Warning - buried pipe" or something similar. The color is based on the type of pipe (gas,water,electric). The hope is that someone will dig up the tape before hitting the pipe if they were not expecting to find a pipe where they were digging.

Tom
__________________
TomW is offline   Reply With Quote
Old 11-09-2004, 04:27 PM   #10
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
Quote:
Originally Posted by tcwilliams
Warning tape, available at home centers, is colored plastic tape with no adhesive with the words "Warning - buried pipe" or something similar. The color is based on the type of pipe (gas,water,electric). The hope is that someone will dig up the tape before hitting the pipe if they were not expecting to find a pipe where they were digging.

Tom
tom/chuck

warning tape is a good idea, however, it has been my experiance that most dunderheads running backhoes etc. will never see it before it is too late!

i have heard every excuse in the book from these guys, ranging from " i didn't think anyone would ever bury electric on the lot line " to " i thought you guys always buried your wire way deeper than that" or "what diggers hotline?"

the result is always the same, a big friggin bill from the friendly power company!

only once have i seen the operator do the "crappie flop" on the ground after taking a shot of 7.2 KV! guy was lucky he wasn't dead!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 11-09-2004, 04:38 PM   #11
Patriotic
 
Chuck's Avatar

 
1973 23' Safari
North of Boston , Massachusetts
Join Date: May 2002
Posts: 4,533
Images: 260
Quote:
Originally Posted by john hd
tom/chuck


only once have i seen the operator do the "crappie flop" on the ground after taking a shot of 7.2 KV! guy was lucky he wasn't dead!

john
you're gonna have to explain that one
__________________
Air:291
Wbcci: 3752
'73 Safari 23'
'00 Dodge Ram 1500 4x4 QC
Chuck is offline   Reply With Quote
Old 11-09-2004, 04:42 PM   #12
Rivet Master
 
Ken J's Avatar
 
1956 22' Flying Cloud
Durango , Colorado
Join Date: Sep 2002
Location: 1975 25' Tradewind
Posts: 3,363
Images: 14
You may not want to know.......... its not pretty if you get my drift


Ken
__________________
1956 Flying Cloud
Founder :
Four Corners Unit
Albuquerque National Balloon Fiesta
Rally
Vintage Trailer Academy - Formerly the original
restoration rally
Ken J is offline   Reply With Quote
Old 11-09-2004, 06:21 PM   #13
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
chuck

a "crappie" is a panfish, when ice fishing you pull them out of the hole. then they flop around on the ice.

that is what the guy was doing...flopping around on the ground!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 11-09-2004, 09:22 PM   #14
4 Rivet Member
 
Join Date: Jan 2004
Posts: 472
Images: 17
Send a message via Yahoo to silver suz
Don't worry, in 5 years you will have no rememberance where that line is run. My husband even makes a map measuring from known points as to where it is and then I come along and decide to plant a tree. oops. wood handle was a good thing. Those warning tapes are kind of useless. silver suz
__________________

__________________
silver suz is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing a Zip Dee awning DavidsonOverlander Awnings 2 09-20-2004 08:59 AM
Installing soil stack covers Will Ackerman Roof Vents, Skylights & Fans 4 09-11-2004 07:20 PM
Installing carpet M&J Siegford Repairing/Replacing Floor &/or Frame 13 04-17-2004 02:55 PM
Installing roof AC. Need a sealant nds Clearcoat, Exterior Paint & Trim 8 07-22-2003 07:33 PM
Removing Old Univolt & Installing New Intellipower 9160 montanaandy Electrical - Systems, Generators, Batteries & Solar 3 07-15-2003 12:08 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.