My restored old Tradewind trips GFCI's if the shore power cable is plugged in to them. I know that this is a fairly common problem.

From what I read, the usual culprit is a ground rail that's bonded to the neutral bus. My problem persists, however, when all of the branch circuit breakers are turned off. From this I figure that the issue is somewhere "central" in the vicinity of the inverter/charger or the batteries.

Anyway, here's the question: Assuming that the problem is bonding, can I just do the old dodge of plugging in with a 3-to-2 connector? It seems to me that this would solve the GFCI problem, because any "ground-faulted" current ends up in the neutral limb anyway. But I'm not sure how bad the consequence of an overall-ungrounded trailer would be. Anybody know?

Thanks!

(Actually, I found this problem out when camping at a state park with GFCI-protected breakers on the 30 A connectors. How rude is that??)
tlsmit1 is offline   Reply With Quote
Old 09-14-2013, 09:12 AM   #2
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
It's often a bad idea to plug a trailer with GFCI circuits into a GFCI shore power pedestal. The "upstream" (pedestal) GFCI can mistakenly recognize the internal circuitry of the trailer's GFCI as a fault.

BTW: Two GFCIs in series offers no more protection than does one GFCI all by itself.

Two work-arounds:
1 - Don't plug into a GFCI-protected pedestal; or
2 - Plug into the GFCI pedestal, but switch off the GFCI breaker in your trailer and don't use that circuit.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 09-14-2013, 09:16 AM   #3
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
If you remove the ground path from the supply chord it is dangerous.

If you really have a short to ground, this means a current carrying wire is touching either a ground wire or some portion of the metal body. When you remove the ground from the supply chord there is no where for a short current to flow, until a person standing on the outside of the trailer touches a metal portion of the trailer. Then that person becomes the ground, the current will flow through that person.

That is precisely what a ground fault breaker is designed to prevent.

To check for a bonded ground: Unplug first, then look inside the breaker box to see if there are two bars that look like the image below. All neutral, white, wires should connect to one. All ground, bare copper and green, wires should connect to the other. If any are on the wrong bar that is the trouble. The bar where all the white wires connect might have a screw that bonds it to the metal breaker box. That is a bonding screw. If this screw has not been removed that could be the problem. If there is only one bar, instead of two, where grounds and neutrals are connected, that is the problem.

Get help if you do not understand this!!!!
Attached Images
 
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 09-14-2013, 09:18 AM   #4
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 6,408
Images: 2
Blog Entries: 2
Sad to choose one circuit or the other.

There is "one" way to work around....if you are capable and assume all risk.

Get a breaker of same type minus the GFCI feature, just a standard breaker.

When in park with that feature on pedestal, swap the breaker to non-GFCI.

I suppose it is "good news" thAt the campground is safer?????
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 09-14-2013, 10:49 AM   #5
Maniacal Engineer
 
barts's Avatar
 
1971 25' Tradewind
Lopez Island , Washington
Join Date: Jan 2010
Posts: 1,244
Images: 1
Blog Entries: 4
One way of quickly determining whether or not the ground and neutral are bonded together is to unplug the trailer, flip off the breakers and then check for continunity (a connection) between ground and neutral with a DVM. There should be no connection.

If you have only one bus bar in the box for both neutral and ground, you or an electrician can add another.

Note that only main entrance panels that have a real connection to ground should connect neutral and ground.

In a campground, the neutral line will _not_ be exactly at ground potential, particularly when there is heavy current draw due to ACs, etc; there will be a voltage drop in the neutral line just as there is in the hot line, so it is not uncommon to see the neutral a few volts above ground.

Of course, if your Airstream connects ground and neutral together, several amps of current will flow as the ground connection takes part of the AC load - and the gfci outside will immediately trip.

- Bart
__________________
Bart Smaalders
Lopez Island, WA
https://tinpickle.blogspot.com
barts is offline   Reply With Quote
Old 09-14-2013, 11:06 AM   #6
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
BTW, it is fairly unusual for a 30 amp park outlet to be GFI protected. It is not a code requirement on the 30 amp ones, but is a code requirement on the 15 and 20 amp outlets. I have only seen a few 30 amp ones GFI protected.

That said, if more 30 amp outlets were GFI protected, you would hear/see/experience a whole lot more RV's with this issue of GFI tripping.

I actually feel that GFI protected 30 amp RV park outlets would be an excellent safety addition, but sure would cause a lot of hair pulling among park owners and RV owners.
idroba is offline   Reply With Quote
Old 09-14-2013, 11:35 AM   #7
Maniacal Engineer
 
barts's Avatar
 
1971 25' Tradewind
Lopez Island , Washington
Join Date: Jan 2010
Posts: 1,244
Images: 1
Blog Entries: 4
Quote:
Originally Posted by idroba View Post
I actually feel that GFI protected 30 amp RV park outlets would be an excellent safety addition, but sure would cause a lot of hair pulling among park owners and RV owners.
While at Burning Man this year, our neighbor's converted bus was tripping the 20A GFI on the spider boxes (power distrib. boxes) we were using.. turned out to be the usual bonded neutral/ground problem.

Carrying a full set of adaptors, and debugging these sorts of problems at home is definitely the way to go for more relaxed traveling .

With all LED lighting, our trailer works quite nicely w/ just a 20A circuit, even with the AC running.

- Bart
__________________
Bart Smaalders
Lopez Island, WA
https://tinpickle.blogspot.com
barts is offline   Reply With Quote
Old 09-14-2013, 08:06 PM   #8
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
Quote:
Originally Posted by A W Warn View Post
To check for a bonded ground: Unplug first, then look inside the breaker box to see if there are two bars that look like the image below. [snip]
Get help if you do not understand this!!!!
The thing is, the pedestal GFCI will trip even if all of the trailer's branch circuits are flipped to "off". So there can't possibly be a path from the output of the inverter/charger through to neutral and/or ground.

But of course the inverter/charger is a load itself. And I don't really understand the innards of the inverter / charger. Because this device sits between the pedestal's GFCI and the breaker box, it is obviously still in the circuit even if all of the trailer's breakers are switched off. So, the question is: can the pedestal GFCI still get tripped by a bonded breaker box with an inverter in the middle, even with all of the branch circuits switched off? Or not?

If not, I would need to look for the fault elsewhere.
tlsmit1 is offline   Reply With Quote
Old 09-14-2013, 08:16 PM   #9
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
Quote:
Originally Posted by A W Warn View Post
If you remove the ground path from the supply chord it is dangerous.

If you really have a short to ground, this means a current carrying wire is touching either a ground wire or some portion of the metal body. When you remove the ground from the supply chord there is no where for a short current to flow, until a person standing on the outside of the trailer touches a metal portion of the trailer. Then that person becomes the ground, the current will flow through that person.

That is precisely what a ground fault breaker is designed to prevent.
But in a bonded trailer, the skin and all the other bits are in continuity with the neutral pin of the supply cable. So there *is* somewhere for the current to go: out the neutral.

I'm certainly not arguing that GFCI's don't make things safer. Of course they do. But a bonded trailer can't be protected by a GFCI'd supply line. The real question that I'm asking is *if* a trailer has a bonded ground, is it made any less safe by removing the ground pin from the supply line? And if so, why?

Seems to me that it might be less safe if the neutral weren't actually at 0 V, but I don't know if this is ever true, or not.
tlsmit1 is offline   Reply With Quote
Old 09-14-2013, 08:19 PM   #10
Rivet Master
 
jdalrymple's Avatar
 
2009 27' FB Flying Cloud
1982 31' International
1991 35' Airstream 350
Jay , Oklahoma
Join Date: Oct 2006
Posts: 1,706
The converter should not be "between" the supply and the trailer's breaker box.

It is simply an 120 volt AC appliance that makes 12 volts DC.

It should be connected to a breaker, in fact.



Regards,

JD
__________________
Jeff & Cindy
'09 27FB Flying Cloud;'82 31 International
'91 350 LE MH; '21 Interstate 24GT


jdalrymple is offline   Reply With Quote
Old 09-14-2013, 09:02 PM   #11
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Quote:
Originally Posted by tlsmit1 View Post
The thing is, the pedestal GFCI will trip even if all of the trailer's branch circuits are flipped to "off". So there can't possibly be a path from the output of the inverter/charger through to neutral and/or ground.

But of course the inverter/charger is a load itself. And I don't really understand the innards of the inverter / charger. Because this device sits between the pedestal's GFCI and the breaker box, it is obviously still in the circuit even if all of the trailer's breakers are switched off. So, the question is: can the pedestal GFCI still get tripped by a bonded breaker box with an inverter in the middle, even with all of the branch circuits switched off? Or not?

If not, I would need to look for the fault elsewhere.
I can say that GFCI's are very sensitive devices and seem at times to have a mind of their own. It helps to understand how they work. I will try to be brief here. The GFCI measures the amp level going out on the hot line, and compares it with the amp level coming back through the neutral line. If they are not the same, within 0.005 amps (5 mA) it shuts the circuit down. The assumption is that the "missing" 5 mA is going through a person to ground. Since there have been recorded cases of death at 15 mA, the number they are set at has to be very low.

Now, that 5 mA could be leaking out through the insulation of the power cord to the trailer and going to ground. It also could be leaking 3 mA through a damp spider web inside the park outlet, and then only 2 more mA somewhere else will trip it out. A bad power cord could also leak internally the 5 mA between the hot and ground. There is also a real possibility that the park GFCI itself is defective and is too sensitive.

In addition, if the neutral and the ground line are bonded together somewhere in the system, part of the current going out the hot line on the GFIC will return on the ground line, not the neutral, and the GFIC will trip out. Again, only tiny amounts of leakage will cause this issue.

I have seen a GFIC trip when there was a leakage in the hot water element on an electric water heater. Most of the current came back through the neutral, but a little leaked to ground via the sheath and water in the heater. Pop goes the GFIC.

And so on...

My suggestion: First, does your trailer pop other GFIC's than the one on the 30 amp circuit in the park? If so, sounds like your trailer has the problem. If it trips the GFCI out with all the breakers in the trailer off, I would disconnect the power cord where it comes into the trailer and is still the rubber cord (first change from rubber cord to something else). If plugging it in (tape the ends of the hot and neutral wire) trips the GFIC, you have a defective cord and plug. If not, the problem is farther into the trailer, including bonding of the neutral and ground lines somewhere.

So, my brief answer became longer... the GFIC description was fairly brief....LOL.
idroba is offline   Reply With Quote
Old 09-14-2013, 09:15 PM   #12
Rivet Master
 
68 TWind's Avatar
 
1968 24' Tradewind
Oxford, , Mississippi
Join Date: May 2009
Posts: 1,564
My 68 was tripping the GFCI. After several tries at finding the cause my Airstream buddy TomW suggested checking the condition of my outside 120 outlet. Sure enough, when I removed the cover the inside was wet and the back of the outlet was very corroded. I replaced the outlet and cover and it solved the problem. I should have thought about it because the problem started after a big rain..
__________________
__________________
Bruce & Rachel
__________________
68 Trade Wind
2001 Toyota Tundra
68 TWind is offline   Reply With Quote
Old 09-14-2013, 09:24 PM   #13
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
Quote:
Originally Posted by idroba View Post
My suggestion: First, does your trailer pop other GFIC's than the one on the 30 amp circuit in the park? If so, sounds like your trailer has the problem. If it trips the GFCI out with all the breakers in the trailer off, I would disconnect the power cord where it comes into the trailer and is still the rubber cord (first change from rubber cord to something else). If plugging it in (tape the ends of the hot and neutral wire) trips the GFIC, you have a defective cord and plug. If not, the problem is farther into the trailer, including bonding of the neutral and ground lines somewhere.
Done those. Yes, the problem is in the trailer, because it'll pop a regular 20A residential GFCI if I plug the trailer into it. And the problem isn't the power cord because plugging the cord (alone) into the circuit doesn't pop the GFCI.

(Incidentally, I read the bit about taping the end of the cord. Yoiks, is the trailer-end of your supply cord MALE? Mine is female. Seems a much better idea!)

I'm still not sure, though, if bonding within the circuit panel that is supplied by the inverter--with all the circuits off--would pop the GFCI or not.
tlsmit1 is offline   Reply With Quote
Old 09-14-2013, 09:28 PM   #14
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
Quote:
Originally Posted by jdalrymple View Post
The converter should not be "between" the supply and the trailer's breaker box. It is simply an 120 volt AC appliance that makes 12 volts DC.
JD
Inverter, not converter
tlsmit1 is offline   Reply With Quote
Old 09-14-2013, 10:09 PM   #15
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Quote:
Originally Posted by tlsmit1 View Post
(Incidentally, I read the bit about taping the end of the cord. Yoiks, is the trailer-end of your supply cord MALE? Mine is female. Seems a much better idea!)
My old trailers always had the flex power cord hard wire attached. I only meant to say if you undid the hard wire to test the cord, tape the ends. Of course my new trailer has a female end to the power cord at the trailer side so it is not live and sticking out there...

You are going to have to do more looking for the problem I guess, especially a bond between the neutral and the ground, a problem with the water heater, the heater in the refrigerator, wet outlets or who knows what other possibility, including a defective converter/charger. You may have to disconnect one circuit at a time, hooking it directly to the GFCI to see which one trips the unit.

Electrical problems are not easy to do long distance, best of luck to you.
idroba is offline   Reply With Quote
Old 09-14-2013, 10:20 PM   #16
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
just tossing this out there.....

didn't some of the older trailers have fans that worked off both ac and dc and if still wired that way could it cause the problem?

if it was refurbished, was the breaker/fuse panel redone?

is the wiring 3 conductor?

since the cord is ok and it trips with the breakers off, wouldn't the issue be between the trailer connector and the breaker buss?

is the cord polarity correct?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 09-15-2013, 08:09 AM   #17
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
The original 110 wiring is still in use for the plugs. The circuits to the "heavy" stuff like the fridge are new, and the batteries / inverter / circuitry to the shore power port are new.

I agree that the problem is somewhere between the breaker bus and the shore power port. I'm not sure whether I can further determine that the problem is between the power port and the inverter/charger, because I'm not sure whether a ground fault in the breaker bus can be "seen" through the inverter. But I am guessing by context that it probably can and will look in there.
tlsmit1 is offline   Reply With Quote
Old 09-15-2013, 01:12 PM   #18
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
[QUOTE=tlsmit1;1354471]But in a bonded trailer, the skin and all the other bits are in continuity with the neutral pin of the supply cable. So there *is* somewhere for the current to go: out the neutral.
QUOTE]

If the ground and neutral are bonded inside the trailer, the trailer is wired incorrectly. The only place the ground and neutral should be bonded is inside the primary meter base and/or primary service panel. The ground and neutral should never be bonded at any point beyond, specifically not in any secondary panel. That defeats the safety factor.

Yes, the ground and neutral would be in continuity once the trailer is plugged in, but they should not be bonded at any point inside the trailer. This secondary connection/path to ground is the safety feature (having the least resistance).

If you would post a photo of the panel inside the trailer, it might help.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 09-15-2013, 02:19 PM   #19
3 Rivet Member
 
tlsmit1's Avatar
 
1962 24' Tradewind
Saint Louis , MO
Join Date: Oct 2010
Posts: 106
I'm not sure where it's bonded. I will take a peek as soon as I can get out there, but the panels are mounted sideways in the rear closet, so I have to be a contortionist to get a good look at them.

My inverter/batteries are too small to drive my A/C, so the overall schematic looks like:

(power in)
|
(main panel with A/C breaker and breaker to inverter)
|
(inverter) <-> (batteries)
|
(panel with all the circuits other than the A/C)

But the system will trip with all breakers on both panels thrown open.

So either or both panel could in principle be bonded. I'll check ASAP.
tlsmit1 is offline   Reply With Quote
Old 09-15-2013, 05:46 PM   #20
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
You keep referring to an "inverter". Do you have an "inverter" and a "converter" in the coach?
If you have an "inverter" wired to the power panel and try to plug it in to shore power. That is not correct. The "inverter" output should not be connected to any device that is connected to the shore power.
On the other hand, a "converter" is powered by 120 volts, then converts it to 12 volts DC to charge the battery(s) and power the DC devices when plugged in to shore power.
You can eliminate, at least temporarily the "converter" by simply unplugging it.
TG Twinkie is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:50 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.